Re: Power failure

2019-10-20 Thread Peter
Each cable are connected to two different UPS.

Yes i am in a process (management approval) to perform a test by powering
of one of its breaker for a minute and verify.

Thanks for the suggestions and i will respond back with the outcome

On Fri, 18 Oct, 2019, 10:18 PM Edward Finnell, <
000248cce9f3-dmarc-requ...@listserv.ua.edu> wrote:

> Each Branch has an Environmental specialist. They'll help you and are
> familiar with Auto-Cad for layouts and loading.
>
> In a message dated 10/18/2019 4:56:15 AM Central Standard Time,
> kees.verno...@klm.com writes:
> Or: open the floor and check if the power cords are really connected to
> different rails.
>
> --
> For IBM-MAIN subscribe / signoff / archive access instructions,
> send email to lists...@listserv.ua.edu with the message: INFO IBM-MAIN
>

--
For IBM-MAIN subscribe / signoff / archive access instructions,
send email to lists...@listserv.ua.edu with the message: INFO IBM-MAIN


Re: Power failure

2019-10-18 Thread Edward Finnell
Each Branch has an Environmental specialist. They'll help you and are familiar 
with Auto-Cad for layouts and loading.

In a message dated 10/18/2019 4:56:15 AM Central Standard Time, 
kees.verno...@klm.com writes:
Or: open the floor and check if the power cords are really connected to 
different rails.

--
For IBM-MAIN subscribe / signoff / archive access instructions,
send email to lists...@listserv.ua.edu with the message: INFO IBM-MAIN


Re: Power failure

2019-10-18 Thread Vernooij, Kees (ITOP NM) - KLM
Or: open the floor and check if the power cords are really connected to 
different rails.

Kees.

> -Original Message-
> From: IBM Mainframe Discussion List [mailto:IBM-MAIN@LISTSERV.UA.EDU] On
> Behalf Of Mike Schwab
> Sent: 18 October, 2019 0:02
> To: IBM-MAIN@LISTSERV.UA.EDU
> Subject: Re: Power failure
> 
> I agree.  By mistake both power cords lead to the same UPS, or even
> the same breaker.  Pick a low impact time.  Turn each breaker off for
> 1 minute then turn back on.  Look for anything that went down and
> change outlets as needed.  Then power off each UPS to check for
> different breakers but same UPS.  Or isn't there a device that will
> send a signal over the line and you can determine which outlets are
> wired to that breaker? Or is that only phone / network lines?
> 
> On Thu, Oct 17, 2019 at 10:27 AM Tom Marchant
> <000a2a8c2020-dmarc-requ...@listserv.ua.edu> wrote:
> >
> > On Thu, 17 Oct 2019 11:41:24 +0400, Peter wrote:
> >
> > >We have a dual... connectivity from UPS wired to z14.
> > >
> > >Even if one goes down and another would take a control
> >
> > That's what you said.
> >
> > Some of us are skeptical that it is actually implemented the way
> > that you intended that it be implemented.
> >
> > --
> > Tom Marchant
> >
> > --
> > For IBM-MAIN subscribe / signoff / archive access instructions,
> > send email to lists...@listserv.ua.edu with the message: INFO IBM-MAIN
> 
> 
> 
> --
> Mike A Schwab, Springfield IL USA
> Where do Forest Rangers go to get away from it all?
> 
> --
> For IBM-MAIN subscribe / signoff / archive access instructions,
> send email to lists...@listserv.ua.edu with the message: INFO IBM-MAIN

For information, services and offers, please visit our web site: 
http://www.klm.com. This e-mail and any attachment may contain confidential and 
privileged material intended for the addressee only. If you are not the 
addressee, you are notified that no part of the e-mail or any attachment may be 
disclosed, copied or distributed, and that any other action related to this 
e-mail or attachment is strictly prohibited, and may be unlawful. If you have 
received this e-mail by error, please notify the sender immediately by return 
e-mail, and delete this message.

Koninklijke Luchtvaart Maatschappij NV (KLM), its subsidiaries and/or its 
employees shall not be liable for the incorrect or incomplete transmission of 
this e-mail or any attachments, nor responsible for any delay in receipt.
Koninklijke Luchtvaart Maatschappij N.V. (also known as KLM Royal Dutch 
Airlines) is registered in Amstelveen, The Netherlands, with registered number 
33014286



--
For IBM-MAIN subscribe / signoff / archive access instructions,
send email to lists...@listserv.ua.edu with the message: INFO IBM-MAIN


Re: [External] Re: Power failure

2019-10-17 Thread Pommier, Rex
Jerry,

That's true (it's also true if you accidentally IPL a test system using the 
production paging subsystem) that corrupting/losing critical DASD will cause 
z/OS to fall over.  However, I believe the OP mentioned that the SEs were 
restarted as well.  I don't recall if the z14 has internal battery backup for 
the SE's or not, but if not, IBM made (in my opinion) a mistake moving from 
laptops with internal batteries to 1u "pizza boxes" for the SEs without BBU.  
It sure smells to me like there was some kind of power issue that impacted both 
of the power feeds coming in to the z14.  

Rex

-Original Message-
From: IBM Mainframe Discussion List  On Behalf Of 
Jerry Whitteridge
Sent: Thursday, October 17, 2019 5:15 PM
To: IBM-MAIN@LISTSERV.UA.EDU
Subject: [External] Re: Power failure

I seem to remember that Peter mentioned that they may have had an outage on 
their Storage Subsystem - if you ripped away all the DASD from under z/OS I'll 
guarantee you'll be reIPL'ing

Jerry Whitteridge
Delivery Manager / Mainframe Architect
GTS - Safeway Account
602 527 4871 Mobile
jerry.whitteri...@ibm.com

IBM Services

IBM Mainframe Discussion List  wrote on
10/17/2019 03:01:57 PM:

> From: Mike Schwab 
> To: IBM-MAIN@LISTSERV.UA.EDU
> Date: 10/17/2019 02:50 PM
> Subject: [EXTERNAL] Re: Power failure
> Sent by: IBM Mainframe Discussion List 
>
> I agree.  By mistake both power cords lead to the same UPS, or even 
> the same breaker.  Pick a low impact time.  Turn each breaker off for
> 1 minute then turn back on.  Look for anything that went down and 
> change outlets as needed.  Then power off each UPS to check for 
> different breakers but same UPS.  Or isn't there a device that will 
> send a signal over the line and you can determine which outlets are 
> wired to that breaker? Or is that only phone / network lines?
>
> On Thu, Oct 17, 2019 at 10:27 AM Tom Marchant 
> <000a2a8c2020-dmarc-requ...@listserv.ua.edu> wrote:
> >
> > On Thu, 17 Oct 2019 11:41:24 +0400, Peter wrote:
> >
> > >We have a dual... connectivity from UPS wired to z14.
> > >
> > >Even if one goes down and another would take a control
> >
> > That's what you said.
> >
> > Some of us are skeptical that it is actually implemented the way 
> > that you intended that it be implemented.
> >
> > --
> > Tom Marchant
> >
> > 
> > -- For IBM-MAIN subscribe / signoff / archive access instructions, 
> > send email to lists...@listserv.ua.edu with the message: INFO 
> > IBM-MAIN
>
>
>
> --
> Mike A Schwab, Springfield IL USA
> Where do Forest Rangers go to get away from it all?
>
> --
> For IBM-MAIN subscribe / signoff / archive access instructions, send 
> email to lists...@listserv.ua.edu with the message: INFO IBM-MAIN
>

--
For IBM-MAIN subscribe / signoff / archive access instructions, send email to 
lists...@listserv.ua.edu with the message: INFO IBM-MAIN


The information contained in this message is confidential, protected from 
disclosure and may be legally privileged.  If the reader of this message is not 
the intended recipient or an employee or agent responsible for delivering this 
message to the intended recipient, you are hereby notified that any disclosure, 
distribution, copying, or any action taken or action omitted in reliance on it, 
is strictly prohibited and may be unlawful.  If you have received this 
communication in error, please notify us immediately by replying to this 
message and destroy the material in its entirety, whether in electronic or hard 
copy format.  Thank you.

--
For IBM-MAIN subscribe / signoff / archive access instructions,
send email to lists...@listserv.ua.edu with the message: INFO IBM-MAIN


Re: Power failure

2019-10-17 Thread Jerry Whitteridge
I seem to remember that Peter mentioned that they may have had an outage on
their Storage Subsystem - if you ripped away all the DASD from under z/OS
I'll guarantee you'll be reIPL'ing

Jerry Whitteridge
Delivery Manager / Mainframe Architect
GTS - Safeway Account
602 527 4871 Mobile
jerry.whitteri...@ibm.com

IBM Services

IBM Mainframe Discussion List  wrote on
10/17/2019 03:01:57 PM:

> From: Mike Schwab 
> To: IBM-MAIN@LISTSERV.UA.EDU
> Date: 10/17/2019 02:50 PM
> Subject: [EXTERNAL] Re: Power failure
> Sent by: IBM Mainframe Discussion List 
>
> I agree.  By mistake both power cords lead to the same UPS, or even
> the same breaker.  Pick a low impact time.  Turn each breaker off for
> 1 minute then turn back on.  Look for anything that went down and
> change outlets as needed.  Then power off each UPS to check for
> different breakers but same UPS.  Or isn't there a device that will
> send a signal over the line and you can determine which outlets are
> wired to that breaker? Or is that only phone / network lines?
>
> On Thu, Oct 17, 2019 at 10:27 AM Tom Marchant
> <000a2a8c2020-dmarc-requ...@listserv.ua.edu> wrote:
> >
> > On Thu, 17 Oct 2019 11:41:24 +0400, Peter wrote:
> >
> > >We have a dual... connectivity from UPS wired to z14.
> > >
> > >Even if one goes down and another would take a control
> >
> > That's what you said.
> >
> > Some of us are skeptical that it is actually implemented the way
> > that you intended that it be implemented.
> >
> > --
> > Tom Marchant
> >
> > --
> > For IBM-MAIN subscribe / signoff / archive access instructions,
> > send email to lists...@listserv.ua.edu with the message: INFO IBM-MAIN
>
>
>
> --
> Mike A Schwab, Springfield IL USA
> Where do Forest Rangers go to get away from it all?
>
> --
> For IBM-MAIN subscribe / signoff / archive access instructions,
> send email to lists...@listserv.ua.edu with the message: INFO IBM-MAIN
>

--
For IBM-MAIN subscribe / signoff / archive access instructions,
send email to lists...@listserv.ua.edu with the message: INFO IBM-MAIN


Re: Power failure

2019-10-17 Thread Mike Schwab
I agree.  By mistake both power cords lead to the same UPS, or even
the same breaker.  Pick a low impact time.  Turn each breaker off for
1 minute then turn back on.  Look for anything that went down and
change outlets as needed.  Then power off each UPS to check for
different breakers but same UPS.  Or isn't there a device that will
send a signal over the line and you can determine which outlets are
wired to that breaker? Or is that only phone / network lines?

On Thu, Oct 17, 2019 at 10:27 AM Tom Marchant
<000a2a8c2020-dmarc-requ...@listserv.ua.edu> wrote:
>
> On Thu, 17 Oct 2019 11:41:24 +0400, Peter wrote:
>
> >We have a dual... connectivity from UPS wired to z14.
> >
> >Even if one goes down and another would take a control
>
> That's what you said.
>
> Some of us are skeptical that it is actually implemented the way
> that you intended that it be implemented.
>
> --
> Tom Marchant
>
> --
> For IBM-MAIN subscribe / signoff / archive access instructions,
> send email to lists...@listserv.ua.edu with the message: INFO IBM-MAIN



-- 
Mike A Schwab, Springfield IL USA
Where do Forest Rangers go to get away from it all?

--
For IBM-MAIN subscribe / signoff / archive access instructions,
send email to lists...@listserv.ua.edu with the message: INFO IBM-MAIN


Re: Power failure

2019-10-17 Thread Tom Marchant
On Thu, 17 Oct 2019 11:41:24 +0400, Peter wrote:

>We have a dual... connectivity from UPS wired to z14.
>
>Even if one goes down and another would take a control

That's what you said.

Some of us are skeptical that it is actually implemented the way 
that you intended that it be implemented.

-- 
Tom Marchant

--
For IBM-MAIN subscribe / signoff / archive access instructions,
send email to lists...@listserv.ua.edu with the message: INFO IBM-MAIN


Re: Power failure

2019-10-17 Thread Peter
We have a dual... connectivity from UPS wired to z14.

Even if one goes down and another would take a control

On Thu, 17 Oct, 2019, 11:39 AM Mike Schwab,  wrote:

> Maybe the NYC/WE is single power source and it lost power momentarily and
> ordered a reboot when it restarted?
>
>
> On Thursday, October 17, 2019, Peter  wrote:
> > Yes... How can a SE reboot a machine on its own
> >
> > On Thu, 17 Oct, 2019, 11:02 AM Vernooij, Kees (ITOP NM) - KLM, <
> > kees.verno...@klm.com> wrote:
> >
> >> Still makes you wonder what *good* reason it had to reboot on its own.
> >>
> >> Kees.
> >>
> >>
> >> > -Original Message-
> >> > From: IBM Mainframe Discussion List [mailto:IBM-MAIN@LISTSERV.UA.EDU]
> On
> >> > Behalf Of Peter
> >> > Sent: 17 October, 2019 8:33
> >> > To: IBM-MAIN@LISTSERV.UA.EDU
> >> > Subject: Re: Power failure
> >> >
> >> > Ibm responded
> >> >
> >> > Says this  system reboot could be due to at SE level.
> >> >
> >> > Half of the log collected got corrupted
> >> >
> >> > Error data not in cache .
> >> >
> >> > Still wondering if SE can really reboot the machine on its own.
> >> >
> >> >
> >> >
> >> > On Wed, 16 Oct, 2019, 6:21 PM Jousma, David, <
> >> > 01a0403c5dc1-dmarc-requ...@listserv.ua.edu> wrote:
> >> >
> >> > > +1 for what Tom says.  I didn’t reply to the earlier email from
> Peter
> >> > this
> >> > > morning, but did you drill down into the "restarted forcibly"
> message
> >> > that
> >> > > you presumably saw on the HMC?  I'd also go look for hardware
> messages
> >> > at
> >> > > the CEC level, there should be events there, that you can also drill
> >> > down
> >> > > into.  While you may not see the shutdown (hopefully there is
> >> > something),
> >> > > you would see more of the startup information.
> >> > >
> >> > >
> >> > >
> >> >
> >>
> __
> >> > ___
> >> > > Dave Jousma
> >> > > AVP | Manager, Systems Engineering
> >> > >
> >> > > Fifth Third Bank  |  1830 East Paris Ave, SE  |  MD RSCB2H  |  Grand
> >> > > Rapids, MI 49546
> >> > > 616.653.8429  |  fax: 616.653.2717
> >> > >
> >> > >
> >> > >
> >> > > -Original Message-
> >> > > From: IBM Mainframe Discussion List  On
> >> Behalf
> >> > > Of Tom Marchant
> >> > > Sent: Wednesday, October 16, 2019 10:07 AM
> >> > > To: IBM-MAIN@LISTSERV.UA.EDU
> >> > > Subject: Re: Power failure
> >> > >
> >> > > **CAUTION EXTERNAL EMAIL**
> >> > >
> >> > > **DO NOT open attachments or click on links from unknown senders or
> >> > > unexpected emails**
> >> > >
> >> > > On Wed, 16 Oct 2019 09:51:34 +0400, Peter wrote:
> >> > >
> >> > > >I looked into audit and log messages during those time frames.
> >> > > >
> >> > > >I just see a message as system was restarted forcibly. It doesn't
> say
> >> > > >what caused it.
> >> > >
> >> > > If power was lost abruptly, there may have been no opportunity to
> log
> >> > > anything.
> >> > >
> >> > > >Does IBM receives more detailed message ?
> >> > >
> >> > > Have you asked IBM?
> >> > >
> >> > > --
> >> > > Tom Marchant
> >> > >
> >> > >
> --
> >> > > For IBM-MAIN subscribe / signoff / archive access instructions, send
> >> > email
> >> > > to lists...@listserv.ua.edu with the message: INFO IBM-MAIN
> **CAUTION
> >> > > EXTERNAL EMAIL**
> >> > >
> >> > > **DO NOT open attachments or click on links from unknown senders or
> >> > > unexpected emails**
> >> > >
> >> > > This e-mail transmission contains information that is confidential
> and
> >> > may
> >

Re: Power failure

2019-10-17 Thread Mike Schwab
Maybe the NYC/WE is single power source and it lost power momentarily and
ordered a reboot when it restarted?


On Thursday, October 17, 2019, Peter  wrote:
> Yes... How can a SE reboot a machine on its own
>
> On Thu, 17 Oct, 2019, 11:02 AM Vernooij, Kees (ITOP NM) - KLM, <
> kees.verno...@klm.com> wrote:
>
>> Still makes you wonder what *good* reason it had to reboot on its own.
>>
>> Kees.
>>
>>
>> > -Original Message-
>> > From: IBM Mainframe Discussion List [mailto:IBM-MAIN@LISTSERV.UA.EDU]
On
>> > Behalf Of Peter
>> > Sent: 17 October, 2019 8:33
>> > To: IBM-MAIN@LISTSERV.UA.EDU
>> > Subject: Re: Power failure
>> >
>> > Ibm responded
>> >
>> > Says this  system reboot could be due to at SE level.
>> >
>> > Half of the log collected got corrupted
>> >
>> > Error data not in cache .
>> >
>> > Still wondering if SE can really reboot the machine on its own.
>> >
>> >
>> >
>> > On Wed, 16 Oct, 2019, 6:21 PM Jousma, David, <
>> > 01a0403c5dc1-dmarc-requ...@listserv.ua.edu> wrote:
>> >
>> > > +1 for what Tom says.  I didn’t reply to the earlier email from Peter
>> > this
>> > > morning, but did you drill down into the "restarted forcibly" message
>> > that
>> > > you presumably saw on the HMC?  I'd also go look for hardware
messages
>> > at
>> > > the CEC level, there should be events there, that you can also drill
>> > down
>> > > into.  While you may not see the shutdown (hopefully there is
>> > something),
>> > > you would see more of the startup information.
>> > >
>> > >
>> > >
>> >
>>
__
>> > ___
>> > > Dave Jousma
>> > > AVP | Manager, Systems Engineering
>> > >
>> > > Fifth Third Bank  |  1830 East Paris Ave, SE  |  MD RSCB2H  |  Grand
>> > > Rapids, MI 49546
>> > > 616.653.8429  |  fax: 616.653.2717
>> > >
>> > >
>> > >
>> > > -Original Message-
>> > > From: IBM Mainframe Discussion List  On
>> Behalf
>> > > Of Tom Marchant
>> > > Sent: Wednesday, October 16, 2019 10:07 AM
>> > > To: IBM-MAIN@LISTSERV.UA.EDU
>> > > Subject: Re: Power failure
>> > >
>> > > **CAUTION EXTERNAL EMAIL**
>> > >
>> > > **DO NOT open attachments or click on links from unknown senders or
>> > > unexpected emails**
>> > >
>> > > On Wed, 16 Oct 2019 09:51:34 +0400, Peter wrote:
>> > >
>> > > >I looked into audit and log messages during those time frames.
>> > > >
>> > > >I just see a message as system was restarted forcibly. It doesn't
say
>> > > >what caused it.
>> > >
>> > > If power was lost abruptly, there may have been no opportunity to log
>> > > anything.
>> > >
>> > > >Does IBM receives more detailed message ?
>> > >
>> > > Have you asked IBM?
>> > >
>> > > --
>> > > Tom Marchant
>> > >
>> > >
--
>> > > For IBM-MAIN subscribe / signoff / archive access instructions, send
>> > email
>> > > to lists...@listserv.ua.edu with the message: INFO IBM-MAIN **CAUTION
>> > > EXTERNAL EMAIL**
>> > >
>> > > **DO NOT open attachments or click on links from unknown senders or
>> > > unexpected emails**
>> > >
>> > > This e-mail transmission contains information that is confidential
and
>> > may
>> > > be privileged.   It is intended only for the addressee(s) named
above.
>> > If
>> > > you receive this e-mail in error, please do not read, copy or
>> > disseminate
>> > > it in any manner. If you are not the intended recipient, any
>> disclosure,
>> > > copying, distribution or use of the contents of this information is
>> > > prohibited. Please reply to the message immediately by informing the
>> > sender
>> > > that the message was misdirected. After replying, please erase it
from
>> > your
>> > > computer system. Your assistance in correcting this error is
>> > appreciated.
>>

Re: Power failure

2019-10-17 Thread Peter
Yes... How can a SE reboot a machine on its own

On Thu, 17 Oct, 2019, 11:02 AM Vernooij, Kees (ITOP NM) - KLM, <
kees.verno...@klm.com> wrote:

> Still makes you wonder what *good* reason it had to reboot on its own.
>
> Kees.
>
>
> > -Original Message-
> > From: IBM Mainframe Discussion List [mailto:IBM-MAIN@LISTSERV.UA.EDU] On
> > Behalf Of Peter
> > Sent: 17 October, 2019 8:33
> > To: IBM-MAIN@LISTSERV.UA.EDU
> > Subject: Re: Power failure
> >
> > Ibm responded
> >
> > Says this  system reboot could be due to at SE level.
> >
> > Half of the log collected got corrupted
> >
> > Error data not in cache .
> >
> > Still wondering if SE can really reboot the machine on its own.
> >
> >
> >
> > On Wed, 16 Oct, 2019, 6:21 PM Jousma, David, <
> > 01a0403c5dc1-dmarc-requ...@listserv.ua.edu> wrote:
> >
> > > +1 for what Tom says.  I didn’t reply to the earlier email from Peter
> > this
> > > morning, but did you drill down into the "restarted forcibly" message
> > that
> > > you presumably saw on the HMC?  I'd also go look for hardware messages
> > at
> > > the CEC level, there should be events there, that you can also drill
> > down
> > > into.  While you may not see the shutdown (hopefully there is
> > something),
> > > you would see more of the startup information.
> > >
> > >
> > >
> >
> __
> > ___
> > > Dave Jousma
> > > AVP | Manager, Systems Engineering
> > >
> > > Fifth Third Bank  |  1830 East Paris Ave, SE  |  MD RSCB2H  |  Grand
> > > Rapids, MI 49546
> > > 616.653.8429  |  fax: 616.653.2717
> > >
> > >
> > >
> > > -Original Message-
> > > From: IBM Mainframe Discussion List  On
> Behalf
> > > Of Tom Marchant
> > > Sent: Wednesday, October 16, 2019 10:07 AM
> > > To: IBM-MAIN@LISTSERV.UA.EDU
> > > Subject: Re: Power failure
> > >
> > > **CAUTION EXTERNAL EMAIL**
> > >
> > > **DO NOT open attachments or click on links from unknown senders or
> > > unexpected emails**
> > >
> > > On Wed, 16 Oct 2019 09:51:34 +0400, Peter wrote:
> > >
> > > >I looked into audit and log messages during those time frames.
> > > >
> > > >I just see a message as system was restarted forcibly. It doesn't say
> > > >what caused it.
> > >
> > > If power was lost abruptly, there may have been no opportunity to log
> > > anything.
> > >
> > > >Does IBM receives more detailed message ?
> > >
> > > Have you asked IBM?
> > >
> > > --
> > > Tom Marchant
> > >
> > > --
> > > For IBM-MAIN subscribe / signoff / archive access instructions, send
> > email
> > > to lists...@listserv.ua.edu with the message: INFO IBM-MAIN **CAUTION
> > > EXTERNAL EMAIL**
> > >
> > > **DO NOT open attachments or click on links from unknown senders or
> > > unexpected emails**
> > >
> > > This e-mail transmission contains information that is confidential and
> > may
> > > be privileged.   It is intended only for the addressee(s) named above.
> > If
> > > you receive this e-mail in error, please do not read, copy or
> > disseminate
> > > it in any manner. If you are not the intended recipient, any
> disclosure,
> > > copying, distribution or use of the contents of this information is
> > > prohibited. Please reply to the message immediately by informing the
> > sender
> > > that the message was misdirected. After replying, please erase it from
> > your
> > > computer system. Your assistance in correcting this error is
> > appreciated.
> > >
> > >
> > > --
> > > For IBM-MAIN subscribe / signoff / archive access instructions,
> > > send email to lists...@listserv.ua.edu with the message: INFO IBM-MAIN
> > >
> >
> > --
> > For IBM-MAIN subscribe / signoff / archive access instructions,
> > send email to lists...@listserv.ua.edu with the message: INFO IBM-MAIN
> 
> For informat

Re: Power failure

2019-10-17 Thread Vernooij, Kees (ITOP NM) - KLM
Still makes you wonder what *good* reason it had to reboot on its own.

Kees.


> -Original Message-
> From: IBM Mainframe Discussion List [mailto:IBM-MAIN@LISTSERV.UA.EDU] On
> Behalf Of Peter
> Sent: 17 October, 2019 8:33
> To: IBM-MAIN@LISTSERV.UA.EDU
> Subject: Re: Power failure
> 
> Ibm responded
> 
> Says this  system reboot could be due to at SE level.
> 
> Half of the log collected got corrupted
> 
> Error data not in cache .
> 
> Still wondering if SE can really reboot the machine on its own.
> 
> 
> 
> On Wed, 16 Oct, 2019, 6:21 PM Jousma, David, <
> 01a0403c5dc1-dmarc-requ...@listserv.ua.edu> wrote:
> 
> > +1 for what Tom says.  I didn’t reply to the earlier email from Peter
> this
> > morning, but did you drill down into the "restarted forcibly" message
> that
> > you presumably saw on the HMC?  I'd also go look for hardware messages
> at
> > the CEC level, there should be events there, that you can also drill
> down
> > into.  While you may not see the shutdown (hopefully there is
> something),
> > you would see more of the startup information.
> >
> >
> >
> __
> ___
> > Dave Jousma
> > AVP | Manager, Systems Engineering
> >
> > Fifth Third Bank  |  1830 East Paris Ave, SE  |  MD RSCB2H  |  Grand
> > Rapids, MI 49546
> > 616.653.8429  |  fax: 616.653.2717
> >
> >
> >
> > -Original Message-
> > From: IBM Mainframe Discussion List  On Behalf
> > Of Tom Marchant
> > Sent: Wednesday, October 16, 2019 10:07 AM
> > To: IBM-MAIN@LISTSERV.UA.EDU
> > Subject: Re: Power failure
> >
> > **CAUTION EXTERNAL EMAIL**
> >
> > **DO NOT open attachments or click on links from unknown senders or
> > unexpected emails**
> >
> > On Wed, 16 Oct 2019 09:51:34 +0400, Peter wrote:
> >
> > >I looked into audit and log messages during those time frames.
> > >
> > >I just see a message as system was restarted forcibly. It doesn't say
> > >what caused it.
> >
> > If power was lost abruptly, there may have been no opportunity to log
> > anything.
> >
> > >Does IBM receives more detailed message ?
> >
> > Have you asked IBM?
> >
> > --
> > Tom Marchant
> >
> > --
> > For IBM-MAIN subscribe / signoff / archive access instructions, send
> email
> > to lists...@listserv.ua.edu with the message: INFO IBM-MAIN **CAUTION
> > EXTERNAL EMAIL**
> >
> > **DO NOT open attachments or click on links from unknown senders or
> > unexpected emails**
> >
> > This e-mail transmission contains information that is confidential and
> may
> > be privileged.   It is intended only for the addressee(s) named above.
> If
> > you receive this e-mail in error, please do not read, copy or
> disseminate
> > it in any manner. If you are not the intended recipient, any disclosure,
> > copying, distribution or use of the contents of this information is
> > prohibited. Please reply to the message immediately by informing the
> sender
> > that the message was misdirected. After replying, please erase it from
> your
> > computer system. Your assistance in correcting this error is
> appreciated.
> >
> >
> > --
> > For IBM-MAIN subscribe / signoff / archive access instructions,
> > send email to lists...@listserv.ua.edu with the message: INFO IBM-MAIN
> >
> 
> --
> For IBM-MAIN subscribe / signoff / archive access instructions,
> send email to lists...@listserv.ua.edu with the message: INFO IBM-MAIN

For information, services and offers, please visit our web site: 
http://www.klm.com. This e-mail and any attachment may contain confidential and 
privileged material intended for the addressee only. If you are not the 
addressee, you are notified that no part of the e-mail or any attachment may be 
disclosed, copied or distributed, and that any other action related to this 
e-mail or attachment is strictly prohibited, and may be unlawful. If you have 
received this e-mail by error, please notify the sender immediately by return 
e-mail, and delete this message.

Koninklijke Luchtvaart Maatschappij NV (KLM), its subsidiaries and/or its 
employees shall not be liable for the incorrect or incomplete transmission of 
this e-mail or any attachments, nor responsible for any delay in receipt.
Koninklijke Luchtvaart Maatschappij N.V. (also known as KLM Royal Dutch 
Airlines) is registered in Amstelveen, The Netherlands, with registered number 
33014286



--
For IBM-MAIN subscribe / signoff / archive access instructions,
send email to lists...@listserv.ua.edu with the message: INFO IBM-MAIN


Re: Power failure

2019-10-17 Thread Peter
Ibm responded

Says this  system reboot could be due to at SE level.

Half of the log collected got corrupted

Error data not in cache .

Still wondering if SE can really reboot the machine on its own.



On Wed, 16 Oct, 2019, 6:21 PM Jousma, David, <
01a0403c5dc1-dmarc-requ...@listserv.ua.edu> wrote:

> +1 for what Tom says.  I didn’t reply to the earlier email from Peter this
> morning, but did you drill down into the "restarted forcibly" message that
> you presumably saw on the HMC?  I'd also go look for hardware messages at
> the CEC level, there should be events there, that you can also drill down
> into.  While you may not see the shutdown (hopefully there is something),
> you would see more of the startup information.
>
>
> _
> Dave Jousma
> AVP | Manager, Systems Engineering
>
> Fifth Third Bank  |  1830 East Paris Ave, SE  |  MD RSCB2H  |  Grand
> Rapids, MI 49546
> 616.653.8429  |  fax: 616.653.2717
>
>
>
> -Original Message-
> From: IBM Mainframe Discussion List  On Behalf
> Of Tom Marchant
> Sent: Wednesday, October 16, 2019 10:07 AM
> To: IBM-MAIN@LISTSERV.UA.EDU
> Subject: Re: Power failure
>
> **CAUTION EXTERNAL EMAIL**
>
> **DO NOT open attachments or click on links from unknown senders or
> unexpected emails**
>
> On Wed, 16 Oct 2019 09:51:34 +0400, Peter wrote:
>
> >I looked into audit and log messages during those time frames.
> >
> >I just see a message as system was restarted forcibly. It doesn't say
> >what caused it.
>
> If power was lost abruptly, there may have been no opportunity to log
> anything.
>
> >Does IBM receives more detailed message ?
>
> Have you asked IBM?
>
> --
> Tom Marchant
>
> --
> For IBM-MAIN subscribe / signoff / archive access instructions, send email
> to lists...@listserv.ua.edu with the message: INFO IBM-MAIN **CAUTION
> EXTERNAL EMAIL**
>
> **DO NOT open attachments or click on links from unknown senders or
> unexpected emails**
>
> This e-mail transmission contains information that is confidential and may
> be privileged.   It is intended only for the addressee(s) named above. If
> you receive this e-mail in error, please do not read, copy or disseminate
> it in any manner. If you are not the intended recipient, any disclosure,
> copying, distribution or use of the contents of this information is
> prohibited. Please reply to the message immediately by informing the sender
> that the message was misdirected. After replying, please erase it from your
> computer system. Your assistance in correcting this error is appreciated.
>
>
> --
> For IBM-MAIN subscribe / signoff / archive access instructions,
> send email to lists...@listserv.ua.edu with the message: INFO IBM-MAIN
>

--
For IBM-MAIN subscribe / signoff / archive access instructions,
send email to lists...@listserv.ua.edu with the message: INFO IBM-MAIN


Re: Power failure

2019-10-16 Thread Jousma, David
+1 for what Tom says.  I didn’t reply to the earlier email from Peter this 
morning, but did you drill down into the "restarted forcibly" message that you 
presumably saw on the HMC?  I'd also go look for hardware messages at the CEC 
level, there should be events there, that you can also drill down into.  While 
you may not see the shutdown (hopefully there is something), you would see more 
of the startup information.

_
Dave Jousma
AVP | Manager, Systems Engineering  

Fifth Third Bank  |  1830 East Paris Ave, SE  |  MD RSCB2H  |  Grand Rapids, MI 
49546
616.653.8429  |  fax: 616.653.2717



-Original Message-
From: IBM Mainframe Discussion List  On Behalf Of Tom 
Marchant
Sent: Wednesday, October 16, 2019 10:07 AM
To: IBM-MAIN@LISTSERV.UA.EDU
Subject: Re: Power failure

**CAUTION EXTERNAL EMAIL**

**DO NOT open attachments or click on links from unknown senders or unexpected 
emails**

On Wed, 16 Oct 2019 09:51:34 +0400, Peter wrote:

>I looked into audit and log messages during those time frames.
>
>I just see a message as system was restarted forcibly. It doesn't say 
>what caused it.

If power was lost abruptly, there may have been no opportunity to log anything.

>Does IBM receives more detailed message ?

Have you asked IBM?

--
Tom Marchant

--
For IBM-MAIN subscribe / signoff / archive access instructions, send email to 
lists...@listserv.ua.edu with the message: INFO IBM-MAIN **CAUTION EXTERNAL 
EMAIL**

**DO NOT open attachments or click on links from unknown senders or unexpected 
emails**

This e-mail transmission contains information that is confidential and may be 
privileged.   It is intended only for the addressee(s) named above. If you 
receive this e-mail in error, please do not read, copy or disseminate it in any 
manner. If you are not the intended recipient, any disclosure, copying, 
distribution or use of the contents of this information is prohibited. Please 
reply to the message immediately by informing the sender that the message was 
misdirected. After replying, please erase it from your computer system. Your 
assistance in correcting this error is appreciated.


--
For IBM-MAIN subscribe / signoff / archive access instructions,
send email to lists...@listserv.ua.edu with the message: INFO IBM-MAIN


Re: Power failure

2019-10-16 Thread Tom Marchant
On Wed, 16 Oct 2019 09:51:34 +0400, Peter wrote:

>I looked into audit and log messages during those time frames.
>
>I just see a message as system was restarted forcibly. It doesn't say what
>caused it.

If power was lost abruptly, there may have been no opportunity to log anything.

>Does IBM receives more detailed message ?

Have you asked IBM?

-- 
Tom Marchant

--
For IBM-MAIN subscribe / signoff / archive access instructions,
send email to lists...@listserv.ua.edu with the message: INFO IBM-MAIN


Re: Power failure

2019-10-15 Thread Peter
I looked into audit and log messages during those time frames.

I just see a message as system was restarted forcibly. It doesn't say what
caused it.

Does IBM receives more detailed message ?

On Tue, 15 Oct, 2019, 9:12 PM Peter,  wrote:

> Gary
>
> When you told about 3380 and we did had some maintenance for DS8K Box. Not
> sure if would cause the z box to restart.
>
> Hopefully log tells more about this.
>
> On Tue, 15 Oct, 2019, 7:16 PM Gary Jacek,  wrote:
>
>> This reminds me of a problem we had with a brand new 3745 a very long
>> time ago at my previous employer.
>>
>> One main selling point of the 3745, touted by IBM, was dual power
>> supplies.
>>
>> We had just completed our move to a new data centre.  Within 24 hours we
>> lost our network.  That 3745 failed.
>> The one flaw in that dual power supply design was a single power cable.
>> And that was the component that failed.
>> We were down for many hours, until a replacement power cable could be
>> flown in from Toronto. (We were in Vancouver)
>>
>> The other failure we had during that move was a "swing DASD" 3380 that
>> just happened to be a sysres pack.
>> Of all the 3380s on the floor, this was the only one painted olive drab.
>> We spent that week making up stories about this 3380 being depth charged in
>> a US submarine or bouncing around in an army drab truck.
>>
>> Gary Jacek - TELUS IT - Western Canada IT Services - tel (604) 695-6282
>>
>> -Original Message-
>> From: IBM Mainframe Discussion List [mailto:IBM-MAIN@LISTSERV.UA.EDU] On
>> Behalf Of Peter
>> Sent: October 15, 2019 04:47 AM
>> To: IBM-MAIN@LISTSERV.UA.EDU
>> Subject: Power failure
>>
>> Hi
>>
>> We had a power failure on our z14 zr1. I couldn't find any reason on the
>> log or hardware message on why it had power failure. Also our z14 box is
>> connected to two different UPS and they never went down .
>>
>> Where can we find the root cause of this power outage? When i checked our
>> Support element was initialising and not sure what made this power outage.
>> As other machines were all working intact.
>>
>> Any clue or suggestions to look into this?
>>
>> Peter
>>
>> --
>> For IBM-MAIN subscribe / signoff / archive access instructions, send
>> email to lists...@listserv.ua.edu with the message: INFO IBM-MAIN
>>
>> --
>> For IBM-MAIN subscribe / signoff / archive access instructions,
>> send email to lists...@listserv.ua.edu with the message: INFO IBM-MAIN
>>
>

--
For IBM-MAIN subscribe / signoff / archive access instructions,
send email to lists...@listserv.ua.edu with the message: INFO IBM-MAIN


Re: Power failure

2019-10-15 Thread Peter
Gary

When you told about 3380 and we did had some maintenance for DS8K Box. Not
sure if would cause the z box to restart.

Hopefully log tells more about this.

On Tue, 15 Oct, 2019, 7:16 PM Gary Jacek,  wrote:

> This reminds me of a problem we had with a brand new 3745 a very long time
> ago at my previous employer.
>
> One main selling point of the 3745, touted by IBM, was dual power supplies.
>
> We had just completed our move to a new data centre.  Within 24 hours we
> lost our network.  That 3745 failed.
> The one flaw in that dual power supply design was a single power cable.
> And that was the component that failed.
> We were down for many hours, until a replacement power cable could be
> flown in from Toronto. (We were in Vancouver)
>
> The other failure we had during that move was a "swing DASD" 3380 that
> just happened to be a sysres pack.
> Of all the 3380s on the floor, this was the only one painted olive drab.
> We spent that week making up stories about this 3380 being depth charged in
> a US submarine or bouncing around in an army drab truck.
>
> Gary Jacek - TELUS IT - Western Canada IT Services - tel (604) 695-6282
>
> -Original Message-
> From: IBM Mainframe Discussion List [mailto:IBM-MAIN@LISTSERV.UA.EDU] On
> Behalf Of Peter
> Sent: October 15, 2019 04:47 AM
> To: IBM-MAIN@LISTSERV.UA.EDU
> Subject: Power failure
>
> Hi
>
> We had a power failure on our z14 zr1. I couldn't find any reason on the
> log or hardware message on why it had power failure. Also our z14 box is
> connected to two different UPS and they never went down .
>
> Where can we find the root cause of this power outage? When i checked our
> Support element was initialising and not sure what made this power outage.
> As other machines were all working intact.
>
> Any clue or suggestions to look into this?
>
> Peter
>
> --
> For IBM-MAIN subscribe / signoff / archive access instructions, send email
> to lists...@listserv.ua.edu with the message: INFO IBM-MAIN
>
> --
> For IBM-MAIN subscribe / signoff / archive access instructions,
> send email to lists...@listserv.ua.edu with the message: INFO IBM-MAIN
>

--
For IBM-MAIN subscribe / signoff / archive access instructions,
send email to lists...@listserv.ua.edu with the message: INFO IBM-MAIN


Re: Power failure

2019-10-15 Thread Gary Jacek
This reminds me of a problem we had with a brand new 3745 a very long time ago 
at my previous employer.

One main selling point of the 3745, touted by IBM, was dual power supplies.

We had just completed our move to a new data centre.  Within 24 hours we lost 
our network.  That 3745 failed.
The one flaw in that dual power supply design was a single power cable.  And 
that was the component that failed.
We were down for many hours, until a replacement power cable could be flown in 
from Toronto. (We were in Vancouver)

The other failure we had during that move was a "swing DASD" 3380 that just 
happened to be a sysres pack.
Of all the 3380s on the floor, this was the only one painted olive drab.  We 
spent that week making up stories about this 3380 being depth charged in a US 
submarine or bouncing around in an army drab truck.

Gary Jacek - TELUS IT - Western Canada IT Services - tel (604) 695-6282 

-Original Message-
From: IBM Mainframe Discussion List [mailto:IBM-MAIN@LISTSERV.UA.EDU] On Behalf 
Of Peter
Sent: October 15, 2019 04:47 AM
To: IBM-MAIN@LISTSERV.UA.EDU
Subject: Power failure

Hi

We had a power failure on our z14 zr1. I couldn't find any reason on the log or 
hardware message on why it had power failure. Also our z14 box is connected to 
two different UPS and they never went down .

Where can we find the root cause of this power outage? When i checked our 
Support element was initialising and not sure what made this power outage.
As other machines were all working intact.

Any clue or suggestions to look into this?

Peter

--
For IBM-MAIN subscribe / signoff / archive access instructions, send email to 
lists...@listserv.ua.edu with the message: INFO IBM-MAIN

--
For IBM-MAIN subscribe / signoff / archive access instructions,
send email to lists...@listserv.ua.edu with the message: INFO IBM-MAIN


Re: Power failure

2019-10-15 Thread Dana Mitchell
I just did a quick look on a z114 HMC,  Single Object Operations -> Console 
Actions -> Audit and Log Management.This log will contain entries for POR 
and Acivtate actions if the CPC was powered on.

Dana 

On Tue, 15 Oct 2019 17:44:16 +0400, Peter  wrote:

>I have a query, if the hardware gets restarted due to power failure does it
>write this message anywhere in the logs ?
>

--
For IBM-MAIN subscribe / signoff / archive access instructions,
send email to lists...@listserv.ua.edu with the message: INFO IBM-MAIN


Re: Power failure

2019-10-15 Thread Peter
I have a query, if the hardware gets restarted due to power failure does it
write this message anywhere in the logs ?

On Tue, 15 Oct, 2019, 4:39 PM Vernooij, Kees (ITOP NM) - KLM, <
kees.verno...@klm.com> wrote:

> Sure. Some time ago we did a check of the power connections before a major
> action on one of the power rails and we also found a couple of devices that
> had their redundant power plugs connected to the same rail.
>
> Kees.
>
> > -Original Message-
> > From: IBM Mainframe Discussion List [mailto:IBM-MAIN@LISTSERV.UA.EDU] On
> > Behalf Of Jousma, David
> > Sent: 15 October, 2019 14:30
> > To: IBM-MAIN@LISTSERV.UA.EDU
> > Subject: Re: Power failure
> >
> > My point about the UPS's is that while I am sure you know they are fine,
> > do you KNOW for sure your z14 is wired to both?   Only your facilities
> > guys can answer that.   We've been known to see a few servers go down
> when
> > our facilities guys take a PDU offline to do some maintenance, only to
> > find that some servers had both of their power feeds coming off the
> > same...
> >
> >
> __
> > ___
> > Dave Jousma
> > AVP | Manager, Systems Engineering
> >
> > Fifth Third Bank  |  1830 East Paris Ave, SE  |  MD RSCB2H  |  Grand
> > Rapids, MI 49546
> > 616.653.8429  |  fax: 616.653.2717
> >
> >
> >
> > -Original Message-
> > From: IBM Mainframe Discussion List  On Behalf
> > Of Peter
> > Sent: Tuesday, October 15, 2019 8:24 AM
> > To: IBM-MAIN@LISTSERV.UA.EDU
> > Subject: Re: Power failure
> >
> > **CAUTION EXTERNAL EMAIL**
> >
> > **DO NOT open attachments or click on links from unknown senders or
> > unexpected emails**
> >
> > We have checked our local UPS and they are fine ..
> >
> > Not sure why SE didn't write anything about this failure and there was no
> > IBM call made from box.
> >
> > There should be somewhere this kind of failure notification would be
> > recorded ?
> >
> > On Tue, 15 Oct, 2019, 3:51 PM Jousma, David, < 01a0403c5dc1-dmarc-
> > requ...@listserv.ua.edu> wrote:
> >
> > > Assuming  you have the box properly installed, and reporting "home" to
> > > IBM, I'd suspect something local.  These boxes have redundant power
> > > supplies, and if one fails, it will phone home.  Maybe what you think
> > > is true about your redundant connections is not really the case?
> > >
> > >
> > >
> > >
> > > __
> > > ___
> > > Dave Jousma
> > > AVP | Manager, Systems Engineering
> > >
> > > Fifth Third Bank  |  1830 East Paris Ave, SE  |  MD RSCB2H  |  Grand
> > > Rapids, MI 49546
> > > 616.653.8429  |  fax: 616.653.2717
> > >
> > >
> > > -----Original Message-
> > > From: IBM Mainframe Discussion List  On
> > > Behalf Of Peter
> > > Sent: Tuesday, October 15, 2019 7:47 AM
> > > To: IBM-MAIN@LISTSERV.UA.EDU
> > > Subject: Power failure
> > >
> > > **CAUTION EXTERNAL EMAIL**
> > >
> > > **DO NOT open attachments or click on links from unknown senders or
> > > unexpected emails**
> > >
> > > Hi
> > >
> > > We had a power failure on our z14 zr1. I couldn't find any reason on
> > > the log or hardware message on why it had power failure. Also our z14
> > > box is connected to two different UPS and they never went down .
> > >
> > > Where can we find the root cause of this power outage? When i checked
> > > our Support element was initialising and not sure what made this power
> > outage.
> > > As other machines were all working intact.
> > >
> > > Any clue or suggestions to look into this?
> > >
> > > Peter
> > >
> > > --
> > > For IBM-MAIN subscribe / signoff / archive access instructions, send
> > > email to lists...@listserv.ua.edu with the message: INFO IBM-MAIN
> > > **CAUTION EXTERNAL EMAIL**
> > >
> > > **DO NOT open attachments or click on links from unknown senders or
> > > unexpected emails**
> > >
> > > This e-mail transmission contains information that is confidenti

Re: Power failure

2019-10-15 Thread Vernooij, Kees (ITOP NM) - KLM
Sure. Some time ago we did a check of the power connections before a major 
action on one of the power rails and we also found a couple of devices that had 
their redundant power plugs connected to the same rail.

Kees.

> -Original Message-
> From: IBM Mainframe Discussion List [mailto:IBM-MAIN@LISTSERV.UA.EDU] On
> Behalf Of Jousma, David
> Sent: 15 October, 2019 14:30
> To: IBM-MAIN@LISTSERV.UA.EDU
> Subject: Re: Power failure
> 
> My point about the UPS's is that while I am sure you know they are fine,
> do you KNOW for sure your z14 is wired to both?   Only your facilities
> guys can answer that.   We've been known to see a few servers go down when
> our facilities guys take a PDU offline to do some maintenance, only to
> find that some servers had both of their power feeds coming off the
> same...
> 
> __
> ___
> Dave Jousma
> AVP | Manager, Systems Engineering
> 
> Fifth Third Bank  |  1830 East Paris Ave, SE  |  MD RSCB2H  |  Grand
> Rapids, MI 49546
> 616.653.8429  |  fax: 616.653.2717
> 
> 
> 
> -Original Message-
> From: IBM Mainframe Discussion List  On Behalf
> Of Peter
> Sent: Tuesday, October 15, 2019 8:24 AM
> To: IBM-MAIN@LISTSERV.UA.EDU
> Subject: Re: Power failure
> 
> **CAUTION EXTERNAL EMAIL**
> 
> **DO NOT open attachments or click on links from unknown senders or
> unexpected emails**
> 
> We have checked our local UPS and they are fine ..
> 
> Not sure why SE didn't write anything about this failure and there was no
> IBM call made from box.
> 
> There should be somewhere this kind of failure notification would be
> recorded ?
> 
> On Tue, 15 Oct, 2019, 3:51 PM Jousma, David, < 01a0403c5dc1-dmarc-
> requ...@listserv.ua.edu> wrote:
> 
> > Assuming  you have the box properly installed, and reporting "home" to
> > IBM, I'd suspect something local.  These boxes have redundant power
> > supplies, and if one fails, it will phone home.  Maybe what you think
> > is true about your redundant connections is not really the case?
> >
> >
> >
> >
> > __
> > ___
> > Dave Jousma
> > AVP | Manager, Systems Engineering
> >
> > Fifth Third Bank  |  1830 East Paris Ave, SE  |  MD RSCB2H  |  Grand
> > Rapids, MI 49546
> > 616.653.8429  |  fax: 616.653.2717
> >
> >
> > -Original Message-
> > From: IBM Mainframe Discussion List  On
> > Behalf Of Peter
> > Sent: Tuesday, October 15, 2019 7:47 AM
> > To: IBM-MAIN@LISTSERV.UA.EDU
> > Subject: Power failure
> >
> > **CAUTION EXTERNAL EMAIL**
> >
> > **DO NOT open attachments or click on links from unknown senders or
> > unexpected emails**
> >
> > Hi
> >
> > We had a power failure on our z14 zr1. I couldn't find any reason on
> > the log or hardware message on why it had power failure. Also our z14
> > box is connected to two different UPS and they never went down .
> >
> > Where can we find the root cause of this power outage? When i checked
> > our Support element was initialising and not sure what made this power
> outage.
> > As other machines were all working intact.
> >
> > Any clue or suggestions to look into this?
> >
> > Peter
> >
> > --
> > For IBM-MAIN subscribe / signoff / archive access instructions, send
> > email to lists...@listserv.ua.edu with the message: INFO IBM-MAIN
> > **CAUTION EXTERNAL EMAIL**
> >
> > **DO NOT open attachments or click on links from unknown senders or
> > unexpected emails**
> >
> > This e-mail transmission contains information that is confidential and
> may
> > be privileged.   It is intended only for the addressee(s) named above.
> If
> > you receive this e-mail in error, please do not read, copy or
> > disseminate it in any manner. If you are not the intended recipient,
> > any disclosure, copying, distribution or use of the contents of this
> > information is prohibited. Please reply to the message immediately by
> > informing the sender that the message was misdirected. After replying,
> > please erase it from your computer system. Your assistance in correcting
> this error is appreciated.
> >
> >
> > --
> > For IBM-MAIN subscribe / signoff / archive access instructions, send
> > email to lists...@listserv.u

Re: Power failure

2019-10-15 Thread Jousma, David
My point about the UPS's is that while I am sure you know they are fine, do you 
KNOW for sure your z14 is wired to both?   Only your facilities guys can answer 
that.   We've been known to see a few servers go down when our facilities guys 
take a PDU offline to do some maintenance, only to find that some servers had 
both of their power feeds coming off the same...

_
Dave Jousma
AVP | Manager, Systems Engineering  

Fifth Third Bank  |  1830 East Paris Ave, SE  |  MD RSCB2H  |  Grand Rapids, MI 
49546
616.653.8429  |  fax: 616.653.2717



-Original Message-
From: IBM Mainframe Discussion List  On Behalf Of 
Peter
Sent: Tuesday, October 15, 2019 8:24 AM
To: IBM-MAIN@LISTSERV.UA.EDU
Subject: Re: Power failure

**CAUTION EXTERNAL EMAIL**

**DO NOT open attachments or click on links from unknown senders or unexpected 
emails**

We have checked our local UPS and they are fine ..

Not sure why SE didn't write anything about this failure and there was no IBM 
call made from box.

There should be somewhere this kind of failure notification would be recorded ?

On Tue, 15 Oct, 2019, 3:51 PM Jousma, David, < 
01a0403c5dc1-dmarc-requ...@listserv.ua.edu> wrote:

> Assuming  you have the box properly installed, and reporting "home" to 
> IBM, I'd suspect something local.  These boxes have redundant power 
> supplies, and if one fails, it will phone home.  Maybe what you think 
> is true about your redundant connections is not really the case?
>
>
>
>
> __
> ___
> Dave Jousma
> AVP | Manager, Systems Engineering
>
> Fifth Third Bank  |  1830 East Paris Ave, SE  |  MD RSCB2H  |  Grand 
> Rapids, MI 49546
> 616.653.8429  |  fax: 616.653.2717
>
>
> -Original Message-
> From: IBM Mainframe Discussion List  On 
> Behalf Of Peter
> Sent: Tuesday, October 15, 2019 7:47 AM
> To: IBM-MAIN@LISTSERV.UA.EDU
> Subject: Power failure
>
> **CAUTION EXTERNAL EMAIL**
>
> **DO NOT open attachments or click on links from unknown senders or 
> unexpected emails**
>
> Hi
>
> We had a power failure on our z14 zr1. I couldn't find any reason on 
> the log or hardware message on why it had power failure. Also our z14 
> box is connected to two different UPS and they never went down .
>
> Where can we find the root cause of this power outage? When i checked 
> our Support element was initialising and not sure what made this power outage.
> As other machines were all working intact.
>
> Any clue or suggestions to look into this?
>
> Peter
>
> --
> For IBM-MAIN subscribe / signoff / archive access instructions, send 
> email to lists...@listserv.ua.edu with the message: INFO IBM-MAIN 
> **CAUTION EXTERNAL EMAIL**
>
> **DO NOT open attachments or click on links from unknown senders or 
> unexpected emails**
>
> This e-mail transmission contains information that is confidential and may
> be privileged.   It is intended only for the addressee(s) named above. If
> you receive this e-mail in error, please do not read, copy or 
> disseminate it in any manner. If you are not the intended recipient, 
> any disclosure, copying, distribution or use of the contents of this 
> information is prohibited. Please reply to the message immediately by 
> informing the sender that the message was misdirected. After replying, 
> please erase it from your computer system. Your assistance in correcting this 
> error is appreciated.
>
>
> --
> For IBM-MAIN subscribe / signoff / archive access instructions, send 
> email to lists...@listserv.ua.edu with the message: INFO IBM-MAIN
>

--
For IBM-MAIN subscribe / signoff / archive access instructions, send email to 
lists...@listserv.ua.edu with the message: INFO IBM-MAIN **CAUTION EXTERNAL 
EMAIL**

**DO NOT open attachments or click on links from unknown senders or unexpected 
emails**

This e-mail transmission contains information that is confidential and may be 
privileged.   It is intended only for the addressee(s) named above. If you 
receive this e-mail in error, please do not read, copy or disseminate it in any 
manner. If you are not the intended recipient, any disclosure, copying, 
distribution or use of the contents of this information is prohibited. Please 
reply to the message immediately by informing the sender that the message was 
misdirected. After replying, please erase it from your computer system. Your 
assistance in correcting this error is appreciated.


--
For IBM-MAIN subscribe / signoff / archive access instructions,
send email to lists...@listserv.ua.edu with the message: INFO IBM-MAIN


Re: Power failure

2019-10-15 Thread Vernooij, Kees (ITOP NM) - KLM
Ask IBM to dial in on the box and check the logs.

Kees.

> -Original Message-
> From: IBM Mainframe Discussion List [mailto:IBM-MAIN@LISTSERV.UA.EDU] On
> Behalf Of Peter
> Sent: 15 October, 2019 14:24
> To: IBM-MAIN@LISTSERV.UA.EDU
> Subject: Re: Power failure
> 
> We have checked our local UPS and they are fine ..
> 
> Not sure why SE didn't write anything about this failure and there was no
> IBM call made from box.
> 
> There should be somewhere this kind of failure notification would be
> recorded ?
> 
> On Tue, 15 Oct, 2019, 3:51 PM Jousma, David, <
> 01a0403c5dc1-dmarc-requ...@listserv.ua.edu> wrote:
> 
> > Assuming  you have the box properly installed, and reporting "home" to
> > IBM, I'd suspect something local.  These boxes have redundant power
> > supplies, and if one fails, it will phone home.  Maybe what you think is
> > true about your redundant connections is not really the case?
> >
> >
> >
> >
> >
> __
> ___
> > Dave Jousma
> > AVP | Manager, Systems Engineering
> >
> > Fifth Third Bank  |  1830 East Paris Ave, SE  |  MD RSCB2H  |  Grand
> > Rapids, MI 49546
> > 616.653.8429  |  fax: 616.653.2717
> >
> >
> > -----Original Message-
> > From: IBM Mainframe Discussion List  On Behalf
> > Of Peter
> > Sent: Tuesday, October 15, 2019 7:47 AM
> > To: IBM-MAIN@LISTSERV.UA.EDU
> > Subject: Power failure
> >
> > **CAUTION EXTERNAL EMAIL**
> >
> > **DO NOT open attachments or click on links from unknown senders or
> > unexpected emails**
> >
> > Hi
> >
> > We had a power failure on our z14 zr1. I couldn't find any reason on the
> > log or hardware message on why it had power failure. Also our z14 box is
> > connected to two different UPS and they never went down .
> >
> > Where can we find the root cause of this power outage? When i checked
> our
> > Support element was initialising and not sure what made this power
> outage.
> > As other machines were all working intact.
> >
> > Any clue or suggestions to look into this?
> >
> > Peter
> >
> > --
> > For IBM-MAIN subscribe / signoff / archive access instructions, send
> email
> > to lists...@listserv.ua.edu with the message: INFO IBM-MAIN **CAUTION
> > EXTERNAL EMAIL**
> >
> > **DO NOT open attachments or click on links from unknown senders or
> > unexpected emails**
> >
> > This e-mail transmission contains information that is confidential and
> may
> > be privileged.   It is intended only for the addressee(s) named above.
> If
> > you receive this e-mail in error, please do not read, copy or
> disseminate
> > it in any manner. If you are not the intended recipient, any disclosure,
> > copying, distribution or use of the contents of this information is
> > prohibited. Please reply to the message immediately by informing the
> sender
> > that the message was misdirected. After replying, please erase it from
> your
> > computer system. Your assistance in correcting this error is
> appreciated.
> >
> >
> > --
> > For IBM-MAIN subscribe / signoff / archive access instructions,
> > send email to lists...@listserv.ua.edu with the message: INFO IBM-MAIN
> >
> 
> --
> For IBM-MAIN subscribe / signoff / archive access instructions,
> send email to lists...@listserv.ua.edu with the message: INFO IBM-MAIN

For information, services and offers, please visit our web site: 
http://www.klm.com. This e-mail and any attachment may contain confidential and 
privileged material intended for the addressee only. If you are not the 
addressee, you are notified that no part of the e-mail or any attachment may be 
disclosed, copied or distributed, and that any other action related to this 
e-mail or attachment is strictly prohibited, and may be unlawful. If you have 
received this e-mail by error, please notify the sender immediately by return 
e-mail, and delete this message.

Koninklijke Luchtvaart Maatschappij NV (KLM), its subsidiaries and/or its 
employees shall not be liable for the incorrect or incomplete transmission of 
this e-mail or any attachments, nor responsible for any delay in receipt.
Koninklijke Luchtvaart Maatschappij N.V. (also known as KLM Royal Dutch 
Airlines) is registered in Amstelveen, The Netherlands, with registered number 
33014286



--
For IBM-MAIN subscribe / signoff / archive access instructions,
send email to lists...@listserv.ua.edu with the message: INFO IBM-MAIN


Re: Power failure

2019-10-15 Thread Peter
We have checked our local UPS and they are fine ..

Not sure why SE didn't write anything about this failure and there was no
IBM call made from box.

There should be somewhere this kind of failure notification would be
recorded ?

On Tue, 15 Oct, 2019, 3:51 PM Jousma, David, <
01a0403c5dc1-dmarc-requ...@listserv.ua.edu> wrote:

> Assuming  you have the box properly installed, and reporting "home" to
> IBM, I'd suspect something local.  These boxes have redundant power
> supplies, and if one fails, it will phone home.  Maybe what you think is
> true about your redundant connections is not really the case?
>
>
>
>
> _
> Dave Jousma
> AVP | Manager, Systems Engineering
>
> Fifth Third Bank  |  1830 East Paris Ave, SE  |  MD RSCB2H  |  Grand
> Rapids, MI 49546
> 616.653.8429  |  fax: 616.653.2717
>
>
> -Original Message-
> From: IBM Mainframe Discussion List  On Behalf
> Of Peter
> Sent: Tuesday, October 15, 2019 7:47 AM
> To: IBM-MAIN@LISTSERV.UA.EDU
> Subject: Power failure
>
> **CAUTION EXTERNAL EMAIL**
>
> **DO NOT open attachments or click on links from unknown senders or
> unexpected emails**
>
> Hi
>
> We had a power failure on our z14 zr1. I couldn't find any reason on the
> log or hardware message on why it had power failure. Also our z14 box is
> connected to two different UPS and they never went down .
>
> Where can we find the root cause of this power outage? When i checked our
> Support element was initialising and not sure what made this power outage.
> As other machines were all working intact.
>
> Any clue or suggestions to look into this?
>
> Peter
>
> --
> For IBM-MAIN subscribe / signoff / archive access instructions, send email
> to lists...@listserv.ua.edu with the message: INFO IBM-MAIN **CAUTION
> EXTERNAL EMAIL**
>
> **DO NOT open attachments or click on links from unknown senders or
> unexpected emails**
>
> This e-mail transmission contains information that is confidential and may
> be privileged.   It is intended only for the addressee(s) named above. If
> you receive this e-mail in error, please do not read, copy or disseminate
> it in any manner. If you are not the intended recipient, any disclosure,
> copying, distribution or use of the contents of this information is
> prohibited. Please reply to the message immediately by informing the sender
> that the message was misdirected. After replying, please erase it from your
> computer system. Your assistance in correcting this error is appreciated.
>
>
> --
> For IBM-MAIN subscribe / signoff / archive access instructions,
> send email to lists...@listserv.ua.edu with the message: INFO IBM-MAIN
>

--
For IBM-MAIN subscribe / signoff / archive access instructions,
send email to lists...@listserv.ua.edu with the message: INFO IBM-MAIN


Re: Power failure

2019-10-15 Thread Jousma, David
Assuming  you have the box properly installed, and reporting "home" to IBM, I'd 
suspect something local.  These boxes have redundant power supplies, and if one 
fails, it will phone home.  Maybe what you think is true about your redundant 
connections is not really the case?



_
Dave Jousma
AVP | Manager, Systems Engineering  

Fifth Third Bank  |  1830 East Paris Ave, SE  |  MD RSCB2H  |  Grand Rapids, MI 
49546
616.653.8429  |  fax: 616.653.2717


-Original Message-
From: IBM Mainframe Discussion List  On Behalf Of 
Peter
Sent: Tuesday, October 15, 2019 7:47 AM
To: IBM-MAIN@LISTSERV.UA.EDU
Subject: Power failure

**CAUTION EXTERNAL EMAIL**

**DO NOT open attachments or click on links from unknown senders or unexpected 
emails**

Hi

We had a power failure on our z14 zr1. I couldn't find any reason on the log or 
hardware message on why it had power failure. Also our z14 box is connected to 
two different UPS and they never went down .

Where can we find the root cause of this power outage? When i checked our 
Support element was initialising and not sure what made this power outage.
As other machines were all working intact.

Any clue or suggestions to look into this?

Peter

--
For IBM-MAIN subscribe / signoff / archive access instructions, send email to 
lists...@listserv.ua.edu with the message: INFO IBM-MAIN **CAUTION EXTERNAL 
EMAIL**

**DO NOT open attachments or click on links from unknown senders or unexpected 
emails**

This e-mail transmission contains information that is confidential and may be 
privileged.   It is intended only for the addressee(s) named above. If you 
receive this e-mail in error, please do not read, copy or disseminate it in any 
manner. If you are not the intended recipient, any disclosure, copying, 
distribution or use of the contents of this information is prohibited. Please 
reply to the message immediately by informing the sender that the message was 
misdirected. After replying, please erase it from your computer system. Your 
assistance in correcting this error is appreciated.


--
For IBM-MAIN subscribe / signoff / archive access instructions,
send email to lists...@listserv.ua.edu with the message: INFO IBM-MAIN


Power failure

2019-10-15 Thread Peter
Hi

We had a power failure on our z14 zr1. I couldn't find any reason on the
log or hardware message on why it had power failure. Also our z14 box is
connected to two different UPS and they never went down .

Where can we find the root cause of this power outage? When i checked our
Support element was initialising and not sure what made this power outage.
As other machines were all working intact.

Any clue or suggestions to look into this?

Peter

--
For IBM-MAIN subscribe / signoff / archive access instructions,
send email to lists...@listserv.ua.edu with the message: INFO IBM-MAIN


Re: PPRC power failure

2019-02-14 Thread Steve Horein
For messaging, review of Message Flood Automation rules would seem to be in
order:
https://www.ibm.com/support/knowledgecenter/SSLTBW_2.2.0/com.ibm.zos.v2r2.ieae200/msgfld.htm


On Wed, Feb 13, 2019 at 9:44 PM Peter  wrote:

> Hi
>
> One of our DS box in DR had a power failure last night and our production
> LPARS logon got impacted . When I checked up the RMF i saw many DASD
> devices were overloaded and flood of PPRC error messages too in SYSLOG.
>
> Once we fixed the power failure and re-established the replication the
> logins and all the application started running.
>
> Is there any relationship to system performance with the PPRC failure ?
>
> Peter
>
> --
> For IBM-MAIN subscribe / signoff / archive access instructions,
> send email to lists...@listserv.ua.edu with the message: INFO IBM-MAIN
>

--
For IBM-MAIN subscribe / signoff / archive access instructions,
send email to lists...@listserv.ua.edu with the message: INFO IBM-MAIN


Re: PPRC power failure

2019-02-14 Thread Richards, Robert B.
Peter,

My experience is over a decade old with XRC, but I imagine the potential for 
some form of read/write/IO pacing is the same and that it could impact 
performance. Open a PMR and ask IBM.

Bob

-Original Message-
From: IBM Mainframe Discussion List [mailto:IBM-MAIN@LISTSERV.UA.EDU] On Behalf 
Of Peter
Sent: Wednesday, February 13, 2019 10:44 PM
To: IBM-MAIN@LISTSERV.UA.EDU
Subject: PPRC power failure

Hi

One of our DS box in DR had a power failure last night and our production
LPARS logon got impacted . When I checked up the RMF i saw many DASD
devices were overloaded and flood of PPRC error messages too in SYSLOG.

Once we fixed the power failure and re-established the replication the
logins and all the application started running.

Is there any relationship to system performance with the PPRC failure ?

Peter

--
For IBM-MAIN subscribe / signoff / archive access instructions,
send email to lists...@listserv.ua.edu with the message: INFO IBM-MAIN

--
For IBM-MAIN subscribe / signoff / archive access instructions,
send email to lists...@listserv.ua.edu with the message: INFO IBM-MAIN


Re: PPRC power failure

2019-02-14 Thread Mike Schwab
On the sending DASD there is a 1 bit per track table of updated
tracks.  When each track is sent the bit is reset.  When it gets
caught up it sets a sync point.

On Wed, Feb 13, 2019 at 9:44 PM Peter  wrote:
>
> Hi
>
> One of our DS box in DR had a power failure last night and our production
> LPARS logon got impacted . When I checked up the RMF i saw many DASD
> devices were overloaded and flood of PPRC error messages too in SYSLOG.
>
> Once we fixed the power failure and re-established the replication the
> logins and all the application started running.
>
> Is there any relationship to system performance with the PPRC failure ?
>
> Peter
>
> --
> For IBM-MAIN subscribe / signoff / archive access instructions,
> send email to lists...@listserv.ua.edu with the message: INFO IBM-MAIN



-- 
Mike A Schwab, Springfield IL USA
Where do Forest Rangers go to get away from it all?

--
For IBM-MAIN subscribe / signoff / archive access instructions,
send email to lists...@listserv.ua.edu with the message: INFO IBM-MAIN


PPRC power failure

2019-02-13 Thread Peter
Hi

One of our DS box in DR had a power failure last night and our production
LPARS logon got impacted . When I checked up the RMF i saw many DASD
devices were overloaded and flood of PPRC error messages too in SYSLOG.

Once we fixed the power failure and re-established the replication the
logins and all the application started running.

Is there any relationship to system performance with the PPRC failure ?

Peter

--