I am glad to see this issue with series strings being brought into 
the discussion.


At 11:53 -0600 3/6/11, Ray Walters wrote:
I've had single strings with equal current through each battery, but 
some batteries would be at 15.5 volts, while others next to it would 
be at 13. The charge controller shuts off when the sum of the 
voltages hits the bulk charge V, but meanwhile some cells are 
chronically overcharged or undercharged. (parallel strings no where 
to be seen)


and..

At 15:10 -0300 3/6/11, James Surrette wrote:
If you hook up 4 x 12V monoblocks for a small 48VDC system and begin 
charging at 58.8V, total voltage will be 58.8V very quickly but 
individual battery voltage will not be 14.7V.  Battery voltage will 
have a large range from 14 to almost 17V.


If you have 4 x 12V monoblocks, they will thrive much better 
connected in parallel than they will in series. The parallel strings 
discussion reappears regularly on this list, and always produces a 
chorus of disapproval, but I think the downsides are over-stated.


Most battery charging regimes are based on bringing the battery up to 
a specific voltage and holding the voltage there for a period of 
time.  This can he achieved with perfect equality for strings of 
batteries in parallel.  (Yes technically you may need to use bus-bars 
to get within millivolts of each other but to be honest who really 
knows the optimum absorption voltage that exactly, and does it 
matter?)   So long as the battery as a whole gets up to and stays at 
the prescribed voltage for long enough, then all the parallel 
batteries will get charged according to the manufacturer's 
instructions.


With batteries in series I am finding that 48V systems are much 
harder to keep properly balanced than in the old days of 12V systems, 
since the current in one string is the same in every cell, whether it 
needs it or not.   Yes you could put diversion load regulators on 
individual 12V batteries in the string, but given the way they are 
priced (by amps) you would end up spending four times as much on 
charge controllers.


To me the issues of unbalanced charging are much worse for batteries 
in series than they are for batteries in parallel.  Now I will go and 
hide from the wrath of the list :-)


have fun,
--
Hugh Piggott

Scoraig
http://www.scoraigwind.co.uk___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] 24 volt Battery Bank comparison

2011-06-03 Thread Ray Walters
I've set electric vehicle parallel strings up like this too. Once a 
month I charge each string separately. At higher charge/ discharge 
rates, the problems of unequal batteries increases dramatically. BTW, 
single strings are not the magic bullet either; I've had single strings 
with equal current through each battery, but some batteries would be at 
15.5 volts, while others next to it would be at 13. The charge 
controller shuts off when the sum of the voltages hits the bulk charge 
V, but meanwhile some cells are chronically overcharged or undercharged. 
(parallel strings no where to be seen)
Manzanita Micro makes a device that shunts current past batteries that 
hit full charge in a string. This monitoring of each individual battery 
is the state of the art right now for Li+ batteries in EVs.
I agree, we need much better battery management and safety devices for 
solar. Its ridiculous some of the mundane issues we discuss here 
sometimes, while hundreds of huge battery packs are just waiting for one 
of us to drop a wrench across the terminals, with zero safety to 
interrupt it, and its all NEC compliant.
Batteries themselves need to have a current limiting device built into 
the positive terminal. Possibly the same device that controls charge 
current to it too?


Dreaming up future BOS equipment,

Ray Walters

On 6/2/2011 7:44 PM, d...@foxfire-energy.com wrote:
What I like best about Mark's set up (the retired phone co. dude w/ 
half a hand), is that he can select individual strings at random. he 
can eq an individual string, or top off a few strings and park them. 
he can even run strings of T 105s, or even nicad (individually of 
course) in the same system as L-16s and the like.. he just reprograms 
the chargers (and logs it). I think he got the design from his days in 
the Navy.


So boB, how about a controller that can be user programed to charge 
multiple battery configurations with a soft switch? i.e. Bank A, Bank 
B...? and while you're at it, maybe a multiple string DC box? 
Something with a shunt and a breaker for each string? A four string 
set up would be nice.


I could use 2% of your first million.

db

Dan Brown
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] 24 volt Battery Bank comparison

2011-06-03 Thread James Surrette

Hi Ray, 

Just a quick chime in on your series string comment. 

If you hook up 4 x 12V monoblocks for a small 48VDC system and begin charging 
at 58.8V, total voltage will be 58.8V very quickly but individual battery 
voltage will not be 14.7V.  Battery voltage will have a large range from 14 to 
almost 17V.  This problem is only exacerbated in higher voltage systems, ie, 
Australian 120VDC.  Stealing from the Telcos, the best solution is an initial 
activation to balance all cells.  When this is completed and assuming all leads 
stay tight, no bad cells, etc the bank will charge and discharge in relative 
harmony.  However, if the cells / batteries are bolted together and discharged 
right out of the gate, there's a good chance SG   Voltages will be all over 
the map in short order.
 
Jamie
 Ray Walters r...@solarray.com 6/3/2011 2:53 PM 
I've set electric vehicle parallel strings up like this too. Once a month I 
charge each string separately. At higher charge/ discharge rates, the problems 
of unequal batteries increases dramatically. BTW, single strings are not the 
magic bullet either; I've had single strings with equal current through each 
battery, but some batteries would be at 15.5 volts, while others next to it 
would be at 13. The charge controller shuts off when the sum of the voltages 
hits the bulk charge V, but meanwhile some cells are chronically overcharged or 
undercharged. (parallel strings no where to be seen)
Manzanita Micro makes a device that shunts current past batteries that hit full 
charge in a string. This monitoring of each individual battery is the state of 
the art right now for Li+ batteries in EVs.
I agree, we need much better battery management and safety devices for solar. 
Its ridiculous some of the mundane issues we discuss here sometimes, while 
hundreds of huge battery packs are just waiting for one of us to drop a wrench 
across the terminals, with zero safety to interrupt it, and its all NEC 
compliant.
Batteries themselves need to have a current limiting device built into the 
positive terminal. Possibly the same device that controls charge current to it 
too?

Dreaming up future BOS equipment,

Ray Walters

On 6/2/2011 7:44 PM, d...@foxfire-energy.com wrote: 


What I like best about Mark's set up (the retired phone co. dude w/ half a 
hand), is that he can select individual strings at random. he can eq an 
individual string, or top off a few strings and park them. he can even run 
strings of T 105s, or even nicad (individually of course) in the same system as 
L-16s and the like.. he just reprograms the chargers (and logs it). I think he 
got the design from his days in the Navy. 



So boB, how about a controller that can be user programed to charge multiple 
battery configurations with a soft switch? i.e. Bank A, Bank B...? and while 
you're at it, maybe a multiple string DC box? Something with a shunt and a 
breaker for each string? A four string set up would be nice.



I could use 2% of your first million. 



db


Dan Brown 
 


This email and its attachments have been scanned by iConnection E-Mail Firewall 
for viruses, spam, and malicious content.
The information transmitted in this email is intended only for the entity or 
person to which it is addressed and may contain confidential/privileged 
material. If you received this in error, please contact the sender and delete 
the material from any computer. Any review, retransmission, dissemination, or 
other use of this information by persons or entities other than the intended 
recipient is strictly prohibited. %^^%
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] 24 volt Battery Bank comparison

2011-06-03 Thread Ray Walters

So would you agree that  battery inequalities show up more at:
a) high discharge/charge rates (greater than C5)
b) higher battery voltages (more cells in series, over 48v)
c) more parallel strings
d) bad/ corroded/ loose connections
e)lack of initial EQ/ activation charge and periodic EQ after long or 
heavy discharges
f) main cables not at least wired to opposite sides of battery bank or 
better: separate parallel cables to buss bar

h) lack of maintenance (watering, uneven cell temperatures)
Did I miss anything?

Ray


On 6/3/2011 12:10 PM, James Surrette wrote:


Hi Ray,


Just a quick chime in on your series string comment.


If you hook up 4 x 12V monoblocks for a small 48VDC system and begin 
charging at 58.8V, total voltage will be 58.8V very quickly but 
individual battery voltage will not be 14.7V.  Battery voltage will 
have a large range from 14 to almost 17V.  This problem is only 
exacerbated in higher voltage systems, ie, Australian 120VDC. 
 Stealing from the Telcos, the best solution is an initial activation 
to balance all cells.  When this is completed and assuming all leads 
stay tight, no bad cells, etc the bank will charge and discharge in 
relative harmony.  However, if the cells / batteries are bolted 
together and discharged right out of the gate, there's a good chance 
SG  Voltages will be all over the map in short order.


Jamie
 Ray Walters r...@solarray.com 6/3/2011 2:53 PM 
I've set electric vehicle parallel strings up like this too. Once a 
month I charge each string separately. At higher charge/ discharge 
rates, the problems of unequal batteries increases dramatically. BTW, 
single strings are not the magic bullet either; I've had single 
strings with equal current through each battery, but some batteries 
would be at 15.5 volts, while others next to it would be at 13. The 
charge controller shuts off when the sum of the voltages hits the bulk 
charge V, but meanwhile some cells are chronically overcharged or 
undercharged. (parallel strings no where to be seen)
Manzanita Micro makes a device that shunts current past batteries that 
hit full charge in a string. This monitoring of each individual 
battery is the state of the art right now for Li+ batteries in EVs.
I agree, we need much better battery management and safety devices for 
solar. Its ridiculous some of the mundane issues we discuss here 
sometimes, while hundreds of huge battery packs are just waiting for 
one of us to drop a wrench across the terminals, with zero safety to 
interrupt it, and its all NEC compliant.
Batteries themselves need to have a current limiting device built into 
the positive terminal. Possibly the same device that controls charge 
current to it too?


Dreaming up future BOS equipment,

Ray Walters

On 6/2/2011 7:44 PM, d...@foxfire-energy.com wrote:

What I like best about Mark's set up (the retired phone co. dude w/ 
half a hand), is that he can select individual strings at random. he 
can eq an individual string, or top off a few strings and park them. 
he can even run strings of T 105s, or even nicad (individually of 
course) in the same system as L-16s and the like.. he just reprograms 
the chargers (and logs it). I think he got the design from his days 
in the Navy.



So boB, how about a controller that can be user programed to charge 
multiple battery configurations with a soft switch? i.e. Bank A, Bank 
B...? and while you're at it, maybe a multiple string DC box? 
Something with a shunt and a breaker for each string? A four string 
set up would be nice.



I could use 2% of your first million.


db


Dan Brown

This email and its attachments have been scanned by iConnection E-Mail 
Firewall for viruses, spam, and malicious content. The information 
transmitted in this email is intended only for the entity or person to 
which it is addressed and may contain confidential/privileged 
material. If you received this in error, please contact the sender and 
delete the material from any computer. Any review, retransmission, 
dissemination, or other use of this information by persons or entities 
other than the intended recipient is strictly prohibited. %^^%



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Re: [RE-wrenches] 24 volt Battery Bank comparison

2011-06-02 Thread The Solar Powered Office of Tom Duffy
Wrenches:

 

This is a really great thread. Here’s my two cents…

I started selling and configuring battery systems when I got out of the Army 
back in 1967 I’m a marine electrician. In the boat environment everybody tries 
to make a big battery out of a bunch of small batteries, Over the years this is 
what I’ve witnessed; All else being equal.

3 parallel strings = 4 ½  to 5 ½ years Max

2 parallel strings = 5 ½ to 6 ½ years Max

1 series string = 8 to 12 years Max

The above seems to hold true if the charge settings, Bulk, Absorb time and 
Voltage are correctly set. But as we all know 85% of the time this is not the 
case.

So my conclusion is that parallel configured banks just about cut the life in 
half. 

And there is always the stories about the guy that drank a quart of Bourbon a 
day and smoked cigars chasing women until he was 102 years old. The same is 
true with batteries… the exception but not the rule.

 

 

  Tom Duffy

  Systems Design Engineer

 

 t...@thesolar.biz

   575-539-2111 X 122

Although no trees were killed in the sending of this message, a large number of 
electrons were terribly inconvenienced.

 

Confidentiality Notice: This message including any attachments is for the sole 
use of the intended recipient(s) and may contain confidential and privileged 
information. Any unauthorized review, use, disclosure or distribution is 
prohibited. If you are not the intended recipient, please contact the sender 
and delete any copies of this message.

  _  

From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Allan Sindelar
Sent: Wednesday, June 01, 2011 11:07 PM
To: re-wrenches@lists.re-wrenches.org
Subject: Re: [RE-wrenches] 24 volt Battery Bank comparison

 

I had done this a few times in the distant past, and also had done it in recent 
years on my own previous battery bank (four strings of S-530s - yes, I know; it 
was in anticipation of future plans to upgrade to 48V, and two strings wouldn't 
have been enough).

It worked fine - and that turned out to be a problem. I had noticed reduced 
capacity, but assumed foolishly that it was simply to age and cycle life (going 
on six years and three teenagers). Found out I had two failed cells in two 
different strings. The parallel connections probably - I'm not sure here - 
allowed the bank to perform more robustly and less obviously weakened. It might 
have even allowed the bank to perform as if both failed cells had been in the 
same string. But it also allowed me to not pay enough attention to a 
potentially serious problem by disguising it.

I blame myself more than the parallel connectors (just some #2 interconnects I 
had lying around). I'm just not sure I would use it on a customer's system.
 

Allan Sindelar
 mailto:al...@positiveenergysolar.com al...@positiveenergysolar.com
NABCEP Certified Photovoltaic Installer
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Positive Energy, Inc.
3201 Calle Marie
Santa Fe, New Mexico 87507
505 424-1112
www.positiveenergysolar.com http://www.positiveenergysolar.com/  

 

 


On 6/1/2011 9:20 AM, toddc...@finestplanet.com wrote: 

Does it make any difference to do as boB recently suggested and inter-connect 
the strings? So in other words, if you have two parallel strings, what happens 
if you parallel each battery in one string with the battery in the other 
string? Has anyone tried this? It might help insure more balance between each 
series string.

 

Todd

 

 

 

On Wednesday, June 1, 2011 3:06am, James Surrette  
mailto:ja...@surrette.com ja...@surrette.com said:

Hi boB,

 

I would say maintenance is a large issue - especially when dealing with L-16's 
or the like, as the number of cells  connections gets large, i.e. 1000-1200AH 
@ 48VDC is three (3) strings, 24 batteries and 72 cells.  Will a client water 
24 cells...maybe - 72??

 

However, from Tech Support days, imbalance is the larger problem.  It seems to 
take 18 months - 3 years and then you would get SG readings where one (1) bank 
was perfect and the other(s) is significantly lower..which is hard to 
overcome without effort (either break the banks  charge independently or 
hammer the banks and allow the high string to get even higher). 

 

One of the key take aways that often gets overlooked is the proper initial 
activation of the strings.  It is impossible for all cells to have identical 
resting voltage.  During commissioning, each string should be charged to 
2.45-2.5VPC and held until all cells read the same voltage.  If running 
multiple strings, then connect the strings and run the entire bank at 
2.45-2.5VPC until all cells measure the same voltage.  Now the bank is well 
balanced and the chances of a major imbalance are greatly reduced.  However, 
even after this effort, if you use an amp clamp, you will notice slight 
differences in the amount of current being accepted by each bank.

 

Best

Re: [RE-wrenches] 24 volt Battery Bank comparison

2011-06-02 Thread Bob-O Schultze
This has been a great string. Battery systems and the weather are the most 
variable things we all have to deal with- and the most misunderstood. I totally 
agree with Darryl here and it makes common sense. PV cells are manufactured 
under seriously strict controls and nearly entirely by machines and robotics, 
yet they still have variance from one individual cell to the next. Battery 
manufacture is better than that? No way.
Having just one string doesn't get you away from the variables, just lessens 
their impact over many cycles and years.
Bob-O
On Jun 2, 2011, at 9:47 AM, Darryl Thayer wrote:

it  is due to differences in the strings; in charging and in discharging 
differentials.  this is due to temp differences very small differences in 
connections and differences in the cells themselves.  
Darry

From: boB Gudgel b...@midnitesolar.com
To: Darryl Thayer daryl_so...@yahoo.com; RE-wrenches 
re-wrenches@lists.re-wrenches.org
Sent: Thursday, June 2, 2011 11:32 AM
Subject: Re: [RE-wrenches] 24 volt Battery Bank comparison

On 6/2/2011 9:03 AM, Darryl Thayer wrote:
 
 Excellent comment tom, so true.  I get concerned that some of my experiences 
 are a collection of exceptions.  I like Larry's comments because he has 
 worked so many systems.  I have seen fires, but  mostly because I have a 
 reputation and people wnat me to come and see what happened.  
 Darryl
 

Now my question would be...  Why ?

I have to think that with more batteries in the system, they are just not 
getting charged as well.

If that's the case, I think this could be fixed. Haven't battery chargers and 
education gotten
better since 1967, Tom ?

boB

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] 24 volt Battery Bank comparison

2011-06-02 Thread Tom Elliot
Not surprised at all about the phone company guy.  It was a phone company guy 
who read me the riot act that no one in their right minds would ever parallel 
battery banks the way PV off-grid systems did and got me to set up my system 
with separate strings connected independently to buss bars.  The battery 
engineer I talked to years ago at Dynasty not only said the same thing but also 
said keeping strings separate meant individual string distance from the bars 
became irrelevant (given correctly sized wire for each string’s parallel 
connectors).  I had a system with 12 100 amphour strings of paired 12v Dynasty 
AGMs which was rock solid until the day I sold the house.   The last time I 
checked the system before the sale no single battery varied from any other in 
the system by more than 1/10 volt and the majority were still holding identical 
voltages.

From: d...@foxfire-energy.com 
Sent: Wednesday, June 01, 2011 4:14 PM
To: RE-wrenches 
Subject: Re: [RE-wrenches] 24 volt Battery Bank comparison

Good thread. Thanks. 
In my experience, it all boils down to the customer. I've seen one temp. set up 
with like 12 strings (for a concert). but they were recharged and sold 
individually within a few weeks.. I've also seen a single string (Teledyne 
aircraft batteries) fail in less than a year.. they were in a brand new 
airplane tug that was never charged -- ever. (the guy said I dunno, it just 
stopped working).

I have one customer who (last I knew) was running 6 strings of mixed aged L-16s 
going on 8 years. Thing is, he's a retired phone company dude (Who's missing 
half of his right hand from using one of those pocket pal screwdriver thingys 
on a key chain in a hot DC rack.. like he'd done hundreds of times before.. but 
that's another tale). But I do like his set up.. he has each string set up with 
it's own fused Disco and Trimetric.. Gives him random control over each string. 
And yes, he keeps a very detailed log, and you can bet that when he takes a 
battery out of service, it's done.


Me? for an average bullet proof off grid system, I shoot for a max of two 
strings for 24V systems (for the redundancy), and manually reconfigure them 
every few years. for 48V systems, I shoot for one string of two Volt cells.. 
thinking that if I loose a cell I can still operate a 46V system until I get a 
replacement.

And Yes, as we all know, there are folks out there that really shouldn't be 
allowed to operate a popsicle stick. 

db



Dan Brown
Foxfire Energy Corp.
Renewable Energy Systems
(802)-483-2564
www.Foxfire-Energy.com
NABCEP #092907-44



   Original Message 
  Subject: Re: [RE-wrenches] 24 volt Battery Bank comparison
  From: Michael Welch michael.we...@re-wrenches.org
  Date: Wed, June 01, 2011 1:43 pm
  To: RE-wrenches re-wrenches@lists.re-wrenches.org

  Every now and then I see reference on this list to the need for thermal 
detection. Here is an interesting, inexpensive piece of equipment that could be 
used for finding hot (loose or corroded) connections, hot batteries, hot PV 
cells in modules, and even poorly insulated spots, its original intended 
purpose:

  http://www.blackanddecker.com/power-tools/TLD100.aspx

  I have one and used it for finding uninsulated spaces, but cannot attest to 
its durability or suitability for the other uses mentioned above.


  boB Gudgel wrote at 01:00 AM 6/1/2011:

  This might be a good reason for an installer to have one of those FLIR (or 
similar) thermal imager cameras.  They're a bit on the expensive side, but 
could
  really be helpful for so many things.  Even just to know if you have left 
a nut loose (under load of course)
  
  boB


  ___
  List sponsored by Home Power magazine

  List Address: RE-wrenches@lists.re-wrenches.org

  Options  settings:
  http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

  List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

  List rules  etiquette:
  www.re-wrenches.org/etiquette.htm

  Check out participant bios:
  www.members.re-wrenches.org





___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org






No virus found in this message.
Checked by AVG - www.avg.com
Version: 10.0.1375 / Virus Database: 1511/3673 - Release Date: 06/01/11
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options

Re: [RE-wrenches] 24 volt Battery Bank comparison

2011-06-02 Thread boB Gudgel



Nobody mentioned this in this thread, but it occurs to me that the 
answer may be made clearer
by looking at the Voc of each battery string after so many Amp-Hours 
(years) of service.


i.e., disconnect the strings' parallel connection and measure the 
individual string voltage after charging them all the best that can be done.


This would be  making the assumption that the batteries themselves were 
fairly equal capacity and voltage at installation time.


And for whatever reasons, connections, temperatures and everything else 
discussed here, the strings degrade differently.


The older and more worn out batteries should have a lower voltage (Voc) 
than the less worn out strings. Thus, the better strings
may be tending to hold up the worse strings by dumping charge into them 
when the whole bank is discharging,

and wasting energy and battery efficiency.

I guess that just large 2V cells are the answer in this case, if at all 
possible.


Thanks for the help on this question !

boB



On 6/2/2011 10:42 AM, Tom Elliot wrote:
Not surprised at all about the phone company guy.  It was a phone 
company guy who read me the riot act that no one in their right minds 
would ever parallel battery banks the way PV off-grid systems did and 
got me to set up my system with separate strings connected 
independently to buss bars.  The battery engineer I talked to years 
ago at Dynasty not only said the same thing but also said keeping 
strings separate meant individual string distance from the bars became 
irrelevant (given correctly sized wire for each string’s parallel 
connectors).  I had a system with 12 100 amphour strings of paired 12v 
Dynasty AGMs which was rock solid until the day I sold the house.   
The last time I checked the system before the sale no single battery 
varied from any other in the system by more than 1/10 volt and the 
majority were still holding identical voltages.

*From:* d...@foxfire-energy.com mailto:d...@foxfire-energy.com
*Sent:* Wednesday, June 01, 2011 4:14 PM
*To:* RE-wrenches mailto:re-wrenches@lists.re-wrenches.org
*Subject:* Re: [RE-wrenches] 24 volt Battery Bank comparison
Good thread. Thanks.
In my experience, it all boils down to the customer. I've seen one 
temp. set up with like 12 strings (for a concert). but they were 
recharged and sold individually within a few weeks.. I've also seen a 
single string (Teledyne aircraft batteries) fail in less than a year.. 
they were in a brand new airplane tug that was never charged -- ever. 
(the guy said I dunno, it just stopped working).
I have one customer who (last I knew) was running 6 strings of mixed 
aged L-16s going on 8 years. Thing is, he's a retired phone company 
dude (Who's missing half of his right hand from using one of those 
pocket pal screwdriver thingys on a key chain in a hot DC rack.. like 
he'd done hundreds of times before.. but that's another tale). But I 
do like his set up.. he has each string set up with it's own fused 
Disco and Trimetric.. Gives him random control over each string. And 
yes, he keeps a very detailed log, and you can bet that when he takes 
a battery out of service, it's done.
Me? for an average bullet proof off grid system, I shoot for a max of 
two strings for 24V systems (for the redundancy), and manually 
reconfigure them every few years. for 48V systems, I shoot for one 
string of two Volt cells.. thinking that if I loose a cell I can still 
operate a 46V system until I get a replacement.
And Yes, as we all know, there are folks out there that really 
shouldn't be allowed to operate a popsicle stick.

db

Dan Brown
Foxfire Energy Corp.
Renewable Energy Systems
(802)-483-2564
www.Foxfire-Energy.com http://www.Foxfire-Energy.com
NABCEP #092907-44


 Original Message 
Subject: Re: [RE-wrenches] 24 volt Battery Bank comparison
From: Michael Welch michael.we...@re-wrenches.org
mailto:michael.we...@re-wrenches.org
Date: Wed, June 01, 2011 1:43 pm
To: RE-wrenches re-wrenches@lists.re-wrenches.org
mailto:re-wrenches@lists.re-wrenches.org

Every now and then I see reference on this list to the need for
thermal detection. Here is an interesting, inexpensive piece of
equipment that could be used for finding hot (loose or corroded)
connections, hot batteries, hot PV cells in modules, and even
poorly insulated spots, its original intended purpose:

http://www.blackanddecker.com/power-tools/TLD100.aspx

I have one and used it for finding uninsulated spaces, but cannot
attest to its durability or suitability for the other uses
mentioned above.


boB Gudgel wrote at 01:00 AM 6/1/2011:

This might be a good reason for an installer to have one of those
FLIR (or similar) thermal imager cameras.  They're a bit on the
expensive side, but could
really be helpful for so many things.  Even just to know if you
have left a nut loose (under load of course)

boB

Re: [RE-wrenches] 24 volt Battery Bank comparison

2011-06-02 Thread boB Gudgel

On 6/2/2011 6:44 PM, d...@foxfire-energy.com wrote:
What I like best about Mark's set up (the retired phone co. dude w/ 
half a hand), is that he can select individual strings at random. he 
can eq an individual string, or top off a few strings and park them. 
he can even run strings of T 105s, or even nicad (individually of 
course) in the same system as L-16s and the like.. he just reprograms 
the chargers (and logs it). I think he got the design from his days in 
the Navy.


So boB, how about a controller that can be user programed to charge 
multiple battery configurations with a soft switch? i.e. Bank A, Bank 
B...? and while you're at it, maybe a multiple string DC box? 
Something with a shunt and a breaker for each string? A four string 
set up would be nice.


I could use 2% of your first million.

db



Well, It's not a bad idea !   I'll forward that question off to Robin.
I have ran into several that use separate and independent battery banks
and switch between them.  I'm not sure why they don't just use those 
L-16 size

2V cells though instead.

But as I mentioned before, I think that a battery balancer device would take
care of  problems with single strings but maybe even parallel strings,
as well as the pesky problem of AGM batteries that like to plump when
you cook 'em !  (I hate when that happens and one battery gets real hot)

Say, maybe a gizmo that goes across each battery (no 2V cells though) to 
keep each
battery in the string at the same voltage.   It would have to be cheap, 
maybe $30.


Great discussion.

boB





Dan Brown
Foxfire Energy Corp.
Renewable Energy Systems
(802)-483-2564
www.Foxfire-Energy.com http://www.Foxfire-Energy.com
NABCEP #092907-44




 Original Message 
Subject: Re: [RE-wrenches] 24 volt Battery Bank comparison
From: boB Gudgel b...@midnitesolar.com mailto:b...@midnitesolar.com
Date: Thu, June 02, 2011 8:56 pm
To: RE-wrenches re-wrenches@lists.re-wrenches.org
mailto:re-wrenches@lists.re-wrenches.org



Nobody mentioned this in this thread, but it occurs to me that the
answer may be made clearer
by looking at the Voc of each battery string after so many
Amp-Hours (years) of service.

i.e., disconnect the strings' parallel connection and measure the
individual string voltage after charging them all the best that
can be done.

This would be  making the assumption that the batteries themselves
were fairly equal capacity and voltage at installation time.

And for whatever reasons, connections, temperatures and everything
else discussed here, the strings degrade differently.

The older and more worn out batteries should have a lower voltage
(Voc) than the less worn out strings. Thus, the better strings
may be tending to hold up the worse strings by dumping charge into
them when the whole bank is discharging,
and wasting energy and battery efficiency.

I guess that just large 2V cells are the answer in this case, if
at all possible.

Thanks for the help on this question !

boB



On 6/2/2011 10:42 AM, Tom Elliot wrote:

Not surprised at all about the phone company guy.  It was a phone
company guy who read me the riot act that no one in their right
minds would ever parallel battery banks the way PV off-grid
systems did and got me to set up my system with separate strings
connected independently to buss bars.  The battery engineer I
talked to years ago at Dynasty not only said the same thing but
also said keeping strings separate meant individual string
distance from the bars became irrelevant (given correctly sized
wire for each string’s parallel connectors).  I had a system with
12 100 amphour strings of paired 12v Dynasty AGMs which was rock
solid until the day I sold the house.   The last time I checked
the system before the sale no single battery varied from any
other in the system by more than 1/10 volt and the majority were
still holding identical voltages.
*From:* d...@foxfire-energy.com mailto:d...@foxfire-energy.com
*Sent:* Wednesday, June 01, 2011 4:14 PM
*To:* RE-wrenches mailto:re-wrenches@lists.re-wrenches.org
*Subject:* Re: [RE-wrenches] 24 volt Battery Bank comparison
Good thread. Thanks.
In my experience, it all boils down to the customer. I've seen
one temp. set up with like 12 strings (for a concert). but they
were recharged and sold individually within a few weeks.. I've
also seen a single string (Teledyne aircraft batteries) fail in
less than a year.. they were in a brand new airplane tug that was
never charged -- ever. (the guy said I dunno, it just stopped
working).
I have one customer who (last I knew) was running 6 strings of
mixed aged L-16s going on 8 years. Thing is, he's a retired phone
company dude (Who's missing half of his right hand from using one
of those pocket pal screwdriver thingys on a key

Re: [RE-wrenches] 24 volt Battery Bank comparison

2011-06-02 Thread Brian Teitelbaum
boB,

If you build it, it will sell.

I’d love to see a battery distribution box, with separate fusing and 
disconnects, and maybe shunts, for each string, with large bus bars in it and 
enclosed in a corrosion resistant box. Oh…and Listed.

It would need to come in a variety of sizes, like 250A, 500A, 1000A, and also 
maybe able to be daisy-chained for really large systems, like up to 100kW at 
48VDC

Hint..hint…

Brian Teitelbaum
AEE Solar

From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of boB Gudgel
Sent: Thursday, June 02, 2011 8:50 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] 24 volt Battery Bank comparison

On 6/2/2011 6:44 PM, d...@foxfire-energy.commailto:d...@foxfire-energy.com 
wrote:
What I like best about Mark's set up (the retired phone co. dude w/ half a 
hand), is that he can select individual strings at random. he can eq an 
individual string, or top off a few strings and park them. he can even run 
strings of T 105s, or even nicad (individually of course) in the same system as 
L-16s and the like.. he just reprograms the chargers (and logs it). I think he 
got the design from his days in the Navy.

So boB, how about a controller that can be user programed to charge multiple 
battery configurations with a soft switch? i.e. Bank A, Bank B...? and while 
you're at it, maybe a multiple string DC box? Something with a shunt and a 
breaker for each string? A four string set up would be nice.

I could use 2% of your first million.

db


Well, It's not a bad idea !   I'll forward that question off to Robin.
I have ran into several that use separate and independent battery banks
and switch between them.  I'm not sure why they don't just use those L-16 size
2V cells though instead.

But as I mentioned before, I think that a battery balancer device would take
care of  problems with single strings but maybe even parallel strings,
as well as the pesky problem of AGM batteries that like to plump when
you cook 'em !  (I hate when that happens and one battery gets real hot)

Say, maybe a gizmo that goes across each battery (no 2V cells though) to keep 
each
battery in the string at the same voltage.   It would have to be cheap, maybe 
$30.

Great discussion.

boB





Dan Brown
Foxfire Energy Corp.
Renewable Energy Systems
(802)-483-2564
www.Foxfire-Energy.comhttp://www.Foxfire-Energy.com
NABCEP #092907-44



 Original Message 
Subject: Re: [RE-wrenches] 24 volt Battery Bank comparison
From: boB Gudgel b...@midnitesolar.commailto:b...@midnitesolar.com
Date: Thu, June 02, 2011 8:56 pm
To: RE-wrenches 
re-wrenches@lists.re-wrenches.orgmailto:re-wrenches@lists.re-wrenches.org



Nobody mentioned this in this thread, but it occurs to me that the answer may 
be made clearer
by looking at the Voc of each battery string after so many Amp-Hours (years) of 
service.

i.e., disconnect the strings' parallel connection and measure the individual 
string voltage after charging them all the best that can be done.

This would be  making the assumption that the batteries themselves were fairly 
equal capacity and voltage at installation time.

And for whatever reasons, connections, temperatures and everything else 
discussed here, the strings degrade differently.

The older and more worn out batteries should have a lower voltage (Voc) than 
the less worn out strings. Thus, the better strings
may be tending to hold up the worse strings by dumping charge into them when 
the whole bank is discharging,
and wasting energy and battery efficiency.

I guess that just large 2V cells are the answer in this case, if at all 
possible.

Thanks for the help on this question !

boB



On 6/2/2011 10:42 AM, Tom Elliot wrote:
Not surprised at all about the phone company guy.  It was a phone company guy 
who read me the riot act that no one in their right minds would ever parallel 
battery banks the way PV off-grid systems did and got me to set up my system 
with separate strings connected independently to buss bars.  The battery 
engineer I talked to years ago at Dynasty not only said the same thing but also 
said keeping strings separate meant individual string distance from the bars 
became irrelevant (given correctly sized wire for each string’s parallel 
connectors).  I had a system with 12 100 amphour strings of paired 12v Dynasty 
AGMs which was rock solid until the day I sold the house.   The last time I 
checked the system before the sale no single battery varied from any other in 
the system by more than 1/10 volt and the majority were still holding identical 
voltages.

From: d...@foxfire-energy.commailto:d...@foxfire-energy.com
Sent: Wednesday, June 01, 2011 4:14 PM
To: RE-wrenchesmailto:re-wrenches@lists.re-wrenches.org
Subject: Re: [RE-wrenches] 24 volt Battery Bank comparison

Good thread. Thanks.
In my experience, it all boils down to the customer. I've seen one temp. set up 
with like 12 strings (for a concert). but they were recharged

Re: [RE-wrenches] 24 volt Battery Bank comparison

2011-06-01 Thread boB Gudgel



OK, I've been hearing for years now that one battery string is best and 
maybe two but no more should be used.


What is the reason for this fear ???What is the experience with 
multiple strings in parallel ??


If it is because of current sharing of the strings, that shouldn't be an 
insurmountable problem if the wiring is done right.


If it has to do with the possibility of fire, which Darryl mentioned, 
seems that series string fuses could mitigate the possibility of that 
issue, if because of shorted cells, just like PV combiners.


Or maybe it has to do with the trouble of getting into the middle of a 
pile of batteries ?  Use battery boxes ?


The strings are in parallel and so they all get the same voltage, 
theoretically anyway if the connections are good.


I would think that the more strings, the LESS stress on individual 
batteries, not more.  The current in each battery should be less than it 
would be I would think.


So what is the real experience ??

Is a battery balancer the answer ??

Thanks,
boB







On May 31, 2011, at 8:23 PM, Wayne Irwin wa...@pureenergysolar.com 
mailto:wa...@pureenergysolar.com wrote:


I think the verdict is*12* - Rolls 2-YS-31 2430 AH @ 20 HR (one 
string) and one dry spare in storage is the best case scenario!


Wayne Irwin, EE
Director of Engineering
Pure Energy Solar International Inc.
State Licensed Solar Contractor
License # CVC56695
wa...@pureenergysolar.com mailto:wa...@pureenergysolar.com
http://pureenergysolar.com
352 377-6527 Office
352 336-3299 Fax
352 316-1637 Cell


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] 24 volt Battery Bank comparison

2011-06-01 Thread boB Gudgel

On 5/31/2011 11:25 PM, Tom Elliot wrote:

Bob,
I totally understand the concern about multiple strings *if the 
strings are connected across the battery bank* as had always been the 
tradition in off-grid installations.  My own experience with such a 
bank in my system  showed why when I had a single cell get to near 
meltdown.  I was lucky to find it.



This might be a good reason for an installer to have one of those FLIR 
(or similar) thermal imager cameras.   They're a bit on the expensive 
side, but could
really be helpful for so many things.   Even just to know if you have 
left a nut loose (under load of course)


boB



Maintenance is another reason, such banks are far more difficult to 
maintain.  But I think those concerns are ameliorated a great deal 
with a buss bar installation and once I did that I never had another 
problem and found the battery bank much easier to maintain because the 
strings no longer had to be right next to each other.  Heck, it would 
be possible to put each series string in its own box for that matter.  
And with the inclusion of string fuses that reduces problems even 
further.
When living with an off-grid system my biggest concern was system 
reliability and redundancy and the idea of a single string failure was 
a big worry which is why I never would consider it.

Tom
*From:* boB Gudgel mailto:b...@midnitesolar.com
*Sent:* Tuesday, May 31, 2011 8:16 PM
*To:* RE-wrenches mailto:re-wrenches@lists.re-wrenches.org
*Subject:* Re: [RE-wrenches] 24 volt Battery Bank comparison


OK, I've been hearing for years now that one battery string is best 
and maybe two but no more should be used.


What is the reason for this fear ???What is the experience with 
multiple strings in parallel ??


If it is because of current sharing of the strings, that shouldn't be 
an insurmountable problem if the wiring is done right.


If it has to do with the possibility of fire, which Darryl mentioned, 
seems that series string fuses could mitigate the possibility of that 
issue, if because of shorted cells, just like PV combiners.


Or maybe it has to do with the trouble of getting into the middle of a 
pile of batteries ?  Use battery boxes ?


The strings are in parallel and so they all get the same voltage, 
theoretically anyway if the connections are good.


I would think that the more strings, the LESS stress on individual 
batteries, not more.  The current in each battery should be less than 
it would be I would think.


So what is the real experience ??

Is a battery balancer the answer ??

Thanks,
boB







On May 31, 2011, at 8:23 PM, Wayne Irwin wa...@pureenergysolar.com 
mailto:wa...@pureenergysolar.com wrote:


I think the verdict is*12* - Rolls 2-YS-31 2430 AH @ 20 HR (one 
string) and one dry spare in storage is the best case scenario!


Wayne Irwin, EE
Director of Engineering
Pure Energy Solar International Inc.
State Licensed Solar Contractor
License # CVC56695
wa...@pureenergysolar.com mailto:wa...@pureenergysolar.com
http://pureenergysolar.com
352 377-6527 Office
352 336-3299 Fax
352 316-1637 Cell



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org


List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



No virus found in this message.
Checked by AVG - www.avg.com http://www.avg.com
Version: 10.0.1375 / Virus Database: 1511/3672 - Release Date: 05/31/11


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] 24 volt Battery Bank comparison

2011-06-01 Thread Darryl Thayer
If one cell gets a higher internal loss than the others is hogs the charging 
current and will over charge its string partners.  It is a problem of the 
temperature of all cells in all parallel strings having the same thermal 
environment, so they all have the same voltage.  (the case of one of 4 parallel 
strings in battery house, big system, the string near the outside south wall 
caught fire)  In particular this is a problem of AGMs, a recent east cost 
problem where batteries had been in business for 2 yrs and for some reason the 
battery room erupted with one of 5 strings in thermal runaway.   this is the 
same as trying to put bipolar transistors in parallel.  

I reciently had 8 parallel strings not of my choice, advised customer of 
potential hazard,   used Midnight combiner with 30 amp breakers on each string, 
so far it is OK but this is playing with fire.  Hopfully if one string goes bad 
in thermal runaway it will trip the breaker feeding that string. .  





From: boB Gudgel b...@midnitesolar.com
To: RE-wrenches re-wrenches@lists.re-wrenches.org
Sent: Wednesday, June 1, 2011 1:16 AM
Subject: Re: [RE-wrenches] 24 volt Battery Bank comparison




OK, I've been hearing for years now that one battery string is best
and maybe two but no more should be used.

What is the reason for this fear ???    What is the experience with
multiple strings in parallel ??

If it is because of current sharing of the strings, that shouldn't
be an insurmountable problem if the wiring is done right.

If it has to do with the possibility of fire, which Darryl
mentioned, seems that series string fuses could mitigate the
possibility of that issue, if because of shorted cells, just like PV
combiners.

Or maybe it has to do with the trouble of getting into the middle of
a pile of batteries ?  Use battery boxes ?

The strings are in parallel and so they all get the same voltage,
theoretically anyway if the connections are good.

I would think that the more strings, the LESS stress on individual
batteries, not more.  The current in each battery should be less
than it would be I would think.

So what is the real experience ?? 

Is a battery balancer the answer ??

Thanks,
boB







On May 31, 2011, at 8:23 PM, Wayne Irwin wa...@pureenergysolar.com wrote:


I think the verdict is12 - Rolls 2-YS-31 2430 AH @ 20 HR (one string) and one 
dry spare in storage is the best case scenario!

Wayne Irwin, EE
Director of Engineering
Pure Energy Solar International Inc. 
State Licensed Solar Contractor
License # CVC56695 
wa...@pureenergysolar.com 
http://pureenergysolar.com 
352 377-6527 Office
352 336-3299 Fax
352 316-1637 Cell

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] 24 volt Battery Bank comparison

2011-06-01 Thread Bill Loesch

Hi Michael,

With all due respect, do the reference idiot lights do that much for you?
I have always thought a thermal camera/viewer/FLIR/etc. would be great but
so would a used car. My digital IR thermometer at several orders of
magnitude difference in price has served me well, if tediously, to do some
of the uses described.

Bill Loesch
Solar 1 - Saint Louis Solar
314 631 1094



- Original Message - 
From: Michael Welch michael.we...@re-wrenches.org
To: RE-wrenches re-wrenches@lists.re-wrenches.org
Sent: Wednesday, June 01, 2011 12:43 PM
Subject: Re: [RE-wrenches] 24 volt Battery Bank comparison


Every now and then I see reference on this list to the need for thermal
detection. Here is an interesting, inexpensive piece of equipment that could
be used for finding hot (loose or corroded) connections, hot batteries, hot
PV cells in modules, and even poorly insulated spots, its original intended
purpose:

http://www.blackanddecker.com/power-tools/TLD100.aspx

I have one and used it for finding uninsulated spaces, but cannot attest to
its durability or suitability for the other uses mentioned above.


boB Gudgel wrote at 01:00 AM 6/1/2011:

This might be a good reason for an installer to have one of those FLIR (or
similar) thermal imager cameras.   They're a bit on the expensive side,
but could
really be helpful for so many things.   Even just to know if you have
left a nut loose (under load of course)

boB


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] 24 volt Battery Bank comparison, Why a single string?

2011-06-01 Thread boB Gudgel

On 6/1/2011 8:41 AM, Larry Crutcher, Starlight Solar Power Systems wrote:

Hi boB,

We know that current will flow through the lowest resistive path. In a 
perfect world, the resistance from end to end of a battery string will 
be identical. Real world conditions show that one or more cells have a 
slightly higher internal resistance. Add to that the imperfect 
terminal crimp, improper torque at battery terminal, and perhaps 
terminal corrosion and we now have paths of differing resistance. The 
parallel strings have an unequal distribution of current and ergo 
undercharged cells. These cells retain a small amount of amorphous 
lead sulphate that, without correction, will begin to crystalize. We 
all know what will happen over time.




The issue of maintenance is a not brainer of course...  i.e. the need to 
add water...


Imperfect crimps would be a problem with a single string of batteries 
too.  If the resistance
is higher in that cell in the one string, then yes, that one string will 
not be working nearly as
hard as the other strings.  Bad workmanship is not an excuse for not 
using multiple strings

as far as I know.


If one string is discharged more than another parallel string, then its 
finishing (ending) Amps
will will certainly happen later than a string that wasn't discharged as 
deep, but if using a
timed Absorb cycle, why does this matter ??   They're all receiving the 
same voltage and
should be treated the same in that case.  Right ??At least for timed 
charging cycles.


As Darryl pointed out, AGMs like to get hot when unbalanced and this is 
definitely what I
have seen.   But that again can happen for a single string rather than 
multiple strings.


One thing that hasn't been mentioned, unless I missed it, is the 
possibility that a shorted
cell in one string can drag down the other strings it is in parallel 
with.   The more strings
in parallel, statistically, there would be more of a chance for that to 
happen.


That would be more of a self discharge issue I would think which isn't good.
boB




Granted, this can be prevented by the proper knowledge and attention 
but I see far too many failures from neglect and/or lack of 
understanding. My experience comes from 10 years of working with 
hundreds of small 12 volt systems with 2 to 6 parallel strings of 
batteries. In our shop we often see 2 to 3 year old battery banks that 
are damaged and I believe this is a contributing factor. It is often 
too late by the time the problem is discovered. So, my opinion is to 
reduce this possibility by decreasing the parallel paths whenever 
possible.


More strings of a given size battery means less stress per string. 
But, if you decrease strings you are normally increasing cell size to 
maintain the capacity so this should not be an issue.


Battery balancing is a great idea. I would like to see an active 
system for shunting current on a string to keep an equal current 
across all strings. I know this is done in the EV business.


Larry Crutcher
Starlight Solar Power Systems
11871 S Fortuna Road, #210
Yuma, AZ 85367

la...@starlightsolar.com mailto:la...@starlightsolar.com
(928) 342-9103



On May 31, 2011, at 11:16 PM, boB Gudgel wrote:




OK, I've been hearing for years now that one battery string is best 
and maybe two but no more should be used.


What is the reason for this fear ???What is the experience with 
multiple strings in parallel ??


If it is because of current sharing of the strings, that shouldn't be 
an insurmountable problem if the wiring is done right.


If it has to do with the possibility of fire, which Darryl mentioned, 
seems that series string fuses could mitigate the possibility of that 
issue, if because of shorted cells, just like PV combiners.


Or maybe it has to do with the trouble of getting into the middle of 
a pile of batteries ?  Use battery boxes ?


The strings are in parallel and so they all get the same voltage, 
theoretically anyway if the connections are good.


I would think that the more strings, the LESS stress on individual 
batteries, not more.  The current in each battery should be less than 
it would be I would think.


So what is the real experience ??

Is a battery balancer the answer ??

Thanks,
boB



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  

Re: [RE-wrenches] 24 volt Battery Bank comparison

2011-06-01 Thread boB Gudgel

On 6/1/2011 10:43 AM, Michael Welch wrote:

Every now and then I see reference on this list to the need for thermal 
detection. Here is an interesting, inexpensive piece of equipment that could be 
used for finding hot (loose or corroded) connections, hot batteries, hot PV 
cells in modules, and even poorly insulated spots, its original intended 
purpose:

http://www.blackanddecker.com/power-tools/TLD100.aspx

I have one and used it for finding uninsulated spaces, but cannot attest to its 
durability or suitability for the other uses mentioned above.


Yep.  These are very handy indeed !  AND they're cheap !

But these types are quite different from what I was talking about when I 
mentioned the very pricey thermal imagers like FLIRs.
For the single point thermometers like the BD device, you must run it 
over EVERY single spot that you want to check
for heat.  Batteries, Connections, Cables and each one individually.  
With something like the FLIR you can just hold it
and stand in one place and it will show you where any hot spots (or cold 
spots) are AND give you the temperature.
That is, if the emissivity is close enough, but you can still see if 
something is really hot with the imager.


I just wish they were cheaper !

boB






boB Gudgel wrote at 01:00 AM 6/1/2011:


This might be a good reason for an installer to have one of those FLIR (or 
similar) thermal imager cameras.   They're a bit on the expensive side, but 
could
really be helpful for so many things.   Even just to know if you have left a 
nut loose (under load of course)

boB


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] 24 volt Battery Bank comparison

2011-06-01 Thread Christopher Warfel
I recently purchased one and it has been useful. It can also be used to 
find poorly insulated buildings, air leaks etc. I have been told that in 
some states, fire departments will make their thermal imaging cameras 
available to qualified people for conducting these types of surveys.

Chris

On 6/1/2011 1:43 PM, Michael Welch wrote:

Every now and then I see reference on this list to the need for thermal 
detection. Here is an interesting, inexpensive piece of equipment that could be 
used for finding hot (loose or corroded) connections, hot batteries, hot PV 
cells in modules, and even poorly insulated spots, its original intended 
purpose:

http://www.blackanddecker.com/power-tools/TLD100.aspx

I have one and used it for finding uninsulated spaces, but cannot attest to its 
durability or suitability for the other uses mentioned above.


boB Gudgel wrote at 01:00 AM 6/1/2011:

   

This might be a good reason for an installer to have one of those FLIR (or 
similar) thermal imager cameras.   They're a bit on the expensive side, but 
could
really be helpful for so many things.   Even just to know if you have left a 
nut loose (under load of course)

boB
 


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


   


--

Christopher Warfel, P.E.
ENTECH Engineering, Inc.
Energy Utilization Experts
(401)466-8978

The information contained within this communication shall
be considered confidential and shall not be retransmitted
without knowledge of the sender. Please contact us if
this email reached you in error. Thank you.

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] 24 volt Battery Bank comparison

2011-06-01 Thread dan
Good thread. Thanks. In my experience, it all boils down to the customer. I've seen one temp. set up with like 12 strings (for a concert). but they were recharged and sold individually within a few weeks.. I've also seen a single string (Teledyne aircraft batteries) fail in less than a year.. they were in a brand new airplane tug that was never charged -- ever. (the guy said "I dunno, it just stopped working"). I have one customer who (last I knew) was running 6 strings of mixed aged L-16s going on 8 years. Thing is, he's a retired phone company dude (Who's missing half of his right hand from using one of those pocket pal screwdriver thingys on a key chain in a hot DC rack.. like he'd done hundreds of times before.. but that's another tale). But I do like his set up.. he has each string set up with it's own fused Disco and Trimetric.. Gives him random control over each string. And yes, he keeps a very detailed log, and you can bet that when he takes a battery out of service, it's done. Me? for an average bullet proof off grid system, I shoot for a max of two strings for 24V systems (for the redundancy), and manually reconfigure them every few years. for 48V systems, I shoot for one string of two Volt cells.. thinking that if I loose a cell I can still operate a 46V system until I get a replacement. And Yes, as we all know, there are folks out there that really shouldn't be allowed to operate a popsicle stick. dbDan BrownFoxfire Energy Corp.Renewable Energy Systems(802)-483-2564www.Foxfire-Energy.comNABCEP #092907-44


 Original Message 
Subject: Re: [RE-wrenches] 24 volt Battery Bank comparison
From: Michael Welch michael.we...@re-wrenches.org
Date: Wed, June 01, 2011 1:43 pm
To: RE-wrenches re-wrenches@lists.re-wrenches.org

Every now and then I see reference on this list to the need for thermal detection. Here is an interesting, inexpensive piece of equipment that could be used for finding hot (loose or corroded) connections, hot batteries, hot PV cells in modules, and even poorly insulated spots, its original intended purpose:

http://www.blackanddecker.com/power-tools/TLD100.aspx

I have one and used it for finding uninsulated spaces, but cannot attest to its durability or suitability for the other uses mentioned above.


boB Gudgel wrote at 01:00 AM 6/1/2011:
 
This might be a good reason for an installer to have one of those FLIR (or similar) thermal imager cameras.   They're a bit on the expensive side, but could
really be helpful for so many things.   Even just to know if you have left a nut loose (under load of course)

boB


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] 24 volt Battery Bank comparison

2011-06-01 Thread Allan Sindelar
any things.   Even just to know if
you have left a nut loose (under load of course)

boB



  
  

  

  Maintenance
is another reason, such banks are far more difficult
to maintain.  But I think those concerns are
ameliorated a great deal with a buss bar
installation and once I did that I never had another
problem and found the battery bank much easier to
maintain because the strings no longer had to be
right next to each other.  Heck, it would be
possible to put each series string in its own box
for that matter.  And with the inclusion of string
fuses that reduces problems even further.


   


  When
living with an off-grid system my biggest concern
was system reliability and redundancy and the idea
of a single string failure was a big worry which is
why I never would consider it.


   


  Tom


   


   


  

   


  
From:
  boB
Gudgel
  
  
Sent:
  Tuesday, May 31, 2011 8:16 PM
  
  
To:
  RE-wrenches
  
  
Subject:
      Re: [RE-wrenches] 24 volt Battery Bank
  comparison
  

  
  
 
  


  

OK, I've been hearing for years now that one battery
string is best and maybe two but no more should be
used.

What is the reason for this fear ???    What is the
experience with multiple strings in parallel ??

If it is because of current sharing of the strings,
that shouldn't be an insurmountable problem if the
wiring is done right.

If it has to do with the possibility of fire, which
Darryl mentioned, seems that series string fuses
could mitigate the possibility of that issue, if
because of shorted cells, just like PV combiners.

Or maybe it has to do with the trouble of getting
into the middle of a pile of batteries ?  Use
battery boxes ?

The strings are in parallel and so they all get the
same voltage, theoretically anyway if the
connections are good.

I would think that the more strings, the LESS stress
on individual batteries, not more.  The current in
each battery should be less than it would be I would
think.

So what is the real experience ??

Is a battery balancer the answer ??

Thanks,
boB





  
  

  
On May 31, 2011, at 8:23 PM, "Wayne Irwin" wa...@pureenergysolar.com
wrote:

  


  
I
  think the verdict is 12 -
  Rolls 2-YS-31 2430 AH @ 20 HR (one string) and
  one dry spare in storage is the best case
  scenario!
  
  Wayne
Irwin, EE
Director of Engineering
 

[RE-wrenches] 24 volt Battery Bank comparison

2011-05-31 Thread Wayne Irwin

Hello Esteemed Battery Gurus,

Which of the following do you believe is the better 24 V battery bank?

A) 13 - Rolls 2-YS-31 2430 AH @ 20 HR (one string) 

or 

B) 9 -  Rolls 8-CS-25P 820 AH @ 20 HR (3 strings of 3)

Thank you in advance for your input!


Wayne Irwin, EE
Director of Engineering

Pure Energy Solar International Inc. 
State Licensed Solar Contractor

License # CVC56695 

wa...@pureenergysolar.com
 

http://pureenergysolar.com
 

352 377-6527 Office
352 336-3299 
Fax
352 316-1637 Cell
The
content of this message is Pure Energy Solar Confidential. If you are 
not the intended
recipient and have received this message in error, any use or 
distribution is
prohibited. Please notify me immediately by reply e-mail and delete this
message from your computer system. Thank you.

  ___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] 24 volt Battery Bank comparison

2011-05-31 Thread James Surrette

Hi Wayne, 

I look forward to the input from the wrenches. 

My recommendation, regardless of the brand, would be for one string. 

Regards, 

Jamie

 Wayne Irwin wa...@pureenergysolar.com 5/31/2011 6:49 PM 
Hello Esteemed Battery Gurus,

Which of the following do you believe is the better 24 V battery bank?

A) 13 - Rolls 2-YS-31 2430 AH @ 20 HR (one string)

or

B) 9 -  Rolls 8-CS-25P 820 AH @ 20 HR (3 strings of 3)

Thank you in advance for your input!


Wayne Irwin, EE
Director of Engineering
Pure Energy Solar International Inc. 
State Licensed Solar Contractor
License # CVC56695 
wa...@pureenergysolar.com ( mailto:pureenergyso...@hotmail.com )
http://pureenergysolar.com ( http://pureenergysolar.net/ )
352 377-6527 Office
352 336-3299 Fax
352 316-1637 Cell

The content of this message is Pure Energy Solar Confidential. If you are not 
the intended recipient and have received this message in error, any use or 
distribution is prohibited. Please notify me immediately by reply e-mail and 
delete this message from your computer system. Thank you. 




This email and its attachments have been scanned by iConnection E-Mail Firewall 
for viruses, spam, and malicious content.
The information transmitted in this email is intended only for the entity or 
person to which it is addressed and may contain confidential/privileged 
material. If you received this in error, please contact the sender and delete 
the material from any computer. Any review, retransmission, dissemination, or 
other use of this information by persons or entities other than the intended 
recipient is strictly prohibited. %^^%
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] 24 volt Battery Bank comparison

2011-05-31 Thread Brian Mehalic
Hi Wayne-
While I think a lot of folks will agree that a single string is better for
the long term health of the batteries as it results in more even charging, I
still like the idea of at least two strings.  That way if a single battery
fails, that string can be removed and the end-user can at least get by on
half of the pack until a replacement can be installed.
Brian

On Tue, May 31, 2011 at 10:19 PM, James Surrette ja...@surrette.com wrote:

  Hi Wayne,

  I look forward to the input from the wrenches.

  My recommendation, regardless of the brand, would be for one string.

  Regards,

  Jamie

  Wayne Irwin wa...@pureenergysolar.com 5/31/2011 6:49 PM 
 Hello Esteemed Battery Gurus,

 Which of the following do you believe is the better 24 V battery bank?

 A) 13 - Rolls 2-YS-31 2430 AH @ 20 HR (one string)

 or

 B) 9 -  Rolls 8-CS-25P 820 AH @ 20 HR (3 strings of 3)

 Thank you in advance for your input!


 Wayne Irwin, EE
 Director of Engineering
 Pure Energy Solar International Inc.
 State Licensed Solar Contractor
 License # CVC56695
 wa...@pureenergysolar.com pureenergyso...@hotmail.com
 http://pureenergysolar.com http://pureenergysolar.net/
 352 377-6527 Office
 352 336-3299 Fax
 352 316-1637 Cell

 The content of this message is Pure Energy Solar Confidential. If you are
 not the intended recipient and have received this message in error, any use
 or distribution is prohibited. Please notify me immediately by reply e-mail
 and delete this message from your computer system. Thank you.



  This email and its attachments have been scanned by iConnection E-Mail
 Firewall for viruses, spam, and malicious content. The information
 transmitted in this email is intended only for the entity or person to which
 it is addressed and may contain confidential/privileged material. If you
 received this in error, please contact the sender and delete the material
 from any computer. Any review, retransmission, dissemination, or other use
 of this information by persons or entities other than the intended recipient
 is strictly prohibited. %^^%

 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org





-- 

Brian Mehalic
NABCEP Certified Solar PV Installer™ R031508-59
IREC ISPQ Certified Affiliated Instructor/PV US-0132
PV Curriculum Developer and Instructor
Solar Energy International
Carbondale, CO 81623
http://www.solarenergy.org
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] 24 volt Battery Bank comparison

2011-05-31 Thread Chris
My one string of 1476 AH IBE 2 V cells went 19 years before retiring them to
a neighbor's off grid system, where they are now working.

One string has my vote!

 

Sincerely,

Chris Worcester

Solar Wind Works
NABCEP Certified PV Installer
Phone: 530-582-4503
Fax: 530-582-4603
www.solarwindworks.com http://www.solarwindworks.com/ 
ch...@solarwindworks.com
Proven Energy Solutions

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Brian
Mehalic
Sent: Tuesday, May 31, 2011 3:25 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] 24 volt Battery Bank comparison

 

Hi Wayne-

While I think a lot of folks will agree that a single string is better for
the long term health of the batteries as it results in more even charging, I
still like the idea of at least two strings.  That way if a single battery
fails, that string can be removed and the end-user can at least get by on
half of the pack until a replacement can be installed.

Brian

On Tue, May 31, 2011 at 10:19 PM, James Surrette ja...@surrette.com wrote:

Hi Wayne, 

 

I look forward to the input from the wrenches. 

 

My recommendation, regardless of the brand, would be for one string. 

 

Regards, 

 

Jamie

 Wayne Irwin wa...@pureenergysolar.com 5/31/2011 6:49 PM 
Hello Esteemed Battery Gurus,

Which of the following do you believe is the better 24 V battery bank?

A) 13 - Rolls 2-YS-31 2430 AH @ 20 HR (one string)

or

B) 9 -  Rolls 8-CS-25P 820 AH @ 20 HR (3 strings of 3)

Thank you in advance for your input!


Wayne Irwin, EE
Director of Engineering
Pure Energy Solar International Inc. 
State Licensed Solar Contractor
License # CVC56695 
wa...@pureenergysolar.com mailto:pureenergyso...@hotmail.com 
http://pureenergysolar.com http://pureenergysolar.net/ 
352 377-6527 Office
352 336-3299 Fax
352 316-1637 Cell

The content of this message is Pure Energy Solar Confidential. If you are
not the intended recipient and have received this message in error, any use
or distribution is prohibited. Please notify me immediately by reply e-mail
and delete this message from your computer system. Thank you. 

 

This email and its attachments have been scanned by iConnection E-Mail
Firewall for viruses, spam, and malicious content. The information
transmitted in this email is intended only for the entity or person to which
it is addressed and may contain confidential/privileged material. If you
received this in error, please contact the sender and delete the material
from any computer. Any review, retransmission, dissemination, or other use
of this information by persons or entities other than the intended recipient
is strictly prohibited. %^^% 


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org






-- 

Brian Mehalic 
NABCEP Certified Solar PV InstallerT R031508-59

IREC ISPQ Certified Affiliated Instructor/PV US-0132

PV Curriculum Developer and Instructor

Solar Energy International
Carbondale, CO 81623
http://www.solarenergy.org

 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] 24 volt Battery Bank comparison

2011-05-31 Thread Bob-O Schultze
Wayne,
First, let's hope you mean 12 of the 2YS31. A single battery string is always 
preferable to multiple strings in my book. The only downside is interconnect 
cables the same size as your inverter cables. That probably means 4/0 CU for 
most 24V, 3KW and up inverters. Two strings in parallel-not too bad. Three 
strings- as far as you want to push it. More strings- Don't go there.
Bob-O

On May 31, 2011, at 2:49 PM, Wayne Irwin wrote:

Hello Esteemed Battery Gurus,

Which of the following do you believe is the better 24 V battery bank?

A) 13 - Rolls 2-YS-31 2430 AH @ 20 HR (one string) 

or 

B) 9 -  Rolls 8-CS-25P 820 AH @ 20 HR (3 strings of 3)

Thank you in advance for your input!


Wayne Irwin, EE
Director of Engineering
Pure Energy Solar International Inc. 
State Licensed Solar Contractor
License # CVC56695 
wa...@pureenergysolar.com 
http://pureenergysolar.com 
352 377-6527 Office
352 336-3299 Fax
352 316-1637 Cell
The content of this message is Pure Energy Solar Confidential. If you are not 
the intended recipient and have received this message in error, any use or 
distribution is prohibited. Please notify me immediately by reply e-mail and 
delete this message from your computer system. Thank you.___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] 24 volt Battery Bank comparison

2011-05-31 Thread Peter Parrish
Fewer number of strings the better. Go with plan A. Why 13 (and not 12) of
the Rolls if I may ask?


 
Peter T. Parrish, Ph.D., President
California Solar Engineering, Inc.
820 Cynthia Ave., Los Angeles, CA 90065
CA Lic. 854779, NABCEP Cert. 031806-26
peter.parr...@calsolareng.com  
Ph 323-258-8883, Mobile 323-839-6108, Fax 323-258-8885

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Wayne Irwin
Sent: Tuesday, May 31, 2011 2:50 PM
To: Wrenches
Subject: [RE-wrenches] 24 volt Battery Bank comparison

Hello Esteemed Battery Gurus,

Which of the following do you believe is the better 24 V battery bank?

A) 13 - Rolls 2-YS-31 2430 AH @ 20 HR (one string) 

or 

B) 9 -  Rolls 8-CS-25P 820 AH @ 20 HR (3 strings of 3)

Thank you in advance for your input!


Wayne Irwin, EE
Director of Engineering
Pure Energy Solar International Inc. 
State Licensed Solar Contractor
License # CVC56695 
wa...@pureenergysolar.com 
http://pureenergysolar.com 
352 377-6527 Office
352 336-3299 Fax
352 316-1637 Cell
The content of this message is Pure Energy Solar Confidential. If you are
not the intended recipient and have received this message in error, any use
or distribution is prohibited. Please notify me immediately by reply e-mail
and delete this message from your computer system. Thank you.


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] 24 volt Battery Bank comparison

2011-05-31 Thread Tom Elliot
From a reliability standpoint I would never want to bet the farm on one 
string.  All it takes is the failure of one cell and the system is useless 
until it is replaced.  Three strings means a cell failure only reduces 
capacity by 33% not 100%.  I’ve always thought in off-grid systems it is a 
good idea to build in as much redundancy as possible whenever possible.  Oh, 
and always use a buss bar system with multiple strings, it makes for a far 
more stable system with less stress on the batteries.

Tom



From: Wayne Irwin 
Sent: Tuesday, May 31, 2011 11:49 AM
To: Wrenches 
Subject: [RE-wrenches] 24 volt Battery Bank comparison

Hello Esteemed Battery Gurus,

Which of the following do you believe is the better 24 V battery bank?

A) 13 - Rolls 2-YS-31 2430 AH @ 20 HR (one string) 

or 

B) 9 -  Rolls 8-CS-25P 820 AH @ 20 HR (3 strings of 3)

Thank you in advance for your input!


Wayne Irwin, EE
Director of Engineering
Pure Energy Solar International Inc. 
State Licensed Solar Contractor
License # CVC56695 
mailto:pureenergyso...@hotmail.com 
http://pureenergysolar.com 
352 377-6527 Office
352 336-3299 Fax
352 316-1637 Cell

The content of this message is Pure Energy Solar Confidential. If you are not 
the intended recipient and have received this message in error, any use or 
distribution is prohibited. Please notify me immediately by reply e-mail and 
delete this message from your computer system. Thank you.







___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org






No virus found in this message.
Checked by AVG - www.avg.com
Version: 10.0.1375 / Virus Database: 1509/3671 - Release Date: 05/31/11
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] 24 volt Battery Bank comparison

2011-05-31 Thread Wayne Irwin

Hello all. 

I am indeed thinking of 13 - 2 volt batteries to make up a 26 volt battery bank 
for the 24 volt system.

Thoughts for or against are welcome.

Wayne Irwin, EE
Director of Engineering

Pure Energy Solar International Inc. 
State Licensed Solar Contractor

License # CVC56695 

wa...@pureenergysolar.com
 

http://pureenergysolar.com
 

352 377-6527 Office
352 336-3299 
Fax
352 316-1637 Cell
The
content of this message is Pure Energy Solar Confidential. If you are 
not the intended
recipient and have received this message in error, any use or 
distribution is
prohibited. Please notify me immediately by reply e-mail and delete this
message from your computer system. Thank you.



From: bo...@electronconnection.com
Date: Tue, 31 May 2011 15:40:14 -0700
To: re-wrenches@lists.re-wrenches.org
Subject: Re: [RE-wrenches] 24 volt Battery Bank comparison



Wayne,First, let's hope you mean 12 of the 2YS31. A single battery string is 
always preferable to multiple strings in my book. The only downside is 
interconnect cables the same size as your inverter cables. That probably means 
4/0 CU for most 24V, 3KW and up inverters. Two strings in parallel-not too bad. 
Three strings- as far as you want to push it. More strings- Don't go there.Bob-O
On May 31, 2011, at 2:49 PM, Wayne Irwin wrote:Hello Esteemed Battery Gurus,

Which of the following do you believe is the better 24 V battery bank?

A) 13 - Rolls 2-YS-31 2430 AH @ 20 HR (one string) 

or 

B) 9 -  Rolls 8-CS-25P 820 AH @ 20 HR (3 strings of 3)

Thank you in advance for your input!


Wayne Irwin, EE
Director of Engineering
Pure Energy Solar International Inc. 
State Licensed Solar Contractor
License # CVC56695 
wa...@pureenergysolar.com 
http://pureenergysolar.com 
352 377-6527 Office
352 336-3299 Fax
352 316-1637 Cell
The content of this message is Pure Energy Solar Confidential. If you are not 
the intended recipient and have received this message in error, any use or 
distribution is prohibited. Please notify me immediately by reply e-mail and 
delete this message from your computer system. Thank you.
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org   ___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] 24 volt Battery Bank comparison

2011-05-31 Thread Wayne Irwin

Just for a little extra.

Wayne Irwin, EE
Director of Engineering

Pure Energy Solar International Inc. 
State Licensed Solar Contractor

License # CVC56695 

wa...@pureenergysolar.com
 

http://pureenergysolar.com
 

352 377-6527 Office
352 336-3299 
Fax
352 316-1637 Cell
The
content of this message is Pure Energy Solar Confidential. If you are 
not the intended
recipient and have received this message in error, any use or 
distribution is
prohibited. Please notify me immediately by reply e-mail and delete this
message from your computer system. Thank you.



 From: peter.parr...@calsolareng.com
 To: re-wrenches@lists.re-wrenches.org
 Date: Tue, 31 May 2011 16:05:06 -0700
 Subject: Re: [RE-wrenches] 24 volt Battery Bank comparison
 
 Fewer number of strings the better. Go with plan A. Why 13 (and not 12) of
 the Rolls if I may ask?
 
 
  
 Peter T. Parrish, Ph.D., President
 California Solar Engineering, Inc.
 820 Cynthia Ave., Los Angeles, CA 90065
 CA Lic. 854779, NABCEP Cert. 031806-26
 peter.parr...@calsolareng.com  
 Ph 323-258-8883, Mobile 323-839-6108, Fax 323-258-8885
 
  
 
 From: re-wrenches-boun...@lists.re-wrenches.org
 [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Wayne Irwin
 Sent: Tuesday, May 31, 2011 2:50 PM
 To: Wrenches
 Subject: [RE-wrenches] 24 volt Battery Bank comparison
 
 Hello Esteemed Battery Gurus,
 
 Which of the following do you believe is the better 24 V battery bank?
 
 A) 13 - Rolls 2-YS-31 2430 AH @ 20 HR (one string) 
 
 or 
 
 B) 9 -  Rolls 8-CS-25P 820 AH @ 20 HR (3 strings of 3)
 
 Thank you in advance for your input!
 
 
 Wayne Irwin, EE
 Director of Engineering
 Pure Energy Solar International Inc. 
 State Licensed Solar Contractor
 License # CVC56695 
 wa...@pureenergysolar.com 
 http://pureenergysolar.com 
 352 377-6527 Office
 352 336-3299 Fax
 352 316-1637 Cell
 The content of this message is Pure Energy Solar Confidential. If you are
 not the intended recipient and have received this message in error, any use
 or distribution is prohibited. Please notify me immediately by reply e-mail
 and delete this message from your computer system. Thank you.
 
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
  ___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] 24 volt Battery Bank comparison

2011-05-31 Thread Jason Szumlanski
If the choice is one or three, I choose one. If the choice is one or two, I 
choose two for the same redundancy benefit echoed by others. However, it 
sometimes depends how remote the system is. 

If you are a few miles down the road from a stocking battery distributor, one 
string is great. If you are a boat ride or a 10 hour 4x4 crawl at 2 mph away, 
redundancy may be critical. It all depends on the situation. I would even 
consider three strings if the location has serious access problems and the 
customer can only survive with 33% capacity loss for a period of time.

While I have my favorite brands, sometimes you have to go with a brand that 
fits the right capacity and string arrangement. Fortunately Rolls has lots of 
options, so you should find a suitable alternative. I start with my desired V, 
aH, and parallel strings, then let the manufacturer or distributor do the work 
and recommend options. Not that I don't do my research, but sometimes they come 
up with a better option than you initially think of.  

Jason Szumlanski
Fafco Solar

On May 31, 2011, at 6:25 PM, Brian Mehalic br...@solarenergy.org wrote:

 Hi Wayne-
 While I think a lot of folks will agree that a single string is better for 
 the long term health of the batteries as it results in more even charging, I 
 still like the idea of at least two strings.  That way if a single battery 
 fails, that string can be removed and the end-user can at least get by on 
 half of the pack until a replacement can be installed.
 Brian
 
 On Tue, May 31, 2011 at 10:19 PM, James Surrette ja...@surrette.com wrote:
 Hi Wayne,
 
 I look forward to the input from the wrenches.
 
 My recommendation, regardless of the brand, would be for one string.
 
 Regards,
 
 Jamie
 
  Wayne Irwin wa...@pureenergysolar.com 5/31/2011 6:49 PM 
 Hello Esteemed Battery Gurus,
 
 Which of the following do you believe is the better 24 V battery bank?
 
 A) 13 - Rolls 2-YS-31 2430 AH @ 20 HR (one string)
 
 or
 
 B) 9 -  Rolls 8-CS-25P 820 AH @ 20 HR (3 strings of 3)
 
 Thank you in advance for your input!
 
 
 Wayne Irwin, EE
 Director of Engineering
 Pure Energy Solar International Inc. 
 State Licensed Solar Contractor
 License # CVC56695 
 wa...@pureenergysolar.com
 http://pureenergysolar.com
 352 377-6527 Office
 352 336-3299 Fax
 352 316-1637 Cell
 The content of this message is Pure Energy Solar Confidential. If you are not 
 the intended recipient and have received this message in error, any use or 
 distribution is prohibited. Please notify me immediately by reply e-mail and 
 delete this message from your computer system. Thank you.
 
 
 This email and its attachments have been scanned by iConnection E-Mail 
 Firewall for viruses, spam, and malicious content. The information 
 transmitted in this email is intended only for the entity or person to which 
 it is addressed and may contain confidential/privileged material. If you 
 received this in error, please contact the sender and delete the material 
 from any computer. Any review, retransmission, dissemination, or other use of 
 this information by persons or entities other than the intended recipient is 
 strictly prohibited. %^^%
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
 
 
 
 
 -- 
 
 Brian Mehalic 
 NABCEP Certified Solar PV Installer™ R031508-59
 IREC ISPQ Certified Affiliated Instructor/PV US-0132
 PV Curriculum Developer and Instructor
 Solar Energy International
 Carbondale, CO 81623
 http://www.solarenergy.org
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] 24 volt Battery Bank comparison

2011-05-31 Thread Bob-O Schultze
Wayne,
I'd recommend against that. To do an effective equalization charge on that bank 
you'll need to get the voltage up to at least 2.6-2.7V per cell. That would 
mean a 13 cell pack voltage of 34-35V. Got any DC loads at all? Danger, Will 
Robinson, Danger!  Using the inverter as a charging source? I think you'll run 
out of transformer windings or at the very least reduce your amperage output 
greatly toward the end of that cycle.
Hopefully, Jamie can jump in with an opinion here as well.
Good Luck!
Bob-O 
On May 31, 2011, at 4:28 PM, Wayne Irwin wrote:

Just for a little extra.

Wayne Irwin, EE
Director of Engineering
Pure Energy Solar International Inc. 
State Licensed Solar Contractor
License # CVC56695 
wa...@pureenergysolar.com 
http://pureenergysolar.com 
352 377-6527 Office
352 336-3299 Fax
352 316-1637 Cell
The content of this message is Pure Energy Solar Confidential. If you are not 
the intended recipient and have received this message in error, any use or 
distribution is prohibited. Please notify me immediately by reply e-mail and 
delete this message from your computer system. Thank you.___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] 24 volt Battery Bank comparison

2011-05-31 Thread Wayne Irwin

 A) With a 13th battery and only one string, if there were a failure in one of 
the cells, the system would most likely demonstrate the failure rather quickly 
and allow for the faulty battery to be removed while still maintaining adequate 
voltage to operate the 24V system. 

 B) On the other hand, Tom presents the exact reason behind the idea of the 3 - 
string design.

This is an off grid system.

I know this may open up a can of (philosophically varied) worms. But, this is 
the reasoning behind the two designs.

PS. Buss bars (if 3 strings) and 4/0 CU would be used. 



Wayne Irwin, EE
Director of Engineering

Pure Energy Solar International Inc. 
State Licensed Solar Contractor

License # CVC56695 

wa...@pureenergysolar.com
 

http://pureenergysolar.com
 

352 377-6527 Office
352 336-3299 
Fax
352 316-1637 Cell
The
content of this message is Pure Energy Solar Confidential. If you are 
not the intended
recipient and have received this message in error, any use or 
distribution is
prohibited. Please notify me immediately by reply e-mail and delete this
message from your computer system. Thank you.



From: t...@wagonmaker.com
To: re-wrenches@lists.re-wrenches.org
Date: Tue, 31 May 2011 13:36:16 -1000
Subject: Re: [RE-wrenches] 24 volt Battery Bank comparison









From a reliability standpoint I would never want to bet the farm on one 
string.  All it takes is the failure of one cell and the system is useless 
until it is replaced.  Three strings means a cell failure only reduces 
capacity by 33% not 100%.  I’ve always thought in off-grid systems it is a 
good idea to build in as much redundancy as possible whenever possible.  
Oh, and always use a buss bar system with multiple strings, it makes for a far 
more stable system with less stress on the batteries.
 
Tom
 
 


 

From: Wayne Irwin 
Sent: Tuesday, May 31, 2011 11:49 AM
To: Wrenches 
Subject: [RE-wrenches] 24 volt Battery Bank 
comparison
 
Hello 
Esteemed Battery Gurus,

Which of the following do you believe is the 
better 24 V battery bank?

A) 13 - Rolls 2-YS-31 2430 AH @ 20 HR (one 
string) 

or 

B) 9 -  Rolls 8-CS-25P 820 AH @ 20 HR (3 strings 
of 3)

Thank you in advance for your input!


Wayne Irwin, EE
Director of 
Engineering
Pure Energy Solar International Inc. 

State Licensed Solar Contractor
License # CVC56695 
mailto:pureenergyso...@hotmail.com 

http://pureenergysolar.com 
352 
377-6527 Office
352 
336-3299 Fax
352 
316-1637 Cell

The content of this 
message is Pure Energy Solar Confidential. If you are not the intended 
recipient 
and have received this message in error, any use or distribution is prohibited. 
Please notify me immediately by reply e-mail and delete this message from your 
computer system. Thank you.




___
List sponsored by Home Power 
magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options 
 
settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List 
rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out 
participant bios:
www.members.re-wrenches.org





No virus found in this 
message.
Checked by AVG - www.avg.com
Version: 10.0.1375 / Virus 
Database: 1509/3671 - Release Date: 05/31/11

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org   ___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] 24 volt Battery Bank comparison

2011-05-31 Thread Wayne Irwin

No DC loads at all. 

Wayne Irwin, EE
Director of Engineering

Pure Energy Solar International Inc. 
State Licensed Solar Contractor

License # CVC56695 

wa...@pureenergysolar.com
 

http://pureenergysolar.com
 

352 377-6527 Office
352 336-3299 
Fax
352 316-1637 Cell
The
content of this message is Pure Energy Solar Confidential. If you are 
not the intended
recipient and have received this message in error, any use or 
distribution is
prohibited. Please notify me immediately by reply e-mail and delete this
message from your computer system. Thank you.



From: bo...@electronconnection.com
Date: Tue, 31 May 2011 16:59:43 -0700
To: re-wrenches@lists.re-wrenches.org
Subject: Re: [RE-wrenches] 24 volt Battery Bank comparison



Wayne,I'd recommend against that. To do an effective equalization charge on 
that bank you'll need to get the voltage up to at least 2.6-2.7V per cell. That 
would mean a 13 cell pack voltage of 34-35V. Got any DC loads at all? Danger, 
Will Robinson, Danger!  Using the inverter as a charging source? I think you'll 
run out of transformer windings or at the very least reduce your amperage 
output greatly toward the end of that cycle.Hopefully, Jamie can jump in with 
an opinion here as well.Good Luck!Bob-O 
On May 31, 2011, at 4:28 PM, Wayne Irwin wrote:Just for a little extra.

Wayne Irwin, EE
Director of Engineering
Pure Energy Solar International Inc. 
State Licensed Solar Contractor
License # CVC56695 
wa...@pureenergysolar.com 
http://pureenergysolar.com 
352 377-6527 Office
352 336-3299 Fax
352 316-1637 Cell
The content of this message is Pure Energy Solar Confidential. If you are not 
the intended recipient and have received this message in error, any use or 
distribution is prohibited. Please notify me immediately by reply e-mail and 
delete this message from your computer system. Thank you.
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org   ___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] 24 volt Battery Bank comparison

2011-05-31 Thread James Surrette

Hi Wayne, 

Why not 12 cells (24VDC) and put the 13th in storage as DRY? 

Regards, 

Jamie

 Wayne Irwin wa...@pureenergysolar.com 5/31/2011 9:01 PM 
 A) With a 13th battery and only one string, if there were a failure in
one of the cells, the system would most likely demonstrate the failure
rather quickly and allow for the faulty battery to be removed while
still maintaining adequate voltage to operate the 24V system.

 B) On the other hand, Tom presents the exact reason behind the idea of
the 3 - string design.

This is an off grid system.

I know this may open up a can of (philosophically varied) worms. But,
this is the reasoning behind the two designs.

PS. Buss bars (if 3 strings) and 4/0 CU would be used.



Wayne Irwin, EE
Director of Engineering
Pure Energy Solar International Inc. 
State Licensed Solar Contractor
License # CVC56695 
wa...@pureenergysolar.com ( mailto:pureenergyso...@hotmail.com )
http://pureenergysolar.com ( http://pureenergysolar.net/ )
352 377-6527 Office
352 336-3299 Fax
352 316-1637 Cell

The content of this message is Pure Energy Solar Confidential. If you
are not the intended recipient and have received this message in error,
any use or distribution is prohibited. Please notify me immediately by
reply e-mail and delete this message from your computer system. Thank
you. 




From: t...@wagonmaker.com
To: re-wrenches@lists.re-wrenches.org
Date: Tue, 31 May 2011 13:36:16 -1000
Subject: Re: [RE-wrenches] 24 volt Battery Bank comparison

.ExternalClass .ecxhmmessage P {padding:0px;} .ExternalClass
body.ecxhmmessage {font-size:10pt;font-family:Tahoma;} 

From a reliability standpoint I would never want to bet the farm on one
string.  All it takes is the failure of one cell and the system is
useless until it is replaced.  Three strings means a cell failure only
reduces capacity by 33% not 100%.  I’ve always thought in off-grid
systems it is a good idea to build in as much redundancy as possible
whenever possible.  Oh, and always use a buss bar system with multiple
strings, it makes for a far more stable system with less stress on the
batteries. 

  

Tom 

  

  

  

From: Wayne Irwin ( mailto:wa...@pureenergysolar.com ) 

Sent: Tuesday, May 31, 2011 11:49 AM 

To: Wrenches ( mailto:re-wrenches@lists.re-wrenches.org ) 

Subject: [RE-wrenches] 24 volt Battery Bank comparison 

  

Hello Esteemed Battery Gurus,

Which of the following do you believe is the better 24 V battery bank?

A) 13 - Rolls 2-YS-31 2430 AH @ 20 HR (one string)

or

B) 9 -  Rolls 8-CS-25P 820 AH @ 20 HR (3 strings of 3)

Thank you in advance for your input!


Wayne Irwin, EE
Director of Engineering
Pure Energy Solar International Inc. 
State Licensed Solar Contractor
License # CVC56695 
mailto:pureenergyso...@hotmail.com
http://pureenergysolar.com ( http://pureenergysolar.net/ )
352 377-6527 Office
352 336-3299 Fax
352 316-1637 Cell

The content of this message is Pure Energy Solar Confidential. If you
are not the intended recipient and have received this message in error,
any use or distribution is prohibited. Please notify me immediately by
reply e-mail and delete this message from your computer system. Thank
you. 



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



No virus found in this message.
Checked by AVG - www.avg.com
Version: 10.0.1375 / Virus Database: 1509/3671 - Release Date: 05/31/11



___ List sponsored by Home
Power magazine List Address: RE-wrenches@lists.re-wrenches.org Options 
settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List
rules  etiquette: www.re-wrenches.org/etiquette.htm Check out
participant bios: www.members.re-wrenches.org 


This email and its attachments have been scanned by iConnection E-Mail Firewall 
for viruses, spam, and malicious content.
The information transmitted in this email is intended only for the entity or 
person to which it is addressed and may contain confidential/privileged 
material. If you received this in error, please contact the sender and delete 
the material from any computer. Any review, retransmission, dissemination, or 
other use of this information by persons or entities other than the intended 
recipient is strictly prohibited. %^^%
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re

Re: [RE-wrenches] 24 volt Battery Bank comparison

2011-05-31 Thread Allan Sindelar


  
  
Tom,
Yes, but if you use individual 2V cells, you can pull one failed
cell out of the string and get by just fine by adjusting setpoints
down by 8% (11/12ths). You'll lose 8% of capacity until a cell is
replaced; or, if the failed cell is the first to go at end-of-life,
just live with the remaining 22V bank while collecting funds for the
replacement set ("You have been setting aside some money each year
for that set, haven't you?"). 

Using two strings is fine, but if the smaller strings are made up of
4V or 6V cases, you no longer can remove just one cell. Rather, you
must disconnect one string and live on 50% capacity (or 67% with two
out of three strings) until a replacement is secured. 

Based on the above, I'd usually go with a single string of the best
batteries I can find. Personally, I like what Chris Worcester wrote:
My one string of 1476 AH IBE 2 V cells went 19 years
before retiring them to a neighbor’s off grid system, where they
are now working. One string has my vote!
as
I just put that exact size of IBE 2V cells in my own home. Here's hoping I get
another 18 years and 10 months out of them. 
Allan



  
  
  Allan Sindelar
  al...@positiveenergysolar.com
NABCEP Certified Photovoltaic
  Installer
  NABCEP Certified Technical Sales Professional
  New Mexico EE98J Journeyman Electrician
  Positive Energy, Inc.
  3201 Calle Marie
  Santa Fe, New Mexico 87507
  505 424-1112
  www.positiveenergysolar.com


On 5/31/2011 5:36 PM, Tom Elliot wrote:

  
  

  From a reliability standpoint I would never want to bet
the farm on one string.  All it takes is the failure of one
cell and the system is useless until it is replaced.  Three
strings means a cell failure only reduces capacity by 33%
not 100%.  I’ve always thought in off-grid systems it is a
good idea to build in as much redundancy as possible
whenever possible.  Oh, and always use a buss bar system
with multiple strings, it makes for a far more stable system
with less stress on the batteries.
   
  Tom

  

  

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] 24 volt Battery Bank comparison

2011-05-31 Thread Jason Szumlanski
Just another thought- If redundancy is an issue with string sizing, having a 
12v inverter handy is sometimes a viable backup option with a 24v bank with 2 
or more parallel strings. 

Jason Szumlanski
Fafco Solar

On May 31, 2011, at 7:55 PM, Jason Szumlanski ja...@fafcosolar.com wrote:

 If the choice is one or three, I choose one. If the choice is one or two, I 
 choose two for the same redundancy benefit echoed by others. However, it 
 sometimes depends how remote the system is. 
 
 If you are a few miles down the road from a stocking battery distributor, one 
 string is great. If you are a boat ride or a 10 hour 4x4 crawl at 2 mph away, 
 redundancy may be critical. It all depends on the situation. I would even 
 consider three strings if the location has serious access problems and the 
 customer can only survive with 33% capacity loss for a period of time.
 
 While I have my favorite brands, sometimes you have to go with a brand that 
 fits the right capacity and string arrangement. Fortunately Rolls has lots of 
 options, so you should find a suitable alternative. I start with my desired 
 V, aH, and parallel strings, then let the manufacturer or distributor do the 
 work and recommend options. Not that I don't do my research, but sometimes 
 they come up with a better option than you initially think of.  
 
 Jason Szumlanski
 Fafco Solar
 
 On May 31, 2011, at 6:25 PM, Brian Mehalic br...@solarenergy.org wrote:
 
 Hi Wayne-
 While I think a lot of folks will agree that a single string is better for 
 the long term health of the batteries as it results in more even charging, I 
 still like the idea of at least two strings.  That way if a single battery 
 fails, that string can be removed and the end-user can at least get by on 
 half of the pack until a replacement can be installed.
 Brian
 
 On Tue, May 31, 2011 at 10:19 PM, James Surrette ja...@surrette.com wrote:
 Hi Wayne,
 
 I look forward to the input from the wrenches.
 
 My recommendation, regardless of the brand, would be for one string.
 
 Regards,
 
 Jamie
 
  Wayne Irwin wa...@pureenergysolar.com 5/31/2011 6:49 PM 
 Hello Esteemed Battery Gurus,
 
 Which of the following do you believe is the better 24 V battery bank?
 
 A) 13 - Rolls 2-YS-31 2430 AH @ 20 HR (one string)
 
 or
 
 B) 9 -  Rolls 8-CS-25P 820 AH @ 20 HR (3 strings of 3)
 
 Thank you in advance for your input!
 
 
 Wayne Irwin, EE
 Director of Engineering
 Pure Energy Solar International Inc. 
 State Licensed Solar Contractor
 License # CVC56695 
 wa...@pureenergysolar.com
 http://pureenergysolar.com
 352 377-6527 Office
 352 336-3299 Fax
 352 316-1637 Cell
 The content of this message is Pure Energy Solar Confidential. If you are 
 not the intended recipient and have received this message in error, any use 
 or distribution is prohibited. Please notify me immediately by reply e-mail 
 and delete this message from your computer system. Thank you.
 
 
 This email and its attachments have been scanned by iConnection E-Mail 
 Firewall for viruses, spam, and malicious content. The information 
 transmitted in this email is intended only for the entity or person to which 
 it is addressed and may contain confidential/privileged material. If you 
 received this in error, please contact the sender and delete the material 
 from any computer. Any review, retransmission, dissemination, or other use 
 of this information by persons or entities other than the intended recipient 
 is strictly prohibited. %^^%
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
 
 
 
 
 -- 
 
 Brian Mehalic 
 NABCEP Certified Solar PV Installer™ R031508-59
 IREC ISPQ Certified Affiliated Instructor/PV US-0132
 PV Curriculum Developer and Instructor
 Solar Energy International
 Carbondale, CO 81623
 http://www.solarenergy.org
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 

Re: [RE-wrenches] 24 volt Battery Bank comparison

2011-05-31 Thread Wayne Irwin

I think the verdict is 12 - Rolls 2-YS-31 2430 AH @ 20 HR (one string) and one 
dry spare in storage is the best case scenario!

Wayne Irwin, EE
Director of Engineering

Pure Energy Solar International Inc. 
State Licensed Solar Contractor

License # CVC56695 

wa...@pureenergysolar.com
 

http://pureenergysolar.com
 

352 377-6527 Office
352 336-3299 
Fax
352 316-1637 Cell
The
content of this message is Pure Energy Solar Confidential. If you are 
not the intended
recipient and have received this message in error, any use or 
distribution is
prohibited. Please notify me immediately by reply e-mail and delete this
message from your computer system. Thank you.



Date: Tue, 31 May 2011 18:16:56 -0600
From: al...@positiveenergysolar.com
To: re-wrenches@lists.re-wrenches.org
Subject: Re: [RE-wrenches] 24 volt Battery Bank comparison



  



  
  
Tom,

Yes, but if you use individual 2V cells, you can pull one failed
cell out of the string and get by just fine by adjusting setpoints
down by 8% (11/12ths). You'll lose 8% of capacity until a cell is
replaced; or, if the failed cell is the first to go at end-of-life,
just live with the remaining 22V bank while collecting funds for the
replacement set (You have been setting aside some money each year
for that set, haven't you?). 



Using two strings is fine, but if the smaller strings are made up of
4V or 6V cases, you no longer can remove just one cell. Rather, you
must disconnect one string and live on 50% capacity (or 67% with two
out of three strings) until a replacement is secured. 



Based on the above, I'd usually go with a single string of the best
batteries I can find. Personally, I like what Chris Worcester wrote:

My one string of 1476 AH IBE 2 V cells went 19 years
before retiring them to a neighbor’s off grid system, where they
are now working. One string has my vote!
as
I just put that exact size of IBE 2V cells in my own home. Here's hoping I 
get
another 18 years and 10 months out of them. 

Allan





  
  Message body
  Allan Sindelar

  al...@positiveenergysolar.com

NABCEP Certified Photovoltaic
  Installer

  NABCEP Certified Technical Sales Professional

  New Mexico EE98J Journeyman Electrician

  Positive Energy, Inc.

  3201 Calle Marie

  Santa Fe, New Mexico 87507

  505 424-1112

  www.positiveenergysolar.com



On 5/31/2011 5:36 PM, Tom Elliot wrote:

  
  

  From a reliability standpoint I would never want to bet
the farm on one string.  All it takes is the failure of one
cell and the system is useless until it is replaced.  Three
strings means a cell failure only reduces capacity by 33%
not 100%.  I’ve always thought in off-grid systems it is a
good idea to build in as much redundancy as possible
whenever possible.  Oh, and always use a buss bar system
with multiple strings, it makes for a far more stable system
with less stress on the batteries.
   
  Tom

  

  


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org   ___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] 24 volt Battery Bank comparison

2011-05-31 Thread Jason Szumlanski
I'd vote to listen to the manufacturer. It's in their best interest to provide 
a reliable solution. Good call. 


On May 31, 2011, at 8:23 PM, Wayne Irwin wa...@pureenergysolar.com wrote:

 I think the verdict is 12 - Rolls 2-YS-31 2430 AH @ 20 HR (one string) and 
 one dry spare in storage is the best case scenario!
 
 Wayne Irwin, EE
 Director of Engineering
 Pure Energy Solar International Inc. 
 State Licensed Solar Contractor
 License # CVC56695 
 wa...@pureenergysolar.com 
 http://pureenergysolar.com 
 352 377-6527 Office
 352 336-3299 Fax
 352 316-1637 Cell
 The content of this message is Pure Energy Solar Confidential. If you are not 
 the intended recipient and have received this message in error, any use or 
 distribution is prohibited. Please notify me immediately by reply e-mail and 
 delete this message from your computer system. Thank you.
 
 
 
 
 
 Date: Tue, 31 May 2011 18:16:56 -0600
 From: al...@positiveenergysolar.com
 To: re-wrenches@lists.re-wrenches.org
 Subject: Re: [RE-wrenches] 24 volt Battery Bank comparison
 
 Tom,
 Yes, but if you use individual 2V cells, you can pull one failed cell out of 
 the string and get by just fine by adjusting setpoints down by 8% (11/12ths). 
 You'll lose 8% of capacity until a cell is replaced; or, if the failed cell 
 is the first to go at end-of-life, just live with the remaining 22V bank 
 while collecting funds for the replacement set (You have been setting aside 
 some money each year for that set, haven't you?). 
 
 Using two strings is fine, but if the smaller strings are made up of 4V or 6V 
 cases, you no longer can remove just one cell. Rather, you must disconnect 
 one string and live on 50% capacity (or 67% with two out of three strings) 
 until a replacement is secured. 
 
 Based on the above, I'd usually go with a single string of the best batteries 
 I can find. Personally, I like what Chris Worcester wrote:
 My one string of 1476 AH IBE 2 V cells went 19 years before retiring them to 
 a neighbor’s off grid system, where they are now working. One string has my 
 vote!
 
 as I just put that exact size of IBE 2V cells in my own home. Here's hoping I 
 get another 18 years and 10 months out of them. 
 Allan
 
 Allan Sindelar
 al...@positiveenergysolar.com
 NABCEP Certified Photovoltaic Installer
 NABCEP Certified Technical Sales Professional
 New Mexico EE98J Journeyman Electrician
 Positive Energy, Inc.
 3201 Calle Marie
 Santa Fe, New Mexico 87507
 505 424-1112
 www.positiveenergysolar.com
 
 On 5/31/2011 5:36 PM, Tom Elliot wrote:
 From a reliability standpoint I would never want to bet the farm on one 
 string.  All it takes is the failure of one cell and the system is useless 
 until it is replaced.  Three strings means a cell failure only reduces 
 capacity by 33% not 100%.  I’ve always thought in off-grid systems it is a 
 good idea to build in as much redundancy as possible whenever possible.  Oh, 
 and always use a buss bar system with multiple strings, it makes for a far 
 more stable system with less stress on the batteries.
  
 Tom
 
 ___ List sponsored by Home Power 
 magazine List Address: RE-wrenches@lists.re-wrenches.org Options  settings: 
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules 
  etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: 
 www.members.re-wrenches.org
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] 24 volt Battery Bank comparison

2011-05-31 Thread Tom Elliot
Good on the buss bars Wayne.  Using them removes the concerns about multiple 
strings and increases redundancy and system stability.  You won’t need 4/0 
between single strings and the buss bar, you can probably easily use smaller 
cable, just size it for the individual string.  4/0 to the inverter of course.

I echo the concern about the higher voltage bank though.  Most off-grid systems 
have some low voltage DC elements, or at least offer the opportunity to add 
them, so the higher voltage could be a problem, especially during equalization. 
 If you use the buss bars, keep system voltage high enough, and the batteries 
are well-cared for, it shouldn’t be necessary to add that one extra battery.

From: Wayne Irwin 
Sent: Tuesday, May 31, 2011 2:05 PM
To: Wrenches 
Subject: Re: [RE-wrenches] 24 volt Battery Bank comparison

No DC loads at all. 

Wayne Irwin, EE
Director of Engineering
Pure Energy Solar International Inc. 
State Licensed Solar Contractor
License # CVC56695 
mailto:pureenergyso...@hotmail.com 
http://pureenergysolar.com 
352 377-6527 Office
352 336-3299 Fax
352 316-1637 Cell

The content of this message is Pure Energy Solar Confidential. If you are not 
the intended recipient and have received this message in error, any use or 
distribution is prohibited. Please notify me immediately by reply e-mail and 
delete this message from your computer system. Thank you.







From: bo...@electronconnection.com
Date: Tue, 31 May 2011 16:59:43 -0700
To: re-wrenches@lists.re-wrenches.org
Subject: Re: [RE-wrenches] 24 volt Battery Bank comparison

Wayne, 
I'd recommend against that. To do an effective equalization charge on that bank 
you'll need to get the voltage up to at least 2.6-2.7V per cell. That would 
mean a 13 cell pack voltage of 34-35V. Got any DC loads at all? Danger, Will 
Robinson, Danger!  Using the inverter as a charging source? I think you'll run 
out of transformer windings or at the very least reduce your amperage output 
greatly toward the end of that cycle.
Hopefully, Jamie can jump in with an opinion here as well.
Good Luck!
Bob-O 

On May 31, 2011, at 4:28 PM, Wayne Irwin wrote:


Just for a little extra.

Wayne Irwin, EE
Director of Engineering
Pure Energy Solar International Inc. 
State Licensed Solar Contractor
License # CVC56695 
mailto:pureenergyso...@hotmail.com 
http://pureenergysolar.com 
352 377-6527 Office
352 336-3299 Fax
352 316-1637 Cell

The content of this message is Pure Energy Solar Confidential. If you are not 
the intended recipient and have received this message in error, any use or 
distribution is prohibited. Please notify me immediately by reply e-mail and 
delete this message from your computer system. Thank you.

___ List sponsored by Home Power 
magazine List Address: RE-wrenches@lists.re-wrenches.org Options  settings: 
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules  
etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: 
www.members.re-wrenches.org 



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org






No virus found in this message.
Checked by AVG - www.avg.com
Version: 10.0.1375 / Virus Database: 1509/3671 - Release Date: 05/31/11
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] 24 volt Battery Bank comparison

2011-05-31 Thread James Jefferson Jarvis

On 2011-05-31 20:14, Tom Elliot wrote:

Good on the buss bars Wayne. Using them removes the concerns about
multiple strings and increases redundancy and system stability. You
won’t need 4/0 between single strings and the buss bar, you can probably
easily use smaller cable, just size it for the individual string. 4/0 to


Part of the argument for having multiple strings is for redundancy. If 
smaller interconnect cables are used, they will likely not have the 
required ampacity and OCPD to support the full load. In the event of 
part of the bank needing to be pulled offline there will be downtime and 
expense associated with upgrading the smaller interconnect cables to 
support the full load or the proportionally increased load.


Food for thought,

-James Jarvis
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] 24 volt Battery Bank comparison

2011-05-31 Thread Larry Crutcher, Starlight Solar Power Systems
Wayne,
Whenever possible, always design a battery bank for a single series string. 
Parallel strings require more attention and increase the probability of early 
failure due to unequal charging.

Larry Crutcher
Starlight Solar Power Systems
11871 S Fortuna Road, #210
Yuma, AZ 85367

la...@starlightsolar.com
(928) 342-9103



On May 31, 2011, at 2:49 PM, Wayne Irwin wrote:

 Hello Esteemed Battery Gurus,
 
 Which of the following do you believe is the better 24 V battery bank?
 
 A) 13 - Rolls 2-YS-31 2430 AH @ 20 HR (one string) 
 
 or 
 
 B) 9 -  Rolls 8-CS-25P 820 AH @ 20 HR (3 strings of 3)
 
 Thank you in advance for your input!
 
 
 Wayne Irwin, EE
 Director of Engineering
 Pure Energy Solar International Inc. 
 State Licensed Solar Contractor
 License # CVC56695 
 wa...@pureenergysolar.com 
 http://pureenergysolar.com 
 352 377-6527 Office
 352 336-3299 Fax
 352 316-1637 Cell
 The content of this message is Pure Energy Solar Confidential. If you are not 
 the intended recipient and have received this message in error, any use or 
 distribution is prohibited. Please notify me immediately by reply e-mail and 
 delete this message from your computer system. Thank you.
 
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] 24 volt Battery Bank comparison

2011-05-31 Thread Larry Crutcher, Starlight Solar Power Systems
Oops! Guess I should have read all the posts before I reply;-

Larry Crutcher


On May 31, 2011, at 5:23 PM, Wayne Irwin wrote:

 I think the verdict is 12 - Rolls 2-YS-31 2430 AH @ 20 HR (one string) and 
 one dry spare in storage is the best case scenario!
 
 Wayne Irwin, EE
 Director of Engineering
 Pure Energy Solar International Inc. 
 State Licensed Solar Contractor
 License # CVC56695 
 wa...@pureenergysolar.com 
 http://pureenergysolar.com 
 352 377-6527 Office
 352 336-3299 Fax
 352 316-1637 Cell
 The content of this message is Pure Energy Solar Confidential. If you are not 
 the intended recipient and have received this message in error, any use or 
 distribution is prohibited. Please notify me immediately by reply e-mail and 
 delete this message from your computer system. Thank you.
 
 
 
 
 Date: Tue, 31 May 2011 18:16:56 -0600
 From: al...@positiveenergysolar.com
 To: re-wrenches@lists.re-wrenches.org
 Subject: Re: [RE-wrenches] 24 volt Battery Bank comparison
 
 Tom,
 Yes, but if you use individual 2V cells, you can pull one failed cell out of 
 the string and get by just fine by adjusting setpoints down by 8% (11/12ths). 
 You'll lose 8% of capacity until a cell is replaced; or, if the failed cell 
 is the first to go at end-of-life, just live with the remaining 22V bank 
 while collecting funds for the replacement set (You have been setting aside 
 some money each year for that set, haven't you?). 
 
 Using two strings is fine, but if the smaller strings are made up of 4V or 6V 
 cases, you no longer can remove just one cell. Rather, you must disconnect 
 one string and live on 50% capacity (or 67% with two out of three strings) 
 until a replacement is secured. 
 
 Based on the above, I'd usually go with a single string of the best batteries 
 I can find. Personally, I like what Chris Worcester wrote:
 My one string of 1476 AH IBE 2 V cells went 19 years before retiring them to 
 a neighbor’s off grid system, where they are now working. One string has my 
 vote!
 as I just put that exact size of IBE 2V cells in my own home. Here's hoping I 
 get another 18 years and 10 months out of them. 
 Allan
 
 Allan Sindelar
 al...@positiveenergysolar.com
 NABCEP Certified Photovoltaic Installer
 NABCEP Certified Technical Sales Professional
 New Mexico EE98J Journeyman Electrician
 Positive Energy, Inc.
 3201 Calle Marie
 Santa Fe, New Mexico 87507
 505 424-1112
 www.positiveenergysolar.com
 
 On 5/31/2011 5:36 PM, Tom Elliot wrote:
 From a reliability standpoint I would never want to bet the farm on one 
 string.  All it takes is the failure of one cell and the system is useless 
 until it is replaced.  Three strings means a cell failure only reduces 
 capacity by 33% not 100%.  I’ve always thought in off-grid systems it is a 
 good idea to build in as much redundancy as possible whenever possible.  Oh, 
 and always use a buss bar system with multiple strings, it makes for a far 
 more stable system with less stress on the batteries.
  
 Tom
 
 ___ List sponsored by Home Power 
 magazine List Address: re-wrenc...@lists.re-wrenches.orgOptions  settings: 
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules 
  etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: 
 www.members.re-wrenches.org___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org