Re: [RE-wrenches] High Voltage Breakers for Conext Mppt-80-600
Eric, definitely what I had seen when we offgrid field tested the mppt- 80 in 2010 ! Totally bullet proof charger and the SQD disco shows there are 127 on the west coast for $115 HU361RB. Typically this is outside and protected where it belongs. It is fine next to the mppt if needed. Just do not land 600vdc in the PDP if you want code compliance and safety of the power system. The newer Mppt-100-600 is just as robust. Dave Angelini Offgrid Solar "we go where powerlines don't" http://members.sti.net/offgridsolar/ [1] e-mail offgridso...@sti.net [2] text 209 813 0060 On Wed, 26 Jan 2022 13:10:12 -0800, Eric Smiley wrote: I looked up the CSA record for the XW PDP and it shows: * Maximum System Voltage (DC) 150V dc * Maximum Battery System Voltage 62 V dc (48V nominal) * Maximum System Voltage (AC) 140/280V ac ERIC SMILEY, Project Manager e...@vecoop.ca [3] T: 250.703.6004 [4] T: 888.386.0116 [5] On Wed, 26 Jan 2022 at 12:53, William Miller wrote: Dave: With all due respect, I don't see this as an issue. All of our building wire is rated at 600 volts. If you segregate your OPCD, work neatly and bundle your various lead groupings I think it is perfectly safe. If one is real paranoid, you could rivet in some partitions or more simply, sleeve the 600 VDC leads in NMLT. I looked all through the documentation for the cabinets and no voltage rating is given. We cannot assume the rating is a limitation until we find one. Let us all know if you are privy to this detail. I would not hesitate to integrate the 600 volt rated Conext branded charge controllers into Conext branded BOS cabinets as long as the workmanship is good. William Miller Miller Solar 17395 Oak Road, Atascadero, CA 93422 805-438-5600 www.millersolar.com [7] CA Lic. 773985 FROM: Dave Angelini Offgrid Solar [mailto:offgridso...@sti.net [8]] SENT: Wednesday, January 26, 2022 11:15 AM TO: will...@millersolar.com [9]; RE-wrenches SUBJECT: Re: [RE-wrenches] High Voltage Breakers for Conext Mppt-80-600 It is 600vdc ! Do you want that in a PDP with your 48Vdc and 120/240vac? I do not believe it to be UL listed for 600vdc in there, and so you are breaking some pretty big rules here. I do not post much anymore here. Keep 600vdc out of the PDP and for Offgrid we always want high reliability. Just good design practice! DAVE ANGELINI OFFGRID SOLAR "WE GO WHERE POWERLINES DON'T" E-MAIL TEXT 209 813 0060 Links: -- [1] http://members.sti.net/offgridsolar/ [2] mailto:offgridso...@sti.net [3] mailto:e...@vecoop.ca [4] http://webmail.sti.net/tel:+12507036004 [5] http://webmail.sti.net/tel:+18883860116 [6] mailto:will...@millersolar.com [7] http://www.millersolar.com/ [8] mailto:offgridso...@sti.net [9] mailto:will...@millersolar.com ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org
Re: [RE-wrenches] High Voltage Breakers for Conext Mppt-80-600
I’m facing this same issue. In the past we’ve used the old SQD disco’s near the inverter and fuses in combiners near the array, but they’re big and expensive. Anyone used these or see any issue with these: https://www.industrialcontroldirect.com/dc-disconnect-si16-pel64r-4-p-4080.html?gclid=Cj0KCQiA_8OPBhDtARIsAKQu0gYOEY75OrhrQHsrDVHHCsUd-E6SiYwEcCi1FwY5vWua5iIFl7ovNxMaAroLEALw_wcB <https://www.industrialcontroldirect.com/dc-disconnect-si16-pel64r-4-p-4080.html?gclid=Cj0KCQiA_8OPBhDtARIsAKQu0gYOEY75OrhrQHsrDVHHCsUd-E6SiYwEcCi1FwY5vWua5iIFl7ovNxMaAroLEALw_wcB> Or these: https://www.industrialcontroldirect.com/dc-disconnects-316/panel-mount-dc-switch-421/?zenid=bo3nrdji7umkvsr93hslphj4g4 <https://www.industrialcontroldirect.com/dc-disconnects-316/panel-mount-dc-switch-421/?zenid=bo3nrdji7umkvsr93hslphj4g4> Seems like a nice clean and not terribly expensive option. Totally agree that Schneider should have provided us with a solution in the PDP. Best Regards, Jeremy Coxon NABCEP # 091308-21 MWBE Certified On Jan 26, 2022, at 4:19 PM, re-wrenches-requ...@lists.re-wrenches.org wrote: Send RE-wrenches mailing list submissions to re-wrenches@lists.re-wrenches.org <mailto:re-wrenches@lists.re-wrenches.org> To subscribe or unsubscribe via the World Wide Web, visit http://lists.re-wrenches.org/listinfo.cgi/re-wrenches-re-wrenches.org <http://lists.re-wrenches.org/listinfo.cgi/re-wrenches-re-wrenches.org> or, via email, send a message with subject or body 'help' to re-wrenches-requ...@lists.re-wrenches.org <mailto:re-wrenches-requ...@lists.re-wrenches.org> You can reach the person managing the list at re-wrenches-ow...@lists.re-wrenches.org <mailto:re-wrenches-ow...@lists.re-wrenches.org> When replying, please edit your Subject line so it is more specific than "Re: Contents of RE-wrenches digest..." When responding to posts within the Digest, be sure to restore the Subject: line to the original, and please edit out any extraneous lines from the quoted message. Today's Topics: 1. Re: High Voltage Breakers for Conext Mppt-80-600 (Pieter Huebner) From: "Pieter Huebner" mailto:pie...@offgridenterprises.org>> Subject: Re: [RE-wrenches] High Voltage Breakers for Conext Mppt-80-600 Date: January 26, 2022 at 4:19:48 PM EST To: mailto:will...@millersolar.com>>, "'RE-wrenches'" mailto:re-wrenches@lists.re-wrenches.org>> I must caution those who are considering the use of touch safe fuse holders in distribution panels. If one of those fuse holders were to be opened under load you will very likely have a fire. Always be sure to only install touch safe fuse holders in such a manner that they cannot be opened by un trained personnel, Those fuse holders are not load break rated. Pieter From: RE-wrenches mailto:re-wrenches-boun...@lists.re-wrenches.org>> On Behalf Of William Miller Sent: Wednesday, January 26, 2022 12:05 PM To: RE-wrenches mailto:re-wrenches@lists.re-wrenches.org>> Subject: Re: [RE-wrenches] High Voltage Breakers for Conext Mppt-80-600 Michael: This seems like a rather stunning oversight—offering a charge controller without any means to integrate it into the BOS built by the same manufacturer. Just now I laid a 600 VDC rated touch-safe fuse holder over a QOU breaker. The fuse holder is smaller than the breaker so it would fit in the PDP. The fuse holder would be a bit recessed which may look awkward and impede the opening of the fuse holder. I do know you can buy DIN rail of varying height. Maybe you could drill out the rivets on the DIN rail and replace a short section of it with high profile DIN Rail and make a somewhat elegant solution??? Good luck. William Miller Miller Solar 17395 Oak Road, Atascadero, CA 93422 805-438-5600 www.millersolar.com <http://www.millersolar.com/> CA Lic. 773985 From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org <mailto:re-wrenches-boun...@lists.re-wrenches.org>] On Behalf Of Michael Morningstar Sent: Tuesday, January 25, 2022 4:53 PM To: RE-wrenches Subject: Re: [RE-wrenches] High Voltage Breakers for Conext Mppt-80-600 Thanks guys, Just wanted to make sure I wasn’t missing something. Curious that Schneider doesn’t have higher voltage input breakers. On Jan 25, 2022, at 4:15 PM, Tump mailto:t...@swnl.net>> wrote: I use the SQD fused disco I mount this next to the CC and use the Flex cobra wire for the low DC voltage and the do have breakers for the context for that On Jan 25, 2022, at 7:04 PM, Tom Duffy mailto:t...@solar-biz.com>> wrote: Hi Mike No breakers I know of that fit the Conext boxes but you could use a MidNite Big Baby and a MidNite 600 volt breaker in it or even a touch safe 1000 volt fuse and holder they’re DIN rail Tom Duffy Senior Solar Design Engineer Supply chain crunches brought on by the pandemic and Omicr
Re: [RE-wrenches] High Voltage Breakers for Conext Mppt-80-600
Wrenches Midnite has them so ask your gut to get them on board, I have gotten them before Jerry On Tue, Jan 25, 2022 at 10:08 AM Michael Morningstar < mjmornings...@gmail.com> wrote: > Wrenches, > > Can anyone direct me to PV input breakers that are rated up to 600VDC that > would work in a Conext Distribution Panel? From what I can tell, Schneider > only offers breakers up to 160VDC. > > Thanks, > Michael > > > > > *Michael **Morningstar* > > * Morningstar Electric* > PO Box 1494 > Mount Shasta, California 96067 > 530-921-0560 > CSLB 949635 > > > > ___ > List sponsored by Redwood Alliance > > Pay optional member dues here: http://re-wrenches.org > > List Address: RE-wrenches@lists.re-wrenches.org > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > There are two list archives for searching. When one doesn't work, try the > other: > https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ > http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org > > List rules & etiquette: > http://www.re-wrenches.org/etiquette.htm > > Check out or update participant bios: > http://www.members.re-wrenches.org > > ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org
Re: [RE-wrenches] High Voltage Breakers for Conext Mppt-80-600
I looked up the CSA record for the XW PDP and it shows: - Maximum System Voltage (DC) 150V dc - Maximum Battery System Voltage 62 V dc (48V nominal) - Maximum System Voltage (AC) 140/280V ac *Eric Smiley,* Project Manager e...@vecoop.ca T: 250.703.6004 <+12507036004> T: 888.386.0116 <+18883860116> *VIRIDIANENERGY.CA <https://viridianenergy.ca/>* * <https://viridianenergy.ca/>* On Wed, 26 Jan 2022 at 12:53, William Miller wrote: > Dave: > > > > With all due respect, I don’t see this as an issue. All of our building > wire is rated at 600 volts. If you segregate your OPCD, work neatly and > bundle your various lead groupings I think it is perfectly safe. If one is > real paranoid, you could rivet in some partitions or more simply, sleeve > the 600 VDC leads in NMLT. > > > > I looked all through the documentation for the cabinets and no voltage > rating is given. We cannot assume the rating is a limitation until we find > one. Let us all know if you are privy to this detail. > > > > I would not hesitate to integrate the 600 volt rated Conext branded charge > controllers into Conext branded BOS cabinets as long as the workmanship is > good. > > > > William Miller > > > > Miller Solar > > 17395 Oak Road, Atascadero, CA 93422 > > 805-438-5600 > > www.millersolar.com > > CA Lic. 773985 > > > > > > *From:* Dave Angelini Offgrid Solar [mailto:offgridso...@sti.net] > *Sent:* Wednesday, January 26, 2022 11:15 AM > *To:* will...@millersolar.com; RE-wrenches > *Subject:* Re: [RE-wrenches] High Voltage Breakers for Conext Mppt-80-600 > > > > It is 600vdc ! Do you want that in a PDP with your 48Vdc and 120/240vac? > I do not believe it to be UL listed for 600vdc in there, and so you are > breaking some pretty big rules here. I do not post much anymore here. Keep > 600vdc out of the PDP and for Offgrid we always want high reliability. Just > good design practice! > > > > *Dave Angelini Offgrid Solar* > > *"we go where powerlines don't"* > > *http://members.sti.net/offgridsolar/ <http://members.sti.net/offgridsolar/>* > > *e-mail offgridso...@sti.net * > > *text 209 813 0060* > > ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org
Re: [RE-wrenches] High Voltage Breakers for Conext Mppt-80-600
Dave: With all due respect, I don’t see this as an issue. All of our building wire is rated at 600 volts. If you segregate your OPCD, work neatly and bundle your various lead groupings I think it is perfectly safe. If one is real paranoid, you could rivet in some partitions or more simply, sleeve the 600 VDC leads in NMLT. I looked all through the documentation for the cabinets and no voltage rating is given. We cannot assume the rating is a limitation until we find one. Let us all know if you are privy to this detail. I would not hesitate to integrate the 600 volt rated Conext branded charge controllers into Conext branded BOS cabinets as long as the workmanship is good. William Miller Miller Solar 17395 Oak Road, Atascadero, CA 93422 805-438-5600 www.millersolar.com CA Lic. 773985 *From:* Dave Angelini Offgrid Solar [mailto:offgridso...@sti.net] *Sent:* Wednesday, January 26, 2022 11:15 AM *To:* will...@millersolar.com; RE-wrenches *Subject:* Re: [RE-wrenches] High Voltage Breakers for Conext Mppt-80-600 It is 600vdc ! Do you want that in a PDP with your 48Vdc and 120/240vac? I do not believe it to be UL listed for 600vdc in there, and so you are breaking some pretty big rules here. I do not post much anymore here. Keep 600vdc out of the PDP and for Offgrid we always want high reliability. Just good design practice! *Dave Angelini Offgrid Solar* *"we go where powerlines don't"* *http://members.sti.net/offgridsolar/ <http://members.sti.net/offgridsolar/>* *e-mail offgridso...@sti.net * *text 209 813 0060* On Wed, 26 Jan 2022 10:04:49 -0800, William Miller wrote: Michael: This seems like a rather stunning oversight—offering a charge controller without any means to integrate it into the BOS built by the same manufacturer. Just now I laid a 600 VDC rated touch-safe fuse holder over a QOU breaker. The fuse holder is smaller than the breaker so it would fit in the PDP. The fuse holder would be a bit recessed which may look awkward and impede the opening of the fuse holder. I do know you can buy DIN rail of varying height. Maybe you could drill out the rivets on the DIN rail and replace a short section of it with high profile DIN Rail and make a somewhat elegant solution??? Good luck. William Miller Miller Solar 17395 Oak Road, Atascadero, CA 93422 805-438-5600 www.millersolar.com CA Lic. 773985 *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *Michael Morningstar *Sent:* Tuesday, January 25, 2022 4:53 PM *To:* RE-wrenches *Subject:* Re: [RE-wrenches] High Voltage Breakers for Conext Mppt-80-600 Thanks guys, Just wanted to make sure I wasn't missing something. Curious that Schneider doesn't have higher voltage input breakers. On Jan 25, 2022, at 4:15 PM, Tump wrote: I use the SQD fused disco I mount this next to the CC and use the Flex cobra wire for the low DC voltage and the do have breakers for the context for that On Jan 25, 2022, at 7:04 PM, Tom Duffy wrote: Hi Mike No breakers I know of that fit the Conext boxes but you could use a MidNite Big Baby and a MidNite 600 volt breaker in it or even a touch safe 1000 volt fuse and holder they're DIN rail *Tom Duffy* *Senior Solar Design Engineer* Supply chain crunches brought on by the pandemic and Omicron's toll on the workforce are causing shortages of goods. Most analysts agree that rising prices — not just in the US, but also across the world — are largely consequences of the Covid-19 crisis rather than policy errors by governments or central banks. Infectious waves have closed factories in Asian manufacturing hubs and caused chaos in transporting products to US markets, creating a spike in demand. Also Americans have cash to burn after two years of canceled vacations, closed restaurants and working from home, a major factor supercharging the price surge. *t...@solar-biz.com * *MAIN TOLL FREE:* *888-826-0939* *DIRECT: 888-503-6772* *International:* *001-575-539-2111* *PANAMA:* *507-836-5588 X 122* *FAX: 520-844-8442* *www.thesolarbiz.com <http://www.thesolarbiz.com/>* CONFIDENTIALITY NOTICE: This electronic mail message and any attached files contain information intended for the exclusive use of the individual or entity to whom it is addressed and may contain information that is proprietary, privileged, confidential and/or exempt from disclosure under applicable law. THE INFORMATION CONTAINED IN THIS ELECTRONIC MAIL TRANSMISSION IS CONFIDENTIAL. If you are not the intended recipient, you are hereby notified that any viewing, copying, disclosure or distribution of this information is strictly prohibited and may be subject to legal restriction or sanction. Please notify the sender immediately by electronic mail of any unintended recipients and delete the original message without making any copies. *From:* RE-wrenches *On Behalf Of* Michael Morningstar *Sent:* Tuesday, January 25, 2022 1:0
Re: [RE-wrenches] High Voltage Breakers for Conext Mppt-80-600
It is 600vdc ! Do you want that in a PDP with your 48Vdc and 120/240vac? I do not believe it to be UL listed for 600vdc in there, and so you are breaking some pretty big rules here. I do not post much anymore here. Keep 600vdc out of the PDP and for Offgrid we always want high reliability. Just good design practice! Dave Angelini Offgrid Solar "we go where powerlines don't" http://members.sti.net/offgridsolar/ [1] e-mail offgridso...@sti.net [2] text 209 813 0060 On Wed, 26 Jan 2022 10:04:49 -0800, William Miller wrote: Michael: This seems like a rather stunning oversight--offering a charge controller without any means to integrate it into the BOS built by the same manufacturer. Just now I laid a 600 VDC rated touch-safe fuse holder over a QOU breaker. The fuse holder is smaller than the breaker so it would fit in the PDP. The fuse holder would be a bit recessed which may look awkward and impede the opening of the fuse holder. I do know you can buy DIN rail of varying height. Maybe you could drill out the rivets on the DIN rail and replace a short section of it with high profile DIN Rail and make a somewhat elegant solution??? Good luck. William Miller Miller Solar 17395 Oak Road, Atascadero, CA 93422 805-438-5600 www.millersolar.com [3] CA Lic. 773985 FROM: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org [4]] ON BEHALF OF Michael Morningstar SENT: Tuesday, January 25, 2022 4:53 PM TO: RE-wrenches SUBJECT: Re: [RE-wrenches] High Voltage Breakers for Conext Mppt-80-600 Thanks guys, Just wanted to make sure I wasn't missing something. Curious that Schneider doesn't have higher voltage input breakers. On Jan 25, 2022, at 4:15 PM, Tump wrote: I use the SQD fused disco I mount this next to the CC and use the Flex cobra wire for the low DC voltage and the do have breakers for the context for that On Jan 25, 2022, at 7:04 PM, Tom Duffy wrote: Hi Mike No breakers I know of that fit the Conext boxes but you could use a MidNite Big Baby and a MidNite 600 volt breaker in it or even a touch safe 1000 volt fuse and holder they're DIN rail TOM DUFFY _SENIOR SOLAR DESIGN ENGINEER_ Supply chain crunches brought on by the pandemic and Omicron's toll on the workforce are causing shortages of goods. Most analysts agree that rising prices -- not just in the US, but also across the world -- are largely consequences of the Covid-19 crisis rather than policy errors by governments or central banks. Infectious waves have closed factories in Asian manufacturing hubs and caused chaos in transporting products to US markets, creating a spike in demand. Also Americans have cash to burn after two years of canceled vacations, closed restaurants and working from home, a major factor supercharging the price surge. MAIN TOLL FREE: 888-826-0939 DIRECT: 888-503-6772 INTERNATIONAL: 001-575-539-2111 PANAMA: 507-836-5588 X 122 FAX: 520-844-8442 __ CONFIDENTIALITY NOTICE: This electronic mail message and any attached files contain information intended for the exclusive use of the individual or entity to whom it is addressed and may contain information that is proprietary, privileged, confidential and/or exempt from disclosure under applicable law. THE INFORMATION CONTAINED IN THIS ELECTRONIC MAIL TRANSMISSION IS CONFIDENTIAL. If you are not the intended recipient, you are hereby notified that any viewing, copying, disclosure or distribution of this information is strictly prohibited and may be subject to legal restriction or sanction. Please notify the sender immediately by electronic mail of any unintended recipients and delete the original message without making any copies. FROM: RE-wrenches ON BEHALF OF Michael Morningstar SENT: Tuesday, January 25, 2022 1:02 PM TO: RE-wrenches SUBJECT: [RE-wrenches] High Voltage Breakers for Conext Mppt-80-600 Wrenches, Can anyone direct me to PV input breakers that are rated up to 600VDC that would work in a Conext Distribution Panel? From what I can tell, Schneider only offers breakers up to 160VDC. Thanks, Michael MICHAEL MORNINGSTAR _Morningstar Electric_ PO Box 1494 Mount Shasta, California 96067 530-921-0560 CSLB 949635 ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org [9] List Address: RE-wrenches@lists.re-wrenches.org [10] Change listserver email address ">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org [11] There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ [12] http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org [13] List rules ">http://www.re-wrenches.org/etiquette.htm [14] Check out or update participant bios: http://www.members.re-wrenches.org [
Re: [RE-wrenches] High Voltage Breakers for Conext Mppt-80-600
Michael: This seems like a rather stunning oversight—offering a charge controller without any means to integrate it into the BOS built by the same manufacturer. Just now I laid a 600 VDC rated touch-safe fuse holder over a QOU breaker. The fuse holder is smaller than the breaker so it would fit in the PDP. The fuse holder would be a bit recessed which may look awkward and impede the opening of the fuse holder. I do know you can buy DIN rail of varying height. Maybe you could drill out the rivets on the DIN rail and replace a short section of it with high profile DIN Rail and make a somewhat elegant solution??? Good luck. William Miller Miller Solar 17395 Oak Road, Atascadero, CA 93422 805-438-5600 www.millersolar.com CA Lic. 773985 *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *Michael Morningstar *Sent:* Tuesday, January 25, 2022 4:53 PM *To:* RE-wrenches *Subject:* Re: [RE-wrenches] High Voltage Breakers for Conext Mppt-80-600 Thanks guys, Just wanted to make sure I wasn’t missing something. Curious that Schneider doesn’t have higher voltage input breakers. On Jan 25, 2022, at 4:15 PM, Tump wrote: I use the SQD fused disco I mount this next to the CC and use the Flex cobra wire for the low DC voltage and the do have breakers for the context for that On Jan 25, 2022, at 7:04 PM, Tom Duffy wrote: Hi Mike No breakers I know of that fit the Conext boxes but you could use a MidNite Big Baby and a MidNite 600 volt breaker in it or even a touch safe 1000 volt fuse and holder they’re DIN rail *Tom Duffy* *Senior Solar Design Engineer* Supply chain crunches brought on by the pandemic and Omicron’s toll on the workforce are causing shortages of goods. Most analysts agree that rising prices — not just in the US, but also across the world — are largely consequences of the Covid-19 crisis rather than policy errors by governments or central banks. Infectious waves have closed factories in Asian manufacturing hubs and caused chaos in transporting products to US markets, creating a spike in demand. Also Americans have cash to burn after two years of canceled vacations, closed restaurants and working from home, a major factor supercharging the price surge. *t...@solar-biz.com * *MAIN TOLL FREE: 888-826-0939* *DIRECT:* *888-503-6772* *International:* *001-575-539-2111* *PANAMA:* *507-836-5588 X 122* *FAX: 520-844-8442* *www.thesolarbiz.com <http://www.thesolarbiz.com/>* CONFIDENTIALITY NOTICE: This electronic mail message and any attached files contain information intended for the exclusive use of the individual or entity to whom it is addressed and may contain information that is proprietary, privileged, confidential and/or exempt from disclosure under applicable law. THE INFORMATION CONTAINED IN THIS ELECTRONIC MAIL TRANSMISSION IS CONFIDENTIAL. If you are not the intended recipient, you are hereby notified that any viewing, copying, disclosure or distribution of this information is strictly prohibited and may be subject to legal restriction or sanction. Please notify the sender immediately by electronic mail of any unintended recipients and delete the original message without making any copies. *From:* RE-wrenches *On Behalf Of *Michael Morningstar *Sent:* Tuesday, January 25, 2022 1:02 PM *To:* RE-wrenches *Subject:* [RE-wrenches] High Voltage Breakers for Conext Mppt-80-600 Wrenches, Can anyone direct me to PV input breakers that are rated up to 600VDC that would work in a Conext Distribution Panel? From what I can tell, Schneider only offers breakers up to 160VDC. Thanks, Michael *Michael Morningstar* *Morningstar Electric* PO Box 1494 Mount Shasta, California 96067 530-921-0560 CSLB 949635 ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org *Tump mailto:t...@swnl.net%22%20%5Co%20%22blocked::mailto:t...@swnl.net>3...@gmail.com <3...@gmail.com>* *www.SWNL.net* http://www.swnl.net/%22%20%5Co%20%22blocked::http://www.swnl.net/> Solarwinds Northernlights * Serving Mid Coast Maine & Northern California* * 207-832-7574 Cl. 610-517-8401 * *Blair "TUMP" May* *
Re: [RE-wrenches] High Voltage Breakers for Conext Mppt-80-600
Thanks guys, Just wanted to make sure I wasn’t missing something. Curious that Schneider doesn’t have higher voltage input breakers. > On Jan 25, 2022, at 4:15 PM, Tump wrote: > > I use the SQD fused disco I mount this next to the CC and use the Flex cobra > wire for the low DC voltage and the do have breakers for the context for that >> On Jan 25, 2022, at 7:04 PM, Tom Duffy > <mailto:t...@solar-biz.com>> wrote: >> >> Hi Mike >> >> No breakers I know of that fit the Conext boxes but you could use a MidNite >> Big Baby and a MidNite 600 volt breaker in it or even a touch safe 1000 volt >> fuse and holder they’re DIN rail >> >> Tom Duffy >> Senior Solar Design Engineer >> >> Supply chain crunches brought on by the pandemic and Omicron’s toll on the >> workforce are causing shortages of goods. Most analysts agree that rising >> prices — not just in the US, but also across the world — are largely >> consequences of the Covid-19 crisis rather than policy errors by governments >> or central banks. >> Infectious waves have closed factories in Asian manufacturing hubs and >> caused chaos in transporting products to US markets, creating a spike in >> demand. Also Americans have cash to burn after two years of canceled >> vacations, closed restaurants and working from home, a major factor >> supercharging the price surge. >> >> t...@solar-biz.com <mailto:t...@solar-biz.com> >> MAIN TOLL FREE: 888-826-0939 >> DIRECT: 888-503-6772 >> International: 001-575-539-2111 >> PANAMA: 507-836-5588 X 122 >> FAX: 520-844-8442 >> www.thesolarbiz.com <http://www.thesolarbiz.com/> >> CONFIDENTIALITY NOTICE: This electronic mail message and any attached files >> contain information intended for the exclusive use of the individual or >> entity to whom it is addressed and may contain information that is >> proprietary, privileged, confidential and/or exempt from disclosure under >> applicable law. THE INFORMATION CONTAINED IN THIS ELECTRONIC MAIL >> TRANSMISSION IS CONFIDENTIAL. If you are not the intended recipient, you >> are hereby notified that any viewing, copying, disclosure or distribution of >> this information is strictly prohibited and may be subject to legal >> restriction or sanction. Please notify the sender immediately by electronic >> mail of any unintended recipients and delete the original message without >> making any copies. >> >> From: RE-wrenches > <mailto:re-wrenches-boun...@lists.re-wrenches.org>> On Behalf Of Michael >> Morningstar >> Sent: Tuesday, January 25, 2022 1:02 PM >> To: RE-wrenches > <mailto:re-wrenches@lists.re-wrenches.org>> >> Subject: [RE-wrenches] High Voltage Breakers for Conext Mppt-80-600 >> >> Wrenches, >> >> Can anyone direct me to PV input breakers that are rated up to 600VDC that >> would work in a Conext Distribution Panel? From what I can tell, Schneider >> only offers breakers up to 160VDC. >> >> Thanks, >> Michael >> >> >> >> >> Michael Morningstar >> >> Morningstar Electric >> PO Box 1494 >> Mount Shasta, California 96067 >> 530-921-0560 >> CSLB 949635 >> >> >> >> ___ >> List sponsored by Redwood Alliance >> >> Pay optional member dues here: http://re-wrenches.org >> <http://re-wrenches.org/> >> >> List Address: RE-wrenches@lists.re-wrenches.org >> <mailto:RE-wrenches@lists.re-wrenches.org> >> >> Change listserver email address & settings: >> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org >> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org> >> >> There are two list archives for searching. When one doesn't work, try the >> other: >> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ >> <https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/> >> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org >> <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org> >> >> List rules & etiquette: >> http://www.re-wrenches.org/etiquette.htm >> <http://www.re-wrenches.org/etiquette.htm> >> >> Check out or update participant bios: >> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/> >> Tump >&g
Re: [RE-wrenches] High Voltage Breakers for Conext Mppt-80-600
I use the SQD fused disco I mount this next to the CC and use the Flex cobra wire for the low DC voltage and the do have breakers for the context for that > On Jan 25, 2022, at 7:04 PM, Tom Duffy wrote: > > Hi Mike > > No breakers I know of that fit the Conext boxes but you could use a MidNite > Big Baby and a MidNite 600 volt breaker in it or even a touch safe 1000 volt > fuse and holder they’re DIN rail > > Tom Duffy > Senior Solar Design Engineer > > Supply chain crunches brought on by the pandemic and Omicron’s toll on the > workforce are causing shortages of goods. Most analysts agree that rising > prices — not just in the US, but also across the world — are largely > consequences of the Covid-19 crisis rather than policy errors by governments > or central banks. > Infectious waves have closed factories in Asian manufacturing hubs and caused > chaos in transporting products to US markets, creating a spike in demand. > Also Americans have cash to burn after two years of canceled vacations, > closed restaurants and working from home, a major factor supercharging the > price surge. > > t...@solar-biz.com <mailto:t...@solar-biz.com> > MAIN TOLL FREE: 888-826-0939 > DIRECT: 888-503-6772 > International: 001-575-539-2111 > PANAMA: 507-836-5588 X 122 > FAX: 520-844-8442 > www.thesolarbiz.com <http://www.thesolarbiz.com/> > CONFIDENTIALITY NOTICE: This electronic mail message and any attached files > contain information intended for the exclusive use of the individual or > entity to whom it is addressed and may contain information that is > proprietary, privileged, confidential and/or exempt from disclosure under > applicable law. THE INFORMATION CONTAINED IN THIS ELECTRONIC MAIL > TRANSMISSION IS CONFIDENTIAL. If you are not the intended recipient, you are > hereby notified that any viewing, copying, disclosure or distribution of this > information is strictly prohibited and may be subject to legal restriction or > sanction. Please notify the sender immediately by electronic mail of any > unintended recipients and delete the original message without making any > copies. > > From: RE-wrenches <mailto:re-wrenches-boun...@lists.re-wrenches.org>> On Behalf Of Michael > Morningstar > Sent: Tuesday, January 25, 2022 1:02 PM > To: RE-wrenches <mailto:re-wrenches@lists.re-wrenches.org>> > Subject: [RE-wrenches] High Voltage Breakers for Conext Mppt-80-600 > > Wrenches, > > Can anyone direct me to PV input breakers that are rated up to 600VDC that > would work in a Conext Distribution Panel? From what I can tell, Schneider > only offers breakers up to 160VDC. > > Thanks, > Michael > > > > > Michael Morningstar > > Morningstar Electric > PO Box 1494 > Mount Shasta, California 96067 > 530-921-0560 > CSLB 949635 > > > > ___ > List sponsored by Redwood Alliance > > Pay optional member dues here: http://re-wrenches.org > <http://re-wrenches.org/> > > List Address: RE-wrenches@lists.re-wrenches.org > <mailto:RE-wrenches@lists.re-wrenches.org> > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org> > > There are two list archives for searching. When one doesn't work, try the > other: > https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ > <https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/> > http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org > <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org> > > List rules & etiquette: > http://www.re-wrenches.org/etiquette.htm > <http://www.re-wrenches.org/etiquette.htm> > > Check out or update participant bios: > http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/> > Tump > mailto:t...@swnl.net%22%20%5Co%20%22blocked::mailto:t...@swnl.net>3...@gmail.com >www.SWNL.net > http://www.swnl.net/%22%20%5Co%20%22blocked::http://www.swnl.net/> > Solarwinds Northernlights >Serving Mid Coast Maine & Northern California > 207-832-7574 Cl. 610-517-8401 > > Blair "TUMP" May > MAINE'S CHARTER > NABCEP"Certified PV Installer" > > MAINE'S CHARTER >
Re: [RE-wrenches] High Voltage Breakers for Conext Mppt-80-600
Hi Mike No breakers I know of that fit the Conext boxes but you could use a MidNite Big Baby and a MidNite 600 volt breaker in it or even a touch safe 1000 volt fuse and holder they're DIN rail Tom Duffy Senior Solar Design Engineer Supply chain crunches brought on by the pandemic and Omicron's toll on the workforce are causing shortages of goods. Most analysts agree that rising prices - not just in the US, but also across the world - are largely consequences of the Covid-19 crisis rather than policy errors by governments or central banks. Infectious waves have closed factories in Asian manufacturing hubs and caused chaos in transporting products to US markets, creating a spike in demand. Also Americans have cash to burn after two years of canceled vacations, closed restaurants and working from home, a major factor supercharging the price surge. [cid:image001.png@01D8121E.5569DE30] t...@solar-biz.com<mailto:t...@solar-biz.com> MAIN TOLL FREE: 888-826-0939 DIRECT: 888-503-6772 International: 001-575-539-2111 PANAMA: 507-836-5588 X 122 FAX: 520-844-8442 www.thesolarbiz.com<http://www.thesolarbiz.com/> CONFIDENTIALITY NOTICE: This electronic mail message and any attached files contain information intended for the exclusive use of the individual or entity to whom it is addressed and may contain information that is proprietary, privileged, confidential and/or exempt from disclosure under applicable law. THE INFORMATION CONTAINED IN THIS ELECTRONIC MAIL TRANSMISSION IS CONFIDENTIAL. If you are not the intended recipient, you are hereby notified that any viewing, copying, disclosure or distribution of this information is strictly prohibited and may be subject to legal restriction or sanction. Please notify the sender immediately by electronic mail of any unintended recipients and delete the original message without making any copies. From: RE-wrenches On Behalf Of Michael Morningstar Sent: Tuesday, January 25, 2022 1:02 PM To: RE-wrenches Subject: [RE-wrenches] High Voltage Breakers for Conext Mppt-80-600 Wrenches, Can anyone direct me to PV input breakers that are rated up to 600VDC that would work in a Conext Distribution Panel? From what I can tell, Schneider only offers breakers up to 160VDC. Thanks, Michael Michael Morningstar Morningstar Electric PO Box 1494 Mount Shasta, California 96067 530-921-0560 CSLB 949635 [cid:image002.gif@01D8121E.5569DE30] ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org
[RE-wrenches] High Voltage Breakers for Conext Mppt-80-600
Wrenches, Can anyone direct me to PV input breakers that are rated up to 600VDC that would work in a Conext Distribution Panel? From what I can tell, Schneider only offers breakers up to 160VDC. Thanks, Michael Michael Morningstar Morningstar Electric PO Box 1494 Mount Shasta, California 96067 530-921-0560 CSLB 949635 ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org