Dee,
Sorry that I can only throw out a guess; I am reading it as required for
130F and lower, and not required above 130F. My guess is that above 130F
there would be reduced corrosion anyway so the galvanized would be
optional.
Several mill projects that I recall used galvanized pipe everywhere
including the kilns and with galv (or SS) attachments and hangers.
Kurt Kingston
Commercial Fire Protection Inc.

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Dee
Lockwood
Sent: Friday, May 18, 2007 3:16 PM
To: [email protected]
Subject: Galvanized sprinkler pipe at 130F

Has anyone experience with accelerated corrosion of hot dipped sprinkler
pipe used in a dry pipe system?

My application is galvanized pipe on a dry pipe system protecting an
attic
that will see temperatures of 130F for a few hours a day and a month or
so
each year.

FM Global Data Sheet 2-8N, 3-2, requires galvanized pipe in dry pipe
system
"except where ambient temperatures exceed 130F." Section 2-3.1
references a
lumber dry kiln. Obviously the operating conditions vary greatly between
an
attic and a dry kiln. The chemistry in a dry kiln is probably very
complex.

I contacted the American Galvanizing Association. They are unaware of
any
accelerated corrosion at 130F and feel galvanizing is stable to 350F.

Thanks

Dee Lockwood P.E. 