2010-01-28 Thread gary
I am using an analog GE kwhmeter on an outback system with battery backup to a protected loads panel. The AC in to the inverteris attached tothe bottom of one leg of the meter and the AC out of the inverter is connected to the top of the other leg. This should give me an accurate record of just

Re: [RE-wrenches] kwh meters

2010-01-28 Thread David Brearley
Is it a Form 12-S meter? If not, that¹s the reason its not working. Here¹s an article you can refer to: http://solarprofessional.com/article/?file=SP1_1_pg16_QandA_3search= David Brearley, Senior Technical Editor SolarPro magazine NABCEP Certified PV Installer 

Re: [RE-wrenches] kwh meters

2010-01-28 Thread Matt Lafferty
Hi Gary, You did say you're using the neutral, so I'm assuming you've got the 5-jaw socket and meter (Form 12S). You also need to make sure the meter itself is non-detented. Once you reconfigure the socket to match the one shown in David's reference you should be good to go. Not sure which

Re: [RE-wrenches] kwh meters

2010-01-28 Thread gary
That's it!! I finally got an answer today from a tech at the meter company and he said the same thing. I should have come here first. What a resource! Gary EastonNABCEP Certified Solar PVNABCEP Certified Solar Thermal APPALACHIAN RENEWABLE POWER LTD.Stewart, Ohio 740-277-8498“I'd put my money on

Re: [RE-wrenches] kwh meters

2010-01-28 Thread toddcory
Here is a repost of this information from 20067 Todd Ok, I called Jake and he forwardedme to Brent Carper (253-395-6818) who works in the Puget Sound Energymetering department. I had a long conversation with him about how tometer battery based, grid tied inverters. The form 12s meter

Re: [RE-wrenches] kwh meters

2010-01-28 Thread Allan Sindelar
Title: Re: [RE-wrenches] kwh meters The 12-S approach in the Solar Pro article only works with 120V inverter systems. I am facing a similar issue with our first XW system, which was chosen for this application because it's the only GTWB 120/240V single inverter unit. We also currently have

Re: [RE-wrenches] kwh meters

2010-01-28 Thread Todd Cory
Title: Re: [RE-wrenches] kwh meters You will have to put a meter on each 120 volt leg... just like on a dual outback system. Todd Allan Sindelar wrote: The 12-S approach in the Solar Pro article only works with 120V inverter systems. I am facing a similar issue with our first XW system