Re: [RE-wrenches] Remote battery disconnects

2023-02-04 Thread Christopher Warfel via RE-wrenches
Thanks for doing this.  Chris On 2/1/2023 4:49 PM, Brian Mehalic via RE-wrenches wrote: Most firefighters are not electrical engineers; nor are most insurance agents. However both of those groups are stakeholders with influence over codes and standards. Some may say too much influence, but the

Re: [RE-wrenches] Remote battery disconnects

2023-02-03 Thread jay via RE-wrenches
As 480.7(B) says single and double homes, that going with the mike holt literal interpretation to me says that even if you have a remote power shed it would still require the remote disconnect. As that section doesn’t say that the power system is in the house or not. (A) doesn’t apply as the

Re: [RE-wrenches] Remote battery disconnects

2023-02-03 Thread Jason Szumlanski via RE-wrenches
>>> advocates. If someone is on the code panel, they are actually limited in >>> how they can suggest new changes to the codes, they can only promote public >>> inputs that are submitted by people like us, so even if it feels like a >>> waist of time, it really is important that we all submi

Re: [RE-wrenches] Remote battery disconnects

2023-02-03 Thread August Goers via RE-wrenches
ly >> want to promote our best interests have something they can leverage for us. >> To those here who do help with the codes and help to advocate for us, THANK >> YOU SO MUCH!!! >> >> Thanks, >> Kienan >> >> >> *Green-Go Solar Distribution LLC Maxfield

Re: [RE-wrenches] Remote battery disconnects

2023-02-03 Thread Jason Szumlanski via RE-wrenches
vocate for us, THANK > YOU SO MUCH!!! > > Thanks, > Kienan > > > *Green-Go Solar Distribution LLC Maxfield Solar LLC (installation and > consulting company) * > *maxfieldso...@hotmail.com* > *(801) 631-5584(Cell)* > -- > *From:* RE-wrenches on behalf > of bob--- vi

Re: [RE-wrenches] Remote battery disconnects

2023-02-02 Thread William Miller via RE-wrenches
Kieran: You’ve got me confused with someone else. I do not pretend to know anything about Sol-arc. ( I do know if I was inventing electrical equipment I would not put “arc” in the name.) Wm On Thu, Feb 2, 2023 at 3:53 PM Kienan Maxfield via RE-wrenches < re-wrenches@lists.re-wrenches.org>

Re: [RE-wrenches] Remote battery disconnects

2023-02-02 Thread Kienan Maxfield via RE-wrenches
t: Re: [RE-wrenches] Remote battery disconnects SPDs or (MOVs) on the PV input side of a charge controller are not wired to snub excessive PV voltage. They are wired from PV+ to GND and the other from PV- to GND and only the two in series, at double the MOV clamp voltage would have any effect o

Re: [RE-wrenches] Remote battery disconnects

2023-02-01 Thread bob--- via RE-wrenches
 SPDs or (MOVs) on the PV input side of a charge controller are not wired to snub excessive PV voltage. They are wired from PV+ to GND and the other from PV- to GND and only the two in series, at double the MOV clamp voltage would have any effect on clamping the PV+/PV- voltage. SPDs are

Re: [RE-wrenches] Remote battery disconnects

2023-02-01 Thread Jason Szumlanski via RE-wrenches
I have been following this discussion intently. I hate to say it, but it all sounds like a major case being made for AC-coupled system architecture, and even integrated "AC Batteries" like Powerwalls and Encharge that integrate the battery and inverter into listed Energy Storage Systems. As

Re: [RE-wrenches] Remote battery disconnects

2023-02-01 Thread Brian Mehalic via RE-wrenches
Most firefighters are not electrical engineers; nor are most insurance agents. However both of those groups are stakeholders with influence over codes and standards. Some may say too much influence, but the fact of the matter is that code making is a group/consensus process, and very often none of

Re: [RE-wrenches] Remote battery disconnects

2023-02-01 Thread James Jefferson Jarvis via RE-wrenches
On 2/1/2023 2:58 PM, Starlight via RE-wrenches wrote: Have you (or any) installed surge suppression on the PV input side to clamp the open circuit voltage surge? That's not where the issue is and isn't really a solution. As I explained in my previous e-mail, the issue is the open circuit on

Re: [RE-wrenches] Remote battery disconnects

2023-02-01 Thread Starlight via RE-wrenches
Have you (or any) installed surge suppression on the PV input side to clamp the open circuit voltage surge? Larry Crutcher Starlight Solar Power Systems On Feb 1, 2023, at 1:23 PM, William Bryce via RE-wrenches wrote: I can also backup what Jim has said, and have seen the same gear

Re: [RE-wrenches] Remote battery disconnects

2023-02-01 Thread William Bryce via RE-wrenches
I can also backup what Jim has said, and have seen the same gear destroyed by removing the battery abruptly when the controller is under heavy load. They can die, and sometimes die spectacularly. Have seen SolArk inverters integrated MPPT controllers blow up when lithium battery BMS disconnects.

Re: [RE-wrenches] Remote battery disconnects

2023-02-01 Thread James Jefferson Jarvis via RE-wrenches
On 2/1/2023 12:25 PM, Alex MeVay via RE-wrenches wrote: Although our controllers are probably smaller than what you would be considering in this discussion, surviving a load dump (suddenly disconnected battery) is an engineering requirement for us, and likely would be for other responsible

Re: [RE-wrenches] Remote battery disconnects

2023-02-01 Thread Jeff Clearwater via RE-wrenches
es; will...@millersolar.com *Subject:* Re: [RE-wrenches] Remote battery disconnects Brian and William, With all due respect, I think your geographical location of California may be limiting in your understanding of the implications of local power security. Where I am in Minnesota and where I work

Re: [RE-wrenches] Remote battery disconnects

2023-02-01 Thread Alex MeVay via RE-wrenches
> Oh, yeah, the charge controller blowing up thing: Does anyone have any > factual data to share on this? Although our controllers are probably smaller than what you would be considering in this discussion, surviving a load dump (suddenly disconnected battery) is an engineering requirement for

Re: [RE-wrenches] Remote battery disconnects

2023-01-30 Thread Jerry Shafer via RE-wrenches
t; supply an AC disconnect (meeting all requirements for accessibility and > marking) that will disconnect all premise wiring except the pressure pump. > > > > By the way, I will of course be trying to apply the logic that the voltage > specification is for nominal battery voltage a

Re: [RE-wrenches] Remote battery disconnects

2023-01-30 Thread Brian Mehalic via RE-wrenches
-wrenches; will...@millersolar.com Subject: Re: [RE-wrenches] Remote battery disconnects   Brian and William,   With all due respect, I think your geographical location of California may

Re: [RE-wrenches] Remote battery disconnects

2023-01-29 Thread William Miller via RE-wrenches
From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *Jeremy Rodriguez via RE-wrenches *Sent:* Saturday, January 28, 2023 10:12 AM *To:* cwar...@entech-engineering.com; RE-wrenches *Cc:* Jeremy Rodriguez *Subject:* Re: [RE-wrenches] Remote battery disconnects  *2020 Code

Re: [RE-wrenches] Remote battery disconnects

2023-01-29 Thread Christopher Warfel via RE-wrenches
*Sent:* Saturday, January 28, 2023 10:12 AM *To:* cwar...@entech-engineering.com; RE-wrenches *Cc:* Jeremy Rodriguez *Subject:* Re: [RE-wrenches] Remote battery disconnects  *2020 Code Language:* /*48

Re: [RE-wrenches] Remote battery disconnects

2023-01-28 Thread Bradley Bassett via RE-wrenches
oth panel types, and then a dc disconnect with no >>> code reference. Was trying to convey a reasonable, safe approach. A lot >>> of bad information from fire department solar consultants making a lot of >>> money fear mongering, which has led to this type of situati

Re: [RE-wrenches] Remote battery disconnects

2023-01-28 Thread Brian Mehalic via RE-wrenches
-5600www.millersolar.comCA Lic. 773985  From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jeremy Rodriguez via RE-wrenchesSent: Saturday, January 28, 2023 10:12 AMTo: cwar...@entech-engineering.com; RE-wrenchesCc: Jeremy RodriguezSubject: Re: [RE-wrenches] Remote

Re: [RE-wrenches] Remote battery disconnects

2023-01-28 Thread James Jarvis via RE-wrenches
t; By the way, I will of course be trying to apply the logic that the >>>> voltage specification is for nominal battery voltage and this project >>>> having a nominal 48 volt bank does not require the battery disconnect. >>>> >>>&

Re: [RE-wrenches] Remote battery disconnects

2023-01-28 Thread Brian Mehalic via RE-wrenches
scadero, CA 93422805-438-5600www.millersolar.comCA Lic. 773985  From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Glenn Burt via RE-wrenchesSent: Friday, January 27, 2023 11:46 AMTo: William Miller via RE-wrenchesCc: Glenn BurtSubject: Re: [RE-wrenches] Remote battery disconnects 

Re: [RE-wrenches] Remote battery disconnects

2023-01-28 Thread William Miller via RE-wrenches
logic that the >>>> voltage specification is for nominal battery voltage and this project >>>> having a nominal 48 volt bank does not require the battery disconnect. >>>> >>>> >>>> >>>> I will let the g

Re: [RE-wrenches] Remote battery disconnects

2023-01-28 Thread James Jarvis via RE-wrenches
ill let the group know what response I receive. Regardless of how >>> this works in this jurisdiction, I think these are both valid arguments >>> worth trying in any jurisdiction requiring the battery disconnect. Some >>> officials are amenable to dialog and negotiation

Re: [RE-wrenches] Remote battery disconnects

2023-01-28 Thread William Miller via RE-wrenches
g and negotiation and some are less so. >> >> >> >> >> >> William Miller >> >> >> >> Miller Solar >> >> 17395 Oak Road, Atascadero, CA 93422 >> >> 805-438-5600 >> >> www.millersolar.com >> >> CA

Re: [RE-wrenches] Remote battery disconnects

2023-01-28 Thread jay via RE-wrenches
> > www.millersolar.com <http://www.millersolar.com/> > CA Lic. 773985 > > > > From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org > <mailto:re-wrenches-boun...@lists.re-wrenches.org>] On Behalf Of Jeremy > Rodriguez via RE-wrenches > Sent

Re: [RE-wrenches] Remote battery disconnects

2023-01-28 Thread William Bryce via RE-wrenches
7395 Oak Road, Atascadero, CA 93422 > > 805-438-5600 > > www.millersolar.com > > CA Lic. 773985 > > > > > > *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On > Behalf Of *Jeremy Rodriguez via RE-wrenches > *Sent:* Saturday,

Re: [RE-wrenches] Remote battery disconnects

2023-01-28 Thread William Miller via RE-wrenches
...@lists.re-wrenches.org] *On Behalf Of *Jeremy Rodriguez via RE-wrenches *Sent:* Saturday, January 28, 2023 10:12 AM *To:* cwar...@entech-engineering.com; RE-wrenches *Cc:* Jeremy Rodriguez *Subject:* Re: [RE-wrenches] Remote battery disconnects  *2020 Code Language:* *480.7 DC Disconnect Methods

Re: [RE-wrenches] Remote battery disconnects

2023-01-28 Thread Kirk Herander via RE-wrenches
t; www.millersolar.com > > CA Lic. 773985 > > > > > > *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On > Behalf Of *Glenn Burt via RE-wrenches > *Sent:* Friday, January 27, 2023 11:46 AM > *To:* William Miller via RE-wrenches > *Cc:* Glenn Burt >

Re: [RE-wrenches] Remote battery disconnects

2023-01-28 Thread Jeremy Rodriguez via RE-wrenches
iller via RE-wrenches Cc: Glenn Burt Subject: Re: [RE-wrenches] Remote battery disconnects Does the AHJ really want the batteries disconnected from conductors, or does he really just want the inverters to stop operating and producing AC within the house? Obviously there is a big difference her

Re: [RE-wrenches] Remote battery disconnects

2023-01-28 Thread Christopher Warfel via RE-wrenches
ne, so please excuse typos and spelling errors. -- Original message-- *From: *William Miller via RE-wrenches *Date: *Fri, Jan 27, 2023 2:26 PM *To: *RE-wrenches; *Cc: *William Miller; *Subject:*[RE-wrenches] Remote battery disconnects Friends: We have a large-ish residential of

Re: [RE-wrenches] Remote battery disconnects

2023-01-27 Thread Mac Lewis via RE-wrenches
;> www.millersolar.com >> >> CA Lic. 773985 >> >> >> >> >> >> *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On >> Behalf Of *Glenn Burt via RE-wrenches >> *Sent:* Friday, January 27, 2023 11:46 AM >> *To:

Re: [RE-wrenches] Remote battery disconnects

2023-01-27 Thread William Miller via RE-wrenches
*Sent:* Friday, January 27, 2023 11:46 AM *To:* William Miller via RE-wrenches *Cc:* Glenn Burt *Subject:* Re: [RE-wrenches] Remote battery disconnects Does the AHJ really want the batteries disconnected from conductors, or does he really just want the inverters to stop operating and producing AC

Re: [RE-wrenches] Remote battery disconnects

2023-01-27 Thread Jeremy Rodriguez via RE-wrenches
I believe midnite still has the remote trip DC PNL mount breakers, but of course, no birdhouse to make it work. Not sure what the trip trigger needs either as far as voltage. -MNEDC250RT Jeremy Rodriguez Solar Installation / Design All Solar, Inc. 1453 M St. Penrose Colorado 81240 Sent by

Re: [RE-wrenches] Remote battery disconnects

2023-01-27 Thread Christopher Warfel via RE-wrenches
errors. -- Original message-- *From: *William Miller via RE-wrenches *Date: *Fri, Jan 27, 2023 2:26 PM *To: *RE-wrenches; *Cc: *William Miller; *Subject:*[RE-wrenches] Remote battery disconnects Friends: We have a large-ish residential off-grid system install coming up.  The AHJ has said

Re: [RE-wrenches] Remote battery disconnects

2023-01-27 Thread Jerry Shafer via RE-wrenches
William We have done 80 kwh Blue planet resi installs in the past (at the time this was as large as we could go in resi) anyway the BMS has a push to start and on/off buttons we just connected into them and we compliant, rotory switch at 24 volts 10 mA is all that is needed, Now not all BMS.s can

Re: [RE-wrenches] Remote battery disconnects

2023-01-27 Thread Jay via RE-wrenches
Good point Glenn. My question is if this system is in its own building. If so it is probably easier to convince the AHJ about not needing a remote battery disco. JayOn Jan 27, 2023, at 12:46 PM, Glenn Burt via RE-wrenches wrote: Does the AHJ really want the batteries disconnected

Re: [RE-wrenches] Remote battery disconnects

2023-01-27 Thread Glenn Burt via RE-wrenches
Does the AHJ really want the batteries disconnected from conductors, or does he really just want the inverters to stop operating and producing AC within the house?Obviously there is a big difference here and it may be changing as the code evolves.-GlennSent from my 'smart'phone, so please

[RE-wrenches] Remote battery disconnects

2023-01-27 Thread William Miller via RE-wrenches
Friends: We have a large-ish residential off-grid system install coming up. The AHJ has said they will require a remote battery disconnect. I suspect there will be fire sprinkler controls and a pressure pump that would become inoperable if this system were engaged. In this case we will apply