Re: [RE-wrenches] Rapid Shutdown Control for a System for a Multimode System Adding an Array to a Subpanel in Garage - Update

2021-12-01 Thread Christopher Warfel
ons. Have a good Thanksgiving  and Stay Safe. Take Care All *From:* RE-wrenches *On Behalf Of *Christopher Warfel *Sent:* Tuesday, November 23, 2021 9:40 AM *To:* August Goers ; RE-wrenches *Subject:* Re: [RE-wrenches] Rapid Shutdown Control for a System for a Multimode System Adding an

Re: [RE-wrenches] Rapid Shutdown Control for a System for a Multimode System Adding an Array to a Subpanel in Garage

2021-11-24 Thread Christopher Warfel
 and Stay Safe. Take Care All *From:* RE-wrenches *On Behalf Of *Christopher Warfel *Sent:* Tuesday, November 23, 2021 9:40 AM *To:* August Goers ; RE-wrenches *Subject:* Re: [RE-wrenches] Rapid Shutdown Control for a System for a Multimode System Adding an Array to a Subpanel in Garage

Re: [RE-wrenches] Rapid Shutdown Control for a System for a Multimode System Adding an Array to a Subpanel in Garage

2021-11-23 Thread Jay
Hi Christopher If it is a newer radian then it has an ac coupling mode. When the batteries start to reach the charge set point, the inverter starts pushing the hz up snd up. Once it gets to 64, all new GT inverters shut off, including enphase. Voltage drops, hz drops, 5 minute delay, rinse

Re: [RE-wrenches] Rapid Shutdown Control for a System for a Multimode System Adding an Array to a Subpanel in Garage

2021-11-23 Thread Jay
You can use the frequency shift in the radian inverter to shut down the micros. Yes gets to 64hz but probably not going to happen very often? Or you could find a remote controlled relay controlled via the radian aux relay. Jay Peltz power. > On Nov 23, 2021, at 7:39 AM, August Goers wrote:

Re: [RE-wrenches] Rapid Shutdown Control for a System for a Multimode System Adding an Array to a Subpanel in Garage

2021-11-23 Thread Christopher Warfel
It was tough for me to figure out how to write my email and not make it confusing. What I am worried about is the microinverter system operating when the utility goes down and the microinverters continuing to operate and charge the batteries as a load.  I need to disconnect the microinverter

Re: [RE-wrenches] Rapid Shutdown Control for a System for a Multimode System Adding an Array to a Subpanel in Garage

2021-11-23 Thread Glenn Burt
ing errors.-- Original message--From: Christopher WarfelDate: Tue, Nov 23, 2021 10:24 AMTo: re-wrenches@lists.re-wrenches.org;Cc: Subject:[RE-wrenches] Rapid Shutdown Control for a System for a Multimode System Adding an Array to a Subpanel in Garage I would appreciate ideas on how to

Re: [RE-wrenches] Rapid Shutdown Control for a System for a Multimode System Adding an Array to a Subpanel in Garage

2021-11-23 Thread August Goers
Hi Chris - If I'm following you right, you have a PV system on a detached garage that ties into a backup subpanel also in the garage? The code only requires the RSID (rapid shutdown initiation device) to be on the exterior of the building. Would it work to put the RSID on the garage exterior? You c

[RE-wrenches] Rapid Shutdown Control for a System for a Multimode System Adding an Array to a Subpanel in Garage

2021-11-23 Thread Christopher Warfel
I would appreciate ideas on how to shut down a proposed microinverter system on a garage that is 100% serviced by an Outback Radian multimode system in the main building that has the garage on the back up service panel in the main building. Garage has a MLO subpanel that is connected to the mu