[RE-wrenches] PAE series surge capacity/ power factor ?

2022-01-09 Thread Jeremy Rodriguez
Hello we have a lot of PAE series magnum inverters out there. One client lately has been experiencing voltage drop and failure of PCBs in two of his household appliances. I know it’s common to have some dimming of the lights when a well pump or other large load kicks on, but has anyone ran

[RE-wrenches] Imax disturbance Error

2022-01-09 Thread Mac Lewis
Hello Wrenches, I've got a customer that has an issue with their ~10 yr old SB8000US connected to a quad stack of Sunny Island system that's off-grid. It looks like it's on and off, trying to make power but seems to think there is a problem on the AC side. Do you have any advice as to what may

Re: [RE-wrenches] Imax disturbance Error

2022-01-09 Thread Carl Adams
Mac, SMA tech support told me this usually indicates a failing transformer so as Marco suggests, the patient does not have long to live. I've seen a couple of these at 10+ years of service on the inverter. Was kind of regards Carl Adams SunRock Solar On Sun, Jan 9, 2022, 12:50 PM Mac Lewis

Re: [RE-wrenches] PAE series surge capacity/ power factor ?

2022-01-09 Thread Ray
Long runs of URD direct buried?  Just a nick into the metal can corrode the cable all the way through over time.  We use conduit for almost everything anymore.  The savings with URD doesn't pan out, when you have to abandon the line after 10 years. Ray Walters Remote Solar 303 505-8760 On

Re: [RE-wrenches] Imax disturbance Error

2022-01-09 Thread Marco Mangelsdorf
Hey Mac, It’s been my experience over the years that the Imax failure is fatal. marco On Sunday, January 9, 2022, Mac Lewis wrote: > Hello Wrenches, > > I've got a customer that has an issue with their ~10 yr old SB8000US > connected to a quad stack of Sunny Island system that's off-grid. > >

Re: [RE-wrenches] PAE series surge capacity/ power factor ?

2022-01-09 Thread Jerry Shafer
I would look at connections first, lug that is not as tight as it ne we do to be, a breaker failing, outlets that are either push in wires or have loose connections. Eliminate what you can before looking at the inverters On Sun, Jan 9, 2022, 11:36 AM Jeremy Rodriguez wrote: > > > Hello > we

Re: [RE-wrenches] Imax disturbance Error

2022-01-09 Thread Garrison
I was troubleshooting a site on Friday with the same Imax error on the same SB8000 inverter. Took the cover off and found a cracked capacitor. Inverter was manufactured 12/2021 and SMA is telling me it’s out of warranty (by a week). I’m trying to appeal to their humanity. Good luck!

Re: [RE-wrenches] Imax disturbance Error

2022-01-09 Thread Ray
AC coupled off grid?  Sounds like a good time to go DC coupled. Ray Walters Remote Solar 303 505-8760 On 1/9/22 3:31 PM, Carl Adams wrote: Mac, SMA tech support told me this usually indicates a failing transformer so as Marco suggests, the patient does not have long to live.  I've seen a