Fellow listers,
Thank you all for your input on this topic. I think I now have a clear path
defined for this project. Your thoughts and opinions on the subject are
greatly appreciated!
--
Doug Nix
Office: (519) 650-4753
Mobile (519) 729-5704
Skype: cic-inc
d...@complianceinsight.ca
-
-
Doug, et al,
It seems that you are describing equipment to controll a process.
The traditional UL standard 508c could apply and the MD/60204 could be
used for Euro/Intl units.
A simpler approach might be to use IEC 61010 process control to cover
the basic unit and add ap
From: jral...@productsafetyinc.com [mailto:jral...@productsafetyinc.com]
Sent: Friday, January 21, 2011 4:23 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] Motor controller standards
It used to be EN50178. Not sure if that got rolled into a part 2 of 60947 or
separate Standard.
- R
It used to be EN50178. Not sure if that got rolled into a part 2 of 60947 or
separate Standard.
- Reply message -
From: "Ted Eckert"
List-Post: emc-pstc@listserv.ieee.org
Date: Fri, Jan 21, 2011 3:51 pm
Subject: [PSES] Motor controller standards
To: "EMC-PSTC@LI
c-p...@ieee.org> [mailto:emc-p...@ieee.org]
<mailto:[mailto:emc-p...@ieee.org]> On Behalf Of Doug Nix
Sent: Friday, January 21, 2011 3:00 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG <mailto:EMC-PSTC@LISTSERV.IEEE.ORG>
Subject: Motor controller standards
All,
I am consulting with a
Doug,
For the motor drives, take a look at the EN 61800 series of standards.
I'd also be wary of using EN 60950-1, at least on its own, for the processors.
If safety is involved (which it is if there are emergency stops involved) then
you have a significantly bigger can of worms on your hands,
In message , dated Fri, 21
Jan 2011, Doug Nix writes:
>I am considering using EN 60950-1 as the base standard for the system
>as it uses some integrated industrial PC's, but I'm a bit stumped on
>what the appropriate electrical safety standard for the drive module
>would be. The module uses a
Would 61010-1 be the better base as it appears to be a control device?
-Doug
-Original Message-
From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of Doug Nix
Sent: Friday, January 21, 2011 3:00 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Motor controller standards
All,
I am
All,
I am consulting with a client that builds automation equipment used with chain
and wire rope hoists. The system is comprised of a group of modules that can
be connected via ethernet with a control console, auxilliary modules and hoist
motor controllers to build a customized system.