RE: Deperming Pier

2008-07-24 Thread Kurt Kingston
I have seen a nice dry standpipe system installation done by a
competitor using HDPE and fusion seal fittings a few years ago on a salt
water pier (Cap Sante Marina, Anacortes, WA.). I cannot remember the
specific brand now, but this link is something similar:
http://corrosion-products.com/PipingProducts/HDPE.htm
IMHO, it looked like using the right tool.
Good success,
Kurt Kingston
[EMAIL PROTECTED]
Commercial Fire Protection Inc.
PO Box 128
Mt Vernon, WA 98273
ph (360)-848-9093 fax (360)-848-1072
 

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of George
Church
Sent: Thursday, July 24, 2008 6:27 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Deperming Pier

I'd be concerned about two things with CPVC-
Effects of sunlight, even under the pier you'd likely get strong
reflections
off the water; and where are you getting 6 CPVC?
I have no idea if regular plumber's PVC would work; if you have a
low-pressure DPV, and you're looking at a 2.5 DPV as your activating
device
(and combo exhauster, it's a pretty big orifice) then wouldn't the air
never
be at high pressure and so it shouldn't be a problem to use PVC?

NFI, just a thought that would save my tax dollars versus SS316.

glc

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Thursday, July 24, 2008 8:49 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Deperming Pier

What if you ran plastic, CPVC is approved for fire protection above
grade
per NFPA 13.  See 6.3 of NFPA 13, 2007.






Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.ch2m.com

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Rick
Green
Sent: Thursday, July 24, 2008 8:19 AM
To: sprinklerforum@firesprinkler.org
Subject: Deperming Pier


I am installing a dry pipe system (no sprinklers) supplying four hose
valves
on a pier.

The dry pipe valve assembly is located in a heated area.  Extending out
from
the dry pipe valve assembly  is 6 galvanized steel pipe.  The steel
pipe is
routed below the pier out to the  location of four hose valves.

The pier is used for Deperming ships, submarines.

Deperming is a procedure for erasing the permanent magnetism from ships
and
submarineshttp://en.wikipedia.org/wiki/Submarines to
camouflagehttp://en.wikipedia.org/wiki/Camouflage them against
magnetic
detection vessels and enemy marine
mineshttp://en.wikipedia.org/wiki/Naval_mines.

Anyway, there is about a 200' section of the pier that requires that all
materials be non-magnetic.

*Galvanized steel pipe that NAVY specified obviously want work.

*CPVC plastic pipe will not work because installing dry system -
correct on this right?

*Provided them pricing for stainless steel, copper, brass and
now
they want pricing for Aluminum,.

So a few questions

o   Ever used aluminum pipe for sprinkler installations?

o   Is there some other pipe type that I am not thinking about

Help would be most appreciated.

Rick E. Green
District Manager
East Coast Fire Protection, Inc.
1113 Cavalier Boulevard
Chesapeake, Virginia 23323
757/485-7486(p), 757/295-0956(direct), 757/328-0131(cell)
[EMAIL PROTECTED]

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: MRI preaction vs cpvc

2008-07-15 Thread Kurt Kingston
Chris,
I believe there are specific prohibitions in some states under their
worker safety laws regarding using PVC (I think CPVC too) for compressed
air systems. You might want to check about that as it could be construed
to include fire sprinkler piping applications.
As a suggestion, maybe explore using dielectric couplings before the
steel fire sprinkler piping enters the MRI space and a bonded ground
system for the piping inside the area? You may find that a ground system
is already being planned for other needs in the MRI space and the
sprinkler piping could use it too.
Good success,
Kurt Kingston
[EMAIL PROTECTED]
Commercial Fire Protection Inc.
Mt Vernon, WA 98273

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Thom
McMahon
Sent: Monday, July 14, 2008 3:02 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: MRI preaction vs cpvc

Have you considered using Pro Press system by VIEGA? You'd need AHJ
approval, but no brazing of the copper required.
Hydro to 200Psi.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Chris
Stovall
Sent: Monday, July 14, 2008 3:12 PM
To: sprinklerforum@firesprinkler.org
Subject: MRI preaction vs cpvc

Greetings,
Were doing an MRI room for Stanford and I wanted to know if anyone knows
where to find info on using cpvc in a preaction system. The 2007
handbook says cpvc can be used with cpvc if low air pressure, timing
requirements and manufacture requirements are met.  Blazemaster, Havel
and Spears all say not to use cpvc in a preaction system. Are the any
other cpvc manufactures? The problem is that to use copper the pipe
needs to be brazed instead of soldered and the extra heat is most likely
going to ruin their lead shielding. The lead shielding is a cloth like
material similar to wall paper. I can have an apprentice stand around
with some kind of heat shield but it would be safer and probably better
if we could use cpvc. Its 2 rooms with 6 heads in each room. 
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

No virus found in this incoming message.
Checked by AVG - http://www.avg.com 
Version: 8.0.138 / Virus Database: 270.4.10/1551 - Release Date:
7/14/2008
6:49 AM



___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Sand or silt clogging strainers

2008-06-25 Thread Kurt Kingston
Nice strainer and a helpful link!
Thom mentioned concerns over the time it would take for your pump to
fail, but has the local FD hooked up to the nearest hydrant and run the
pump in their truck to see what will happen if THEY try to respond to a
fire?
Although it would not be a velocity flush, air scouring might be an
option.
Link to explanatory article:
http://www.environmental-expert.com/files/8563/articles/4055/4055.pdf.
I have seen it used with good improvement on a project some years ago
involving old underground hydronic mains.
Just thinking about it while working on a much simpler problems,
Kurt Kingston
Commercial Fire Protection Inc.

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Thom
McMahon
Sent: Tuesday, June 24, 2008 1:54 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Sand or silt clogging strainers

A self cleaning strainer! That's a new one for me, and listed to boot!
Sounds like this may be the answer.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Tuesday, June 24, 2008 2:45 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Sand or silt clogging strainers

I don't know if it fits the specific situation, but I have used Hellan
strainers for situations involving zebra mussels (sp?). 

Admittedly, I have only glanced over the responses.

Here's the link:

http://www.hellanstrainer.com/

I hope this helps.

James L.(Jim) Roberts, PE/SET
Fluor Corporation
100 Fluor Daniel Drive - C104F
Greenville, SC 29607
864.281.5149
864.281.4916(Fax)


Fletcher, Ron [EMAIL PROTECTED] Sent by:
[EMAIL PROTECTED]
06/24/2008 04:08 PM
Please respond to sprinklerforum

To
sprinklerforum@firesprinkler.org
cc

Subject
RE: Sand or silt clogging strainers



Hi Thom,

Sorry the main is 12 and we opened hydrants to verify fire flow at
about
4,200 gpm. The strainer to the PLD and in the cooling line plugged up
and we
had rocks o-plenty.

Then one day the pump started for an unknown reason, overheated, burst
into
flame and would have burnt down the pump house if it weren't for the
sprinklers. Hey there's sprinkler success story.

What we are hoping to find is some type of self cleaning strainer. We
are
even considering putting a solenoid in a flushing line to discharge
outside
whenever the pump is running. Probably a little bit outside any sort of
recognized code or standard but at this point we are just looking for a
way
to save the pump should there be a major event. The pump serves an
600,000
sqft. warehouse distribution center via the yard loop with hydrants.

Ron Fletcher 

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Thom
McMahon
Sent: Tuesday, June 24, 2008 12:23 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Sand or silt clogging strainers

I'm surprised that there is enough turbidity to raise the sand and mud
in a
16 main at 1500 gpm, That main must just be full of mud when there is
no
flow, since at 1500 your only about 1 FPS. If it's half full of mud,
your
probably moving the water at 3 or 4 FPS over the sediment. 
With a problem like yours the only thing that can eliminate the sediment
is
some type of settling pond, but I'm sure your pump is not sized to
operate
without the incoming water pressure. You never said but I'm assuming
that
before the pump test is over you strainers are full, and plugging up the
works. Large strainers on the pilot lines may resolve the situation long
enough to run the test, but what happens when there is a real fire? How
long
until it fails then?
Good Luck! 

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926


-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Matthew
J.
Willis
Sent: Tuesday, June 24, 2008 12:36 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Sand or silt clogging strainers


- 
- It's a potable city water main that was not properly
- flushed and at this time the city doesn't have the pump
- capacity to achieve any where near 10 fps.
- 
Watch NFPA #20,..., the flushing values are a bit higher when there is a
pump involved..., table 14.1.1.1(a).
R/

Matt

Matthew J. Willis
Living Water Fire Protection, LLC.
1160 McKenzie Rd.
PO Box 877
Cantonment, FL. 32533
850-937-1850 Voice
850-937-1852 Facsimile
[EMAIL PROTECTED]
 
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: NFPA 13 Building with residential heads

2008-04-18 Thread Kurt Kingston
Dewayne,
A short summary of my experience in this situation was the AHJ required
the 3000 square feet if it was a 13 system.
I did use 7psi head pressure to prove a minimum area density of
0.10/3000 vs. the residential head listing pressure required for the
spacing within the 3,000 square feet.
I hope someone else can give you better news.
Kurt Kingston
Commercial Fire Protection Inc.
Mt Vernon, WA 

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Dewayne
Martinez
Sent: Friday, April 18, 2008 4:30 AM
To: sprinklerforum@firesprinkler.org
Subject: NFPA 13 Building with residential heads

NFPA 13 (07ed)
 
I am designing a sprinkler system for a Hotel that falls under NFPA 13.
The floors containing the residential units have a combustible concealed
space
that does not require sprinklers (8.15.1.2.6) but does not qualify for
the 3000 sq ft 
exemption of 11.2.3.1.4 (4)  for unsprinklered combustible concealed
spaces.
If I am using residential sprinklers, are they exempt from this rule
because they are
a specific application sprinkler and not an area/density or room design
method?
Thanks,
Dewayne 
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: CPVC Issues - Plumber's soldering flux

2008-03-04 Thread Kurt Kingston
FWIW we have had several CPVC leaks develop within a couple of years of
flux dripping onto the CPVC. The copper plumbing was installed above our
CPVC piping. The areas became chemically degraded into a softer material
where the spots of flux landed.
With these wild steel/metal price increases it would be nice if it was a
better alternative.
Kurt Kingston
[EMAIL PROTECTED]
Commercial Fire Protection Inc.
Mt Vernon, WA 98273

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Kohl's

2008-02-28 Thread Kurt Kingston
Joe,
FWIW I haven't done a Kohl's but my ESFR-25 notes say you will need a
minimum 36clearance to commodities.
It sounds like you have 2'.
Kurt Kingston
Commercial Fire Protection Inc.

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Joe
Burtell
Sent: Thursday, February 28, 2008 1:43 PM
To: sprinklerforum@firesprinkler.org
Subject: Kohl's

Has anyone done a Kohl's store lately? In particular I am interested
what
was done in the storage room. I asked some questions about the storage
and I
get the usual, we've never done that before response. Here is what they
have:
17' to deck
15' of storage, 2' wide solid shelf racks, they are really shelf storage
but
it over the 30 limit due to back to back configuration Class I-V and
Group
A plastics Cartoned, unexpanded

I let them know that due to the solid shelf they will need 1 level of
in-rack sprinklers. They gave a .45/2000 which works fine without solid
shelves. Any opinions?



Joe Burtell, SET, CFPS
Burtell Fire Protection, Inc.
[EMAIL PROTECTED]
www.burtellfire.com


___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: ICC Version of 13d

2008-02-25 Thread Kurt Kingston
Michael,
I am admittedly a suspicious curmudgeon where NAHB is involved, but
aren't those trade-offs, exceptions and exemptions in the footnotes on
page RP29 and RP30 far more generous than IBC?
Thanks for posting the link as I had not seen it yet and found it very
interesting.
Kurt Kingston
[EMAIL PROTECTED]
Commercial Fire Protection Inc.
Mt Vernon, WA 98273

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Michael
O'Brian
Sent: Friday, February 22, 2008 6:19 PM
To: SprinklerFORUM
Subject: ICC Version of 13d

Okay Sprinkler Guys

 

Today at the ICC code hearings the Plumbing Committee heard RP3 and RP8.

 

See the code change here (scroll one or two changes down to RP3)

 

http://www.iccsafe.org/cs/codes/2007-08cycle/ProposedChanges/V2_RP1-8.pd
f

 

This is a code change which would give installation requirements for
multi-purpose piping for sprinkler systems in the body of the
residential
code (a modified pipe schedule like system).  RP3 passed and RP8 was
denied.
Now this was the committee action and it may be debated on the final
action
hearings in September.  

 

The code change only applies to multipurpose piping in one and two
family
dwellings.  It has many layers of built in safety.  A designer would
still
be allowed to utilize a 13d system and this really provides an option
for
the user.

 

I am just curious what you all think?  I know as sprinkler designers we
may
feel like we should not like this, but the intent is to make sprinkler
installation in homes as convenient as possible.

 

(ps there was a floor amendment which clarified hangers and some other
issues)

 

Michael O'Brian

Code Savvy Consultants

313-618-6401

fax 313-557-0294

www.codesavvyconsultants.com

www.inspector911.com

 
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Parking Garage Sprinkler System

2008-01-31 Thread Kurt Kingston
Reza,
A few random comments:
2- When we have the pressure and flows available the Tyco EC uprights
(like EC-11) have worked out well on a few recent jobs but you really
start accumulating over discharge on the branch lines quickly with the
higher end head pressures. That issue also tends to fight dry system
design goals by creating bigger pipe size, more system volume, etc., so
IMHO for some layouts a good argument can be made for standard coverage
heads instead of EC's.
4- It is not necessary to sprinkler above each car.
5- Fully sprinklered would include the ramps too if covered.
9-  A couple of FWIW notes that come to mind on a single dry riser for
the building you describe = concerns over dry system trip time, total
dry system volume and air compressor size.
Good success,
Kurt Kingston
Commercial Fire Protection Inc.
Mt. Vernon, WA.

 
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Reza
Esmaeili
Sent: Thursday, January 31, 2008 8:17 AM
To: sprinklerforum@firesprinkler.org
Subject: Parking Garage Sprinkler System

Hi All,
  I would like to ask about sprinkler system design in a car parking
garage. The parking garage has two stories (Basement  Ground floor). It
is only for car parking application which can hold about 350 cars.
  There is No mechanical devices to transport cars, and cars will drive
to their own parking palaces.
  The area of each story is about 44,000 square feet, and ceiling high
is about 10 feet.
  We are going to design a dry pipe sprinkler system for this car
parking garage as piping are subjected to freezing during the cold
weather.
   
  I looked up in NFPA codes for designing car parking garage, but I
couldn't find that much helpfull information in NFPA-88A.
   
  In NFPA-13 I saw that automobile parking and showrooms are specified
as 
  Ordinary hazard occupancies (Group 1).
   
  I am going to design a tree dry pipe sprinkler system  some inside
fire hoses in the garage.
   
  My questions are as followings:
   
  1- What is your recommended Area of sprinkler operation and Density
for my application after determining from the Density/Area curve?
   
  2- I am going to use upright sprinklers, what kind of sprinkler is
more common for such an application? standards coverage/extended
coverage...?
   
  3- What is the common distance between sprinklers and maximum area of
coverage per sprinkler for a parking garage?
   
  4- Is it necessary place a sprinkler exactly at above each car or not?
   
  5- Is it necessary to place sprinklers in corridors  ramps where no
cars are parked and only cars are moving?
   
  6- What is the NFPA recommended duration for sprinkler system  inside
hose stream?
   
  7- Can I connect the inside hose to the dry sprinkler system piping?
or shoud I connect the inside hose piping directly to the fire pumps?
   
  8- I will place some insde fire hoses in the garage that provides 1
1/2 in. hose stations and according to NFPA-14 the minimum residual
pressure at the outlet of most remote 1 1/2 in. hose stations should be
65 psi for hydraulically designed systems, so I think my fire pump head
should be at least 80 psi? What do you think about this fire pump head,
do you think it is low, high or good?
   
  9- I want to protect both strories with a single riser using a 4 dry
pipe system to feed my sprinkler system  fire hoses, what do you think
about it?
   
  Thanks for your kind help in advance,
  Reza
   

   
-
Looking for last minute shopping deals?  Find them fast with Yahoo!
Search.
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Seismic Bracing and 2002 NFPA 13 Appendix

2008-01-18 Thread Kurt Kingston
In my situation I have an AHJ that is saying that a gridded system
doesn't use branch lines but rather all piping components in a grid
system are either feed or cross mains and so even 2 and smaller piping
needs to be braced.
I sent him a copy of the Appendix brace location examples for gridded
systems in December and was hoping he would go away, but I may end up
doing as Roland suggested and send in for a formal interpretation.
Thank you all for your comments,
Kurt Kingston
Commercial Fire Protection Inc.
ph (360)-848-9093 fax (360)-848-1072
 
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Jeff
Hewitt
Sent: Friday, January 18, 2008 11:45 AM
To: sprinklerforum@firesprinkler.org
Subject: Re: Seismic Bracing and 2002 NFPA 13 Appendix

Tom,

I feel that this should be clarified further.

My understanding, at least as affected by the ICC Codes, is as follows:

The 2003 edition of IBC removes the reference to the use of NFPA 13 from

ASCE 7 2002 edition. (The version of NFPA 13 referenced is NFPA 13,
1999, 
NOT NFPA 13 2002).  NFPA 13, 2002 TIA 02-1 was the fix for this snub,
but 
IBC never actually issued a formal interpretation or Supplement
judgement 
stating that.

The 2006 edition of IBC does not have the same verbage removing NFPA 13
that 
IBC 2003 did, and also uses the NFPA 13, 2002 edition as the reference 
document, NOT NFPA 13, 1999, but does add other stipulations for its
use.

The 2007 Supplement to the 2006 IBC removes all remaining hurdles by
simply 
adding a new section to the IBC 2006 Earthquake provisions, allowing the
use 
of NFPA 13 , with no other stipulations.  Please note that the NFPA 13
2002 
version is STILL the reference document to IBC 2006, NOT NFPA 13, 2007.

There is currently no version of IBC that references NFPA 13 2007.


Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (FAX)

This e-mail and any attachments are CONFIDENTIAL and may be protected by
one 
or more legal privileges.  It is intended solely for the use of the 
addressee identified above.  If you are not the intended recipient, any
use, 
disclosure, copying or distribution of this e-mail is unauthorized.  If
you 
received this e-mail in error, please notify the sender immediately at
the 
above captioned address.
- Original Message - 
From: Thom McMahon [EMAIL PROTECTED]
To: sprinklerforum@firesprinkler.org
Sent: Friday, January 18, 2008 12:43 PM
Subject: Re: Seismic Bracing and 2002 NFPA 13 Appendix


 Remember that if your spec. requires you to meet ASCE 7 requirements
that 
 NFPA 13, 2002 was found not to meet these, however 2007 was accepted
as 
 substantially meeting these requirements. Also there was a TIA to 2002
to 
 move toward meeting ASCE 7, but 2007 is much better.
 Most AHJ's will accept the new Standard if presented as an alternate.

 Thom McMahon
 Firetech, Inc.
 2560 Copper Ridge Dr
 Steamboat Springs, CO 80488-2136
 Tel: 970-879-7952
 Fax: 970-879-7926
 - Original Message - 
 From: Kurt Kingston [EMAIL PROTECTED]
 To: sprinklerforum@firesprinkler.org
 Sent: Friday, January 18, 2008 10:10 AM
 Subject: RE: Seismic Bracing and 2002 NFPA 13 Appendix


 I'm re-posting this and any opinions or comments as to whether the
 seismic bracing locations shown figures in the 2002 NFPA 13 Appendix
are
 OK to use would be appreciated.
 Kurt Kingston
 Commercial Fire Protection Inc.

 -Original Message-
 From: [EMAIL PROTECTED]
 [mailto:[EMAIL PROTECTED] On Behalf Of Kurt
 Kingston
 Sent: Monday, December 17, 2007 8:57 AM
 To: sprinklerforum@firesprinkler.org
 Subject: Seismic Bracing and 2002 NFPA 13 Appendix

 I would like to obtain your opinions as to whether the locations for
the
 seismic bracing in the 2002 NFPA 13 Appendix figures
 A.9.3.5.6(a),(b),(c), and (d) are OK to use as shown if 2 and smaller
 branch lines, and the structure is adequate to support the brace
 spacing.
 Thank you for your time,
 Kurt Kingston
 [EMAIL PROTECTED]
 Commercial Fire Protection Inc.
 Mt Vernon, WA 98273
 
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Seismic Bracing and 2002 NFPA 13 Appendix

2008-01-18 Thread Kurt Kingston
I'm re-posting this and any opinions or comments as to whether the
seismic bracing locations shown figures in the 2002 NFPA 13 Appendix are
OK to use would be appreciated.
Kurt Kingston
Commercial Fire Protection Inc.

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Kurt
Kingston
Sent: Monday, December 17, 2007 8:57 AM
To: sprinklerforum@firesprinkler.org
Subject: Seismic Bracing and 2002 NFPA 13 Appendix

I would like to obtain your opinions as to whether the locations for the
seismic bracing in the 2002 NFPA 13 Appendix figures
A.9.3.5.6(a),(b),(c), and (d) are OK to use as shown if 2 and smaller
branch lines, and the structure is adequate to support the brace
spacing.
Thank you for your time,
Kurt Kingston
[EMAIL PROTECTED]
Commercial Fire Protection Inc.
Mt Vernon, WA 98273
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Non-Hangar Hangar

2008-01-09 Thread Kurt Kingston
Greg,
Also:
-  An item to note I've seen applied by a building department from NFPA
409 whether you are using NFPA 13 or not is when a new hangar can become
a hangar complex with existing structures, changing the classifications
as well as add perimeter protection - references such as 409,2-2, 
2-3.3 might help explain.
- Some of the new hangar doors fold in half length wise and then swing
out and up like this link shows:
http://www.hydroswing.com/
Good success,
Kurt Kingston
Commercial Fire Protection Inc.
Mt Vernon, WA 98273
 



-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Greg
McGahan
Sent: Wednesday, January 09, 2008 4:02 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Non-Hangar Hangar

As I have relayed to this forum before, qualified FP engineers, and/or
PE's
with significant experience above Ordinary Hazard are non-existent down
here. Because of this we are often backed into this corner where we MUST
supply a price which would include the engineer's fee for the entire
job;
get the job and then get the engineer involved. No price - no job. The
engineer we want to use is unavailable so I asked the question on the
forum.

Thanks for the replies.
Greg McGahan

Living Water Fire Protection, LLC
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
Fax: 850-937-1852

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Steve
Leyton
Sent: Tuesday, January 08, 2008 6:07 PM
To: AFSA Forum
Subject: Re: Non-Hangar Hangar

Not that simple (unfortunately) sometimes.  Did one last year that was
called a Maintenance Hangar on a design-build basis for the USMC (Navy
rules).  They didn't even have design criteria so we negotiated an
ad-lib
taken from the ceiling protection criteria in 409. I think we provided
.17/5,000 sq. ft.  But our building was WAY smaller and especially it
was
shorter too.  Depending on door height, yours could meet the dimensional
criteria for a Type 1 or Type 2 hangar, so I do agree with Todd that you
should tread lightly. 

Steve Leyton

Away from the office - sent from my BlackBerry

-Original Message-
From: Todd Williams - FPDC [EMAIL PROTECTED]

Date: Tue, 08 Jan 2008 18:21:57 
To:sprinklerforum@firesprinkler.org
Subject: Re: Non-Hangar Hangar


Greg,

If the design documents call it a hanger, I would consider it as a 
hanger and figure the systems accordingly. You may run into a 
liability issue if you don't. Or at least end up with an underbid 
job. I would assume that all of the fuel has been removed from the 
tanks and they have been purged before the planes end up in the 
space. Hopefully the Engineer (when he or she becomes available) will 
be able to clarify the spec and doesn't ask you to do his job


At 05:20 PM 1/8/2008, you wrote:
We have a hangar for the storage of retired - stripped aircraft that is
specified in the design documents to be referred to as a hangar, but it
is
not a hangar by definition or military definitions. This is on a
military
base but is a non military building. The aircraft will be stripped of
almost
everything but the seats and maybe wiring.

YES, I want the engineer to do his job, but he is unavailable and the
GC
needs a budget immediately. In addition, the engineer will probably be
looking for input as well:

87' tall at the peak, 45' at the eaves with flexible membrane (no info
available at this time) covering.

Question: Would this be more suited for Ordinary Hazard or should this
fall
into the real Hangar protection in 409?

Thanks for any quick input,
Greg

Living Water Fire Protection, LLC
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
Fax: 850-937-1852


___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Riser or Riser Nipple Revisited

2008-01-08 Thread Kurt Kingston
I don't have a copy here at the moment, but is there anything in the IBC
Section 1621 design requirement references for components and ASCE 9.6
that provide exemptions of items that weigh less than x pounds that
might help? If so, maybe it could be applied to a 6 oz. riser nipple and
that might satiate the literal mind?
Kurt Kingston
Commercial Fire Protection Inc.
Mt Vernon, WA 


-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Roland
Huggins
Sent: Tuesday, January 08, 2008 10:22 AM
To: sprinklerforum@firesprinkler.org
Subject: Re: Riser or Riser Nipple Revisited

Hopefully the fact that smaller branch lines are not required to have  
sway braces would influence the decision making on the 4-way brace.

Roland

On Jan 8, 2008, at 9:42 AM, Jason Norton wrote:

 I think Roland it the nail on the head with excessively literal  
 mind.
 There is no way NFPA can come up with a code that tells you exactly  
 what
 to do in every situation.

 DSA is quickly becoming the new OSHPD. Just double your bid next time
 and you can afford to do what the excessively literal mind wants. Of
 course that is not the best solution, education is.

 Jason

 -Original Message-
 From: [EMAIL PROTECTED]
 [mailto:[EMAIL PROTECTED] On Behalf Of Ed Cyr
 Sent: Tuesday, January 08, 2008 8:58 AM
 To: sprinklerforum@firesprinkler.org
 Subject: RE: Riser or Riser Nipple Revisited

 Thanks for the feed back.

 I'd like to pursue this thread further.

 When running a branch line with offsets for duct work or any other
 obstruction, do you 4 way brace both sides of the vertical offset or
 just the riser side in the direction of water flow?

 Is there a point to when to much bracing can be detrimental?

 Wouldn't line restraint in lieu of seismic bracing prove to be  
 adequate
 for all portion of the branch line including the riser nipple? Also
 finding adequate structure to brace to can also become a problem.

 Utilizing a 4 way brace on a 1 1/4 x 06 RN seems like over kill.

 Do you subtract lateral load factors from main braces for the added
 bracing of the branch line?

 Thanks,
 Ed Cyr




 -Original Message-
 From: [EMAIL PROTECTED]
 [mailto:[EMAIL PROTECTED] On Behalf Of Jason
 Norton
 Sent: Monday, January 07, 2008 3:33 PM
 To: sprinklerforum@firesprinkler.org
 Subject: RE: Riser or Riser Nipple?

 DSA has also been trying to require all drops over 4 ft. to be
 restrained. Seems they think a drop is no different than a sprig. Go
 figure.
 Jason

 -Original Message-
 From: [EMAIL PROTECTED]
 [mailto:[EMAIL PROTECTED] On Behalf Of Roland
 Huggins
 Sent: Monday, January 07, 2008 3:07 PM
 To: sprinklerforum@firesprinkler.org
 Subject: Re: Riser or Riser Nipple?

 Sprigs are a separate category independent from risers.  That alone
 would not convince many folks  that have an excessively literal mind.
 Fortunately, we can then ask, if a 4-way brace is required why  
 would 13
 state:  Sprigs greater than 4 ft shall be restrained?

 This issue come to our attention when looking at riser nipples.
 That's why we now have the 3 ft allowance.  Beyond that, if it's  
 feeding
 more than one sprinkler, I think you have to treat it like any other
 riser.

 Roland

 On Jan 7, 2008, at 2:36 PM, Ed Cyr wrote:

 Forum,



 In the past I posted a thread about an AHJ requiring that riser
 nipples regardless of length be 4- way braced at the top. NFPA 13
 defines a riser as any vertical pipe.

 Recently, the Dept of State Architects (DSA) in California has  
 brought

 this issue up again.



 Riser nipples of any length with or without flexible couplings are on
 their radar.



 Question:

 1.   Is a riser nipple a riser requiring a 4 way brace, or a branch
 line
 component requiring restraint only?
 2.   Does every change of elevation (vertically) on a branch line
 also
 require a 4 way brace?



 Comments anyone?



 Thanks,

 Ed Cyr



 Alpha Fire Sprinkler Corp.

 San Luis Obispo, CA


___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: construction type - extra heads

2007-12-26 Thread Kurt Kingston
Todd,
I'm not sure I've got the big picture on this one, but it sounds like
the only exposed combustibles is the exposed deck at the top of the
beams?
Maybe the HVAC guys/equal could take up rolls of sheet metal sheared
2'9 through the ceiling access, screw it onto the underside of the
deck. Then does it become a '02 8.14.2.1 limited combustible space not
requiring sprinklers?
If you still need sprinklers, maybe they could do two layers of metal
and the lower level would make your 22?
Kurt Kingston
Commercial Fire Protection Inc.


-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Roland
Huggins
Sent: Wednesday, December 26, 2007 9:00 AM
To: sprinklerforum@firesprinkler.org
Subject: Re: construction type - extra heads

bulls-eye

I guess one could simply use those bowed wire every couple of feet  
(like one uses for insulation under the flooring in a house) but I  
wouldn't be comfortable with that. What are you guys typically using  
to reliable hold the insulation up?

Roland

On Dec 26, 2007, at 8:06 AM, Dewayne Martinez wrote:

 Todd,
 I think we talked somewhat about this in prior postings that the 22
 deflector distance couldn't be modified so one of the ideas was to  
 have
 non-combustible insulation installed at the deck to make the deflector
 to now within the 22 limit.  Now keeping the insulation up in the
 pockets bring about another problem.
 Dewayne

 -Original Message-
 From: [EMAIL PROTECTED]
 [mailto:[EMAIL PROTECTED] On Behalf Of Todd
 Williams - FPDC
 Sent: Wednesday, December 26, 2007 9:56 AM
 To: sprinklerforum@firesprinkler.org
 Subject: Re: construction type - extra heads

 I have 30 deep beams spaced at 2'-9 o.c. If I space sprinklers in
 every pocket, I have 18 sprinklers protecting a 625 sqft unoccupied
 room. I was trying to look for a way out of it, since it does seem
 excessive and will have a monstrous effect on the calcs. The space is
 only accessible by a 2' x 2' hatch with a ladder, so bringing up
 sheetrock to cover the ceiling is not practical. Looking for  
 thoughts or
 ideas.


 At 10:37 AM 12/26/2007, you wrote:
 did you start with the definitions?  How can you call it anything but
 obstructed?  I ASSUME the TC put the 3 to 7-1/2 ft since beam and
 girders assemblies are TYPICALLY  spaced at a minimum but structural
 loads are not always typical so neither are the beam placements.
 Don't let the general description in the ANNEX get in the way of
 defining ceiling type since it does NOT conflict with the base
 definition.   Considering wood joists have the same impact on heat
 flow and discharge, where's the beef?

 The only time the minimum spacing will cause a REAL problem is
 exceeding the 22 inch below the ceiling with concrete tees that are
 less than 3 ft apart.  Twin tees are pretty common.

 Roland

 On Dec 24, 2007, at 5:38 AM, Todd Williams - FPDC wrote:

 I am working on room that is approximately 25 x 25. The roof deck is
 two layers of 3 thick tongue-and-grooved plank. Supporting this  
 is a
 series of 30 deep steel beams spaced 2'-9 O.C. This room is
 presently unoccupied and will remain that way. (The space above was
 contained a water tank. This is in a tower of an old mill). In my
 pre-Christmas reading of the construction types, this seems to be an
 anomaly. How do you address construction where the beam spacing is
 less than 3 feet? Obstructed Construction only includes beams spaced
 between 3 and 7.5 feet.

 If you go to Chapter 8, assume obstructed construction and look  
 at the

 deflector distances, I would have to include a sprinkler in each bay
 (since my beam depth exceeds 22). I know I shouldn't be applying
 logic to sprinklers, but 18 sprinklers to protect a 25 x
 25 unoccupied room does seem to be overkill. Any thoughts? I think
 they are way over budget on this project, so the idea of adding a
 ceiling will be met with resistance. Any thoughts?

 Merry Christmas to all

 Todd G. Williams, PE
 Fire Protection Design/Consulting
 Stonington, Connecticut
 www.fpdc.com
 860.535.2080  ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


Seismic Bracing and 2002 NFPA 13 Appendix

2007-12-17 Thread Kurt Kingston
I would like to obtain your opinions as to whether the locations for the
seismic bracing in the 2002 NFPA 13 Appendix figures
A.9.3.5.6(a),(b),(c), and (d) are OK to use as shown if 2 and smaller
branch lines, and the structure is adequate to support the brace
spacing.
I am encountering differing opinions as to whether additional bracing is
required on branch lines and which ones those would be.
Thank you for your time,
Kurt Kingston
[EMAIL PROTECTED]
Commercial Fire Protection Inc.
Mt Vernon, WA 98273
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: boat storage

2007-08-10 Thread Kurt Kingston
Same in this NW Washington State area; boats loaded with fuel and full
gear. The storage operators even advertise how quickly they can have
your boat in the water after you call them.
The boat rack issues seem very similar to Pod Storage Facility concerns,
but with Roland H's additional comment of water filled boat weights and
structural support.
I'm not very fond of adding more technology to our sprinkler systems,
but it seems that the only hope of dealing with boat racks or pod
storage is to use rack deluge zones capable of multiple types of sensing
in addition to the overhead system.
But now we have no testing, applicable standards, or guidelines for
either.
Kurt Kingston
Commercial Fire Protection Inc.

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Cliff
Whitfield
Sent: Friday, August 10, 2007 9:29 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: boat storage

Craig,

The boats that are stored in these facilities around this part of the
country do not have the fuel tanks purged or the batteries disconnected.
They are usually 18' to 25' pleasure/ski/fishing boats that can be
removed
from the rack, dropped in the water and ready to go in a few minutes.

Like someone has already mentioned, this is the kind of job to walk away
from until there is definite guidance given by an NFPA standard.

Cliff Whitfield
Fire Design, Inc.

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Friday, August 10, 2007 10:29 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: boat storage

In doing some reading on the topic is appears from a risk standpoint
that the boats stored in the rack configuration had a lower risk of
being involved in a fire than those which are moored in the water under
the dock roof.  Reason being that those stored on the racks were drained
of fuel and had batteries disconnected and had no access from the owners
or others during storage.  The boats that were stored in the water were
often larger and while docked were involved in more on-board repair work
as well as having on-board heaters running (while unoccupied) during
cold weather to prevent plumbing pipes from freezing.  It appears that
heaters were a common source of on-board fires.  Ignition of flammable
vapors ranked up there as well.

But agreed, the rack storage arrangement is a very complex situation
with little to no guidance from the Code realm.  

In one recent project this situation came up and NFPA 312 Standard for
Fire Protection of Vessels During Construction, Conversion, Repair and
Lay-up was applied along with NFPA 306 Standard for the Control of Gas
Hazards on Vessels.   Note: that this was not a pleasure craft facility.
But there was no way NFPA 13 could be applied to this facility.  NFPA
312 has very strict procedural guidelines and also ties into some CFR
Regs.   Those tightly restrictive procedures allow for a more simplistic
approach to fire protection.  


Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com


-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Greg
McGahan
Sent: Friday, August 10, 2007 11:02 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: boat storage

True that.

Some of the steel people are beginning to figure the weight of the water
in the rack design.

This issue MUST be addressed and put to rest by the IBC, NFPA, FM or
someone soon, or I think disaster is in the wings. 

I have no replies with successful saves IN a boat storage facility from
this forum.

Greg

Living Water Fire Protection, LLC
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
Fax: 850-937-1852


-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Roland
Huggins
Sent: Friday, August 10, 2007 9:56 AM
To: sprinklerforum@firesprinkler.org
Subject: Re: boat storage

The issue is not boats in a berth sitting in the water.  That one is  
simple since it is just a building covering a low level of storage.   
He is asking about boats stored on racks several levels high.  It's a
nasty item.  No contractor in their right mind should attempt to DESIGN
it.  Even with the engineers copying designs from contractors in the
Florida panhandle, LEAVE IT TO THE ENGINEER.  Now I can say no engineer
in their right mind would touch it unless the client was willing to make
some very limiting modifications to the layout of the racks.

Many of the facilities have adjustable racks to accommodate boats of
different heights.  I've heard of people putting side wall heads in the
columns to cover the area beneath the boats.  You think maybe they were
ignoring that you need the heads to activate in order for the water
throw to count as covering the area?  Group A plastics on racks with
LOTS

RE: Backflow: Sprinkler System

2007-07-16 Thread Kurt Kingston
Don't causing any more backflow trouble by asking those kind of
questions!
http://www.campbellmfg.com/catalog/j01.htm
Next the water district girls will be out there with their little hard
hats and confined space equipment inspecting RP's in the vaults we are
going to be required to put in front of every hydrant...vaults with sump
pumps in case they flood. Oh and the pump discharge through an oil/water
separator:
Kurt Kingston
Commercial Fire Protection Inc.


-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Thom
McMahon
Sent: Monday, July 16, 2007 10:20 AM
To: sprinklerforum@firesprinkler.org
Subject: Re: Backflow: Sprinkler System

Technically Yes this is a potential cross connection, and should be 
protected. But who owned these fire hydrants? Usually the water
authority. 
And who is responsible for a cross connection control policy? Right, the

water authority. So obviously their policy is to ignore this situation,
at 
least until all the other possible cross connections have been
addressed. Or 
until someone invents a cost effective way to protect this that isn't a 
maint. nightmare. Buried 7 ft underground.

All you would be inventors out there, here's your chance at fame and 
fortune.
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
- Original Message - 
From: Matsuda, Richard [EMAIL PROTECTED]
To: sprinklerforum@firesprinkler.org
Sent: Monday, July 16, 2007 10:00 AM
Subject: RE: Backflow: Sprinkler System


I like this Forum...so many varied perspectives from so many different
parts of the country and so many different occupations.

Here in Dallas we use dry barrel fire hydrants so they don't freeze
during the winter. All of them have a small weep hole
below grade to allow the water in barrel to drain after use...I guess
it's something like the ball drip on the fire dept connection. The fire
hydrant is usually located near the street, and the ground there is
subject to all kinds of pollutants, like grease, oil, and even an
occasional dog.

So here are my questions:
1.  Is this arrangement a cross-connection?
2.  If so, then is backflow prevention required?
3.  If not, then why not?

I'm not expressing any opinion...just asking some questions.
The earlier responses on this subject were slowing down so I thought
stir the pot again.

rick matsuda, city of dallas, bldg insp dept.
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: What does not fully functional mean?

2007-07-02 Thread Kurt Kingston
We often have difficulty getting the underground velocity flush
certificate on projects and that results in completed systems remaining
off.
Kurt Kingston
Commercial Fire Protection Inc.


-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Karen
Purvis
Sent: Monday, July 02, 2007 5:48 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: What does not fully functional mean?

My guess is that someone had not turned the water on. If it was tested
and
passed the inspection than the only thing missing would be water. Maybe
they
felt that the water should not be turned on until the building was
occupied.

Karen Purvis
Designer
Facility Systems Consultants
714 S Gay St
Knoxville, TN 37902
ph.865-246-0164
fax 865-246-1084
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Thomas
Reinhardt
Sent: Monday, July 02, 2007 8:38 AM
To: sprinklerforum@firesprinkler.org
Subject: What does not fully functional mean?

 Detail.url  
The message is ready to be sent with the following file or link
attachments:

Shortcut to:
http://www.myfoxtampabay.com/myfox/pages/News/Detail?contentId=3634335v
ersi
on=17locale=EN-USlayoutCode=TSTYpageId=3.2.1


Note: To protect against computer viruses, e-mail programs may prevent
sending or receiving certain types of file attachments.  Check your
e-mail
security settings to determine how attachments are handled.

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: ceiling change

2007-05-25 Thread Kurt Kingston
Todd,
I'm working on a similar sounding situation in an IHOP Restaurant
currently in review by the AHJ with 14/12 pitch and a flat area about 3'
wide at the peak.
As Scott posted the heads probably would activate better on the flat,
but...it seems in a situation of a steeply pitched ceiling and a narrow
flat area that the slope interferes with the spray pattern of a head
installed on the flat.
I chose on the slope and within 1'.
Kurt Kingston
Commercial Fire Protection Inc.


-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd
Williams - work
Sent: Wednesday, May 23, 2007 2:53 AM
To: sprinklerforum@firesprinkler.org
Subject: ceiling change

I am working on a project in a church sanctuary that has (until now) 
a sloped ceiling that goes to a peak in the middle. There are 4 
branch lines running the length of the sanctuary, parallel to the 
ridge line. The architect now wants to flatten a section of the 
ceiling in the center. Of course the two center lines, which are 
already piped, are located right above the change from slope to flat. 
We now have to locate the sprinklers either on the slope or on the 
flat, but within a foot or two of the joint. What would be the 
preferred location?

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
860-535-2080
www.fpdc.com 

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Galvanized sprinkler pipe at 130F

2007-05-19 Thread Kurt Kingston
Dee,
Sorry that I can only throw out a guess; I am reading it as required for
130F and lower, and not required above 130F. My guess is that above 130F
there would be reduced corrosion anyway so the galvanized would be
optional.
Several mill projects that I recall used galvanized pipe everywhere
including the kilns and with galv (or SS) attachments and hangers.
Kurt Kingston
Commercial Fire Protection Inc.

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Dee
Lockwood
Sent: Friday, May 18, 2007 3:16 PM
To: sprinklerforum@firesprinkler.org
Subject: Galvanized sprinkler pipe at 130F

Has anyone experience with accelerated corrosion of hot dipped sprinkler
pipe used in a dry pipe system?

My application is galvanized pipe on a dry pipe system protecting an
attic
that will see temperatures of 130F for a few hours a day and a month or
so
each year.

FM Global Data Sheet 2-8N, 3-2, requires galvanized pipe in dry pipe
system
except where ambient temperatures exceed 130F. Section 2-3.1
references a
lumber dry kiln. Obviously the operating conditions vary greatly between
an
attic and a dry kiln. The chemistry in a dry kiln is probably very
complex.

I contacted the American Galvanizing Association. They are unaware of
any
accelerated corrosion at 130F and feel galvanizing is stable to 350F.

Thanks

Dee Lockwood P.E. 

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Flammable liquid storage cabinets in retail stores

2007-04-13 Thread Kurt Kingston
Michael,
One solution we used to keep everybody happy (happier) was to use some
commercial Velcro in strips on the cabinet face and also on the backs of
empty product containers. The products are displayed on the exterior
that way.
I think I was watching a news story of a human dart contest in NZ with
guys throwing their Velcro jumpsuit equipped mates onto the walls in a
bar, so you must have ready access to the Velcro product down there?
Kurt Kingston
Commercial Fire Protection Inc.
 

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Michael
James
Sent: Thursday, April 12, 2007 7:37 PM
To: [EMAIL PROTECTED]
Subject: Flammable liquid storage cabinets in retail stores

Hello,

We have a retail store that sells a limited amount of class 1B flammable
liquids in 4 litre plastic containers for paint thinning and brush
cleaning
and the sprinkler protection schemes seem very expensive compared to
what is
required for the rest of the store. The quantity stored is around 500
litres
hence our AHJ has suggested that flammable liquid storage cabinets would
be
an acceptable alternative.

Does anyone know of a manufacturer of flammable liquid storage cabinets
complying with NFPA 30 that would be suitable for a retail store i.e not
a
bright red or yellow steel box but possibly something with fire rated
glass
fronted doors or a roller shutter closing on a fusible link. While I
don't
mind the look of a bright red box the merchandising department has other
ideas.



Thanks,

Michael James
Fire Safety Engineer
Pacific Consultants
Auckland
NZ

___
Sprinklerforum mailing list
[EMAIL PROTECTED]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
[EMAIL PROTECTED]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Outside Restaurant Seating

2006-12-11 Thread Kurt Kingston
Greg,
We were recently looking at a very similar situation and did not see
anything definitive either but decided to go ahead and protect it since
the regular use of tables, chairs, equipment, might be construed as
combustible storage per 2002 8.14.7.4.
Kurt Kingston
Commercial Fire Protection Inc.



-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Greg
McGahan
Sent: Monday, December 11, 2006 9:17 AM
To: sprinklerforum@firesprinkler.org
Subject: Outside Restaurant Seating

We are looking at a large (1,300 sqft) noncombustible balcony that is
going
to be used as restaurant seating as part of a Country Club.

Previously we bid this as protected because the balconies had exposed
combustible ceilings. Since they have revised this to stucco
noncombustible
finishes I am not sure how to look at it.

Thanks for your help,
Greg McGahan


___