Re: Ground Fill on Multi-Layer PCBs

2002-06-25 Thread Fred Townsend

Darrell, one can only guess whether it is necessary to fill unused ground area.
You haven't supplied enough information to tell.  If the ground is a reference
ground plane for establishing impedance anywhere then you must fill the plane.
If thermal considerations exist then fill it.  If current considerations exist
then fill it.  It's hard to make a case for not filling.

To consider this trade-off at all makes me wonder how hard it is to do the
extra work.  Ground fill is a simple thing to do in most modern CAD systems
and would be an automatic for me unless I had some excess capacitance in a
circuit to worry about.

Fred Townsend

Darrell Locke wrote:

 Group,

 On two layer boards its always good to fill unused area with ground (signal
 return) for tight coupling.  What about a six layer board with high speed
 traces sandwiched between two ground/power planes.  Should the layer with
 only signals have ground fill?  I don't think it would hurt EMC performance,
 but is the gain in decoupling worth the extra work?  Anyone have expereince
 with this or know of technical papers on the subject?

 Thanks

 Darrell Locke
 Advanced Input Devices

 ---
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.

 Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

 To cancel your subscription, send mail to:
  majord...@ieee.org
 with the single line:
  unsubscribe emc-pstc

 For help, send mail to the list administrators:
  Ron Pickard:  emc-p...@hypercom.com
  Dave Heald:   davehe...@attbi.com

 For policy questions, send mail to:
  Richard Nute:   ri...@ieee.org
  Jim Bacher: j.bac...@ieee.org

 All emc-pstc postings are archived and searchable on the web at:
 http://ieeepstc.mindcruiser.com/
 Click on browse and then emc-pstc mailing list


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


RE: SEMI - EN standards cross reference

2002-06-25 Thread LCrane
 Nick, 

I have worked with the SEMI safety guidelines development committee for many
years, and also with CE-Marking compliance... 

Generally speaking, there is no correlation between SEMI standards and EN
Standards. That is to say, typically end users request line-by-line
assessment of products to SEMI safety guidelines of thier choice. Typically
this is SEMI S2 is requested which, in turn references several other SEMI
safety guidelines as normative references (Such as SEMI S8-ergonomics, SEMI
S1-hazard warning labels, SEMI S13-user documentation). 

No SEMI Safety guideline contains a statement such as demonstration of
conformance to EN XX may be taken as conformance to this guideline and,
of course, no EN standard has equivalent line items to the SEMI safety
guidelines. 

Although SEMI safety guidelines may be coorelated to EN standards that
address similar topics or range of topics, the assessment challange is in
the details and the details are often quite different. 

Regards, 

Lauren Crane
TUV America
Product Service Division
Cedar Park, TX

512 401-4922.



-Original Message-
From: Nick Williams
To: emc-p...@majordomo.ieee.org
Sent: 6/25/2002 10:19 AM
Subject: SEMI - EN standards cross reference


We've had an enquiry from someone who wants to sell CE marked 
semiconductor manufacturing plant to a location in the far east. They 
are hoping that they can find a way of correlating the EN standards 
which they have already applied for CE marking purposes to the SEMI 
standards which their customer is demanding.

If anyone has experience or relevant documentation for this type of 
project, please would they get in touch. I would expect to pay an 
appropriate amount for suitable materials.

Regards

Nick.



Conformance Ltd - Product safety, approvals and CE-marking consultants
Tel. + 44 1298 873800, Fax. +44 1298 873801
Registered in England, Company No. 3478646

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


Re: Environmental question

2002-06-25 Thread Jacob Schanker

Andrew:

One could theorize that the better growth had nothing to do with RF, but
with the tower not competing with the surrounding trees for nutrients. Did
New Scientist make any cause and effect comments?

I wonder what the EMC-PSTC group thinks of this issue - should there be
concern for irradiating trees with cellular phone calls? My own opinion
mimics the tag line of John Stoessel on a US ABC-TV news magazine show:
Give me a break.  (idomatic expression meaning something like go away,
don't you have better things to worry about?)

Regards,

Jacob Z. Schanker, P.E.
65 Crandon Way
Rochester, NY 14618
Phone: 585 442 3909
Fax: 585 442 2182
j.schan...@ieee.org

- Original Message -
From: Andrew Carson andrew_car...@uk.xyratex.com
To: Scott Douglas dougl...@naradnetworks.com; Muriel Bittencourt de
Liz mur...@eel.ufsc.br; Lista de EMC da IEEE emc-p...@ieee.org
Sent: Tuesday, June 25, 2002 11:13 AM
Subject: RE: Environmental question


I remember reading an article about this in New Scientist. After several
years of operation they had found the Trees to either side of the
antenna were growing taller and stronger than the rest of those in the
Forest.



Andrew Carson

Senior Compliance Engineer

Xyratex, UK



-Original Message-
From: Scott Douglas [mailto:dougl...@naradnetworks.com]
Sent: 25 June 2002 13:16
To: Muriel Bittencourt de Liz; Lista de EMC da IEEE
Subject: Re: Environmental question



Muriel,

Don't know if there are any agency type regulations but can remember
this issue came up when the government wanted to install a
communications antenna in the north woods of Wisconsin. The antenna was
to be used to communicate to submarines deep under water using something
like 30 Hz or 60 Hz radio waves. The antenna was a long (miles long)
cable buried underground. There were many battles between the local
citizens, various environmental and animal groups, and the government
(US Navy?). If I recall correctly, there were even court cases trying to
prevent the antenna from being installed. The concerns were related to
what effect the RF would have on the environment to include plants and
animals. Don't know for sure, but I believe the antenna was actually
installed and was/is operating. Might be worth a look to see what came
of that and to see what arguments were made pro/con. Might even be
something came out of all that related to what you want to know.

Regards,
Scott



Senior Compliance Engineer
Narad Networks
515 Groton Road
Westford, MA 01886
office:  978 589-1869
cell: 978-239-0693
dougl...@naradnetworks.com
www.naradnetworks.com http://www.naradnetworks.com/



At 06:13 PM 6/24/02 -0300, Muriel Bittencourt de Liz wrote:

Hello Group,

We already know the standards related to human exposure to
electromagnetic
fields (e.g. ANSI/IEEE). However some people have asked us if
there is any
standard/recommendations limiting the exposure of forests,
lakes/rivers,
animals, etc to RF fields.

Do you know any FDA and EPA (or another agency) that regulate
this subject
of RF fields incidence?

Example: Imagine a radio-base station (mobile comm) or antenna
(TV or radio)
put in the middle of a forest, where there is not human
habitation, but we
have animals, trees and waters. Is there any
standard/recommendation related
to this case (only for non-ionizing radiation, ie, EM
radiation).

Thanks in advance and Regards,

Muriel












---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


RE: mechanical deformation rating under repeated impact

2002-06-25 Thread Ron Baugh

Chet,

You might want to look in UL Safety Standard 508 starting with Part 1 Paragraph
6.  This standards requires some very aggressive mechanical tests for
enclosures.

Ron Baugh
VeriFone, Inc.

-Original Message-
From:   Summers, Chet [SMTP:csumm...@pelco.com]
Sent:   Tuesday, June 25, 2002 10:23 AM
To: Emc-Pstc (E-mail)
Subject:mechanical deformation rating under repeated impact


Hello group,

I am looking for a standard (or standards) that rates the repeated
impact or
detent withstand of small electronic enclosures (app. one cubic foot
or
less in volume).  I am aware of UL's impact rating test, but I am
looking
for something a bit more aggressive.  Is there such a standard or
guideline
published that characterizes the amount of deformation an enclosure
exhibits
under repeated hammer blows, for example?  The object delivering the
blow is
not limited to hammers, it could be any such weapon--lead pipe, pipe
wrench, ice pick, screwdriver, combat boot(?)...   Any info or direction
is
much appreciated!


Chet Summers
Compliance Engineering Group
Pelco
Ph: (559) 292-1981















---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


Re: Environmental question

2002-06-25 Thread Ken Javor

The following represents my thoughts on the matter.  For the original query,
and those looking for information on actual standards/recommendations on the
original subject matter, there is none to be found in the answer below.

Since I am self-employed, I need not concern myself with embarrassing anyone
but myself:

The original question related to rf fields in a forest or other uninhabited
area.  That last being an intrinsically species-ist statement, because the
concern necessarily relates to the non-human denizens of the forest, fauna
and for all I know flora as well.  I lived in the Upper Peninsula of
Michigan in the early '70s and recall the controversy surrounding the
submarine communications system, predictions of cows not giving milk, etc.
As pointed out by others, that was an underground ELF installation and
likely not the kind of thing the original query addressed.  That sounded to
me more like a cell phone or other type of repeater tower installation.  I
would expect that whatever effects might be postulated, the effects of ELF
vs. VHF/UHF are considerable.  Further, a VHF/UHF tower would not immerse
the innocent forest dwellers in the same kind of large area immersion
associated with a buried ELF conductor whose purpose it is to transmit
signals throughout a significant fraction of the globe's surface.  The
repeater's main beam, even if omni-directional, has a null towards the
ground.

To my knowledge there is no correlation established between a particular rf
exposure and health effects in humans, other than gross heating at very high
illumination intensities.  Before everyone jumps on that and starts citing
study after study, the point I am making is that there is no known unsafe or
safe level beyond which predictions of a particular effect with high
certainty can be made.  All that you really have is the doctrine of prudent
avoidance, the idea that if someone, anyone, can imagine a possible harm,
even without any evidence to support it, then prudence dictates avoidance
and control.

Such is the current state of the art.  Given that, it would seem a bit
premature, indeed arrogant, to levy restrictions on rf emissions that might
impinge on non-human, indeed non-animal life.  I suppose if one were greatly
concerned about the occasional bird that flew through an rf beam and was
momentarily illuminated, one could use the same kind of heating calculations
applied to humans and adjust for bird sizes and probable illumination times
and arrive at a limit on ERP.  Mind you I am recommending no such thing, but
I'll bet there are people out there right now who if they read this thread
would immediately hop on their cell phones and discuss the need for exactly
such measures.

One caveat.  Simply due to the again species-ist tendency of man to use
guinea pigs rather than humans as test cases, there is likely a large body
of knowledge on the effects of all kinds of different electromagnetic
radiation on small animals and perhaps plants as well.  There is no doubt
that at SOME level of immersion/illumination that ill effects are perceived.
It is the nature of the people who do such work to linearly extrapolate
those results to obtain safe levels of exposure orders of magnitude below
the test levels.  I'm obviously not trying to be diplomatic here, but real
students of nature recognize that linear models, while extremely useful, can
not in the general case accurately predict the functional relationship
between an independent and dependent variable while the independent variable
takes on ranges over several orders of magnitude.

End of rant.
--
From: mark_mayn...@dell.com
To: mur...@eel.ufsc.br, emc-p...@ieee.org
Subject: RE: Environmental question
Date: Tue, Jun 25, 2002, 10:26 AM



 The Nordic countries (Sweden, Norway, Finland, Denmark) have done the most
 research into this issue, that I am aware of.  If you look into the TCO
 (Swedish Workers Union) website, you can find standards relating to ELF 
 VLF magnetic and electrical fields exposure.

 http://www.tco.se/eng/

 Thanks-
 Mark M.


 -Original Message-
 From: Muriel Bittencourt de Liz [mailto:mur...@eel.ufsc.br]
 Sent: Monday, June 24, 2002 4:13 PM
 To: Lista de EMC da IEEE
 Subject: Environmental question



 Hello Group,

 We already know the standards related to human exposure to electromagnetic
 fields (e.g. ANSI/IEEE). However some people have asked us if there is any
 standard/recommendations limiting the exposure of forests, lakes/rivers,
 animals, etc to RF fields.

 Do you know any FDA and EPA (or another agency) that regulate this subject
 of RF fields incidence?

 Example: Imagine a radio-base station (mobile comm) or antenna (TV or radio)
 put in the middle of a forest, where there is not human habitation, but we
 have animals, trees and waters. Is there any standard/recommendation related
 to this case (only for non-ionizing radiation, ie, EM radiation).

 Thanks in advance and Regards,

 Muriel






 

mechanical deformation rating under repeated impact

2002-06-25 Thread Summers, Chet

Hello group,

I am looking for a standard (or standards) that rates the repeated impact or
detent withstand of small electronic enclosures (app. one cubic foot or
less in volume).  I am aware of UL's impact rating test, but I am looking
for something a bit more aggressive.  Is there such a standard or guideline
published that characterizes the amount of deformation an enclosure exhibits
under repeated hammer blows, for example?  The object delivering the blow is
not limited to hammers, it could be any such weapon--lead pipe, pipe
wrench, ice pick, screwdriver, combat boot(?)...   Any info or direction is
much appreciated!


Chet Summers
Compliance Engineering Group
Pelco
Ph: (559) 292-1981















---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


Re: Class 2 Power Unit

2002-06-25 Thread Art Michael

Hello Brian,

To my recollection (and in simplified form):

Maximum Output voltage, less than 30V rms/42.2V peak/60V DC (including
 open circuit)

Maximum Output current, less than 8 Amps, at one minute of overload,
 including short-circuit

Charts and Tables within the standard further clarify the requisites.

Best regards, Art Michael
 
The Safety Link www.safetylink.com
o-o-o-o-o-o-o-o-o-o-o-o-o-0-o-o-o-o-o-o-o-o-o-o-o-o-o
   The Web's Most Comprehensive Collection 
 of Electrical Product Safety  Standards Resources



On Tue, 25 Jun 2002, Brian McAuliffe wrote:

 
 Can anyone define, or point me to a definition of, a Class 2 Power Unit i.e.
 as covered by UL 1310.
 
 I know I could buy the standard to find out but ..
 
 
 
 Brian McAuliffe
 
 MCA Compliance Solutions Ltd
 Unit 2 Lissane Business Park|Clarecastle|Co.Clare|Ireland
 
 w: www.mcac.ie
 e: i...@mcac.ie
 t: +353 (0)65 6823452
 m: +353 (0)87 2352554
 
 
 ---
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.
 
 Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/
 
 To cancel your subscription, send mail to:
  majord...@ieee.org
 with the single line:
  unsubscribe emc-pstc
 
 For help, send mail to the list administrators:
  Ron Pickard:  emc-p...@hypercom.com
  Dave Heald:   davehe...@attbi.com
 
 For policy questions, send mail to:
  Richard Nute:   ri...@ieee.org
  Jim Bacher: j.bac...@ieee.org
 
 All emc-pstc postings are archived and searchable on the web at:
 http://ieeepstc.mindcruiser.com/
 Click on browse and then emc-pstc mailing list
 


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


RE: SEMI - EN standards cross reference

2002-06-25 Thread Collins, Jeffrey

Nick,

What EN's did your product meet? EN 1010, EN60204 and EN292-1  2 are the
closest relevant spec's I've used which relate to SEMI S2.  You may want to
look at the Machinery Directive, Low Voltage Directive and the EMAS
Voluntary Directive ( Environmental Management and Audit Scheme) for their
applicability to your product type.

Remember Semi S2 is not a standard it is a design guideline primarily for US
based customers.
You should also review some US standards such as NFPA 70  79, National
Electric Code ( NEC), the UBC / UFC ( Uniform Fire Code / Uniform Building
Code) and 29CFR-1910 ( OSHA )

You may want to get a copy of SEMI S2 and identify the delta's between S2
and your EN certifications to your customers. 


Good Luck,

Jeffrey Collins
Sr. HW Engineering Manager 
EMC/ NEBS/ Safety/ Reliability
CIENA  Core Switching Division
10480 Ridgeview Court, Cupertino, CA. 95014
(408) 366-4806, Fax (408) 366-4866
jcoll...@ciena.com
http://www.ciena.com


-Original Message-
From: Nick Williams [mailto:nick.willi...@conformance.co.uk]
Sent: Tuesday, June 25, 2002 7:19 AM
To: emc-p...@majordomo.ieee.org
Subject: SEMI - EN standards cross reference



We've had an enquiry from someone who wants to sell CE marked 
semiconductor manufacturing plant to a location in the far east. They 
are hoping that they can find a way of correlating the EN standards 
which they have already applied for CE marking purposes to the SEMI 
standards which their customer is demanding.

If anyone has experience or relevant documentation for this type of 
project, please would they get in touch. I would expect to pay an 
appropriate amount for suitable materials.

Regards

Nick.



Conformance Ltd - Product safety, approvals and CE-marking consultants
Tel. + 44 1298 873800, Fax. +44 1298 873801
Registered in England, Company No. 3478646

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


Units, Symbols and Style Guide

2002-06-25 Thread Chuck Mullett

My attempt to attach these files for all of you to download did not
work, as the system won't allow the attachments.

Here's the plan:

If you would like a copy of PSMA's Units, Symbols and Style Guide, and
my Writing Guide, just send me an email.  I'll reply with a .pdf file
for each.

It will take some time, but we are planning to make both of them
available at no charge on the PSMA Web site (psma.com).  PSMA presently
offers, and will continue to offer, the Units, Symbols and Style Guide
as a notebook insert, 3-hole punched with index tab, printed on coated
card stock for $0.30 in lots of 10.

Chuck Mullett
Chairman, Power Sources Mfg. Assn.
Principal Systems Engr., ON Semiconductor


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


Re: TOUCH CURRENT LIMIT

2002-06-25 Thread Ron Pickard


Hi Xing,

Find my comments below marked with ***.

Your email stated:
Our test lab receive a CB TEST REPORT FOR NATIONAL RECOGNIZATION,
the EUT is a class II ac adapter having a bridging capacitor (4700pF)across 
the reinforced
insulation
The touch current measured by CB is 0.17mA(4700pF declared)
but the value we measure is 0.28mA(4700pF)
which one is correct ?

*** To answer your question, you/we will need to know the applied voltage and 
frequency across that
capacitor. On the surface, it does appear that the CB and your lab measured 
this parameter under
different conditions. Also, was this single capacitor the only component that 
was bridging the
reinforced barrier during the CB's test?

it depend on test equipment?

*** Possibly.

How to judge

*** This can easily be calculated. The measured results should be very close to 
the calculated
results. For instance:
 @120V 60Hz, I = 0.213 mA
 @220V 50Hz, I = 0.325 mA
 @240V 50Hz, I = 0.354 mA
 @264V 50Hz, I = 0.390 mA

How to obtain accurate result?

*** Use good quality instruments (I'm sure that you are) with suitable 
measurement resolution.

I hope this will assist you in approaching a satisfactory resolution to your 
problem.

Comments anyone?

Best regards,

Ron Pickard
rpick...@hypercom.com



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


RE: Formaldehyde requirements for Europe

2002-06-25 Thread Mark_Maynard

This website is for the German RAL agency, which has responsibility for the
Blue Angel environmental requirements for products in Germany.

http://www.blauer-engel.de/willkommen/willkommen.htm

Thanks-
Mark M.

-Original Message-
From: Tyra, John [mailto:john_t...@bose.com]
Sent: Monday, June 24, 2002 9:00 AM
To: 'emc-p...@majordomo.ieee.org'
Subject: Formaldehyde requirements for Europe



Hello Everyone,

I am new to the list and was hoping that someone could help me with the
following question. I have been tasked with researching  Formaldehyde out
gasssing regulations for products utilizing composite ( particle board)
material. Our speaker cabinets utilize this material.

I have recently received some information concerning German regulations
which seems to indicate that our speakers must be subjected to testing by a
recognized authority in Germany.

Does anyone have any information on this subject or have any sources they
can direct me too?

I am happy to share the limited info I have so if you are interested please
e-mail me privately.

Thanks in advance for your help.

regards,


John Tyra
Design Assurance Engineering,
Product Safety  Regulatory Manager

Bose Corporation
The Mountain, M.S.-450
Framingham, MA 01701-9168
508-766-1502 Phone
508-766-1145 Fax
john_t...@bose.com


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


RE: Environmental question

2002-06-25 Thread Mark_Maynard

The Nordic countries (Sweden, Norway, Finland, Denmark) have done the most
research into this issue, that I am aware of.  If you look into the TCO
(Swedish Workers Union) website, you can find standards relating to ELF 
VLF magnetic and electrical fields exposure.

http://www.tco.se/eng/

Thanks-
Mark M.


-Original Message-
From: Muriel Bittencourt de Liz [mailto:mur...@eel.ufsc.br]
Sent: Monday, June 24, 2002 4:13 PM
To: Lista de EMC da IEEE
Subject: Environmental question



Hello Group,

We already know the standards related to human exposure to electromagnetic
fields (e.g. ANSI/IEEE). However some people have asked us if there is any
standard/recommendations limiting the exposure of forests, lakes/rivers,
animals, etc to RF fields.

Do you know any FDA and EPA (or another agency) that regulate this subject
of RF fields incidence?

Example: Imagine a radio-base station (mobile comm) or antenna (TV or radio)
put in the middle of a forest, where there is not human habitation, but we
have animals, trees and waters. Is there any standard/recommendation related
to this case (only for non-ionizing radiation, ie, EM radiation).

Thanks in advance and Regards,

Muriel






---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


RE: ESAs certification to 95/54/EC

2002-06-25 Thread Chris Chileshe

More info - very good info I think - at 

http://www.rfi-wireless.com/pages/press/articles/ART014.htm

Regards

- Chris


-Original Message-
From:   Fang Han [SMTP:f...@qualcomm.com]
Sent:   Monday, June 24, 2002 6:45 PM
To: emc-p...@majordomo.ieee.org
Subject:ESAs certification to 95/54/EC

Hi Colleagues,

It looks like all products for vehicle application, even they have been 
certified to EMC Directive or RTTE Directive, must be certified to 
95/54/EC (vehicle EMC directive) before Oct 1, 2002.  It seems to me that 
the certification route for vehicle EMC directive is different with EMC 
directive or RTTE directive certification.   I am looking for an accredited 
lab/body that is authorized to certify ESAs products to 95/54/EC.  I wonder 
if all these labs/bodies are located in Europe or there are some in USA.  I 
understand that these labs/bodies should be authorized by the Ministry of 
Transportation of a EU member state.  A certification done by such a lab 
will be accepted by all other EU member states.

I appreciate it very much if someone familiar with this can shed some light.

Thanks a lot,

Fang




This e-mail has been scanned for all viruses by Star Internet. The
service is powered by MessageLabs. For more information on a proactive
anti-virus service working around the clock, around the globe, visit:
http://www.star.net.uk
  
File: ATT5.htm  


This e-mail has been scanned for all viruses by Star Internet. The
service is powered by MessageLabs. For more information on a proactive
anti-virus service working around the clock, around the globe, visit:
http://www.star.net.uk


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


RE: Environmental question

2002-06-25 Thread Andrew Carson
I remember reading an article about this in New Scientist. After several
years of operation they had found the Trees to either side of the
antenna were growing taller and stronger than the rest of those in the
Forest.

 

Andrew Carson

Senior Compliance Engineer

Xyratex, UK

 

-Original Message-
From: Scott Douglas [mailto:dougl...@naradnetworks.com] 
Sent: 25 June 2002 13:16
To: Muriel Bittencourt de Liz; Lista de EMC da IEEE
Subject: Re: Environmental question

 

Muriel,

Don't know if there are any agency type regulations but can remember
this issue came up when the government wanted to install a
communications antenna in the north woods of Wisconsin. The antenna was
to be used to communicate to submarines deep under water using something
like 30 Hz or 60 Hz radio waves. The antenna was a long (miles long)
cable buried underground. There were many battles between the local
citizens, various environmental and animal groups, and the government
(US Navy?). If I recall correctly, there were even court cases trying to
prevent the antenna from being installed. The concerns were related to
what effect the RF would have on the environment to include plants and
animals. Don't know for sure, but I believe the antenna was actually
installed and was/is operating. Might be worth a look to see what came
of that and to see what arguments were made pro/con. Might even be
something came out of all that related to what you want to know.

Regards,
Scott



Senior Compliance Engineer
Narad Networks
515 Groton Road 
Westford, MA 01886
office:  978 589-1869
cell: 978-239-0693
dougl...@naradnetworks.com
www.naradnetworks.com http://www.naradnetworks.com/ 



At 06:13 PM 6/24/02 -0300, Muriel Bittencourt de Liz wrote:

Hello Group,

We already know the standards related to human exposure to
electromagnetic
fields (e.g. ANSI/IEEE). However some people have asked us if
there is any
standard/recommendations limiting the exposure of forests,
lakes/rivers,
animals, etc to RF fields.

Do you know any FDA and EPA (or another agency) that regulate
this subject
of RF fields incidence?

Example: Imagine a radio-base station (mobile comm) or antenna
(TV or radio)
put in the middle of a forest, where there is not human
habitation, but we
have animals, trees and waters. Is there any
standard/recommendation related
to this case (only for non-ionizing radiation, ie, EM
radiation).

Thanks in advance and Regards,

Muriel







 



RE: Class 2 Power Unit

2002-06-25 Thread McKinney, Alex

Here is the link to the scope on UL's website.

http://ulstandardsinfonet.ul.com/scopes/1310.html

Regards,

Alex McKinney
Safety Engineer
LXE, Inc.
Tel: 770-447-4224 x3606
Fax: 770-447-6928



-Original Message-
From: Brian McAuliffe [mailto:i...@mcac.ie]
Sent: Tuesday, June 25, 2002 8:46 AM
To: Emc-Pstc Post
Subject: Class 2 Power Unit



Can anyone define, or point me to a definition of, a Class 2 Power Unit i.e.
as covered by UL 1310.

I know I could buy the standard to find out but ..



Brian McAuliffe

MCA Compliance Solutions Ltd
Unit 2 Lissane Business Park|Clarecastle|Co.Clare|Ireland

w: www.mcac.ie
e: i...@mcac.ie
t: +353 (0)65 6823452
m: +353 (0)87 2352554


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


SEMI - EN standards cross reference

2002-06-25 Thread Nick Williams


We've had an enquiry from someone who wants to sell CE marked 
semiconductor manufacturing plant to a location in the far east. They 
are hoping that they can find a way of correlating the EN standards 
which they have already applied for CE marking purposes to the SEMI 
standards which their customer is demanding.


If anyone has experience or relevant documentation for this type of 
project, please would they get in touch. I would expect to pay an 
appropriate amount for suitable materials.


Regards

Nick.



Conformance Ltd - Product safety, approvals and CE-marking consultants
Tel. + 44 1298 873800, Fax. +44 1298 873801
Registered in England, Company No. 3478646

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
majord...@ieee.org
with the single line:
unsubscribe emc-pstc

For help, send mail to the list administrators:
Ron Pickard:  emc-p...@hypercom.com
Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
Richard Nute:   ri...@ieee.org
Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
   http://ieeepstc.mindcruiser.com/
   Click on browse and then emc-pstc mailing list


RE: Units, symbols

2002-06-25 Thread Peter Tarver


I don't have a copy, but if we were to refer to ISO
31-0:1992, I'm certain answers to these questions would be
revealed.

Abstract from the ISO web site:

Gives general information about principles concerning
physical quantities, equations, quantity and unit symbols,
and coherent unit systems, especially the International
System of Units, SI, including recommendations for printing
symbols and numbers. Annex A includes a guide to terms used
in names for physical quantities, Annex B a guide to the
rounding of numbers, Annex C international organizations in
the field of quantities and units.


Regards,

Peter L. Tarver, PE
Product Safety Manager
Sanmina-SCI Homologation Services
San Jose, CA
peter.tar...@sanmina-sci.com


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


Class 2 Power Unit

2002-06-25 Thread Brian McAuliffe

Can anyone define, or point me to a definition of, a Class 2 Power Unit i.e.
as covered by UL 1310.

I know I could buy the standard to find out but ..



Brian McAuliffe

MCA Compliance Solutions Ltd
Unit 2 Lissane Business Park|Clarecastle|Co.Clare|Ireland

w: www.mcac.ie
e: i...@mcac.ie
t: +353 (0)65 6823452
m: +353 (0)87 2352554


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


TOUCH CURRENT LIMIT

2002-06-25 Thread georgea



Xing,

Section 5.2.3 of IEC 60950 (2nd edition) shows how this
measurement is made for Class II equipment.  This should
be the same in China's GB 4943? standard.

See the paragraph near the end of 5.2.2 describing that
for Class II, accessible conductive parts or metal foil
wrapped around the unit are used to measure the current
to either phase or neutral.  If your adapter is plastic
enclosed, with no exposed metal, the leakage should be
quite small.

You could also use the output pins as the ground side,
but these may not qualify as being exposed.

George




xingwb xingwb%cesi.ac...@interlock.lexmark.com on 06/25/2002 05:56:33 AM

Please respond to xingwb xingwb%cesi.ac...@interlock.lexmark.com

To:   Peter Merguerian pmerguerian%itl.co...@interlock.lexmark.com
cc:   emc-pstc%majordomo.ieee@interlock.lexmark.com (bcc: George
  Alspaugh/Lex/Lexmark)
Subject:  Re: TOUCH CURRENT LIMIT



Hi Mr. Peter:


Our test lab receive a CB TEST REPORT FOR NATIONAL RECOGNIZATION,
the EUT is a class II ac adapter having a bridging capacitor (4700pF)across the
reinforced insulation

The touch current measured by CB is 0.17mA(4700pF declared)
but the value we measure is 0.28mA(4700pF)

which one is correct ?
it depend on test equipment?

How to judge

How to obtain accurate result?

any comments are appreciated

Xing weibing
2002-06-25 17:56
  - Original Message -
  From: Peter Merguerian
  To: 'xingwb' ; Robert Johnson ; Peter Merguerian
  Cc: emc-p...@majordomo.ieee.org
  Sent: Tuesday, June 25, 2002 6:38 PM
  Subject: RE: TOUCH CURRENT LIMIT


  Xing,

  Yes, 0.25mA is very strict for 950. However, I can assure you that depeding on
the test lab and uncertainty of the test equipment, you will obtain slightly
different results.

  This e-mail message may contain privileged or confidential information. If you
are not the intended recipient, you may not disclose, use, disseminate,
distribute, copy or rely upon this message or attachment in any way. If you
received this e-mail message in error, please return by forwarding the message
and its attachments to the sender.







  PETER S. MERGUERIAN

  Technical Director

  I.T.L. (Product Testing) Ltd.

  26 Hacharoshet St., POB 211

  Or Yehuda 60251, Israel

  Tel: + 972-(0)3-5339022  Fax: + 972-(0)3-5339019

  Mobile: + 972-(0)54-838175

  http://www.itl.co.il

  http://www.i-spec.com




-Original Message-
From: xingwb [mailto:xin...@cesi.ac.cn]
Sent: Tuesday, June 25, 2002 11:13 AM
To: Robert Johnson; Peter Merguerian
Cc: emc-p...@majordomo.ieee.org
Subject: Re: TOUCH CURRENT LIMIT


Dear SIRS:

Thanks for your e-mail

A further question for touch current:

 Is it (0.25mA) strict for Class II equipment ?

0.28mA rms is OK FOR IEC60065
0.28mA rms is not OK for IEC60950


Any comments are appreciated


Best Regards

XING WEIBING
2002-06-25
  - Original Message -
  From: Peter Merguerian
  To: 'xingwb' ; emc-p...@majordomo.ieee.org
  Cc: Ilan Cohen ; Michael G ; Shmuel Gnatt ; Sima Beloborodov ; Valery
Rodionov
  Sent: Monday, June 24, 2002 9:00 PM
  Subject: RE: TOUCH CURRENT LIMIT


  Xing Hello!
  ake a look at IEC 60990, Methods of measurement of touch current and
protective conductor current. The limits in IEC 60 950 are based on this
particular standard.


  Best Regards

  This e-mail message may contain privileged or confidential information. If
you are not the intended recipient, you may not disclose, use, disseminate,
distribute, copy or rely upon this message or attachment in any way. If you
received this e-mail message in error, please return by forwarding the message
and its attachments to the sender.







  PETER S. MERGUERIAN

  Technical Director

  I.T.L. (Product Testing) Ltd.

  26 Hacharoshet St., POB 211

  Or Yehuda 60251, Israel

  Tel: + 972-(0)3-5339022  Fax: + 972-(0)3-5339019

  Mobile: + 972-(0)54-838175

  http://www.itl.co.il

  http://www.i-spec.com




-Original Message-
From: xingwb [mailto:xin...@cesi.ac.cn]
Sent: Monday, June 24, 2002 1:57 AM
To: emc-p...@majordomo.ieee.org
Cc: Rich Nute
Subject: TOUCH CURRENT LIMIT


Dear colleagues

I have a question regarding touch current limit of IEC 60950?

We can read from table 5A of IEC60950:1999:

Touch current limit for accessible parts and circuits not connected

to protective earth: 0.25 mA

question 1 : How does it (0.25mA) come from and what  it is based on?

based on IEC479? OR other source
why it is not 0.5mA(based on IEC60479)

question 2 :for hand-held equipment it is 0.75mA
why ?

Please shed some light for above questions


Any comments are appreciated

Best Regards


Xing weibing

2002-06-24



---

RE: TOUCH CURRENT LIMIT

2002-06-25 Thread Peter Merguerian
Xing,
 
Look up Annex D of the IEC 60950 standard. This annex gives you two
alternative methods for the measuring instrument (figures D.1 and D.2). 
 
Regards
 

This e-mail message may contain privileged or confidential information. If
you are not the intended recipient, you may not disclose, use, disseminate,
distribute, copy or rely upon this message or attachment in any way. If you
received this e-mail message in error, please return by forwarding the
message and its attachments to the sender.






PETER S. MERGUERIAN

Technical Director

I.T.L. (Product Testing) Ltd.

26 Hacharoshet St., POB 211

Or Yehuda 60251, Israel

Tel: + 972-(0)3-5339022  Fax: + 972-(0)3-5339019

Mobile: + 972-(0)54-838175

http://www.itl.co.il http://www.itl.co.il/ 

http://www.i-spec.com http://www.i-spec.com/ 



-Original Message-
From: xingwb [mailto:xin...@cesi.ac.cn]
Sent: Tuesday, June 25, 2002 11:57 AM
To: Peter Merguerian
Cc: emc-p...@majordomo.ieee.org
Subject: Re: TOUCH CURRENT LIMIT


Hi Mr. Peter:
 
 
Our test lab receive a CB TEST REPORT FOR NATIONAL RECOGNIZATION,
the EUT is a class II ac adapter having a bridging capacitor (4700pF)across
the reinforced insulation
 
The touch current measured by CB is 0.17mA(4700pF declared)
but the value we measure is 0.28mA(4700pF)
 
which one is correct ?
it depend on test equipment?
 
How to judge
 
How to obtain accurate result?
 
any comments are appreciated
 
Xing weibing
2002-06-25 17:56

- Original Message -  
From: Peter  mailto:pmerguer...@itl.co.il Merguerian 
To: 'xingwb' mailto:xin...@cesi.ac.cn  ; Robert
mailto:john...@itesafety.com Johnson ; Peter Merguerian
mailto:pmerguer...@itl.co.il  
Cc: emc-p...@majordomo.ieee.org mailto:emc-p...@majordomo.ieee.org  
Sent: Tuesday, June 25, 2002 6:38 PM
Subject: RE: TOUCH CURRENT LIMIT

Xing,
 
Yes, 0.25mA is very strict for 950. However, I can assure you that depeding
on the test lab and uncertainty of the test equipment, you will obtain
slightly different results.
 

This e-mail message may contain privileged or confidential information. If
you are not the intended recipient, you may not disclose, use, disseminate,
distribute, copy or rely upon this message or attachment in any way. If you
received this e-mail message in error, please return by forwarding the
message and its attachments to the sender.






PETER S. MERGUERIAN

Technical Director

I.T.L. (Product Testing) Ltd.

26 Hacharoshet St., POB 211

Or Yehuda 60251, Israel

Tel: + 972-(0)3-5339022  Fax: + 972-(0)3-5339019

Mobile: + 972-(0)54-838175

http://www.itl.co.il http://www.itl.co.il/ 

http://www.i-spec.com http://www.i-spec.com/ 



-Original Message-
From: xingwb [mailto:xin...@cesi.ac.cn]
Sent: Tuesday, June 25, 2002 11:13 AM
To: Robert Johnson; Peter Merguerian
Cc: emc-p...@majordomo.ieee.org
Subject: Re: TOUCH CURRENT LIMIT


Dear SIRS:
 
Thanks for your e-mail
 
A further question for touch current:
 
 Is it (0.25mA) strict for Class II equipment ?
 
0.28mA rms is OK FOR IEC60065
0.28mA rms is not OK for IEC60950
 
 
Any comments are appreciated
 
 
Best Regards
 
XING WEIBING
2002-06-25

- Original Message - 
From: Peter  mailto:pmerguer...@itl.co.il Merguerian 
To: 'xingwb' mailto:xin...@cesi.ac.cn  ; emc-p...@majordomo.ieee.org
mailto:emc-p...@majordomo.ieee.org  
Cc: Ilan Cohen mailto:ico...@itl.co.il  ; Michael G
mailto:micha...@itl.co.il  ; Shmuel  mailto:sgn...@itl.co.il Gnatt ;
Sima  mailto:si...@itl.co.il Beloborodov ; Valery Rodionov
mailto:vale...@itl.co.il  
Sent: Monday, June 24, 2002 9:00 PM
Subject: RE: TOUCH CURRENT LIMIT

Xing Hello!
ake a look at IEC 60990, Methods of measurement of touch current and
protective conductor current. The limits in IEC 60 950 are based on this
particular standard.
 
 
Best Regards
 

This e-mail message may contain privileged or confidential information. If
you are not the intended recipient, you may not disclose, use, disseminate,
distribute, copy or rely upon this message or attachment in any way. If you
received this e-mail message in error, please return by forwarding the
message and its attachments to the sender.






PETER S. MERGUERIAN

Technical Director

I.T.L. (Product Testing) Ltd.

26 Hacharoshet St., POB 211

Or Yehuda 60251, Israel

Tel: + 972-(0)3-5339022  Fax: + 972-(0)3-5339019

Mobile: + 972-(0)54-838175

http://www.itl.co.il http://www.itl.co.il 

http://www.i-spec.com http://www.i-spec.com/ 



-Original Message-
From: xingwb [mailto:xin...@cesi.ac.cn]
Sent: Monday, June 24, 2002 1:57 AM
To: emc-p...@majordomo.ieee.org
Cc: Rich Nute
Subject: TOUCH CURRENT LIMIT



Dear colleagues
 
I have a question regarding touch current limit of IEC 60950?
 
We can read from table 5A of IEC60950:1999:
 
Touch current limit for accessible parts and circuits not connected 
 
to protective earth: 0.25 mA
 
question 1 : How does it (0.25mA) come from and what  it is based on?
 
based on IEC479? OR other source
why it is not 0.5mA(based on IEC60479)
 
question 

Re: Environmental question

2002-06-25 Thread Scott Douglas

Muriel,

Don't know if there are any agency type regulations but can remember this 
issue came up when the government wanted to install a communications 
antenna in the north woods of Wisconsin. The antenna was to be used to 
communicate to submarines deep under water using something like 30 Hz or 60 
Hz radio waves. The antenna was a long (miles long) cable buried 
underground. There were many battles between the local citizens, various 
environmental and animal groups, and the government (US Navy?). If I recall 
correctly, there were even court cases trying to prevent the antenna from 
being installed. The concerns were related to what effect the RF would have 
on the environment to include plants and animals. Don't know for sure, but 
I believe the antenna was actually installed and was/is operating. Might be 
worth a look to see what came of that and to see what arguments were made 
pro/con. Might even be something came out of all that related to what you 
want to know.


Regards,
Scott

Senior Compliance Engineer
Narad Networks
515 Groton Road
Westford, MA 01886
office:  978 589-1869
cell: 978-239-0693
dougl...@naradnetworks.com
www.naradnetworks.com



At 06:13 PM 6/24/02 -0300, Muriel Bittencourt de Liz wrote:


Hello Group,

We already know the standards related to human exposure to electromagnetic
fields (e.g. ANSI/IEEE). However some people have asked us if there is any
standard/recommendations limiting the exposure of forests, lakes/rivers,
animals, etc to RF fields.

Do you know any FDA and EPA (or another agency) that regulate this subject
of RF fields incidence?

Example: Imagine a radio-base station (mobile comm) or antenna (TV or radio)
put in the middle of a forest, where there is not human habitation, but we
have animals, trees and waters. Is there any standard/recommendation related
to this case (only for non-ionizing radiation, ie, EM radiation).

Thanks in advance and Regards,

Muriel











RE: case of units

2002-06-25 Thread Chris Chileshe

Spot on Tom!

I have always stuck with lower case k - even when entering values
in a database which is all in upper case! Of course, this scientific
correctness lasts only a few days before someone spots my wonderful
room temperature components, dips them in liquid nitrogen and the
next thing I know they are all temperatures in Kelvin (10K)!!

I will admit though, to not putting any space between the number and the 
unit, but I remember the look my physics teacher used to give us if 
someone had the misfortune to call the unit degrees Kelvin instead of
plain Kelvin.

For your information http://physics.nist.gov/cuu/Units/
has it all.

Regards

- Chris



-Original Message-
From:   T.Sato [SMTP:vef00...@nifty.ne.jp]
Sent:   Tuesday, June 25, 2002 3:39 AM
To: emc-p...@majordomo.ieee.org
Subject:Re: case of units


On Mon, 24 Jun 2002 11:17:18 -0700,
  Robert Macy m...@california.com wrote:

 Still use KHz
 
 For me it's a logical carrier over from
 small letter = small value
 capital letter = large value

SI units are originally described in The International System of
Units (strictly, in French) from BIPM, and it states kilo is k,
not K.
Although they are very rarely used these days, h (hecto = 10^2)
and da (deca = 10^1) are written in small letters, too.

Regards,
Tom

--
Tomonori Sato  vef00...@nifty.ne.jp
URL: http://member.nifty.ne.jp/tsato/

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


This e-mail has been scanned for all viruses by Star Internet. The
service is powered by MessageLabs. For more information on a proactive
anti-virus service working around the clock, around the globe, visit:
http://www.star.net.uk



This e-mail has been scanned for all viruses by Star Internet. The
service is powered by MessageLabs. For more information on a proactive
anti-virus service working around the clock, around the globe, visit:
http://www.star.net.uk


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


RE: TOUCH CURRENT LIMIT

2002-06-25 Thread Peter Merguerian
Xing,
 
Yes, 0.25mA is very strict for 950. However, I can assure you that depeding
on the test lab and uncertainty of the test equipment, you will obtain
slightly different results.
 

This e-mail message may contain privileged or confidential information. If
you are not the intended recipient, you may not disclose, use, disseminate,
distribute, copy or rely upon this message or attachment in any way. If you
received this e-mail message in error, please return by forwarding the
message and its attachments to the sender.






PETER S. MERGUERIAN

Technical Director

I.T.L. (Product Testing) Ltd.

26 Hacharoshet St., POB 211

Or Yehuda 60251, Israel

Tel: + 972-(0)3-5339022  Fax: + 972-(0)3-5339019

Mobile: + 972-(0)54-838175

http://www.itl.co.il http://www.itl.co.il/ 

http://www.i-spec.com http://www.i-spec.com/ 



-Original Message-
From: xingwb [mailto:xin...@cesi.ac.cn]
Sent: Tuesday, June 25, 2002 11:13 AM
To: Robert Johnson; Peter Merguerian
Cc: emc-p...@majordomo.ieee.org
Subject: Re: TOUCH CURRENT LIMIT


Dear SIRS:
 
Thanks for your e-mail
 
A further question for touch current:
 
 Is it (0.25mA) strict for Class II equipment ?
 
0.28mA rms is OK FOR IEC60065
0.28mA rms is not OK for IEC60950
 
 
Any comments are appreciated
 
 
Best Regards
 
XING WEIBING
2002-06-25

- Original Message - 
From: Peter  mailto:pmerguer...@itl.co.il Merguerian 
To: 'xingwb' mailto:xin...@cesi.ac.cn  ; emc-p...@majordomo.ieee.org
mailto:emc-p...@majordomo.ieee.org  
Cc: Ilan Cohen mailto:ico...@itl.co.il  ; Michael G
mailto:micha...@itl.co.il  ; Shmuel Gnatt mailto:sgn...@itl.co.il  ;
Sima Beloborodov mailto:si...@itl.co.il  ; Valery Rodionov
mailto:vale...@itl.co.il  
Sent: Monday, June 24, 2002 9:00 PM
Subject: RE: TOUCH CURRENT LIMIT

Xing Hello!
ake a look at IEC 60990, Methods of measurement of touch current and
protective conductor current. The limits in IEC 60 950 are based on this
particular standard.
 
 
Best Regards
 

This e-mail message may contain privileged or confidential information. If
you are not the intended recipient, you may not disclose, use, disseminate,
distribute, copy or rely upon this message or attachment in any way. If you
received this e-mail message in error, please return by forwarding the
message and its attachments to the sender.






PETER S. MERGUERIAN

Technical Director

I.T.L. (Product Testing) Ltd.

26 Hacharoshet St., POB 211

Or Yehuda 60251, Israel

Tel: + 972-(0)3-5339022  Fax: + 972-(0)3-5339019

Mobile: + 972-(0)54-838175

http://www.itl.co.il http://www.itl.co.il 

http://www.i-spec.com http://www.i-spec.com/ 



-Original Message-
From: xingwb [mailto:xin...@cesi.ac.cn]
Sent: Monday, June 24, 2002 1:57 AM
To: emc-p...@majordomo.ieee.org
Cc: Rich Nute
Subject: TOUCH CURRENT LIMIT



Dear colleagues
 
I have a question regarding touch current limit of IEC 60950?
 
We can read from table 5A of IEC60950:1999:
 
Touch current limit for accessible parts and circuits not connected 
 
to protective earth: 0.25 mA
 
question 1 : How does it (0.25mA) come from and what  it is based on?
 
based on IEC479? OR other source
why it is not 0.5mA(based on IEC60479)
 
question 2 :for hand-held equipment it is 0.75mA
why ?
 
Please shed some light for above questions
 
 
Any comments are appreciated
 
Best Regards
 
 
Xing weibing
 
2002-06-24



Re: TOUCH CURRENT LIMIT

2002-06-25 Thread xingwb
Hi Mr. Peter:


Our test lab receive a CB TEST REPORT FOR NATIONAL RECOGNIZATION,
the EUT is a class II ac adapter having a bridging capacitor (4700pF)across the 
reinforced insulation

The touch current measured by CB is 0.17mA(4700pF declared)
but the value we measure is 0.28mA(4700pF)

which one is correct ?
it depend on test equipment?

How to judge

How to obtain accurate result?

any comments are appreciated

Xing weibing
2002-06-25 17:56
  - Original Message -  
  From: Peter Merguerian 
  To: 'xingwb' ; Robert Johnson ; Peter Merguerian 
  Cc: emc-p...@majordomo.ieee.org 
  Sent: Tuesday, June 25, 2002 6:38 PM
  Subject: RE: TOUCH CURRENT LIMIT


  Xing,

  Yes, 0.25mA is very strict for 950. However, I can assure you that depeding 
on the test lab and uncertainty of the test equipment, you will obtain slightly 
different results.

  This e-mail message may contain privileged or confidential information. If 
you are not the intended recipient, you may not disclose, use, disseminate, 
distribute, copy or rely upon this message or attachment in any way. If you 
received this e-mail message in error, please return by forwarding the message 
and its attachments to the sender.







  PETER S. MERGUERIAN

  Technical Director

  I.T.L. (Product Testing) Ltd.

  26 Hacharoshet St., POB 211

  Or Yehuda 60251, Israel

  Tel: + 972-(0)3-5339022  Fax: + 972-(0)3-5339019

  Mobile: + 972-(0)54-838175

  http://www.itl.co.il

  http://www.i-spec.com




-Original Message-
From: xingwb [mailto:xin...@cesi.ac.cn]
Sent: Tuesday, June 25, 2002 11:13 AM
To: Robert Johnson; Peter Merguerian
Cc: emc-p...@majordomo.ieee.org
Subject: Re: TOUCH CURRENT LIMIT


Dear SIRS:

Thanks for your e-mail

A further question for touch current:

 Is it (0.25mA) strict for Class II equipment ?

0.28mA rms is OK FOR IEC60065
0.28mA rms is not OK for IEC60950


Any comments are appreciated


Best Regards

XING WEIBING
2002-06-25
  - Original Message - 
  From: Peter Merguerian 
  To: 'xingwb' ; emc-p...@majordomo.ieee.org 
  Cc: Ilan Cohen ; Michael G ; Shmuel Gnatt ; Sima Beloborodov ; Valery 
Rodionov 
  Sent: Monday, June 24, 2002 9:00 PM
  Subject: RE: TOUCH CURRENT LIMIT


  Xing Hello!
  ake a look at IEC 60990, Methods of measurement of touch current and 
protective conductor current. The limits in IEC 60 950 are based on this 
particular standard.


  Best Regards

  This e-mail message may contain privileged or confidential information. 
If you are not the intended recipient, you may not disclose, use, disseminate, 
distribute, copy or rely upon this message or attachment in any way. If you 
received this e-mail message in error, please return by forwarding the message 
and its attachments to the sender.







  PETER S. MERGUERIAN

  Technical Director

  I.T.L. (Product Testing) Ltd.

  26 Hacharoshet St., POB 211

  Or Yehuda 60251, Israel

  Tel: + 972-(0)3-5339022  Fax: + 972-(0)3-5339019

  Mobile: + 972-(0)54-838175

  http://www.itl.co.il

  http://www.i-spec.com




-Original Message-
From: xingwb [mailto:xin...@cesi.ac.cn]
Sent: Monday, June 24, 2002 1:57 AM
To: emc-p...@majordomo.ieee.org
Cc: Rich Nute
Subject: TOUCH CURRENT LIMIT


Dear colleagues

I have a question regarding touch current limit of IEC 60950?

We can read from table 5A of IEC60950:1999:

Touch current limit for accessible parts and circuits not connected 

to protective earth: 0.25 mA

question 1 : How does it (0.25mA) come from and what  it is based on?

based on IEC479? OR other source
why it is not 0.5mA(based on IEC60479)

question 2 :for hand-held equipment it is 0.75mA
why ?

Please shed some light for above questions


Any comments are appreciated

Best Regards


Xing weibing

2002-06-24

Re: TOUCH CURRENT LIMIT

2002-06-25 Thread xingwb
Dear SIRS:

Thanks for your e-mail

A further question for touch current:

 Is it (0.25mA) strict for Class II equipment ?
 
0.28mA rms is OK FOR IEC60065
0.28mA rms is not OK for IEC60950


Any comments are appreciated


Best Regards

XING WEIBING
2002-06-25
  - Original Message - 
  From: Peter Merguerian 
  To: 'xingwb' ; emc-p...@majordomo.ieee.org 
  Cc: Ilan Cohen ; Michael G ; Shmuel Gnatt ; Sima Beloborodov ; Valery 
Rodionov 
  Sent: Monday, June 24, 2002 9:00 PM
  Subject: RE: TOUCH CURRENT LIMIT


  Xing Hello!
  ake a look at IEC 60990, Methods of measurement of touch current and 
protective conductor current. The limits in IEC 60 950 are based on this 
particular standard.


  Best Regards

  This e-mail message may contain privileged or confidential information. If 
you are not the intended recipient, you may not disclose, use, disseminate, 
distribute, copy or rely upon this message or attachment in any way. If you 
received this e-mail message in error, please return by forwarding the message 
and its attachments to the sender.







  PETER S. MERGUERIAN

  Technical Director

  I.T.L. (Product Testing) Ltd.

  26 Hacharoshet St., POB 211

  Or Yehuda 60251, Israel

  Tel: + 972-(0)3-5339022  Fax: + 972-(0)3-5339019

  Mobile: + 972-(0)54-838175

  http://www.itl.co.il

  http://www.i-spec.com




-Original Message-
From: xingwb [mailto:xin...@cesi.ac.cn]
Sent: Monday, June 24, 2002 1:57 AM
To: emc-p...@majordomo.ieee.org
Cc: Rich Nute
Subject: TOUCH CURRENT LIMIT


Dear colleagues

I have a question regarding touch current limit of IEC 60950?

We can read from table 5A of IEC60950:1999:

Touch current limit for accessible parts and circuits not connected 

to protective earth: 0.25 mA

question 1 : How does it (0.25mA) come from and what  it is based on?

based on IEC479? OR other source
why it is not 0.5mA(based on IEC60479)

question 2 :for hand-held equipment it is 0.75mA
why ?

Please shed some light for above questions


Any comments are appreciated

Best Regards


Xing weibing

2002-06-24

Reminder - Joint EMC NPSS Meeting Tomorrow, June 26th

2002-06-25 Thread Matt Campanella

All,

Our joint NPSS and EMC Society meeting tomorrow, June 26th, features two
speakers.  Due to the extensive technical program, the social hour with
light refreshments will begin at 6:30 PM and the technical meeting will
start at 7:00 PM.   The joint meeting will be held at EMC Corporation's
Customer Briefing Center in Hopkinton, MA.  The first technical
presentation will start at 7:00 PM with a 45 minute expected duration.
Our second technical presentation will start around 7:45 PM or
immediately after any questions for our first speaker.

Doug Smith, IEEE EMC Society Distinguished Lecturer, will present this
month’s first topic concerning Computer Security for the Engineer, 'The
Knock in the Middle of the Night'.  What is the worst thing that can
happen to your computer?  It may be much worse than just losing your
files or having them posted on the Internet for all to see.  Doug’s talk
will cover some of the things that can happen and how to avoid them.
Screen shots from an attack on Doug's computer will be shown to
illustrate some of the things that can happen.  The remote diagnosis
feature provided by many laptop manufacturers, including Doug's, leaves
them wide open to attack from hackers.  During a recent trip, that
weakness was probed 4 times in 2 hours over a dialup by hackers!   Bring
your laptop with a modem and check it out real time.  As food for
thought, a recording of the emissions from Doug's home computer as heard
on a short-wave radio will be played to show that different computer
activities, such as surfing the Internet and printing, can be
identified.

Vincent DeGiorgio, Senior Risk Consultant for ArupRisk Consulting will
be presenting this month’s second technical topic concerning the risk
assessment process and it’s application.  Risk can be found everywhere
such as when you are driving your car, entering your place of work or
taking an airplane flight to start your vacation.  By definition risk is
a measure of the potential for loss in terms of both the likelihood
(events/year) of the incident and the consequences (effects/event) of
the incident.  In order to measure the level of risk, a systemic
approach known as the risk assessment process is employed.  This process
can be used to assess a wide range of risks related to facilities,
equipment, seismic, 911, etc.  This presentation will examine the risk
assessment process and see how it can be applied to address risks that
may be of concern to you.

The 2002 NPSS meeting schedule is available on the NPSS website at
http://www.nepss.org/meetings/npss2002kf.html.

Further information about the Northeast Product Safety Society and how
to become a member is available at http://www.nepss.org.  You can also
contact one of the NPSS officers via links at
http://www.nepss.org/secretary/officerskf.html.

Directions:
From Route 495 North or South take exit 21B to South Street.
At the first traffic light, turn left (Note: This is on South direction
side of Route 495).
EMC Corporation is the second driveway on the right.


Matt Campanella
   NPSS Secretary

Compliance Engineer
Motorola, Inc.
Broadband Communications Sector
3 Highwood Drive East
Tewksbury, MA 01876

(978) 858-2303   Direct
(978) 858-2300   Main
(978) 858-2399   Fax

matthew.campane...@motorola.com  email









---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


Re: case of units

2002-06-25 Thread Wan Juang Foo


Dear all,
The capital W is probably a font translation error that was not spotted.  I
had much heart ache over this whenever I print something in a different
computer.   I have had much experience with entire documents that have the
greek lower case m (micro=u=greak mu) being subsituted for a plain lower
case m etc...  It is very frustrating.

This bring to mind a similar and more widely use practice in marking
electrolytic capacitors e.g. 10mfd instead of 10uF.  It is oblivious to the
experienced engineer, mfd is read as micro Farad knowing that the mili
Farad component is probably the size of a chair!  I wonder if this will
catch any technical types by surprise.
:-)

Tim Foo





  Cortland Richmond 

  72146.373@compuserve. To:  Brent DeWitt 
bdew...@ix.netcom.com, ieee pstc list
  com   emc-p...@ieee.org

  Sent by:   cc:  (bcc: Wan Juang 
Foo/ece/staff/npnet)  
  owner-emc-pstc@majordo Subject: Re: case of units 

  mo.ieee.org   





  06/25/02 01:53 PM 

  Please respond to 

  Cortland Richmond 










Another interesting thing -- not the same as this -- is what happens to
the upper-case Omega some documents use instead of spelling out ohms;
some software turns it into W. I could have SWORN I'd see a 1000 W
resistor on a modem card!

Cortland










---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


Re: case of units

2002-06-25 Thread Cortland Richmond

Another interesting thing -- not the same as this -- is what happens to
the upper-case Omega some documents use instead of spelling out ohms;
some software turns it into W. I could have SWORN I'd see a 1000 W
resistor on a modem card! 

Cortland

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


Re: Class 2 Power Unit

2002-06-25 Thread John Barnes

Brian,
The short answer is that a Class 2 Power Unit is what we would
normally call a wall wart or a brick power supply.

Clause 1.1 of UL 1310 (August 21, 1992) says:
These requirements cover (1) direct plug-in Class 2 power units
intended for connection to a 15-ampere nominal 120- or 240-volt ac
branch circuit, and (2) cord-connected Class 2 power units intended for
connection to a 15- or 20-ampere ac branch circuit with a potential of
150 volts or less to ground.  These products utilize an isolating
transformer and may incorporate rectifiers and other components to
provide a source of alternating- or direct-current supply.  These
products provide Class 2 power levels in accordance with the National
Electrical Code, and are intended primarily to provide power to low
voltage, electrically operated devices.

Other clauses in the Scope say that UL 1310 does not cover:
*  Products whose input power could exceed 660W.
*  Battery chargers for charging engine-starting batteries.
*  Power supplies for toys.
*  Products with other than Class 2 outputs.
*  Battery chargers to charge batteries for wheelchairs and other 
   mobility aids.
*  Class 2 transformers intended for field connection (i.e. bell 
   transformers).

Section 725 of the National Electrical Code (NEC) covers Class 1, Class
2, and Class 3 Remote-Control, Signalling, and Power-Limited Circuits. 
The Scope in 725-1 says that (these) are not an integral part of a 
device or appliance.  The Definition in 725-2 says Due to its power
limitations, a Class 2 circuit considers safety from a fire initiation
standpoint and provides acceptable protection from electric shock.

Chapter 9, Tables 11(a) and 11(b) of the NEC show:
*  Class 2 ac source is limited to:
   -  For 0 to 20V output,  8A output under any load conditions, with
  a nameplate rating  5*Vmax volt-amps and  5.0 Amps.
   -  For 20 to 30V output,  8A output under any load conditions, with
  a nameplate rating  100 volt-amps and  100/Vmax Amps.
   -  For 30 to 150V output,  0.005A output under any load conditions, 
  with a nameplate rating  0.005*Vmax volt-amps and  0.005 Amps.
*  Class 2 dc source is limited to:
   -  For 0 to 20V output,  8A output under any load conditions, with
  a nameplate rating  5*Vmax volt-amps and  5.0 Amps.
   -  For 20 to 30V output,  8A output under any load conditions, with
  a nameplate rating  100 volt-amps and  100/Vmax Amps.
   -  For 30 to 60V output,  150/Vmax output under any load conditions, 
  with a nameplate rating  100 volt-amps and  100/Vmax Amps.

John Barnes
dBi Corporation

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


RE: TOUCH CURRENT LIMIT

2002-06-25 Thread Robert Johnson
The history is lost in committee activities from years ago, but I can
provide my own thoughts.

The limit for accessible parts on circuits not connected to protective
earth is set below the threshold of sensation, since that current is
likely to pass through the user in normal use if he touches the part.

The limit for hand held equipment is set low enough that if the earth
path fails, the resulting shock is not likely to cause someone to drop
what they are holding.

Note that the higher limits of 3.5 ma for the general case can provide a
substantial but not harmful shock under single fault conditions.

 

Bob Johnson

ITE http://www.itesafety.com/  Safety

 

-Original Message-
From: owner-emc-p...@majordomo.ieee.org
[mailto:owner-emc-p...@majordomo.ieee.org] On Behalf Of xingwb
Sent: Sunday, June 23, 2002 7:57 PM
To: emc-p...@majordomo.ieee.org
Cc: Rich Nute
Subject: TOUCH CURRENT LIMIT

 

Dear colleagues

 

I have a question regarding touch current limit of IEC 60950?

 

We can read from table 5A of IEC60950:1999:

 

Touch current limit for accessible parts and circuits not connected 

 

to protective earth: 0.25 mA

 

question 1 : How does it (0.25mA) come from and what  it is based on?

 

based on IEC479? OR other source

why it is not 0.5mA(based on IEC60479)

 

question 2 :for hand-held equipment it is 0.75mA

why ?

 

Please shed some light for above questions

 

 

Any comments are appreciated

 

Best Regards

 

 

Xing weibing

 

2002-06-24

attachment: Robert Johnson.vcf

Re: case of units

2002-06-25 Thread T.Sato

On Mon, 24 Jun 2002 11:17:18 -0700,
  Robert Macy m...@california.com wrote:

 Still use KHz
 
 For me it's a logical carrier over from
 small letter = small value
 capital letter = large value

SI units are originally described in The International System of
Units (strictly, in French) from BIPM, and it states kilo is k,
not K.
Although they are very rarely used these days, h (hecto = 10^2)
and da (deca = 10^1) are written in small letters, too.

Regards,
Tom

--
Tomonori Sato  vef00...@nifty.ne.jp
URL: http://member.nifty.ne.jp/tsato/

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


Re: Environmental question

2002-06-25 Thread Jacob Schanker

Muriel:

I know of no such standards or recommendations. Unfortunately, if you could
think to ask the question, someone else is eventually going to think that
there should be such recommendations or regulations.

Considering that the forest, lakes, land are bombarded with 1 kW per square
meter of solar radiation, I would think that radiation from cell towers,
broadcast towers, etc, is almost totally insignificant in comparison.

I think that perhaps the rain forest is more threatened by other factors
than by RF.

You asked an interesting question, is there some particular reason why you
asked?

Regards,

Jacob Z. Schanker, P.E.
65 Crandon Way
Rochester, NY 14618
Phone: 585 442 3909
Fax: 585 442 2182
j.schan...@ieee.org


- Original Message -
From: Muriel Bittencourt de Liz mur...@eel.ufsc.br
To: Lista de EMC da IEEE emc-p...@ieee.org
Sent: Monday, June 24, 2002 5:13 PM
Subject: Environmental question


|
| Hello Group,
|
| We already know the standards related to human exposure to electromagnetic
| fields (e.g. ANSI/IEEE). However some people have asked us if there is any
| standard/recommendations limiting the exposure of forests, lakes/rivers,
| animals, etc to RF fields.
|
| Do you know any FDA and EPA (or another agency) that regulate this subject
| of RF fields incidence?
|
| Example: Imagine a radio-base station (mobile comm) or antenna (TV or
radio)
| put in the middle of a forest, where there is not human habitation, but we
| have animals, trees and waters. Is there any standard/recommendation
related
| to this case (only for non-ionizing radiation, ie, EM radiation).
|
| Thanks in advance and Regards,
|
| Muriel
|
|
|
|
|
|
| ---
| This message is from the IEEE EMC Society Product Safety
| Technical Committee emc-pstc discussion list.
|
| Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/
|
| To cancel your subscription, send mail to:
|  majord...@ieee.org
| with the single line:
|  unsubscribe emc-pstc
|
| For help, send mail to the list administrators:
|  Ron Pickard:  emc-p...@hypercom.com
|  Dave Heald:   davehe...@attbi.com
|
| For policy questions, send mail to:
|  Richard Nute:   ri...@ieee.org
|  Jim Bacher: j.bac...@ieee.org
|
| All emc-pstc postings are archived and searchable on the web at:
| http://ieeepstc.mindcruiser.com/
| Click on browse and then emc-pstc mailing list
|



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


Re: case of units

2002-06-25 Thread Doug McKean

Don, you're probably right in that it went the other way. 
My super and I had quite a laugh about it till some poor 
purchaser told us what was up.  - Doug McKean 



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


Units, symbols

2002-06-25 Thread Chuck Mullett

Hi folks,

I'm glad this subject came up, and am glad to offer some help.  The
subject of these units, notations, etc. has fascinated me for years, and
finally I set about to get to the authoritative sources.  Over the past
couple of years, I've done the research and published the results.

Here are two documents that I'm sure will be helpful.  There is NO
original information here---it's all from well-recognized, world-class
authorities.  You'll find these conventions followed by most of the
international companies that publish respected catalogs and technical
brochures, such as Agilent, Tektronix, and others.  These companies have
obviously looked up the standards, as I have, and put them to practice.
Because they are instrument companies, they deal with almost every
electrical unit in existence.

One important caution:  Don't assume that what you see in print (trade
press ads, articles, papers, etc.) is correct.  Much has been written in
ignorance of these standards, simply because the editors aren't aware
that international standards exist.

The first publication, Units, Symbols and Style Guide, is available
from the Power Sources Manufacturers Association.  It's a heavy-weight,
coated-paper card with index tab and three-hole punch, for use in
three-ring binders.  See the PSMA Web site, psma.com.  You can buy
copies, but here's the text---free.

The second one, Writing Guide, has not been formally published.  I
wrote it after realizing that there were some common errors that weren't
covered in the Units, Symbols, and Style Guide.  Once you are familiar
with the units conventions (i.e. Capitalize the symbols such as V, A, Hz
and don't capitalize the units in text such as hertz, volts, amperes,
even though they are names), the one page Writing Guide is about all you
need to hang on your wall.

Comments welcome.

Chuck Mullett, P.E.
Chairman, Power Sources Manufacturers Association


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list