On Thu, 19 Oct 2017, Drew Plaster wrote:


The topology is:
UPS TOPAPC, Data link to master, Power supply to master, slave1 and 
slave2
UPS MIDAPC, Data link to master, Power supply to master, slave1 and 
slave2
UPS BOTAPC, Data link to master, Power supply to master, slave1 and 
slave2

Shutdown plan: When wall power fails for any of the three UPS units, 
they continue powering the master and the two slaves.  When two of the 
UPS battery have been depleted and the last (MINSUPPLIES 1) UPS unit 
reaches the status [OB LB]. the two slaves are shut down, and then the 
master is shutdown and sends shutdown signal to UPS (#POWERDOWNFLAG 
/etc/killpower) has been temporarily remarked out in the masters 
upsmon.conf to test if the slaves would shutdown vai hotsync or 
deadtime. Anyway, that is how I was envisioning it functioning with the 
current config files; I may be mis-understanding something but that is 
the desired shutdown plan.


Drew, it seems to me that your Shutdown plan means living dangerously! 
You have triplicated power backup for maximum system security, yet you let 
it run down until just one UPS is operational, and then only for a short 
time since it is in status [OB LB].


Are the three UPS units fed by the same utility, or by different sources?

Case 1: They share the same utility and they are behaving as one huge UPS 
delivered in three separate boxes.  Assuming they are of the same capacity 
and have the same load, they will run down at the same rate. In this case, 
perhaps it would be better to specify MINSUPPLIES 3 so that the first to 
go [OB LB] drives the shutdown.  Perhaps the slaves will respond correctly 
to this.


Case 2: They have different power sources.  The logic in this case may be 
beyond what is possible with the NUT configuration files.  You may need to 
use additional hardware such as an automatic power transfer switch, and/or 
implement your shutdown logic in a program (sometimes called upssched-cmd) 
called by the upssched.conf CMDSCRIPT directive.  This would mean that the 
upsmon.conf NOTIFYCMD directive would point to upssched, and that 
upssched-cmd would be responsible for sysadmin notifications.


I do not have any direct experience of a logic such as your Shutdown plan 
- perhaps other readers of this list have a deeper insight.


Roger

___
Nut-upsuser mailing list
Nut-upsuser@lists.alioth.debian.org
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser


Re: [Nut-upsuser] debian 8 "jessie" nut 2.7.2 slaves not shutting down

2017-10-19 Thread Drew Plaster
Roger,

The topology is:
UPS TOPAPC, Data link to master, Power supply to master, slave1 and 
slave2
UPS MIDAPC, Data link to master, Power supply to master, slave1 and 
slave2
UPS BOTAPC, Data link to master, Power supply to master, slave1 and 
slave2

Shutdown plan:
When wall power fails for any of the three UPS units, they continue powering 
the master and the two slaves.  When two of the UPS battery have been depleted 
and the last (MINSUPPLIES 1) UPS unit reaches the status [OB LB]. the two 
slaves are shut down, and then the master is shutdown and sends shutdown signal 
to UPS (#POWERDOWNFLAG /etc/killpower) has been temporarily remarked out in the 
masters upsmon.conf to test if the slaves would shutdown vai hotsync or 
deadtime.
Anyway, that is how I was envisioning it functioning with the current config 
files; I may be mis-understanding something but that is the desired shutdown 
plan.

I don't know if this helps with anything but if I execute upsmon -c fsd on any 
of the three systems that system does shutdown but when I execute it on the 
master system it does not shutdown either of the slave systems.
 
Drew Plaster | Systems Administrator
808 SW 3rd Avenue, Suite 300 | Portland, OR 97204
o: 503.415.2385 | c: 503.484.0168 | f: 503.415.2498
www.otak.com
 
at Otak, we consider the environment before printing emails.
 
Disclaimer:
The information transmitted in this e-mail message and attachments, if any, may 
contain confidential material, and is intended only for the use of the 
individual or entity named above. Distribution to, or review by, unauthorized 
persons is prohibited. In the event of the unauthorized use of any material in 
this transmission, neither Otak nor the sender shall have any liability and the 
recipient shall defend, indemnify and hold harmless the sender, Otak and its 
principals, agents, employees and subconsultants from all related claims and 
damages. The recipient understands and agrees that any use or distribution of 
the material in this transmission is conditioned upon the acceptance of the 
terms stated in this disclaimer. If you have received this transmission in 
error, immediately notify the sender and permanently delete this transmission 
including attachments, if any.

-Original Message-
From: Nut-upsuser 
[mailto:nut-upsuser-bounces+drew.plaster=otak@lists.alioth.debian.org] On 
Behalf Of Roger Price
Sent: Thursday, October 19, 2017 2:49 AM
To: nut-upsuser Mailing List
Subject: Re: [Nut-upsuser] debian 8 "jessie" nut 2.7.2 slaves not shutting down

On Wed, 18 Oct 2017, Drew Plaster wrote:

>   MASTER SYSTEM
>
>   nut.conf
> MODE=netserver
>
>   ups.conf
> [TOPAPC]
> driver = usbhid-ups
>   port = auto
>  pollonly
>  serial = "IS1309002707"
>  desc = "TOPAPC"
> [MIDAPC]
>   driver = usbhid-ups
> port = auto
>pollonly
>serial = "IS1309001233"
>desc = "MIDAPC"
> [BOTAPC]
>   driver = usbhid-ups
> port = auto
>pollonly
>serial = "IS1309001213"
>desc = "BOTAPC"

Just to be sure that I understand your topology:

UPS TOPAPC, Data link to master, Power supply to master UPS MIDAPC, Data link 
to master, Power supply to slave1 UPS BOTAPC, Data link to master, Power supply 
to slave2

Shutdown plan:  When wall power fails for any one of the three UPS units, they 
continue powering the master and the two slaves.  When any one of the three UPS 
units reaches the status [OB LB]. the two slaves are shut down, and then the 
master is shutdown.

Is this correct? 
Roger

___
Nut-upsuser mailing list
Nut-upsuser@lists.alioth.debian.org
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser
___
Nut-upsuser mailing list
Nut-upsuser@lists.alioth.debian.org
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser

Re: [Nut-upsuser] debian 8 "jessie" nut 2.7.2 slaves not shutting down

2017-10-19 Thread Roger Price

On Wed, 18 Oct 2017, Drew Plaster wrote:


MASTER SYSTEM

nut.conf
MODE=netserver

ups.conf
[TOPAPC]
driver = usbhid-ups
  port = auto
 pollonly
 serial = "IS1309002707"
 desc = "TOPAPC"
[MIDAPC]
  driver = usbhid-ups
port = auto
   pollonly
   serial = "IS1309001233"
   desc = "MIDAPC"
[BOTAPC]
  driver = usbhid-ups
port = auto
   pollonly
   serial = "IS1309001213"
   desc = "BOTAPC"


Just to be sure that I understand your topology:

UPS TOPAPC, Data link to master, Power supply to master 
UPS MIDAPC, Data link to master, Power supply to slave1 
UPS BOTAPC, Data link to master, Power supply to slave2


Shutdown plan:  When wall power fails for any one of the three UPS units, 
they continue powering the master and the two slaves.  When any one of the 
three UPS units reaches the status [OB LB]. the two slaves are shut down, 
and then the master is shutdown.


Is this correct? 