2002-10-25 Thread Ken Javor

I investigated the phenomenon of capacitor damage by transients and found 
caps to be very resistant to damage from short duration, especially high
source impedance (50 Ohm) spikes.  There is a complete write up entitled,
Investigation Into the Effects of Microsecond Power Line Transients on
Line-Connected Capacitors NASA/CR-2000-209906 at:

http://see.msfc.nasa.gov/

As I write this, I cannot access the site and get you the precise page it is
on, but it is usually accessible to the public (a pdf download).  I also
have the original in MS Word that I can send if necessary.



--
From: Chris Chileshe chris.chile...@ultronics.com
To: 'EMC-PSTC List' emc-p...@majordomo.ieee.org
Subject: Baffled by EFT test results (EN61000-4-4)
Date: Fri, Oct 25, 2002, 6:55 AM



 Hi Group,

 So I went ahead and built a test PCB with my inductors and ferrites in PI
 filter formation with capacitors - just like I threatened to do a few months
 ago ( e-mail subject header Designing for low power radiated and conducted
 immunity describing a small 3-wire low power DC pressure sensor).

 The analog circuit simulating a pressure sensor is simply a 5V regulator
 (LP2985) supplying a AD623 IN-amp monitoring the differential voltage across a
 wheatstone bridge (4k7) connected to the same 5V rail. The output then
 simply connects to an Avometer (through a PI filter of course). A variant of
the
 test PCB doesn't even have the regulator. It is that simple.

 I took the PCB through radiated immunity testing to EN 61000-4-3 and met
 100V/m, and through conducted immunity testing to EN 61000-4-6 and met
 the 10V level.  All tests were done with unscreened cable. I also proved the
 protected circuit was susceptible when the filter was removed.

 Having decided I had sized my inductors, ferrites and caps appropriately,
 and done the PCB layout correctly, I then proceeded to add small SMT varistors
 for transients to EN 61000-4-4. The test PCB was again good for 2kV. I
 then shuffled the relative positions of the varistors in the circuit
 (initially pre-
 PI filter, then post PI filter ) and it didn't seem to make any difference.
The
 idea was to get some permutations of varistor location and then repeat the
 RF immunity tests in case the varistors introduced susceptibility (an
 observation I have made in the past).

 I then took the varistors off the board altogether and still the PCB meets the
 2kV stress levels ( I am using the levels of EN 61000-6-2 ). I am not
 too keen to raise the stakes to 4kV just now because there are more tests
 I would like to perform on the PCB before I let it go up in smoke.

 This is probably the first time I have seen anything get through transients
 testing without any explicit measures to mitigate against failure. Has anyone
 experienced this? Is there an explanation for this?

 I have always used varistors almost as a matter of course, so you can
understand
 my surprise.

 Could it be I have over-designed my RF filter to the point it is good
 enough for the EFTs as well? The caps are only rated for 50V though ( the
clamping
  voltages of the varistors).

 Could it be the caps are in fact rated for such transients although this may
not
 be stated explicitly? Should I prolong the exposure of the varistor-free
 circuit at
 2kV to see if I am dealing with delayed failure potentially? I have been
setting
 my burst duration to 1 minute.

 Any pointers?

 Regards

 - Chris Chileshe
 - Ultronics Ltd



 
 This e-mail has been scanned for all viruses by Star Internet. The
 service is powered by MessageLabs. For more information on a proactive
 anti-virus service working around the clock, around the globe, visit:
 http://www.star.net.uk
 

 ---
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.

 Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

 To cancel your subscription, send mail to:
  majord...@ieee.org
 with the single line:
  unsubscribe emc-pstc

 For help, send mail to the list administrators:
  Ron Pickard:  emc-p...@hypercom.com
  Dave Heald:   davehe...@attbi.com

 For policy questions, send mail to:
  Richard Nute:   ri...@ieee.org
  Jim Bacher: j.bac...@ieee.org

 All emc-pstc postings are archived and searchable on the web at:
 http://ieeepstc.mindcruiser.com/
 Click on browse and then emc-pstc mailing list
 

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list

Re: Baffled by EFT test results (EN61000-4-4)

2002-10-25 Thread John Woodgate

I read in !emc-pstc that Chris Chileshe chris.chile...@ultronics.com
wrote (in 01c27c25.d813b6c0.chris.chile...@ultronics.com) about
'Baffled by EFT test results (EN61000-4-4)' on Fri, 25 Oct 2002:

This is probably the first time I have seen anything get through transients 
testing without any explicit measures to mitigate against failure. Has anyone
experienced this? Is there an explanation for this? 

Yes, sometimes you get lucky!

I have always used varistors almost as a matter of course, so you can 
understand
my surprise.  

Could it be I have over-designed my RF filter to the point it is good 
enough for the EFTs as well? The caps are only rated for 50V though ( the 
clamping
 voltages of the varistors). 

If you can afford it, you haven't over-designed it. (The converse is
not, unfortunately, always true.)

Could it be the caps are in fact rated for such transients although this may 
not
be stated explicitly? Should I prolong the exposure of the varistor-free 
circuit 
at 
2kV to see if I am dealing with delayed failure potentially? I have been 
setting
my burst duration to 1 minute. 

Without knowing what type the capacitors are, and the exact circuit
configuration, one cannot say. How much of the 2 kV actually appears
across the caps? (Measure, it might not be what you expect). Leave the
varistors in if you can afford to and they don't cause a problem if/when
they explode.
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk 
Interested in professional sound reinforcement and distribution? Then go to 
http://www.isce.org.uk
PLEASE do NOT copy news posts to me by E-MAIL!

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


Baffled by EFT test results (EN61000-4-4)

2002-10-25 Thread Chris Chileshe

Hi Group,

So I went ahead and built a test PCB with my inductors and ferrites in PI 
filter formation with capacitors - just like I threatened to do a few months 
ago ( e-mail subject header Designing for low power radiated and conducted
immunity describing a small 3-wire low power DC pressure sensor).

The analog circuit simulating a pressure sensor is simply a 5V regulator 
(LP2985) supplying a AD623 IN-amp monitoring the differential voltage across a
wheatstone bridge (4k7) connected to the same 5V rail. The output then 
simply connects to an Avometer (through a PI filter of course). A variant of 
the 
test PCB doesn't even have the regulator. It is that simple.

I took the PCB through radiated immunity testing to EN 61000-4-3 and met
100V/m, and through conducted immunity testing to EN 61000-4-6 and met
the 10V level.  All tests were done with unscreened cable. I also proved the
protected circuit was susceptible when the filter was removed.

Having decided I had sized my inductors, ferrites and caps appropriately, 
and done the PCB layout correctly, I then proceeded to add small SMT varistors 
for transients to EN 61000-4-4. The test PCB was again good for 2kV. I 
then shuffled the relative positions of the varistors in the circuit (initially 
pre-
PI filter, then post PI filter ) and it didn't seem to make any difference. The
idea was to get some permutations of varistor location and then repeat the
RF immunity tests in case the varistors introduced susceptibility (an
observation I have made in the past). 

I then took the varistors off the board altogether and still the PCB meets the 
2kV stress levels ( I am using the levels of EN 61000-6-2 ). I am not
too keen to raise the stakes to 4kV just now because there are more tests 
I would like to perform on the PCB before I let it go up in smoke.

This is probably the first time I have seen anything get through transients 
testing without any explicit measures to mitigate against failure. Has anyone
experienced this? Is there an explanation for this? 

I have always used varistors almost as a matter of course, so you can understand
my surprise.  

Could it be I have over-designed my RF filter to the point it is good 
enough for the EFTs as well? The caps are only rated for 50V though ( the 
clamping
 voltages of the varistors). 

Could it be the caps are in fact rated for such transients although this may not
be stated explicitly? Should I prolong the exposure of the varistor-free 
circuit at 
2kV to see if I am dealing with delayed failure potentially? I have been 
setting
my burst duration to 1 minute. 

Any pointers?

Regards

- Chris Chileshe
- Ultronics Ltd




This e-mail has been scanned for all viruses by Star Internet. The
service is powered by MessageLabs. For more information on a proactive
anti-virus service working around the clock, around the globe, visit:
http://www.star.net.uk


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list