Re: [RE-wrenches] Wago Connectors (221 series)

2021-05-09 Thread Glenn Burt
So like I said, although logic may dictate that it will operate at a high voltage DC level, having not been tested explicitly for that, it does not have UL listing – we will not use them on the DC side of our installations for that reason. -Glenn From: RE-wrenches On Behalf Of Dan

Re: [RE-wrenches] Wago Connectors (221 series)

2021-05-09 Thread Glenn Burt
I made the comment that they were not listed for use on DC circuits after I had reviewed the UL testing criteria, and the specifications from the manufacturer – It was not a lighthearted comment… -Glenn From: RE-wrenches On Behalf Of Jason Szumlanski Sent: Friday, May 07, 2021 5:11 PM

Re: [RE-wrenches] Wago Connectors (221 series)

2021-05-09 Thread Glenn Burt
This technology has been in use for a dozen years in European equipment and has been used in many inverters that we install. It creates a gas-tight connection and is fully vetted through many manufacturers. I don’t think we need to be concerned about its ability to create a reliable connection

Re: [RE-wrenches] Wago Connectors (221 series)

2021-05-09 Thread Glenn Burt
Soladeck has been offering their product with DIN rail mounted terminal blocks (I forget the manufacturer, Wiedmueller or Phoenix Contact maybe) for years now, and listed for 600VDC use. -Glenn From: RE-wrenches On Behalf Of Ray Sent: Saturday, May 08, 2021 2:31 PM To:

Re: [RE-wrenches] Breakers weakening?

2021-05-09 Thread drake . chamberlin
I've replaced breakers with those symptoms and solved the problem. --- On 2021-05-09 08:52, Kirk Herander, VSE wrote: That's what I expected to find, i.e. evidence of a heat event / loose connection at the breaker terminals (discolored and / or melted wire insulation, etc.), no visual

Re: [RE-wrenches] Breakers weakening?

2021-05-09 Thread Dave Angelini Offgrid Solar
Not sure what specific design type of CB this is. You guys/gals do know that most CB's are designed to Failsafe. They will trip before the rating if there is anything internal that has been damaged or changed. Designed in for protection. It is extremely rare that a CB from a quality

Re: [RE-wrenches] DC transfer switch

2021-05-09 Thread Brian Mehalic
I believe the 30-200 A versions of Eaton/C-H’s line of heavy duty DPDT safety switches are 600 VDC. Brian > On May 9, 2021, at 7:06 AM, Kirk Herander, VSE wrote: > >  > Yep, I've used them before as high voltage array discos. But no double-throw > models exist unfortunately. The IMO

Re: [RE-wrenches] Breakers weakening?

2021-05-09 Thread Brian Mehalic
Yikes. Didn’t realize that about the ConnectDER. Repeated tripping due to a fault can certainly damage internal parts and contacts, leading to resistance and operation and lower than the rated current. Brian > On May 9, 2021, at 7:06 AM, Kirk Herander, VSE wrote: > >  > The breaker is

Re: [RE-wrenches] DC transfer switch

2021-05-09 Thread Kirk Herander, VSE
Yep, I've used them before as high voltage array discos. But no double-throw models exist unfortunately. The IMO assembly looks identical to the ones used in all Solaredge on-board disconnects. Available in the US from  www.industrialcontroldirect.com [www.industrialcontroldirect.com]. Kirk

Re: [RE-wrenches] Breakers weakening?

2021-05-09 Thread Kirk Herander, VSE
The breaker is actually in a "connectder", a meter collar add-on which plugs into the meter socket, and the house meter plugs into it. It creates a point of interconnect outside of the house panel. Unfortunately the breaker itself cannot be removed and replaced. The entire collar must be.

Re: [RE-wrenches] Breakers weakening?

2021-05-09 Thread Kirk Herander, VSE
That's what I expected to find, i.e. evidence of a heat event / loose connection at the breaker terminals (discolored and / or melted wire insulation, etc.), no visual evidence or smell. Kirk Herander / kirkh@vermont.solar [mailto:kirkh@vermont.solar] Owner|Principal, VT Solar, LLC Celebrating

Re: [RE-wrenches] Breakers weakening?

2021-05-09 Thread Chris Mason
I'm presuming this is a breaker in a load center. Breakers fail, that's not unusual. Breakers for inverters undergo constant load so they will run hot all the time and will be prone to failure. It may have always been out of tolerance, most applications never push the breaker close to the limit. I