Re: Extinguisher Effectiveness

2011-04-17 Thread Stewart Kidd
Data on portable extinguisher use in the UK is published by the FIA.  You can 
download a summary of the 2011 report at:

http://www.fia.uk.com/filemanager/root/site_assets/articles/ifp_-_portables.pdf

This shows that 88% of fires tacked with extinguishers were put out. 

Stewart
On 17 Apr 2011, at 01:55, Chris Mak wrote:

 The Europeans relatively recently (in the 2000's?) carried out surveys and 
 found similar statistics. From memory, somewhere in the 80%'s.
 
 I'm sure that Alan Brinson would have this data.
 
 Our Sprinkler Standard calls up for extinguishers for this reason. Put out 
 the small fire before the sprinkler operates, and thereby minimise damage.
 
 Regards
 
 
 
 Chris Mak | Aon New Zealand
 Technical Services Manager
 Level 1, 4 Fred Thomas Drive Takapuna
 t: +6494869761 | f: +6494860112 | m: +64274344058
 e: chris@aon.co.nz
 
 Please consider the environment before printing this email.
 
 
 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org 
 [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Doug Hicks
 Sent: Sunday, 17 April 2011 12:52 PM
 To: sprinklerforum@firesprinkler.org; fpech...@embarqmail.com
 Subject: Re: PC- 3 Laboratories
 
 
 Before I left the fire service 20 + years ago, the Oregon State FM had an 
 article in the Gated Wye, about fire extinguisher use in reported fires.  I 
 do not remember the exact figures now, of the reported fires,  about 93 % of 
 the fires that fire extinguishers were used on, were controlled by  fire 
 extinguishers. Of the fires controlled by fire extinguishers, a very small 
 number of the fires are  reported to the FD.  Fire extinguishers can help 
 control an incipient fire.
 
 Douglas Hicks
 General Fire Equipment Co of Eastern Oregon
 
 
 -Original Message-
 From: Chris Cahill
 Sent: Friday, April 15, 2011 3:43 PM
 To: sprinklerforum@firesprinkler.org
 Subject: Re: PC- 3 Laboratories
 
 I don't concur with the statement they don't have a stellar success rate.
 In some sprinkler research I found a statistically significant number of 
 fires put out with extinguishers in SPRINKLERED buildings.  We including I 
 often speak of the holy grail of sprinklers but these very cheap cousins are 
 valuable.  I guarantee they have put out more fires than fires alarms with 
 all the strobes and costs. And lost in the data is a fire knocked down so 
 it's smaller than would have been when the FD arrived.
 
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
 
 For Technical Assistance, send an email to: supp...@firesprinkler.org
 
 To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)
 
 
 
 This communication (and any attachments) is directed in confidence to the 
 addressee(s) listed above, and may not otherwise be distributed, copied or 
 used. The contents of this communication may also be subject to privilege, 
 and all rights to that privilege are expressly claimed and not waived. If you 
 have received this communication in error, please notify us by reply e-mail 
 or by telephone and delete this communication (and any attachments) without 
 making a copy.
 
 Before opening or using attachments, you should check them for viruses and 
 defects. We do not accept liability in connection with computer virus, data 
 corruption, delay, interruption, unauthorised access or unauthorised 
 amendment.
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
 
 For Technical Assistance, send an email to: supp...@firesprinkler.org
 
 To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


Re: Extinguisher Effectiveness

2011-04-17 Thread Stewart Kidd
Scot

All the so-called clean agents containing halocarbons are only 'clean' when in 
storage.  If they are discharged in a fire there is a very high probability 
that corrosive by products will be formed.

Para 13.2 of BS 5306 Part 0: 2011 makes the point well:
 
Halocarbon agents can decompose when coming into contact with high 
temperatures. Of particular concern would be hazards where hot surfaces might 
be present such as furnaces, ovens, etc. When and where decomposition products 
occur, they are corrosive. The main decomposition product is hydrogen fluoride 
(HF) and prompt venting of the space after discharge can reduce the likelihood 
of corrosive action on materials.
 
My own experience of FM 200 (which appears to be the agent which generates most 
HF)  suggests that following discharge into confined spaces containing 
significant quantities of pvc cable, corrosive by-products are invariably 
formed and that damage to the contents of the space should be anticipated. I 
have not proposed, specified or recommended any of the halocarbon based agents 
for more that 10 years and have recommended the replacement of quite a few 
FM200 systems by inert gases or watermist/sprinklers.

I too would hope that these agents will be phased out.

Stewart


On 17 Apr 2011, at 11:06, å...  wrote:

 Statistics we can use...thanks for those!
 
 Fire extinguishers can work, but
 if the facility is valuable and not occupied 24/7...
 
 Fluorinated-foam and dry chem will be corrosive on sensitive equipment.
 De-ionized Water mist and clean-agent are alternatives, although
  if the clean-agent contains fluorine, I am betting
  what is marketed as clean today will be billed more
  realistically
  after 20 years of history.
 
 If we have the courage to encourage occupants to use portables,
  then how fine a line is it in our minds to allow
  an occupant to choose to use a  hose line?
 
 scot deal
 excelsior fire
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
 
 For Technical Assistance, send an email to: supp...@firesprinkler.org
 
 To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


Re: Extinguisher Effectiveness

2011-04-17 Thread Ron Greenman
Scot,

Rules of thumb I use regarding fire extinguishers:

Untrained--run
Trained layman--run if fire is bigger than you
Trained fire professional--run, there are too few to risk/spare
Firefighter--your call


On Sun, Apr 17, 2011 at 3:06 AM, å...  eurekaig...@gmail.com wrote:
 Statistics we can use...thanks for those!

 Fire extinguishers can work, but
 if the facility is valuable and not occupied 24/7...

 Fluorinated-foam and dry chem will be corrosive on sensitive equipment.
 De-ionized Water mist and clean-agent are alternatives, although
  if the clean-agent contains fluorine, I am betting
  what is marketed as clean today will be billed more
  realistically
  after 20 years of history.

 If we have the courage to encourage occupants to use portables,
  then how fine a line is it in our minds to allow
  an occupant to choose to use a  hose line?

 scot deal
  excelsior fire
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

 For Technical Assistance, send an email to: supp...@firesprinkler.org

 To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)




-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

rgreen...@bates.ctc.edu

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis
Bacon, essayist, philosopher, and statesman (1561-1626)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


Re: Extinguisher Effectiveness

2011-04-17 Thread Stewart Kidd
Ron

Would this include running if you have a stove top fire in your kitchen and 
your house is 35 minutes response time from the nearest FD unit ?

Stewart
On 17 Apr 2011, at 15:55, Ron Greenman wrote:

 Scot,
 
 Rules of thumb I use regarding fire extinguishers:
 
 Untrained--run
 Trained layman--run if fire is bigger than you
 Trained fire professional--run, there are too few to risk/spare
 Firefighter--your call
 
 
 On Sun, Apr 17, 2011 at 3:06 AM, å...  eurekaig...@gmail.com wrote:
 Statistics we can use...thanks for those!
 
 Fire extinguishers can work, but
 if the facility is valuable and not occupied 24/7...
 
 Fluorinated-foam and dry chem will be corrosive on sensitive equipment.
 De-ionized Water mist and clean-agent are alternatives, although
  if the clean-agent contains fluorine, I am betting
  what is marketed as clean today will be billed more
  realistically
  after 20 years of history.
 
 If we have the courage to encourage occupants to use portables,
  then how fine a line is it in our minds to allow
  an occupant to choose to use a  hose line?
 
 scot deal
  excelsior fire
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
 
 For Technical Assistance, send an email to: supp...@firesprinkler.org
 
 To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)
 
 
 
 
 -- 
 Ron Greenman
 Instructor
 Fire Protection Engineering Technology
 Bates Technical College
 1101 So. Yakima Ave.
 Tacoma, WA 98405
 
 rgreen...@bates.ctc.edu
 
 http://www.bates.ctc.edu/fireprotection/
 
 253.680.7346
 253.576.9700 (cell)
 
 Member:
 ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC
 
 They are happy men whose natures sort with their vocations. -Francis
 Bacon, essayist, philosopher, and statesman (1561-1626)
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
 
 For Technical Assistance, send an email to: supp...@firesprinkler.org
 
 To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


Re: Extinguisher Effectiveness

2011-04-17 Thread Michael Fitz
Easy answer for that - I installed a sprinkler system.  (And I am a fire 
professional)


Michael M. Fitz, P.E., C.F.E.I., C.F.P.S.
MDE Inc. 700 S. Industrial Way, Seattle, WA 98101
Home Office P.O. Box G, Shelton, WA  98584
206-321-1804


On 4/17/2011 9:00 AM, Stewart Kidd wrote:

Ron

Would this include running if you have a stove top fire in your kitchen and 
your house is 35 minutes response time from the nearest FD unit ?

Stewart
On 17 Apr 2011, at 15:55, Ron Greenman wrote:


Scot,

Rules of thumb I use regarding fire extinguishers:

Untrained--run
Trained layman--run if fire is bigger than you
Trained fire professional--run, there are too few to risk/spare
Firefighter--your call


On Sun, Apr 17, 2011 at 3:06 AM, å... eurekaig...@gmail.com  wrote:

Statistics we can use...thanks for those!

Fire extinguishers can work, but
if the facility is valuable and not occupied 24/7...

Fluorinated-foam and dry chem will be corrosive on sensitive equipment.
De-ionized Water mist and clean-agent are alternatives, although
  if the clean-agent contains fluorine, I am betting
  what is marketed as clean today will be billed more
  realistically
  after 20 years of history.

If we have the courage to encourage occupants to use portables,
  then how fine a line is it in our minds to allow
  an occupant to choose to use a  hose line?

scot deal
  excelsior fire
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)




--
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

rgreen...@bates.ctc.edu

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis
Bacon, essayist, philosopher, and statesman (1561-1626)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


__ Information from ESET Smart Security, version of virus signature 
database 6050 (20110417) __

The message was checked by ESET Smart Security.

http://www.eset.com








__ Information from ESET Smart Security, version of virus signature 
database 6050 (20110417) __

The message was checked by ESET Smart Security.

http://www.eset.com

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


Re: Extinguisher Effectiveness

2011-04-17 Thread Ron Greenman
Stewart,

Just my advice. Ever watch someone with no training fiddle for many
seconds just trying to break the seal and then shooting agent at the
top of the flames. The intuitive thing to do is pull instead of twist
and to attack the flame instead of the fuel. Unfortunately the
intuitive thing is, like trying to break a fall buy putting out your
hands out instead of collapsing, twisting and spreading the fall out
across lots of bouncy leg, butt, and shoulder muscle instead of thin
skin and inflexible bone, wrong. I've voluntarily jumped out of
perfectly good airplanes, dumped motorcycles, fallen off small cliffs
and roofs and have been bruised and battered but never broken.

On Sun, Apr 17, 2011 at 9:07 AM, Michael Fitz mf...@mde.com wrote:
 Easy answer for that - I installed a sprinkler system.  (And I am a fire
 professional)

 Michael M. Fitz, P.E., C.F.E.I., C.F.P.S.
 MDE Inc. 700 S. Industrial Way, Seattle, WA 98101
 Home Office P.O. Box G, Shelton, WA  98584
 206-321-1804


 On 4/17/2011 9:00 AM, Stewart Kidd wrote:

 Ron

 Would this include running if you have a stove top fire in your kitchen
 and your house is 35 minutes response time from the nearest FD unit ?

 Stewart
 On 17 Apr 2011, at 15:55, Ron Greenman wrote:

 Scot,

 Rules of thumb I use regarding fire extinguishers:

 Untrained--run
 Trained layman--run if fire is bigger than you
 Trained fire professional--run, there are too few to risk/spare
 Firefighter--your call


 On Sun, Apr 17, 2011 at 3:06 AM, å... eurekaig...@gmail.com  wrote:

 Statistics we can use...thanks for those!

 Fire extinguishers can work, but
 if the facility is valuable and not occupied 24/7...

 Fluorinated-foam and dry chem will be corrosive on sensitive equipment.
 De-ionized Water mist and clean-agent are alternatives, although
  if the clean-agent contains fluorine, I am betting
  what is marketed as clean today will be billed more
  realistically
  after 20 years of history.

 If we have the courage to encourage occupants to use portables,
  then how fine a line is it in our minds to allow
  an occupant to choose to use a  hose line?

 scot deal
  excelsior fire
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

 For Technical Assistance, send an email to: supp...@firesprinkler.org

 To Unsubscribe, send an email
 to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)



 --
 Ron Greenman
 Instructor
 Fire Protection Engineering Technology
 Bates Technical College
 1101 So. Yakima Ave.
 Tacoma, WA 98405

 rgreen...@bates.ctc.edu

 http://www.bates.ctc.edu/fireprotection/

 253.680.7346
 253.576.9700 (cell)

 Member:
 ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC

 They are happy men whose natures sort with their vocations. -Francis
 Bacon, essayist, philosopher, and statesman (1561-1626)
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

 For Technical Assistance, send an email to: supp...@firesprinkler.org

 To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)

 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

 For Technical Assistance, send an email to: supp...@firesprinkler.org

 To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)


 __ Information from ESET Smart Security, version of virus
 signature database 6050 (20110417) __

 The message was checked by ESET Smart Security.

 http://www.eset.com







 __ Information from ESET Smart Security, version of virus signature
 database 6050 (20110417) __

 The message was checked by ESET Smart Security.

 http://www.eset.com

 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

 For Technical Assistance, send an email to: supp...@firesprinkler.org

 To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)




-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

rgreen...@bates.ctc.edu

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis
Bacon, essayist, philosopher, and statesman (1561-1626)
___
Sprinklerforum mailing list

Re: Extinguisher Effectiveness

2011-04-17 Thread Stewart Kidd
That's why I spent 20 years of my life training people to use fire 
extinguishers - train them at work, save them at home. I even trained expat 
kids in Hong Kong and Saudi Arabia.

Of course sprinklers are the ideal but what percentage of US homes have them - 
and you have installing them for 40 years - we've only be doing it for 15.

Stewart
On 17 Apr 2011, at 17:24, Ron Greenman wrote:

 Stewart,
 
 Just my advice. Ever watch someone with no training fiddle for many
 seconds just trying to break the seal and then shooting agent at the
 top of the flames. The intuitive thing to do is pull instead of twist
 and to attack the flame instead of the fuel. Unfortunately the
 intuitive thing is, like trying to break a fall buy putting out your
 hands out instead of collapsing, twisting and spreading the fall out
 across lots of bouncy leg, butt, and shoulder muscle instead of thin
 skin and inflexible bone, wrong. I've voluntarily jumped out of
 perfectly good airplanes, dumped motorcycles, fallen off small cliffs
 and roofs and have been bruised and battered but never broken.
 
 On Sun, Apr 17, 2011 at 9:07 AM, Michael Fitz mf...@mde.com wrote:
 Easy answer for that - I installed a sprinkler system.  (And I am a fire
 professional)
 
 Michael M. Fitz, P.E., C.F.E.I., C.F.P.S.
 MDE Inc. 700 S. Industrial Way, Seattle, WA 98101
 Home Office P.O. Box G, Shelton, WA  98584
 206-321-1804
 
 
 On 4/17/2011 9:00 AM, Stewart Kidd wrote:
 
 Ron
 
 Would this include running if you have a stove top fire in your kitchen
 and your house is 35 minutes response time from the nearest FD unit ?
 
 Stewart
 On 17 Apr 2011, at 15:55, Ron Greenman wrote:
 
 Scot,
 
 Rules of thumb I use regarding fire extinguishers:
 
 Untrained--run
 Trained layman--run if fire is bigger than you
 Trained fire professional--run, there are too few to risk/spare
 Firefighter--your call
 
 
 On Sun, Apr 17, 2011 at 3:06 AM, å... eurekaig...@gmail.com  wrote:
 
 Statistics we can use...thanks for those!
 
 Fire extinguishers can work, but
 if the facility is valuable and not occupied 24/7...
 
 Fluorinated-foam and dry chem will be corrosive on sensitive equipment.
 De-ionized Water mist and clean-agent are alternatives, although
  if the clean-agent contains fluorine, I am betting
  what is marketed as clean today will be billed more
  realistically
  after 20 years of history.
 
 If we have the courage to encourage occupants to use portables,
  then how fine a line is it in our minds to allow
  an occupant to choose to use a  hose line?
 
 scot deal
  excelsior fire
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
 
 For Technical Assistance, send an email to: supp...@firesprinkler.org
 
 To Unsubscribe, send an email
 to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)
 
 
 
 --
 Ron Greenman
 Instructor
 Fire Protection Engineering Technology
 Bates Technical College
 1101 So. Yakima Ave.
 Tacoma, WA 98405
 
 rgreen...@bates.ctc.edu
 
 http://www.bates.ctc.edu/fireprotection/
 
 253.680.7346
 253.576.9700 (cell)
 
 Member:
 ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC
 
 They are happy men whose natures sort with their vocations. -Francis
 Bacon, essayist, philosopher, and statesman (1561-1626)
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
 
 For Technical Assistance, send an email to: supp...@firesprinkler.org
 
 To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
 
 For Technical Assistance, send an email to: supp...@firesprinkler.org
 
 To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)
 
 
 __ Information from ESET Smart Security, version of virus
 signature database 6050 (20110417) __
 
 The message was checked by ESET Smart Security.
 
 http://www.eset.com
 
 
 
 
 
 
 
 __ Information from ESET Smart Security, version of virus signature
 database 6050 (20110417) __
 
 The message was checked by ESET Smart Security.
 
 http://www.eset.com
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
 
 For Technical Assistance, send an email to: supp...@firesprinkler.org
 
 To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)
 
 
 
 
 -- 
 Ron Greenman
 Instructor
 Fire Protection 

Re: Extinguisher Effectiveness

2011-04-17 Thread Michael Fitz
A more important statistic that this forum should determine and use for 
sales work - what percentage of the members don't live in a sprinklered 
house and why?  How can we sell it to a homeowner, contractor or city 
council if we don't practice what we preach?


Michael M. Fitz, P.E., C.F.E.I., C.F.P.S.
MDE Inc. 700 S. Industrial Way, Seattle, WA 98101
Home Office P.O. Box G, Shelton, WA  98584
206-321-1804


On 4/17/2011 2:03 PM, Stewart Kidd wrote:

That's why I spent 20 years of my life training people to use fire 
extinguishers - train them at work, save them at home. I even trained expat 
kids in Hong Kong and Saudi Arabia.

Of course sprinklers are the ideal but what percentage of US homes have them - 
and you have installing them for 40 years - we've only be doing it for 15.

Stewart
On 17 Apr 2011, at 17:24, Ron Greenman wrote:


Stewart,

Just my advice. Ever watch someone with no training fiddle for many
seconds just trying to break the seal and then shooting agent at the
top of the flames. The intuitive thing to do is pull instead of twist
and to attack the flame instead of the fuel. Unfortunately the
intuitive thing is, like trying to break a fall buy putting out your
hands out instead of collapsing, twisting and spreading the fall out
across lots of bouncy leg, butt, and shoulder muscle instead of thin
skin and inflexible bone, wrong. I've voluntarily jumped out of
perfectly good airplanes, dumped motorcycles, fallen off small cliffs
and roofs and have been bruised and battered but never broken.

On Sun, Apr 17, 2011 at 9:07 AM, Michael Fitzmf...@mde.com  wrote:

Easy answer for that - I installed a sprinkler system.  (And I am a fire
professional)

Michael M. Fitz, P.E., C.F.E.I., C.F.P.S.
MDE Inc. 700 S. Industrial Way, Seattle, WA 98101
Home Office P.O. Box G, Shelton, WA  98584
206-321-1804


On 4/17/2011 9:00 AM, Stewart Kidd wrote:

Ron

Would this include running if you have a stove top fire in your kitchen
and your house is 35 minutes response time from the nearest FD unit ?

Stewart
On 17 Apr 2011, at 15:55, Ron Greenman wrote:


Scot,

Rules of thumb I use regarding fire extinguishers:

Untrained--run
Trained layman--run if fire is bigger than you
Trained fire professional--run, there are too few to risk/spare
Firefighter--your call







__ Information from ESET Smart Security, version of virus signature 
database 6050 (20110417) __

The message was checked by ESET Smart Security.

http://www.eset.com

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


Re: Extinguisher Effectiveness

2011-04-17 Thread Ron Greenman
Because retrofits, as you know, are very expensive, and try to get a loan for 
putting in sprinks. Now if I were doing a general remodel I'd certainly include 
them in the budget. And for me they'd be cheaper than for the many reading 
this. I don't know how many here can design and seal their own plans, have a 
materials account, and the requisite fitter's skills, or own a sprinkler 
company. And if a general is involved in a remodel they'll be stepping hard on 
the sprinklers even though they'll blame the high price on the sprinks while 
whining about not making money. There's a reason that when you go to get a 
contractor's license you have a special line to stand in (everybody else goes 
to a general business license line) and have to post a sudstantial bond, or why 
I'm right this minute listening to an LI radio ad giving me, the consumer, 
hints on how to keep from getting ripped off by a contractor. Hard to imagine 
in this age of concern for honesty  integrity over greed  avar
 ice, but it does happen. 

Ron Greenman 
...On the phone

On Apr 17, 2011, at 2:08 PM, Michael Fitz mf...@mde.com wrote:

 A more important statistic that this forum should determine and use for sales 
 work - what percentage of the members don't live in a sprinklered house and 
 why?  How can we sell it to a homeowner, contractor or city council if we 
 don't practice what we preach?
 
 Michael M. Fitz, P.E., C.F.E.I., C.F.P.S.
 MDE Inc. 700 S. Industrial Way, Seattle, WA 98101
 Home Office P.O. Box G, Shelton, WA  98584
 206-321-1804
 
 
 On 4/17/2011 2:03 PM, Stewart Kidd wrote:
 That's why I spent 20 years of my life training people to use fire 
 extinguishers - train them at work, save them at home. I even trained expat 
 kids in Hong Kong and Saudi Arabia.
 
 Of course sprinklers are the ideal but what percentage of US homes have them 
 - and you have installing them for 40 years - we've only be doing it for 15.
 
 Stewart
 On 17 Apr 2011, at 17:24, Ron Greenman wrote:
 
 Stewart,
 
 Just my advice. Ever watch someone with no training fiddle for many
 seconds just trying to break the seal and then shooting agent at the
 top of the flames. The intuitive thing to do is pull instead of twist
 and to attack the flame instead of the fuel. Unfortunately the
 intuitive thing is, like trying to break a fall buy putting out your
 hands out instead of collapsing, twisting and spreading the fall out
 across lots of bouncy leg, butt, and shoulder muscle instead of thin
 skin and inflexible bone, wrong. I've voluntarily jumped out of
 perfectly good airplanes, dumped motorcycles, fallen off small cliffs
 and roofs and have been bruised and battered but never broken.
 
 On Sun, Apr 17, 2011 at 9:07 AM, Michael Fitzmf...@mde.com  wrote:
 Easy answer for that - I installed a sprinkler system.  (And I am a fire
 professional)
 
 Michael M. Fitz, P.E., C.F.E.I., C.F.P.S.
 MDE Inc. 700 S. Industrial Way, Seattle, WA 98101
 Home Office P.O. Box G, Shelton, WA  98584
 206-321-1804
 
 
 On 4/17/2011 9:00 AM, Stewart Kidd wrote:
 Ron
 
 Would this include running if you have a stove top fire in your kitchen
 and your house is 35 minutes response time from the nearest FD unit ?
 
 Stewart
 On 17 Apr 2011, at 15:55, Ron Greenman wrote:
 
 Scot,
 
 Rules of thumb I use regarding fire extinguishers:
 
 Untrained--run
 Trained layman--run if fire is bigger than you
 Trained fire professional--run, there are too few to risk/spare
 Firefighter--your call
 
 
 
 
 
 __ Information from ESET Smart Security, version of virus signature 
 database 6050 (20110417) __
 
 The message was checked by ESET Smart Security.
 
 http://www.eset.com
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
 
 For Technical Assistance, send an email to: supp...@firesprinkler.org
 
 To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


Re: Extinguisher Effectiveness

2011-04-17 Thread Ron Greenman
Stewart, 

Spent a lot of training time myself and it's paid off a couple of times when 
the twelve year old used an extinguisher on an oven fire (overkill but better 
safe...) and the same son about ten years later used one on a brush fire before 
it took off. Knocked down enough so that when my other son got some water over 
to the site the we were able to overhaul his work successfully.

Ron Greenman 
...On the phone

On Apr 17, 2011, at 2:03 PM, Stewart Kidd stewart-k...@ndirect.co.uk wrote:

 That's why I spent 20 years of my life training people to use fire 
 extinguishers - train them at work, save them at home. I even trained expat 
 kids in Hong Kong and Saudi Arabia.
 
 Of course sprinklers are the ideal but what percentage of US homes have them 
 - and you have installing them for 40 years - we've only be doing it for 15.
 
 Stewart
 On 17 Apr 2011, at 17:24, Ron Greenman wrote:
 
 Stewart,
 
 Just my advice. Ever watch someone with no training fiddle for many
 seconds just trying to break the seal and then shooting agent at the
 top of the flames. The intuitive thing to do is pull instead of twist
 and to attack the flame instead of the fuel. Unfortunately the
 intuitive thing is, like trying to break a fall buy putting out your
 hands out instead of collapsing, twisting and spreading the fall out
 across lots of bouncy leg, butt, and shoulder muscle instead of thin
 skin and inflexible bone, wrong. I've voluntarily jumped out of
 perfectly good airplanes, dumped motorcycles, fallen off small cliffs
 and roofs and have been bruised and battered but never broken.
 
 On Sun, Apr 17, 2011 at 9:07 AM, Michael Fitz mf...@mde.com wrote:
 Easy answer for that - I installed a sprinkler system.  (And I am a fire
 professional)
 
 Michael M. Fitz, P.E., C.F.E.I., C.F.P.S.
 MDE Inc. 700 S. Industrial Way, Seattle, WA 98101
 Home Office P.O. Box G, Shelton, WA  98584
 206-321-1804
 
 
 On 4/17/2011 9:00 AM, Stewart Kidd wrote:
 
 Ron
 
 Would this include running if you have a stove top fire in your kitchen
 and your house is 35 minutes response time from the nearest FD unit ?
 
 Stewart
 On 17 Apr 2011, at 15:55, Ron Greenman wrote:
 
 Scot,
 
 Rules of thumb I use regarding fire extinguishers:
 
 Untrained--run
 Trained layman--run if fire is bigger than you
 Trained fire professional--run, there are too few to risk/spare
 Firefighter--your call
 
 
 On Sun, Apr 17, 2011 at 3:06 AM, å... eurekaig...@gmail.com  wrote:
 
 Statistics we can use...thanks for those!
 
 Fire extinguishers can work, but
 if the facility is valuable and not occupied 24/7...
 
 Fluorinated-foam and dry chem will be corrosive on sensitive equipment.
 De-ionized Water mist and clean-agent are alternatives, although
 if the clean-agent contains fluorine, I am betting
 what is marketed as clean today will be billed more
 realistically
 after 20 years of history.
 
 If we have the courage to encourage occupants to use portables,
 then how fine a line is it in our minds to allow
 an occupant to choose to use a  hose line?
 
 scot deal
 excelsior fire
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
 
 For Technical Assistance, send an email to: supp...@firesprinkler.org
 
 To Unsubscribe, send an email
 to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)
 
 
 
 --
 Ron Greenman
 Instructor
 Fire Protection Engineering Technology
 Bates Technical College
 1101 So. Yakima Ave.
 Tacoma, WA 98405
 
 rgreen...@bates.ctc.edu
 
 http://www.bates.ctc.edu/fireprotection/
 
 253.680.7346
 253.576.9700 (cell)
 
 Member:
 ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC
 
 They are happy men whose natures sort with their vocations. -Francis
 Bacon, essayist, philosopher, and statesman (1561-1626)
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
 
 For Technical Assistance, send an email to: supp...@firesprinkler.org
 
 To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
 
 For Technical Assistance, send an email to: supp...@firesprinkler.org
 
 To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)
 
 
 __ Information from ESET Smart Security, version of virus
 signature database 6050 (20110417) __
 
 The message was checked by ESET Smart Security.
 
 http://www.eset.com
 
 
 
 
 
 
 
 __ Information from ESET Smart Security, version of virus signature
 database 6050 (20110417) __
 
 The