RE: SxL rule

2008-05-12 Thread Dewayne Martinez
Roland,
So what you are trying to tell me so delicately is that I was wrong and
my sprinkler is over spaced according to rules.  I really appreciate
this forum for all the guidance it provides.  
Dewayne  

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Roland
Huggins
Sent: Friday, May 09, 2008 3:25 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: SxL rule

The starting point is the explicit guidance that addresses the last
sprinkler or branch line against a wall.  You apply the longest
dimension from either side for both S and L.  This places the sprinkler
in the center of the imaginary rectangle.  The same philosophy applies
to non-symmetrical layouts within the system.  Yep there is a lot of
overlap but it provides a consistent methodology.

Roland

On May 9, 2008, at 5:30 AM, Dewayne Martinez wrote:

 I have recently had a disagreement with a AHJ on how to determine the 
 protection area of coverage for a sprinkler.
 In my situation, we have an OH II area which has extended coverage 
 sprinklers (14x14) and one standard throw sprinkler.
 The distance between the extended and standard sprinkler is 12 ft.  I 
 was taught that since we are proving the EC sprinkler at 14x14, you 
 would take 7ft off the distance between the sprinklers and use 5ft as 
 the one of distances (x2=10ft) to determine the area of coverage for 
 the standard sprinkler.  He states that per NFPA, you would use the 
 distance between the sprinklers (ie:12ft).
 We are going 13ft between sprinklers the other dimension so using my 
 way we are at 130sq ft but his way we are 156sq ft.
 Which way is right?
 Thanks,
 Dewayne
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

 To Unsubscribe, send an email 
 to:[EMAIL PROTECTED]
 (Put the word unsubscribe in the subject field)


___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


Re: SxL rule

2008-05-12 Thread Roland Huggins
Being in the center of your rectangle (sounds like new wave psych-  
babble) does not necessarily mean splitting the difference.  It gets  
more confused with different types of sprinklers especially since it  
is NOT defined by 13.  I  too would count the boundary as the 7 ft  
mark from the EC.  The distance on the other side of the standard  
sprinkler is the driving variable.  Is it more than 2-1/2 ft from a  
wall OR 10 ft to the next standard sprinkler along that line.  If it  
is not, the 5 ft dimension toward the EC is the larger variable, the  
sprinkler is in the center of its rectangle, and the world is good.


Roland

On May 12, 2008, at 4:37 AM, Dewayne Martinez wrote:


Roland,
So what you are trying to tell me so delicately is that I was wrong  
and

my sprinkler is over spaced according to rules.  I really appreciate
this forum for all the guidance it provides.
Dewayne

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Roland
Huggins
Sent: Friday, May 09, 2008 3:25 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: SxL rule

The starting point is the explicit guidance that addresses the last
sprinkler or branch line against a wall.  You apply the longest
dimension from either side for both S and L.  This places the  
sprinkler

in the center of the imaginary rectangle.  The same philosophy applies
to non-symmetrical layouts within the system.  Yep there is a lot of
overlap but it provides a consistent methodology.

Roland


___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


SxL rule

2008-05-09 Thread Dewayne Martinez
I have recently had a disagreement with a AHJ on how to determine the
protection area of coverage for a sprinkler.
In my situation, we have an OH II area which has extended coverage
sprinklers (14x14) and one standard throw sprinkler.
The distance between the extended and standard sprinkler is 12 ft.  I
was taught that since we are proving the EC sprinkler at 14x14, you
would take 7ft off the distance between the sprinklers and use 5ft as
the one of distances (x2=10ft) to determine the area of coverage for the
standard sprinkler.  He states that per NFPA, you would use the distance
between the sprinklers (ie:12ft).
We are going 13ft between sprinklers the other dimension so using my way
we are at 130sq ft but his way we are 156sq ft.
Which way is right?
Thanks,
Dewayne
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


Re: SxL rule

2008-05-09 Thread Roland Huggins
The starting point is the explicit guidance that addresses the last  
sprinkler or branch line against a wall.  You apply the longest  
dimension from either side for both S and L.  This places the  
sprinkler in the center of the imaginary rectangle.  The same  
philosophy applies to non-symmetrical layouts within the system.  Yep  
there is a lot of overlap but it provides a consistent methodology.


Roland

On May 9, 2008, at 5:30 AM, Dewayne Martinez wrote:


I have recently had a disagreement with a AHJ on how to determine the
protection area of coverage for a sprinkler.
In my situation, we have an OH II area which has extended coverage
sprinklers (14x14) and one standard throw sprinkler.
The distance between the extended and standard sprinkler is 12 ft.  I
was taught that since we are proving the EC sprinkler at 14x14, you
would take 7ft off the distance between the sprinklers and use 5ft as
the one of distances (x2=10ft) to determine the area of coverage for  
the
standard sprinkler.  He states that per NFPA, you would use the  
distance

between the sprinklers (ie:12ft).
We are going 13ft between sprinklers the other dimension so using my  
way

we are at 130sq ft but his way we are 156sq ft.
Which way is right?
Thanks,
Dewayne
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)



___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)