I’ve never had LED flicker on the inverter but when battery charging for sure.
The radian has a setting for that.
jay
> On Feb 4, 2022, at 2:12 PM, Bradley Bassett wrote:
>
> I’ve had LED lights, with multiples in one fixture, flicker on grid power.
>
> Brad
>
> Sent from my iPhone
>
HI Eric,
Check that the transfer delay is as short as it can go, about 6 cycles
You might raise the lower voltage limit from 108
Check to make sure all the voltage readings on each inverter are as close as
possible. A real weakness of the OB platform is that you have to calibrate
each item:
I’ve had LED lights, with multiples in one fixture, flicker on grid power.
Brad
Sent from my iPhone
> On Feb 4, 2022, at 7:18 AM, Dana Orzel wrote:
>
> Ditto on misc flickering w LEDs on my Off grid Radian system
> I have some LEDs that are absolutely stable all the time and some of the
>
Friends:
For those of you using Optics, the Event History page has changed. There
is a filter drop-down that you need to use to see things like AGS
activation. I did not notice this at first and it caused me some brief
confusion and wasted time. Hopefully this heads-up will save you from the
Aloha All,
Does anyone have the contact info for the Enphase sales rep for Hawaii ( I
believe the same person is in charge of Northern CA as well) ?
The number I have does not work and customer support was of no help.
___
List sponsored by Redwood
Ditto on misc flickering w LEDs on my Off grid Radian system
I have some LEDs that are absolutely stable all the time and some of the
smaller I guess I’d call them decorative type ones in a hanging lamp over a
dining table seem to be unstable all the time and I would attribute that to
Cheaper
Some LEDs will flicker at times with off grid AC coupled systems. I've
seen this with Outback and Magnum. Some brands of LED seem stable.
Drake Chamberlin
Athens Electric LLC
Ohio Electrical Contractor’s License 44810
CO Master Electrician’s License 4526
NABCEP Certified PV Installation
Not sure about the radians (I've rarely used them) but with the VFX series,
that symptom can sometimes be avoided by programming a cool down period so
that the inverters drop the generator while it is still running at full
speed. Alternatively, by narrowing the generator voltage window at the
I have an off grid system with three GS8048A inverters.
Every time it switches from generator charging to inverting - at the end of
absorption - the lights flicker and a propane boiler in the house goes into
fault.
I'm using Advanced AGS on the Mate3S.
The loads don't exceed about 6 kW right now.
9 matches