Hi William, You might try reaching out to Roy Dyngen of SMA - he is a good contact for these types of general questions. Email me off list if you would like his contact info. Is the SMA BATFUSE available in the US? Anyway, SMA has always recommended connecting the negative of the batteries

Re: [RE-wrenches] Power-One customer service

2014-01-30 Thread August Goers
Jason, We've been able to get a hold of tech support at 877.261.1374 which I think is the normal number they have on their website. Good luck. -August *From:* re-wrenches-boun...@lists.re-wrenches.org [mailto: re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *Jason Szumlanski *Sent:*

Re: [RE-wrenches] Tray cable with PV-Wire on roof

2014-01-28 Thread August Goers
of no return from sun exposure although the color definitely fades. We also bonded both ends of the tray per NEC 250.97 which added a little complexity to the installation. NEC article 392 Cable Trays is worth reading if you haven't already. -August August Goers Principal Luminalt Energy

Re: [RE-wrenches] Concrete tight versus raintight

2014-01-16 Thread August Goers
Hi William, About 5 years ago this became a big issue up in San Francisco and we had to learn the hard way. We used to just go buy outdoor EMT fittings and we were okay, then the inspectors started requiring fittings that say raintight or wet location (often stamped “wetloc”) on them. I don’t

Re: [RE-wrenches] Concrete tight versus raintight

2014-01-16 Thread August Goers
-boun...@lists.re-wrenches.org [ mailto:re-wrenches-boun...@lists.re-wrenches.orgre-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *August Goers *Sent:* Thursday, January 16, 2014 8:00 AM *To:* RE-wrenches *Subject:* Re: [RE-wrenches] Concrete tight versus raintight Hi William, About 5

[RE-wrenches] Deka AGMs

2014-01-06 Thread August Goers
All Battery Wrenches, I’m servicing an existing battery backup system with some big Deka AGM battery banks. I believe they are about 12 years old. Does anyone have any general comments about Deka batteries? Any suggestions about how I would test these would be greatly appreciated. Here’s a link

Re: [RE-wrenches] Return on investment information

2013-12-11 Thread August Goers
Hi Chris, Another free option might be RETscreen: http://www.retscreen.net/ang/version4.php OnGrid and Clean Power Finance Tools are two popular paid options, both offer free trials I believe. -August *From:* re-wrenches-boun...@lists.re-wrenches.org [mailto:

Re: [RE-wrenches] Power One Micro inverters

2013-12-11 Thread August Goers
Hi Roland, We’ve installed around ten Power-One micro systems with mostly good results. All in all, I’d say the installation is very similar to an Enphase M215 based system if you are familiar with those. As William mentioned on a separate post, the cabling is a bit expensive but otherwise

Re: [RE-wrenches] Mike Holt Solar Video - LIVE in your town, limited time only

2013-12-09 Thread August Goers
Hi Glenn, This is a confusing passage without seeing the context from the other parts of 690.47 (A, B, C etc). Can you send the full passage if it’s handy for you? My 2014 NEC is in the mail so I have yet to see the full implications of this section. Best, August *From:*

Re: [RE-wrenches] A related question - Individual AC conductors through separate conduits

2013-11-20 Thread August Goers
]. On 2013/11/19, 12:38, August Goers wrote: Hi All – On a related note, I’ve become good friends with some of the inspectors in San Francisco and they called me yesterday with a question. Is it okay to run *individual* DC conductors through EMT for wire management purposes? We have always run

Re: [RE-wrenches] PV Wiring methods

2013-11-19 Thread August Goers
in conduit so the question had never occurred to me. Obviously, you have to bond both ends of the conduit if it is over 250 v. I know that AC would have induction issues with running individual conductors but I’m not sure with DC. Thanks, August August Goers Principal Luminalt Energy

Re: [RE-wrenches] PV Wiring methods

2013-11-19 Thread August Goers
a return leg which would have no pair back to the combiner/junction box? jay peltz power On Nov 19, 2013, at 9:38 AM, August Goers wrote: Hi All – On a related note, I’ve become good friends with some of the inspectors in San Francisco and they called me yesterday with a question

Re: [RE-wrenches] PV Wiring methods

2013-11-14 Thread August Goers
Hi All – I’m not sure whether Hellermann Tyton is related to Heyco, but I know of the SunBundler product through Heyco: http://www.heyco.com/Alternative_Energy_Products/pdf/1-15-new.pdf -August *From:* re-wrenches-boun...@lists.re-wrenches.org [mailto:

Re: [RE-wrenches] RE-wrenches Digest, Vol 6, Issue 423

2013-11-12 Thread August Goers
in the box. Luckily it didn’t spread to the roof – it was still arcing away when I busted open the rusted lid. That seems like a workmanship the materials selection issue to me. Best, August August Goers Luminalt Energy Corporation o: 415.641.4000 m: 415.559.1525 www.luminalt.com *From

Re: [RE-wrenches] smaller 3-phase commercial inverters

2013-10-21 Thread August Goers
they might be worth checking out. -August *August Goers* Principal Luminalt Energy Corporation o: 415.641.4000 m: 415.559.1525 www.luminalt.com On Fri, Oct 18, 2013 at 9:45 AM, August Goers aug...@luminalt.com wrote: Hi Bill - Thanks, this is helpful info. Do you know how to calculate

Re: [RE-wrenches] smaller 3-phase commercial inverters

2013-10-18 Thread August Goers
Chris, Good point, we've installed a few of these P1 10k units and have been relatively happy. My understanding is that the first batch being sold in the US was very problematic but I think they're ironing out the kinks now. We have had a couple of failures but P1 tech support swapped them with

Re: [RE-wrenches] smaller 3-phase commercial inverters

2013-10-18 Thread August Goers
Hi Bill - Thanks, this is helpful info. Do you know how to calculate or approximate how we would keep the unbalanced voltage to less than 3%? I guess I need to check out ANSI/C84.1-2011 but I thought maybe there are some ballpark rules of thumb. Thanks, August *August Goers

Re: [RE-wrenches] Fronius Installer Support Sucks- but who else?

2013-10-17 Thread August Goers
Don - Unfortunately I believe the Sunny Tripower is only good for 480 V applications. I'm not aware of other 240 V 3-phase inverters on the market (other than the Fronius). We run into a lot of 208 V 3-phase here in the Bay Area and unfortunately can't use these cool new 3-phase inverters from

Re: [RE-wrenches] Enphase and Line Noise

2013-10-16 Thread August Goers
yet where it didn't work. Our pricing has this cost worked into it. Best, August *August Goers* Principal Luminalt Energy Corporation o: 415.641.4000 m: 415.559.1525 www.luminalt.com On Wed, Oct 16, 2013 at 1:01 PM, ma...@berkeleysolar.com wrote: Guys, I am thinking of getting back

[RE-wrenches] Solar City Aquires Zep

2013-10-09 Thread August Goers
Wrenches, Have you folks seen this: http://www.greentechmedia.com/articles/read/SolarCity-Acquires-Zep-Solar-For-158-Million Lots of interesting ramifications for us smaller guys as the bigger companies move closer and closer to vertical integration. -August

Re: [RE-wrenches] Point of connection question

2013-10-09 Thread August Goers
William, You have 9 M190s each running at 800 mA according to spec sheet. That equals 7.2 A nominal output current. Plus you have 10 M250s (if you look at your drawing) each running at 1 A = 10 A. 7.2 A + 10 A = 17.2 A * 1.25 = 21.5 A min breaker size. So, you'll need to round your breaker to a

Re: [RE-wrenches] transformerless inverters and conductor colors

2013-10-04 Thread August Goers
All - Just a quick follow up to this thread. My understanding is that you can use black USE-2 or PV Wire under the 2008 and 2011 NEC for all grounded and ungrounded conductors. 2008 NEC has section 200.6(A)(2) Grounded Conductors which reads (it is section 200.6(A)(6) in 2001 NEC): A

Re: [RE-wrenches] SatCon Inverter Maintenance Manuals

2013-10-02 Thread August Goers
Jason, There is a small ex-Satcon employee group supporting their inverters for a fee. If you're interested contact me off list and I'll get you a contact or two. Best, August *August Goers* Luminalt Energy Corporation o: 415.641.4000 m: 415.559.1525 *From:* re-wrenches

Re: [RE-wrenches] Using legacy modules on micro-inverters

2013-09-28 Thread August Goers
All - If you haven't already seen it, you might want to try playing with the numbers on Enphase's online calculator: http://enphase.com/module-compatibility-calculator-m250-update/ -August *August Goers* Principal Luminalt Energy Corporation o: 415.641.4000 m: 415.559.1525

Re: [RE-wrenches] transformerless inverters and conductor colors

2013-09-27 Thread August Goers
] transformerless inverters and conductor colors Thanks. Does this wire have “PV Wire” written on the insulation jacket? *From:* re-wrenches-boun...@lists.re-wrenches.org [ mailto:re-wrenches-boun...@lists.re-wrenches.orgre-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *August Goers *Sent

Re: [RE-wrenches] transformerless inverters and conductor colors

2013-09-27 Thread August Goers
they say Photovoltaic in the spec sheet, I am not sure that this is PV Wire. I don't see anywhere that it actually uses those exact words, and that is the designation in the NEC. Blessings, Kelly On Sep 27, 2013, at 10:38 AM, August Goers wrote: Marco, Yes, there is single jacketed PV

Re: [RE-wrenches] Energy usage for an electric car

2013-09-27 Thread August Goers
Here's a good place to go to find mileage: http://www.fueleconomy.gov/feg/Find.do?action=sbsid=32557 38 kW-hrs/100 mi for the Tesla Model S. Todd, isn't your estimate below off by a decimal? Best, August *From:* re-wrenches-boun...@lists.re-wrenches.org [mailto:

Re: [RE-wrenches] GEC sizing for a high amp, low voltage PV system with microinverters

2013-09-18 Thread August Goers
Hi Charlie, I can't help but be intrigued by your setup here. It seems like the complete opposite of where our commercial systems are going with transformerless 1000 V inverters entering the market. Anyway, I'm sure it's an interesting project and there may very well be advantages to the system

Re: [RE-wrenches] copper roof

2013-09-16 Thread August Goers
to be the issue here. Looks like a nice building! Best, August *August Goers* Luminalt Energy Corporation o: 415.641.4000 m: 415.559.1525 *From:* re-wrenches-boun...@lists.re-wrenches.org [mailto: re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *Nik Ponzio, Building Energy *Sent

Re: [RE-wrenches] Flat Roof PV Attachments with Tapered Insulation

2013-09-11 Thread August Goers
://solar.hollaender.com/ I'm looking forward to seeing if anyone else knows about off the shelf longer stanchions. Unirac used to make custom longer lengths of their steel standoff but no longer offer it. Best, August *August Goers* Luminalt Energy Corporation o: 415.641.4000 m

Re: [RE-wrenches] Flat Roof PV Attachments with Tapered Insulation

2013-09-11 Thread August Goers
wondering if multiple 7 Unirac 2-piece Stand-Offs cylinders threaded together with all-thread would be a structurally sound solution. I'll pass that option by the engineers... Still hoping for an off-the-shelf solution... J ason On Tue, Sep 10, 2013 at 4:38 PM, August Goers aug

Re: [RE-wrenches] double-insulated PV wire

2013-08-30 Thread August Goers
Marco, You might try http://pv-cables.com/ my contact there is Bryan. They sell all kinds of PV wire, connectors, etc for good prices. Do you have 1000 V TL inverters or just 600 V? If you are using 1000 V the whole wiring game changes quite a bit. Best, August Luminalt *From:*

Re: [RE-wrenches] 1000 V meters?

2013-08-23 Thread August Goers
also use a Seaward Solar PV150 solar test kit for testing strings. On Thu, Aug 22, 2013 at 4:03 PM, August Goers aug...@luminalt.com wrote: Hi Wrenches, It's new tool time! We're starting engineering for our first 1000 V small and medium commercial systems. There are all kinds of details

[RE-wrenches] 1000 V meters?

2013-08-22 Thread August Goers
376 which also measures AC and DC current but it is a bit expensive. The Fluke T5 is much cheaper, measures 1000 VDC, but doesn't measure DC current. Anyone have a meter that they like that can handle 1000 V? Best, August *August Goers* Luminalt Energy Corporation o: 415.641.4000 m

[RE-wrenches] Battery backup under attack in CA

2013-08-08 Thread August Goers
battery power to the grid. Thoughts? -August *August Goers* Luminalt Energy Corporation o: 415.641.4000 m: 415.559.1525 ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Change email address settings

[RE-wrenches] Onyx walkable PV floor

2013-08-01 Thread August Goers
. I am skeptical to say the least. Best, August *August Goers* Luminalt Energy Corporation o: 415.641.4000 m: 415.559.1525 ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Change email address

Re: [RE-wrenches] Adding similar but updated modules to same inverter

2013-07-16 Thread August Goers
. These two circuits in parallel will be fine for your MPPT, you'll have essentially the same voltages but slightly higher current in your new second string. DKC On 2013/7/12 19:27, August Goers wrote: Hi Wrenches, I have a client with a small system consisting of 6 SunPower 230s and a SMA SB

Re: [RE-wrenches] Painting rails

2013-07-05 Thread August Goers
Hi Benn, This sounds tricky. We've occasionally painted silver rail black on the ends with Rust-Oleum matte black paint. It always seems to adhere well but I don't know for sure how long it will last. I've never tried painting silver over black. Is the client unhappy with black rail and silver

Re: [RE-wrenches] EGC for Enphases

2013-07-05 Thread August Goers
Hi Dave, I'm not sure I'm understanding your scenario clearly but I'll take a crack at it. The Enphase system should have a bare #6 GEC for each micro and can then transition to a #8 green GEC once in conduit and run all the way back to the main ground electrode system. The #6 and #8 should be

Re: [RE-wrenches] EGC for Enphases

2013-07-05 Thread August Goers
PM, August Goers aug...@luminalt.com wrote: Hi Dave, I'm not sure I'm understanding your scenario clearly but I'll take a crack at it. The Enphase system should have a bare #6 GEC for each micro and can then transition to a #8 green GEC once in conduit and run all the way back to the main ground

Re: [RE-wrenches] double insulated wire

2013-07-02 Thread August Goers
The most common mistake I've seen is not correctly using white/gray for the grounded conductor on the DC side. I've seen errors most commonly with positive grounded systems (SunPower) but often times installers use black in place of white or something along those lines. It definitely gets

Re: [RE-wrenches] SHW expansion tank pressure

2013-07-02 Thread August Goers
Hi Carl, I'm glad you're making some progress. I've always had good luck following the Schuco table for setting the expansion tank pressure. I would expect the pressure in the expansion tank to be higher than the glycol charge pressure under most fully charged circumstances. For example, if you

Re: [RE-wrenches] SHW expansion tank pressure

2013-06-24 Thread August Goers
Hi Carl, Daniel's points all seem good. We have had a Schuco system with a blown expansion tank bladder exhibiting similar behavior to what you describe. It sounds like you said that the expansion tank has the correct pressure at 26 psi but you might want to bleed the expansion tank through

Re: [RE-wrenches] 200 Amp Main Equip for 60A Solar

2013-06-13 Thread August Goers
Jeff, Why are you looking to do a supply side connection? If you're going with new equipment you could go with a 225 A main panel with a 200 A main breaker and do a load side connection. Best, August *From:* re-wrenches-boun...@lists.re-wrenches.org [mailto:

Re: [RE-wrenches] Monitoring - The Dilemma

2013-06-03 Thread August Goers
Hi All - Thanks for all the valuable advice. I think all of our recommendations are right on and we will take them into account when coming up with our revised policies. As always, the Wrenches list is indispensable! Best, August *August Goers* Luminalt Energy Corporation o

[RE-wrenches] Monitoring - The Dilemma

2013-06-01 Thread August Goers
and expectations for their monitoring systems? Any ideas out there on how to put more responsibility on the client while still keeping them happy? Thanks in advance, August August Goers Luminalt Energy Corporation o: 415.641.4000 m: 415.559.1525 ___ List sponsored

Re: [RE-wrenches] SE or SW

2013-05-14 Thread August Goers
Does PVWatts really account for hourly weather data such as overcast conditions in the afternoon? I think it just accounts for average solar radiation for a particular location on a monthly basis but I could be wrong. Anyone care to chime in? -August *August Goers* VP, Engineering o

Re: [RE-wrenches] Enphase / Inverter failures

2013-05-09 Thread August Goers
This is fascinating - the majority of the Enphase failures reported on this list seem to be near coastal areas. I know that is true for us. We've had extensive failures on the M190 and M210 units close to the ocean. We have yet to have a single M215 failure so I have my fingers crossed. SMA has

Re: [RE-wrenches] Wire Gutters

2013-04-27 Thread August Goers
Most jurisdictions around here allow the AC and DC wires to be bundled/separated by cable ties. Best, August *From:* re-wrenches-boun...@lists.re-wrenches.org [mailto: re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *Aaron Mandelkorn *Sent:* Saturday, April 27, 2013 2:07 PM *To:*

Re: [RE-wrenches] Stainless Steel Cable Ties

2013-04-25 Thread August Goers
I too share the concern about standard plastic zip ties. However, I started in the industry in 1997 and have yet to see zip ties that are falling apart. Does anyone on the list have firsthand experience with failed plastic zip ties? Best, August August Goers Luminalt Energy

Re: [RE-wrenches] Fuse sizing in battery circuits

2013-04-16 Thread August Goers
. R.Ray Walters CTO, Solarray, Inc Nabcep Certified PV Installer, Licensed Master Electrician Solar Design Engineer 303 505-8760 On 4/15/2013 2:20 PM, August Goers wrote: Hi Drake, The Sunny Island System runs at 48 V nominal so I don't believe 250.162(A) applies. We have some really

Re: [RE-wrenches] Fuse sizing in battery circuits

2013-04-15 Thread August Goers
, X 747 M: 530.277.4894 *From:* re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.orgre-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *August Goers *Sent:* Wednesday, April 10, 2013 9:45 AM *To:* RE-wrenches *Subject:* Re: [RE-wrenches] Fuse sizing

Re: [RE-wrenches] Advanced PV Training Recommendations

2013-04-12 Thread August Goers
Eric, NABCEP just had an annual continuing education conference in Sacramento with three days of various hands on classes including a good deal focusing on battery backup systems. It was initially only open to NABCEP certified folks but registration was eventually opened up to others. You might

Re: [RE-wrenches] Flat Tile Roofs

2013-04-01 Thread August Goers
: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org -- August Goers Luminalt Energy Corporation 1320 Potrero Avenue San Francisco, CA 94110 O: 415.641.4000 M

Re: [RE-wrenches] Conductor Sizing for Supply Side Connection

2013-02-27 Thread August Goers
the manufacturer to list the entire service and line tap in my experience. You might want to look into that if you think your jurisdiction might have similar concerns. Good luck! Best, August August Goers Luminalt Energy Corporation 1320 Potrero Avenue San Francisco, CA 94110 m

Re: [RE-wrenches] Conductor Sizing for Supply Side Connection

2013-02-27 Thread August Goers
Jeremy, Good point. Even under the 2008 NEC 690.64(B)(2) you can install up to a 40 Amp breaker on the load side as long as it is on the opposite side of the input feed per 690.64(B)(7). Garrison, do you need a 60 A breaker? I haven't used this product myself, but if the continuous output

Re: [RE-wrenches] Conductor Sizing for Supply Side Connection

2013-02-27 Thread August Goers
rather than through the battery inverter but this definitely has the potential to open up doors and potentially reduce equipment cost. Best, August August Goers Luminalt Energy Corporation 1320 Potrero Avenue San Francisco, CA 94110 m: 415.559.1525 o: 415.641.4000 aug

Re: [RE-wrenches] Corrugated roofing mounts

2013-02-16 Thread August Goers
Hi William, You may have already seen this corrugated bracket from S-5: http://www.s-5.com/clamps/index_2624.cfm I believe it’s best to have the screws go into purlins. These are fairly low cost; contact me offlist if you want me to send you distributor contact info. As far as figuring out

[RE-wrenches] getting PV modules up to the roof

2013-02-07 Thread August Goers
Hi Wrenches, I imagine that all of us working in rooftop PV have put some good hard thought on the best way to get the modules up to the roof. There are various lifts on the market, you can hoist them with ropes manually, or walk them up a ladder (sling them over your back). I find that the

Re: [RE-wrenches] getting PV modules up to the roof

2013-02-07 Thread August Goers
-0950 *From:* re-wrenches-boun...@lists.re-wrenches.org [mailto: re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *August Goers *Sent:* Thursday, February 07, 2013 12:44 PM *To:* RE-wrenches *Subject:* [RE-wrenches] getting PV modules up to the roof Hi Wrenches, I imagine that all

Re: [RE-wrenches] Are PV Systems Mechanical Equipment

2013-02-01 Thread August Goers
Hi Jason, Perhaps you can point out that NEC 690 addresses photovoltaics and points to other sections of the code as necessary. I don't think NEC 690 mentions that PV is mechanical equipment. -August *From:* re-wrenches-boun...@lists.re-wrenches.org [mailto:

Re: [RE-wrenches] Bonding bushings?

2013-01-24 Thread August Goers
clarification point and directs you to 250.92(B)(2) through (B)(4). Best, August August Goers Luminalt Energy Corporation 1320 Potrero Avenue San Francisco, CA 94110 m: 415.559.1525 o: 415.641.4000 aug...@luminalt.com -Original Message- From: re-wrenches-boun...@lists.re-wrenches.org

Re: [RE-wrenches] Equipment Rating vs. Terminal/Lug Rating

2013-01-24 Thread August Goers
Hi Chris, Here are my thoughts on your questions/notes below. Please note that I'm in no way an expert in this field, I've only had to deal with it from time to time through our workings with various situations and AHJs. 1. I believe terminal and equipment ratings can vary within one

Re: [RE-wrenches] PV permitting standards

2013-01-21 Thread August Goers
Marco, Nearly all jurisdictions in the SF Bay Area require design drawings in order to obtain a permit. However, the City of San Francisco has an expedited permit process for systems of 4 kW or less. If you sign off on all for their requirements on a checklist you do not need to submit drawings

Re: [RE-wrenches] Best racking systems (was Awkward Mid-clamps jigs for installing or removing modules?)

2013-01-18 Thread August Goers
All - This thread brought up a question I've been mulling over for a while - what is the best flush mount rack out there these days on the market? I've tried a lot of different racks and am always on the hunt to find something better but the more experience I get I keep going back to Pro Solar

Re: [RE-wrenches] Best racking systems (was Awkward Mid-clamps jigs for installing or removing modules?)

2013-01-18 Thread August Goers
that justifies stocking another type of panel and or racking system. Best, August August Goers Luminalt Energy Corporation 1320 Potrero Avenue San Francisco, CA 94110 m: 415.559.1525 o: 415.641.4000 aug...@luminalt.com *From:* re-wrenches-boun...@lists.re-wrenches.org [mailto: re

Re: [RE-wrenches] GEC for Micro-Inverters and ACPV Modules

2013-01-16 Thread August Goers
Thanks Brian. This has been a helpful thread for me. Mark Frye, thanks for kicking it off. Best, August August Goers Luminalt Energy Corporation 1320 Potrero Avenue San Francisco, CA 94110 m: 415.559.1525 o: 415.641.4000 aug...@luminalt.com *From:* re-wrenches-boun...@lists.re

Re: [RE-wrenches] GEC for Micro-Inverters and ACPV Modules

2013-01-15 Thread August Goers
-Original Message- From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of August Goers Sent: Monday, January 14, 2013 4:32 PM To: RE-wrenches Subject: Re: [RE-wrenches] GEC for Micro-Inverters and ACPV Modules Hi Mark, There have

Re: [RE-wrenches] GEC for Micro-Inverters and ACPV Modules

2013-01-14 Thread August Goers
Hi Mark, There have been some recent threads on this list touching on this topic. As far as I understand, Enphase microinvertes still require a GEC up to and including the 2011 NEC. I don't know about the 2014 NEC. Enphase bonds the positive DC module conductor to ground. Pages 16 and 17 of

Re: [RE-wrenches] EPDM Roof Attachment/Flashing

2013-01-02 Thread August Goers
Hi Larry - Chem Curbs might work for the application you're describing: http://chemlink.com/content/docs_new/brochures/brochure3.pdf The curb is about 2 high if I remember correctly so a 3 stanchion will work. Best, August *From:* re-wrenches-boun...@lists.re-wrenches.org

Re: [RE-wrenches] RFI Interference with Ham radios

2012-12-26 Thread August Goers
I haven't seen Enphase units interfering with any radio equipment and we do have several clients with really specialized radio gear. However, I've seen all sorts of relatively unexplainable electrical interference affecting the communications with the Envoy box. This may either be between the

Re: [RE-wrenches] off grid PV connected to generator

2012-12-13 Thread August Goers
Hi All -- Thanks for the feedback. Yea, we've always used Sunny Islands with batteries for anything that needs to run off grid. This was more of just a theoretical question. From what I heard, it sounds like the excess current from the PV might damage the generator (or I suppose anything

[RE-wrenches] off grid PV connected to generator

2012-12-12 Thread August Goers
Hi Wrenches, I have a quick theoretical question related to trying to run a standard grid tied PV system off grid with a generator. A client called me wondering if he could run his small Honda generator off grid connected to his load center and then turn on his PV system. What would happen if

Re: [RE-wrenches] Power One Microinverters

2012-12-10 Thread August Goers
*To:* RE-wrenches *Subject:* Re: [RE-wrenches] Power One Microinverters Hi August. I'm curious about these inverters as well. Have you learned anything outside of the Wrenches list about their track record? Take care. Bruce On 10/30/2012 9:08 AM, August Goers wrote: Hi Wrenches - Has anyone

Re: [RE-wrenches] EGC vs GEC, separately derived system

2012-11-29 Thread August Goers
installed costs. Best, August August Goers Luminalt Energy Corporation 1320 Potrero Avenue San Francisco, CA 94110 m: 415.559.1525 o: 415.641.4000 aug...@luminalt.com *From:* re-wrenches-boun...@lists.re-wrenches.org [mailto: re-wrenches-boun...@lists.re-wrenches.org] *On Behalf

[RE-wrenches] Power One Microinverters

2012-10-30 Thread August Goers
device called Aurora CDD communicates wirelessly with the microinverters compared to power line communications with Enphase. They also seem to be at a higher price point compared to Enphase although they are higher wattage at 250 and 300 Watts. Best, August August Goers Luminalt Energy

Re: [RE-wrenches] AC Modules ready for primetime?

2012-10-30 Thread August Goers
the SolarBridge AC module but I'm not sure about availability. Good luck with it. Best, August August Goers Luminalt Energy Corporation San Francisco, CA 94110 m: 415.559.1525 o: 415.641.4000 aug...@luminalt.com *From:* re-wrenches-boun...@lists.re-wrenches.org [mailto: re

Re: [RE-wrenches] Enphase and Romex

2012-10-25 Thread August Goers
Jason, Glenn's point below sounds correct to me. We've run several microinverter projects with romex, but always have to do the transition in the attic because romex is not rated for wet locations. Some of the local jurisdictions around the Bay Area are onto this point. Also, NEC 250.64(B)

Re: [RE-wrenches] Ten K Solar

2012-10-22 Thread August Goers
tenKsolar has contacted me several times recently about their product. They have a slightly interesting concept with the cross woven cell wiring but otherwise I'm not sold. Not only am I not sold but I'd stay away with a 10' pole. At least for me, the last thing I need is to be experimenting with

[RE-wrenches] center fed main panel and 120% rule

2012-10-15 Thread August Goers
, is it okay to install our inverter breaker on either the bottom or the top? If not, then our only resort is to either upgrade the service or downsize the main breaker which isn't always possible to do. Thanks for your thoughts in advance. Best, August August Goers Luminalt Energy

Re: [RE-wrenches] center fed main panel and 120% rule

2012-10-15 Thread August Goers
Mountain Solar, Inc. www.bluemountainsolar.com On 10/15/2012 9:32 AM, August Goers wrote: Hi Wrenches, Here is yet another 120% rule question as it relates to center fed main panels. 2011 NEC 705.12 deals with inverter point of connection and 705.12(D)(7) reads: *Inverter Output Connection

Re: [RE-wrenches] Two NEC questions

2012-10-14 Thread August Goers
Hi David and Rebecca - We're still in the 2008 code cycle here in California so AFCI hasn't become an issue yet. I just listened to a webinar by SMA last week and I believe that their AFCI Sunny Boys wont' be shipping for at least a couple of months. Rebecca, have you already installed this

Re: [RE-wrenches] Two NEC questions

2012-10-14 Thread August Goers
replacing PV arrays and other products may be far more costly than installing an AFCI detector. Bill. *From:* re-wrenches-boun...@lists.re-wrenches.org [ mailto:re-wrenches-boun...@lists.re-wrenches.orgre-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *August Goers *Sent:* Sunday

[RE-wrenches] Independent vs common trip breakers

2012-09-25 Thread August Goers
Hi Wrenches, Do any of you know the reason why we might use an independent trip versus a common trip two pole breaker for a solar inverter? My understanding is that the independent trip will only trip the individual line effected by the overcurrent condition compared to the common trip which

Re: [RE-wrenches] Independent vs common trip breakers

2012-09-25 Thread August Goers
William, Good points. Keep in mind that both of these breakers have handle ties (both are two pole), it's just that one can trip independently and the other forces both to trip. What is the correct solution for 240 V solar inverters? It seems like common trip is the best way to go but I've not

[RE-wrenches] corrosion on SHW storage tank fitting

2012-09-05 Thread August Goers
nipple to corrode so quickly. I wonder if there is a grounding issue with the tank or maybe it's just the nature of galvanized fittings. Best, August August Goers Luminalt Energy Corporation 1320 Potrero Avenue San Francisco, CA 94110 m: 415.559.1525 o: 415.641.4000 aug

Re: [RE-wrenches] Power line communications interference

2012-08-23 Thread August Goers
William, You might try calling Enphase again. I was discussing a similar issue with them recently and they said that they have a noise filter option for handling noisy lines. As with all tech support, some representatives are better than others. -August August Goers Luminalt Energy

Re: [RE-wrenches] S5! question

2012-08-20 Thread August Goers
All - We attempted a couple of jobs with the S5! kit and no rails and lining everything up was tough. Pro Solar rail directly to the S5! clamps works great or Unirac with L feet even gives more installation flexibility. Sounds like almost all of the responses are along these same lines.

Re: [RE-wrenches] Best practices for comp shingle flashing?

2012-08-17 Thread August Goers
Hi Eric, We've used TTi, EcoFasten, and Quick Mount. I like Quick Mount the best but they are a bit pricy so we've been using Eco Fasten for the majority of our work over the last year. If anything, I've found that TTi requires more labor and is more likely to require shingle cutting plus I'm

Re: [RE-wrenches] Wind Turbines killing birds and bats

2012-06-22 Thread August Goers
Hi All Wind Wrenches, We have 5 turbines recently installed in the Golden Gate National park land in San Francisco. They are small 1 kW vertical axis units - I was not happy about installing vertical axis but that was what the client wanted. The good news is that each turbine is being monitored

Re: [RE-wrenches] Wind Turbines killing birds and bats

2012-06-22 Thread August Goers
) to see. Thank you, Jason Lerner Waldron Power and Light Co. On Jun 22, 2012, at 8:01 AM, August Goers wrote: Hi All Wind Wrenches, We have 5 turbines recently installed in the Golden Gate National park land in San Francisco. They are small 1 kW vertical axis units - I was not happy about

Re: [RE-wrenches] Solar sub-contractors barred from project publication

2012-06-13 Thread August Goers
Jeff, Yea, sounds like a pain. We've been through this before with several high profile projects in the Bay Area. Luckily, we have a lawyer on staff and have gone through the waiver process in order to obtain marketing approval. It might be possible to obtain a waiver that blankets the future

[RE-wrenches] Independent vs common trip two-pole breakers

2012-05-11 Thread August Goers
busbars) seems to be more prevalent on the common trip models. Anyone a breaker guru who can explain why one might one or the other? Thanks, August August Goers Luminalt Energy Corporation 1320 Potrero Avenue San Francisco, CA 94110 o: 415.641.4000 aug...@luminalt.com

Re: [RE-wrenches] 120% Rule - applying to multiple load centers etc

2012-05-08 Thread August Goers
that there's an enormous fusion reactor safely banked a few million miles from us. It delivers more than we could ever use in just about 8 minutes. And it's wireless! ~William McDonough On Mon, May 7, 2012 at 10:55 AM, August Goers aug...@luminalt.com wrote: Hi Wrenches, Please see question below

[RE-wrenches] 120% Rule - applying to multiple load centers etc

2012-05-07 Thread August Goers
Hi Wrenches, Please see question below forwarded from one of my fellow engineers. Thanks, August *From:* Eric Schoonbaert [mailto:e...@luminalt.com] *Sent:* Monday, May 07, 2012 9:38 AM *To:* August Goers *Subject:* 120% Rule The 120% rule, and how it is applied to panel board bus size

Re: [RE-wrenches] under performing Enphase inverters

2011-11-04 Thread August Goers
We have over 1000 Enphase units installed of multiple types - mostly M210s and M190s. We just had our first overt failure of an M190. It just went dead after a couple of months of operation. I'll keep my eye out for underperforming units but haven't noticed any yet. -August *From:*

[RE-wrenches] SHW collector absorber plate issue

2011-09-23 Thread August Goers
Hi Wrenches, We have several installations from a few years ago where we're noticing strange discoloration around the corners of the absorber plate: I'll keep the manufacturer anonymous at this point but I'm wondering if any of you have experience with this and if so what the problem might

[RE-wrenches] Invitation to connect on LinkedIn

2011-09-22 Thread August Goers via LinkedIn
LinkedIn August Goers requested to add you as a connection on LinkedIn: -- Doug, I'd like to add you to my professional network on LinkedIn. - August Accept invitation from August Goers http://www.linkedin.com/e/-xy4d8h-gsvto1jz-3

[RE-wrenches] working spaces for disconnects and meter sockets

2011-08-17 Thread August Goers
to be mounted above a sloped driveway. Any opinions and interpretations would be appreciated. Thanks, August August Goers Luminalt Energy Corporation 1320 Potrero Avenue San Francisco, CA 94110 m: 415.559.1525 o: 415.641.4000 aug...@luminalt.com

Re: [RE-wrenches] Odd Inverter Behavior

2011-07-01 Thread August Goers
and the modules were operated at to high a voltage above the Vmp voltage, I replaced the inverter and problem fixed. -- *From:* August Goers aug...@luminalt.com *To:* RE-wrenches re-wrenches@lists.re-wrenches.org *Sent:* Thu, February 3, 2011 6:01:11 PM *Subject:* [RE