...@thermofisher.com
From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of Brian
O'Connell
Sent: Tuesday, June 05, 2007 3:15 PM
To: emc-p...@ieee.org
Subject: RE: Surge coupler anomaly
As I have not seen this extreme (for a correctly constructed UUT) I
would have to assume that none of my
; if you can, pls advise on the root
cause.
luck,
Brian
From: emc-p...@ieee.org [mailto:emc-p...@ieee.org]On Behalf Of Bob
Richards
Sent: Tuesday, June 05, 2007 11:35 AM
To: ieee
Subject: Surge coupler anomaly
In surge testing a product to 61000-4-5, we had a failure that could not
be explained
,
Brian
From: emc-p...@ieee.org [mailto:emc-p...@ieee.org]On Behalf Of Bob
Richards
Sent: Tuesday, June 05, 2007 11:35 AM
To: ieee
Subject: Surge coupler anomaly
In surge testing a product to 61000-4-5, we had a failure that could not
be explained. So, we investigated and found that during a 2kv
In surge testing a product to 61000-4-5, we had a failure that could not be
explained. So, we investigated and found that during a 2kv surge line-PE, we
were seeing about 1.6kv line-neutral. The spec only requires 1kv line-neutral,
and 2kv line-PE and neutral-PE. But when we surge line-PE we get