Re: [PSES] fire safety test methods for different country standards

2016-06-10 Thread Ralph McDiarmid
: Thursday, June 09, 2016 6:00 AM To: EMC-PSTC@LISTSERV.IEEE.ORG Subject: Re: [PSES] fire safety test methods for different country standards Ralph, This might be true but that is not how we saw it way back when. The 240VA "Energy Hazard" was not a consideration for the protection ag

Re: [PSES] fire safety test methods for different country standards

2016-06-09 Thread Richard Nute
> This is my recollection of where 240VA came from and > how it was used. In a 1966 UL meeting with industry on the requirements in UL 478, the minutes report: "Where high current is available at potentials down to about 2 volts, enough energy is available to melt and splatter metal from neck

Re: [PSES] fire safety test methods for different country standards

2016-06-09 Thread Richard Nute
> The 240VA "Energy Hazard" was not a > consideration for the protection against Fire but a limit > value for accessible parts by the User. The energy hazard requirement (in the 950-series standards) is that the conductors shall not be bridged by the test finger (which has a spherical tip). If

Re: [PSES] fire safety test methods for different country standards

2016-06-09 Thread Kunde, Brian
2016 3:11 PM To: EMC-PSTC@LISTSERV.IEEE.ORG Subject: Re: [PSES] fire safety test methods for different country standards Hi Chuck, A poor choice of words on my part. I should have written, "in most of the standards I have worked in". Those include CSA107.1, UL1741, UL1012, and IEC62

Re: [PSES] fire safety test methods for different country standards

2016-06-08 Thread Richard Nute
> The 15W is the *dissipated* power level to determine if > PIS. The standard is somewhat ambiguous because it uses > the term 'location' in definition, but 'circuit' in 6.2. Well... the intent was the maximum power available into a fault. Rich -

Re: [PSES] fire safety test methods for different country standards

2016-06-08 Thread Brian O'Connell
-PSTC@LISTSERV.IEEE.ORG Subject: Re: [PSES] fire safety test methods for different country standards > Example: I measure and determine that an electrolytic > capacitor temperature is compliant with the standard, but > what happens when that capacitor eventually fails due to > large ri

Re: [PSES] fire safety test methods for different country standards

2016-06-08 Thread Richard Nute
> Example: I measure and determine that an electrolytic > capacitor temperature is compliant with the standard, but > what happens when that capacitor eventually fails due to > large ripple current and then overheats and catches fire. > That's a single fault condition (a component fault), but

Re: [PSES] fire safety test methods for different country standards

2016-06-08 Thread Ralph McDiarmid
PM To: Ralph McDiarmid <ralph.mcdiar...@schneider-electric.com> Cc: EMC-PSTC@LISTSERV.IEEE.ORG Subject: RE: [PSES] fire safety test methods for different country standards Tried a flint and steel recently? Lots of history! >-Original Message- >From: Ralph McDiarmid [mailto:

Re: [PSES] fire safety test methods for different country standards

2016-06-08 Thread Brian O'Connell
@LISTSERV.IEEE.ORG Subject: Re: [PSES] fire safety test methods for different country standards > So, for the protection against FIRE, we have two energy > rates, 100VA and 240VA, used across quite a number of > standards, and the units are wrong. Should be Watts. Agree. But, for pessimis

Re: [PSES] fire safety test methods for different country standards

2016-06-08 Thread Richard Nute
> So, for the protection against FIRE, we have two energy > rates, 100VA and 240VA, used across quite a number of > standards, and the units are wrong. Should be Watts. Agree. But, for pessimism, use VA. My experience and tests show that a product fire can be started by 15 watts! The

Re: [PSES] fire safety test methods for different country standards

2016-06-08 Thread Richard Nute
> " Safety standards are not tested to see if they accomplish > the objective" > > I'm not sure how one would go about doing that, other > than gathering data from customer returns and from > product recalls. All safety standards include means to determine if the product complies with the

Re: [PSES] fire safety test methods for different country standards

2016-06-08 Thread Brian O'Connell
- From: Ralph McDiarmid [mailto:ralph.mcdiar...@schneider-electric.com] Sent: Wednesday, June 08, 2016 1:31 PM To: EMC-PSTC@LISTSERV.IEEE.ORG Subject: Re: [PSES] fire safety test methods for different country standards So, for the protection against FIRE, we have two energy rates, 100VA and 240VA

Re: [PSES] fire safety test methods for different country standards

2016-06-08 Thread John Woodgate
ERV.IEEE.ORG >Subject: Re: [PSES] fire safety test methods for different country standards > To >assume a prototype or two accurately represents a field population of say >10,000 >units is an act of faith, and hoping that the odds are with you. > >Ralph McDiarmid >Product Com

Re: [PSES] fire safety test methods for different country standards

2016-06-08 Thread John Woodgate
Tried a flint and steel recently? Lots of history! >-Original Message- >From: Ralph McDiarmid [mailto:ralph.mcdiar...@schneider-electric.com] >Sent: Wednesday, June 8, 2016 5:27 PM >To: EMC-PSTC@LISTSERV.IEEE.ORG >Subject: Re: [PSES] fire safety test methods for di

Re: [PSES] fire safety test methods for different country standards

2016-06-08 Thread Ralph McDiarmid
C-PSTC@LISTSERV.IEEE.ORG Subject: Re: [PSES] fire safety test methods for different country standards Hi Chuck, A poor choice of words on my part. I should have written, "in most of the standards I have worked in". Those include CSA107.1, UL1741, UL1012, and IEC62109-1 The 240VA (I think they

Re: [PSES] fire safety test methods for different country standards

2016-06-08 Thread Nyffenegger, Dave
: [PSES] fire safety test methods for different country standards > Not following instructions is foreseeable misuse... Depends. I define "misuse" as using the product for some use other than its intended use. Standing on a chair is misuse of the chair. Misuse (my defin

Re: [PSES] fire safety test methods for different country standards

2016-06-08 Thread Nyffenegger, Dave
Subject: Re: [PSES] fire safety test methods for different country standards Hi Chuck, A poor choice of words on my part. I should have written, "in most of the standards I have worked in". Those include CSA107.1, UL1741, UL1012, and IEC62109-1 The 240VA (I think they meant 240W) must

Re: [PSES] fire safety test methods for different country standards

2016-06-08 Thread Ralph McDiarmid
ri...@ieee.org] Sent: Sunday, May 22, 2016 2:39 PM To: EMC-PSTC@LISTSERV.IEEE.ORG Subject: Re: [PSES] fire safety test methods for different country standards Our most common and serious safety issue is that of product electrically-caused fire. I subscribe to "In Compliance" weekly recal

Re: [PSES] fire safety test methods for different country standards

2016-06-08 Thread Richard Nute
240 VA (not W) is defined as "energy hazard" in UL/IEC 60950 and its predecessors, UL 950 and UL 478. "Energy hazard" only applies if the potential is 2 V or more. (The dimension for energy is the Joule, not the volt-ampere.) The standards state: "A risk of injury due to an energy

Re: [PSES] fire safety test methods for different country standards

2016-06-08 Thread Kunde, Brian
.@schneider-electric.com] Sent: Wednesday, June 08, 2016 3:11 PM To: EMC-PSTC@LISTSERV.IEEE.ORG Subject: Re: [PSES] fire safety test methods for different country standards Hi Chuck, A poor choice of words on my part. I should have written, "in most of the standards I have worked in".

Re: [PSES] fire safety test methods for different country standards

2016-06-08 Thread Ralph McDiarmid
uck August-McDowell [mailto:chu...@meyersound.com] Sent: Wednesday, June 08, 2016 11:22 AM To: Ralph McDiarmid <ralph.mcdiar...@schneider-electric.com> Subject: RE: [PSES] fire safety test methods for different country standards Hi Ralph, I live in the IEC/EN/UL 60065 standard world. Could yo

Re: [PSES] fire safety test methods for different country standards

2016-06-08 Thread Richard Nute
> Not following instructions is foreseeable misuse... Depends. I define "misuse" as using the product for some use other than its intended use. Standing on a chair is misuse of the chair. Misuse (my definition) cannot be foreseeable because it depends on what the user needs to do (and has

Re: [PSES] fire safety test methods for different country standards

2016-06-08 Thread Ralph McDiarmid
- From: Richard Nute [mailto:ri...@ieee.org] Sent: Sunday, May 22, 2016 5:40 PM To: EMC-PSTC@LISTSERV.IEEE.ORG Subject: Re: [PSES] fire safety test methods for different country standards Hi John: Thanks for your additional comments. > Could it be that the scenarios which the standa

Re: [PSES] fire safety test methods for different country standards

2016-05-22 Thread John Woodgate
11:11 PM > To: EMC-PSTC@LISTSERV.IEEE.ORG > Subject: Re: [PSES] fire safety test methods for different country standards > > Rich. > > Could it be that the scenarios which the standards committees envisage are not > "the real deal", OR that the products

Re: [PSES] fire safety test methods for different country standards

2016-05-22 Thread Richard Nute
Hi John: Thanks for your additional comments. > Could it be that the scenarios which the standards > committees envisage are not "the real deal" In my opinion, this is the case. > OR that the > products which cause the fires just don't comply with the > standards? Of course, counterfeit and

Re: [PSES] fire safety test methods for different country standards

2016-05-22 Thread John Allen
2:39 To: EMC-PSTC@LISTSERV.IEEE.ORG Subject: Re: [PSES] fire safety test methods for different country standards Our most common and serious safety issue is that of product electrically-caused fire. I subscribe to "In Compliance" weekly recall notices; most are fire. As Ge

Re: [PSES] fire safety test methods for different country standards

2016-05-22 Thread Richard Nute
Our most common and serious safety issue is that of product electrically-caused fire. I subscribe to "In Compliance" weekly recall notices; most are fire. As Gert Gremmen has stated, no fault-testing has resulted in a product fire in the test lab, yet product fires continue to occur in the

Re: [PSES] fire safety test methods for different country standards

2016-05-22 Thread Ted Eckert
@LISTSERV.IEEE.ORG Subject: Re: [PSES] fire safety test methods for different country standards Gert In many instances I think you are probably on the right track - but mainly w.r.t. to 61010 kit for professional / semi-professional use, as opposed to 60950 where a lot of the kit certified

Re: [PSES] fire safety test methods for different country standards

2016-05-22 Thread John Allen
RG Subject: Re: [PSES] fire safety test methods for different country standards I was wondering if these type of fire propagation tests are still of any relevance. Nowadays most electronic designs have been built with compliant (be it UL or VDE or any other reputable test house) and wir

Re: [PSES] fire safety test methods for different country standards

2016-05-22 Thread ce-test, qualified testing bv - Gert Gremmen
E.ORG Subject: Re: [PSES] fire safety test methods for different country standards Hi Scott: “In general, the users and testing houses are referring to the rating of UL yellow card rather than the actual test on individual final designed pcb.   Should we use it to object their normal pra

Re: [PSES] fire safety test methods for different country standards

2016-05-21 Thread Richard Nute
Hmm. Thanks to Ted Eckert, the small tablet may have been methenamine. Rich - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your

Re: [PSES] fire safety test methods for different country standards

2016-05-21 Thread Richard Nute
Thanks, Brian. I recall now. I used hexamine tablets. I used two sizes, one about ½ inch diameter and ¼ inch thick, and the other about the size of an aspirin tablet. I placed the hexamine on top of the component I expected to catch fire, ignite the pellet, put the enclosure back on,

Re: [PSES] fire safety test methods for different country standards

2016-05-21 Thread Ted Eckert
reflect those of my employer. From: Brian O'Connell [mailto:oconne...@tamuracorp.com] Sent: Saturday, May 21, 2016 3:51 PM To: EMC-PSTC@LISTSERV.IEEE.ORG Subject: Re: [PSES] fire safety test methods for different country standards Rich, Congratulations on your IEEE Fellow appointment. Do we

Re: [PSES] fire safety test methods for different country standards

2016-05-21 Thread Brian O'Connell
by igniting several bars in sealed chamber, then marching the troops in to subsequently remove their masks to sing our ‘tribal song’. Brian From: Richard Nute [mailto:ri...@ieee.org] Sent: Saturday, May 21, 2016 10:32 AM To: EMC-PSTC@LISTSERV.IEEE.ORG Subject: Re: [PSES] fire safety test methods

Re: [PSES] fire safety test methods for different country standards

2016-05-21 Thread John Woodgate
EE.ORG; 'John Woodgate' <jmw1...@btinternet.com> Subject: RE: [PSES] fire safety test methods for different country standards BTW: if that “safety expert” had looked closer, I think he would have found that something like 60065 would have been far more difficult with which to comply than

Re: [PSES] fire safety test methods for different country standards

2016-05-21 Thread John Allen
[mailto:john_e_al...@blueyonder.co.uk] Sent: 21 May 2016 20:44 To: EMC-PSTC@LISTSERV.IEEE.ORG Subject: Re: [PSES] fire safety test methods for different country standards John Re “I had an enquiry once as to whether IEC 60065 could be applied to a 10 kW industrial fan heater, because

Re: [PSES] fire safety test methods for different country standards

2016-05-21 Thread John Allen
From: John Allen [mailto:john_e_al...@blueyonder.co.uk] Sent: Saturday, May 21, 2016 7:47 PM To: EMC-PSTC@LISTSERV.IEEE.ORG Subject: Re: [PSES] fire safety test methods for different country standards Rich With respect to actual testing of the materials in the enclosure, that was also

Re: [PSES] fire safety test methods for different country standards

2016-05-21 Thread John Woodgate
ct: Re: [PSES] fire safety test methods for different country standards Rich With respect to actual testing of the materials in the enclosure, that was also impractical because there was (still is) a wide range of lengths and diameters, which were always very well populated because the

Re: [PSES] fire safety test methods for different country standards

2016-05-21 Thread John Allen
was adequate – and we were! John E Allen W. London, UK From: Richard Nute [mailto:ri...@ieee.org] Sent: 21 May 2016 18:32 To: 'John Allen'; EMC-PSTC@LISTSERV.IEEE.ORG Subject: RE: [PSES] fire safety test methods for different country standards Hi John: Thanks for your comments

Re: [PSES] fire safety test methods for different country standards

2016-05-21 Thread Richard Nute
Hi John: Thanks for your comments. In the end, the “solution” was a different sort of pragmatic approach because the boards were always enclosed in hermetically sealed high pressure (10,000 psi+) / temperature (180C+) -resistant stainless steel tubes which have very little

Re: [PSES] fire safety test methods for different country standards

2016-05-21 Thread Richard Nute
Hi Scott: “In general, the users and testing houses are referring to the rating of UL yellow card rather than the actual test on individual final designed pcb. Should we use it to object their normal practice. How often is it successful?” Testing in place is a

Re: [PSES] fire safety test methods for different country standards

2016-05-21 Thread John Allen
@LISTSERV.IEEE.ORG Subject: Re: [PSES] fire safety test methods for different country standards In my last job I tried to do something similar w.r.t. PWB materials for applications where V-1 or better materials aren’t any good because the retardants result in reduced service lives

Re: [PSES] fire safety test methods for different country standards

2016-05-20 Thread Scott Xe
Hi Rich, Thanks for your sharing experience! In general, the users and testing houses are referring to the rating of UL yellow card rather than the actual test on individual final designed pcb. Should we use it to object their normal practice. How often is it successful? Regards, Scott

Re: [PSES] fire safety test methods for different country standards

2016-05-20 Thread Richard Nute
In my last job I tried to do something similar w.r.t. PWB materials for applications where V-1 or better materials aren’t any good because the retardants result in reduced service lives in hostile equipment environments, whereas some specific (and very special!) HB materials last much

Re: [PSES] fire safety test methods for different country standards

2016-05-19 Thread Adam Dixon
ld lead you to UL > 723 (ASTM E84) amongst other things > > > > John E Allen > > > > *From:* John Allen [mailto:john_e_al...@blueyonder.co.uk] > *Sent:* 19 May 2016 18:31 > *To:* 'Adam Dixon'; 'EMC-PSTC@LISTSERV.IEEE.ORG' > *Subject:* RE: [PSES] fire s

Re: [PSES] fire safety test methods for different country standards

2016-05-19 Thread John Allen
for assessing the fire hazard of electrotechnical products – General guidelines” John E Allen. W.London, UK From: Adam Dixon [mailto:lanterna.viri...@gmail.com] Sent: 19 May 2016 13:44 To: EMC-PSTC@LISTSERV.IEEE.ORG Subject: [PSES] fire safety test methods for different country standards

Re: [PSES] fire safety test methods for different country standards

2016-05-19 Thread John Allen
of electrotechnical products – General guidelines” John E Allen. W.London, UK From: Adam Dixon [mailto:lanterna.viri...@gmail.com] Sent: 19 May 2016 13:44 To: EMC-PSTC@LISTSERV.IEEE.ORG Subject: [PSES] fire safety test methods for different country standards Apart from purchasing multiple standards

[PSES] fire safety test methods for different country standards

2016-05-19 Thread Adam Dixon
Apart from purchasing multiple standards, are there reference materials that may guide preliminary in-house fire safety testing (flame spread) for materials categorized as building components? I have come across summary descriptions of multiple test standards (BS476, ISO9705, ISO5660, DIN-4102,