Michael,
I am admittedly a suspicious curmudgeon where NAHB is involved, but
aren't those trade-offs, exceptions and exemptions in the footnotes on
page RP29 and RP30 far more generous than IBC?
Thanks for posting the link as I had not seen it yet and found it very
interesting.
Kurt Kingston
[EMAIL PROTECTED]
Commercial Fire Protection Inc.
Mt Vernon, WA 98273

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Michael
O'Brian
Sent: Friday, February 22, 2008 6:19 PM
To: SprinklerFORUM
Subject: ICC Version of 13d

Okay Sprinkler Guys

 

Today at the ICC code hearings the Plumbing Committee heard RP3 and RP8.

 

See the code change here (scroll one or two changes down to RP3)

 

http://www.iccsafe.org/cs/codes/2007-08cycle/ProposedChanges/V2_RP1-8.pd
f

 

This is a code change which would give installation requirements for
multi-purpose piping for sprinkler systems in the body of the
residential
code (a modified pipe schedule like system).  RP3 passed and RP8 was
denied.
Now this was the committee action and it may be debated on the final
action
hearings in September.  

 

The code change only applies to multipurpose piping in one and two
family
dwellings.  It has many layers of built in safety.  A designer would
still
be allowed to utilize a 13d system and this really provides an option
for
the user.

 

I am just curious what you all think?  I know as sprinkler designers we
may
feel like we should not like this, but the intent is to make sprinkler
installation in homes as convenient as possible.

 

(ps there was a floor amendment which clarified hangers and some other
issues)

 

Michael O'Brian

Code Savvy Consultants

313-618-6401

fax 313-557-0294

www.codesavvyconsultants.com

www.inspector911.com

 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to