[RE-wrenches] Two Buildings, Two Services, One Roof

2011-04-18 Thread Nick Vida
It seems like it should be fine if you run one conduit to your shop inverter, and another to a dc disconnect and underground to the house inverter, but I see you running a bonding wire for the 2 GECs as well for some reason. You should go through the part of 250 about different GEC for

Re: [RE-wrenches] Two Buildings, Two Services, One Roof

2011-04-18 Thread Mark Frye
Thanks Nick, 250 talks about two seperate buildings with one service, and 230 talks about one building with two services. I don't think this particular situation has been contempated by the Code. How big a deal would it be to just bond the two ground electrode systems together and go along

Re: [RE-wrenches] Two Buildings, Two Services, One Roof

2011-04-18 Thread Kent Osterberg
Mark, NEC 230.2(A) specifically allows two services for parallel power production sources. While a feeder from the house is technically not the same as a service, it should be allowed provided that there is a disconnect grouped with the main service disconnect. A discussion with the inspector

Re: [RE-wrenches] balasted racks

2011-04-18 Thread Max Balchowsky
Sollega, cheap and easy.. Max Balchowsky Design Engineer SEE Systems 1048 Irvine Ave Suite 217 Newport Beach, Ca. 92660 760-403-6810 From: David Katz dk...@asis.com To: RE-wrenches re-wrenches@lists.re-wrenches.org Sent: Sat, April 16, 2011 10:52:24 PM

Re: [RE-wrenches] Two Buildings, Two Services, One Roof

2011-04-18 Thread Mark Frye
Thanks Ken, I still don't see any configuration of equipment that would not involve making an electrical connection between the two grounding systems of the two seperate dwellings In order to provide the required GFP for the PV modules, it seems both inverters would have to mounted on the

Re: [RE-wrenches] Two Buildings, Two Services, One Roof

2011-04-18 Thread Kent Osterberg
Mark, Separately derived is defined in article 100. Basically, a separately derived system has no common conductors other than possibly equipment ground. By the definition in article 100 the feeder from the house may be a separately derived system at the shop. It may not be if the house and

Re: [RE-wrenches] Two Buildings, Two Services, One Roof

2011-04-18 Thread Mark Frye
Thanks Ken, I appreciate the information. But I am still not feeling very confident about this. Yes, you can run a feeder with a EGC from one building with a service to an outbuilding and bond that EGC to a GE at the outbuilding, assuming that there is no service at that out building. If there

Re: [RE-wrenches] Two Buildings, Two Services, One Roof

2011-04-18 Thread Brian Teitelbaum
Mark, Are both buildings being fed from the same utility transformer? I thank that may be a key question here Brian Teitelbaum AEE Solar From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Mark Frye Sent: Monday, April 18, 2011 12:42

Re: [RE-wrenches] Two Buildings, Two Services, One Roof

2011-04-18 Thread Mark Frye
I have not yet visited the site to see, but I would guess that they are feed from the same transformer. If they were, how would that make it OK? Mark Frye Berkeley Solar Electric Systems 303 Redbud Way Nevada City, CA 95959 (530) 401-8024 http://www.berkeleysolar.com/

Re: [RE-wrenches] Two Buildings, Two Services, One Roof

2011-04-18 Thread Glenn Burt
Would be a good one to ask John Wiles - he has been very responsive to my questions. Glenn Burt From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Mark Frye Sent: Sunday, April 17, 2011 9:09 PM To: 'RE-wrenches' Subject:

Re: [RE-wrenches] Two Buildings, Two Services, One Roof

2011-04-18 Thread Dana
If each is separately derived, grounded and properly installed, Why not? Imagine a parking structure centrally located and 2 PV systems installed on the roof for 2 separate buildings with independent utility meters. Dana Orzel Great Solar Works, Inc E - d...@solarwork.com V -

Re: [RE-wrenches] Two Buildings, Two Services, One Roof

2011-04-18 Thread Mark Frye
Dana, Exactly, why not? I can't find anything in the Code that says 'Thou shalt not make a connection between the grounding system of two seperate services located on two seperate buildings. But re your example in this case the PV for both building will be located on only one of the two.

Re: [RE-wrenches] Wiles (was Two Buildings, Two Services, One Roof)

2011-04-18 Thread Allan Sindelar
In John's last Code Corner, he noted that it would be his last column, so I'm no longer sure if he's as accessible as he has been. If anyone knows more, please post here. Allan HP142: "Note: This will be the last Code Corner written by John Wiles. He will

Re: [RE-wrenches] Two Buildings, Two Services, One Roof

2011-04-18 Thread Mark Frye
Or another way to illustrate this problem: There is nothing in the Code that would stop me from hauling out the old #6 and bonding my GEC to my next door neighbors GEC, if I wanted to? Mark Frye Berkeley Solar Electric Systems 303 Redbud Way Nevada City, CA 95959 (530) 401-8024

Re: [RE-wrenches] Two Buildings, Two Services, One Roof

2011-04-18 Thread Hans Frederickson
I don't think you'll find anything in the NEC to prohibit that. NEC 250.52(A)(1) requires you to bond a metal underground water pipe (if it exists) to the grounding electrode system. In older neighborhoods with metal water pipes, the grounding electrode systems for all the houses are bonded

Re: [RE-wrenches] Two Buildings, Two Services, One Roof

2011-04-18 Thread Mark Frye
OK Thanks everyone for your thoughtful support. I did visit the AHJ and the lead plan checker did not see any reason to prohibit the work. He will be running it by his field electrical inspector to be sure he agrees as well. I will let you know if they come up with a reason to dis-allow

Re: [RE-wrenches] Two Buildings, Two Services, One Roof

2011-04-18 Thread Brian Teitelbaum
I don't know, Mark, but it seems to me that it might be an issue. If you have two buildings, each with their own service, and connected to a single T-former on a pole, I would think that you would create a ground loop if you connected the grounds on the two services together. They would be

Re: [RE-wrenches] Two Buildings, Two Services, One Roof

2011-04-18 Thread Mark Frye
Folks, I did send the question to John Wiles and he was gracious enough to reply. Here is his response: Mark: Better ask the utility involved. Probably depends if they are on a common transformer or not. Mark Frye Berkeley Solar Electric Systems 303 Redbud Way Nevada City, CA 95959

Re: [RE-wrenches] Trickle charge a generator cranking battery?

2011-04-18 Thread William Miller
David: Thanks for the reply. Today I installed a 6 watt module. This job is a long drive so I could not pre-measure the idle draw. The generator draws 145 mA when not running. The 6 watt module charges at 300 mA. As I figure it, with 4.5 average full sun hours, my module has about 1/2 as