Re: [RE-wrenches] Sunny Boy constant off line problem

2011-10-24 Thread maver...@mavericksolar.com
Jeff, I suggest high AC volts is the issues. The second inverter may not have the same settings as the first. The voltage is already being pushed up by the first inverter, maybe the second one is adjusted a little tighter. The SMA config tool can show the settings. Thank you, Maverick

Re: [RE-wrenches] XW on 120v

2011-10-27 Thread maver...@mavericksolar.com
Jay, You need to download Addendum to the Install Manual 976-0222-01-01 rev B and perform the rewriting to 120Vac and install new software using the gateway or System Configuration Tool using 120v software. Let me know if you these off list and I can send them to you. Thank you, Maverick

Re: [RE-wrenches] What inverter? (was Faulty PM-60 circuit board)

2011-11-09 Thread maver...@mavericksolar.com
Joel, That is the fork in the road... To battery-backup or to Not Battery-backup... That is question. If you decide to battery-backup, then the SW is still sweet until it just dies. Any day now... You could switch to a Outback GVFX 3648 or XW 6048 and keep going battery-backup. If the fork

Re: [RE-wrenches] Canadian Solar blemish

2011-11-09 Thread maver...@mavericksolar.com
I have seen this pattern twice. 1. Lightning strike near the array. But the canals are bright white or deep black. I have two of those panels for testing and they still work sorta. 2. A bad batch of EVA or an over-cooked batch of EVA during assembly perhaps. Of course, the photo does not lend

Re: [RE-wrenches] High Voltage MPPT units; Adding battery backup

2011-11-09 Thread maver...@mavericksolar.com
I googled 600 volt switch dual throw and found a cutler-hammer DT363URK. From http://www.alliedelec.com/Images/Products/Datasheets/BM/EATON_CUTLER_HAMMER/416-0447.PDF Not sure if it carries a DC rating all the way to 600v. Thank you, Maverick Maverick Brown BSEET, NABCEP Certified

Re: [RE-wrenches] What inverter? (was Faulty PM-60 circuit board)

2011-11-10 Thread maver...@mavericksolar.com
I agree that one SMA costs less than 24 M190s, but I get two main advantages, 1. individual monitoring of these old modules. (ok, two in string). Any module that can fire up the inverter will report to the enlighten website. 2. Simple expansion of the system. 24 inverters will already be at

Re: [RE-wrenches] Small Off-Grid Inverter Recommendation

2011-11-11 Thread maver...@mavericksolar.com
If you do not need a charger, Exeltech sp1100 or sp600. If you do need a charger, magnum mms1012 Thank you, Maverick Maverick Brown BSEET, NABCEP Certified Solar PV Installer ® President CEO Maverick Solar Enterprises, Inc. Office: 512-919-4493 Cell:512-460-9825 Sent from my

Re: [RE-wrenches] Convert Grid Tie SW4048 to Backup System; Add New Inverter, AC Coupled

2011-11-17 Thread maver...@mavericksolar.com
Dick, What are the customers goals? Battery backup works, but requires knowledge of the customer's expectations (energy, power and flexibility). What is the budget for the upgrades. Do they want more solar? They don't want battery maintenance, will they want generator maintenance? Ask these

Re: [RE-wrenches] High-power MPPT/Charge Controllers?

2011-11-19 Thread maver...@mavericksolar.com
Wow! The most I have in one Outback install is 8 MX60s and 8 VFX3648s. Overall the customer has been happy with the performance and the stacking power save feature helps with idle power draw. As for the OPs request, the most PV still remains to be about 5000 watts gross power per controller

Re: [RE-wrenches] System Performance | Battery Based Grid Tie

2011-12-20 Thread maver...@mavericksolar.com
What is the battery size versus kw of PV? Thank you, Maverick Maverick Brown BSEET, NABCEP Certified Solar PV Installer ® President CEO Maverick Solar Enterprises, Inc. Office: 512-919-4493 Cell:512-460-9825 Sent from my HondaJet! On Dec 20, 2011, at 7:44 PM, Wayne Irwin

Re: [RE-wrenches] Concorde AGMs

2012-02-23 Thread maver...@mavericksolar.com
...@mavericksolar.com maver...@mavericksolar.com wrote: Wrenches, Has anyone else had Concorde AGMs leak around the terminal? Especially the negative post. If so, what did you do? Thank you, Maverick Maverick Brown BSEET, NABCEP Certified Solar PV Installer ® President CEO

Re: [RE-wrenches] broken glass

2012-04-16 Thread maver...@mavericksolar.com
I agree. There is one Group X panel. The 72 cell mono. 24v nominal, 62.2 x 31.8 with varying frame thickness. I use them for all grid interactive and off grid systems. They are more ergonomic and higher voltage helps as well. Conergy, Mage, suntech, astroenrgy, sharp, and many other make or

Re: [RE-wrenches] Xantrex 600v charge controller

2012-05-16 Thread maver...@mavericksolar.com
We used a big ol' fat square D HU361RB for the disco. Too bad Xantrex did not have the forethought to build a SMA type fused segmenting disco. I even thought about building one or buying the SMA type. So budget that extra expense. Unfortunately, Xantrex also reserved the bottom of the chassis

Re: [RE-wrenches] Small battery bank vs too large array

2012-07-19 Thread maver...@mavericksolar.com
I say it is waste of time. 1. AGM batteries can take the high current and you are right, the absorb voltage is reached and the absorb current is tapered rather quickly. Current generation charge controllers are rather fast at the transitions. I have a bunch of data from a system with a

Re: [RE-wrenches] Reliable Cheap Modsine Inverter

2013-03-13 Thread maver...@mavericksolar.com
How about the Exeltech XP125? We have used a few of those and of course many of the Morningstar units. Thank you, Maverick Maverick Brown BSEET, NABCEP Certified Solar PV Installer ® President CEO Maverick Solar Enterprises, Inc. Office: 512-919-4493 Cell:512-460-9825 Sent from

Re: [RE-wrenches] pozi drive

2016-10-09 Thread maver...@mavericksolar.com
Klein makes one and I got it at HomeDepot. Sent from my iPhone > On Oct 9, 2016, at 5:52 PM, jay wrote: > > HI All, > > In looking at the CBI breaker cut sheets, they specify a Pozidrive combi head > tip. > > I know what I Pozi drive tip is and thats what I use, but I

Re: [RE-wrenches] Welding

2017-12-11 Thread maver...@mavericksolar.com
Bill I’m using a Millermatic 212 on a single XW6048 with 16 each PVX3050 AGMs and a 1.4kw array. It typically draws about 4kw to weld at setting 6 out of 10 (1/8” material thickness) using 0.035 wire. I also have a Spectrum 375 and you can not run them both at the same time with only a 6kw

Re: [RE-wrenches] Fullriver Battery meltdown

2018-05-10 Thread maver...@mavericksolar.com
Looks like a mix of old and new Batteries in a cabinet too small to drain excessive heat gain. Was the cabinet shaded? Or exposed to direct sun? Temp sensor on charging source? What size interconnect cables were used? Was it a bus system? Absorb with End Amps was turned on? Sent from my

Re: [RE-wrenches] GENERAC EcoGen 6kw problem

2018-01-08 Thread maver...@mavericksolar.com
Check to see if it’s programming matches its wired and expected voltage output configuration. Sent from my iPhone > On Jan 8, 2018, at 6:13 PM, David Palumbo wrote: > > I am troubleshooting a 6kw EcoGen LP gas generator in my neighborhood that > starts quickly > •

Re: [RE-wrenches] Conext Insight Portal issues

2018-03-09 Thread maver...@mavericksolar.com
I hadn’t noticed, but I also hadn’t been cross checking. I can compare a couple sites to see if it is happening here. Sent from my iPhone > On Mar 9, 2018, at 12:55 PM, Kevin Pegg wrote: > > Hello Wrenches, > > I am curious if others out there are using the