Hi Christopher
If it is a newer radian then it has an ac coupling mode.
When the batteries start to reach the charge set point, the inverter starts
pushing the hz up snd up. Once it gets to 64, all new GT inverters shut off,
including enphase.
Voltage drops, hz drops, 5 minute delay, rinse
You can use the frequency shift in the radian inverter to shut down the
micros. Yes gets to 64hz but probably not going to happen very often?
Or you could find a remote controlled relay controlled via the radian aux
relay.
Jay
Peltz power.
> On Nov 23, 2021, at 7:39 AM, August Goers wrote:
It was tough for me to figure out how to write my email and not make it
confusing.
What I am worried about is the microinverter system operating when the
utility goes down and the microinverters continuing to operate and
charge the batteries as a load. I need to disconnect the microinverter
ing errors.-- Original
message--From: Christopher WarfelDate: Tue, Nov 23, 2021 10:24 AMTo:
re-wrenches@lists.re-wrenches.org;Cc: Subject:[RE-wrenches] Rapid Shutdown
Control for a System for a Multimode System Adding an Array to a Subpanel in
Garage
I would appreciate ideas on how to
Hi Chris - If I'm following you right, you have a PV system on a detached
garage that ties into a backup subpanel also in the garage? The code only
requires the RSID (rapid shutdown initiation device) to be on the exterior
of the building. Would it work to put the RSID on the garage exterior? You
c
I would appreciate ideas on how to shut down a proposed microinverter
system on a garage that is 100% serviced by an Outback Radian multimode
system in the main building that has the garage on the back up service
panel in the main building.
Garage has a MLO subpanel that is connected to the mu