Is USE-2 (#8 and #6 AWG) available in white? If so, from whom? Dave David Palumbo, NABCEP Certified PV Installer Independent Power LLC Offices in Lamoille and the Champlain Valley 802.888.7194 www.independentpowerllc.com ___ List sponsor

Re: [RE-wrenches] USE-2 in white?

2010-08-02 Thread Dave Palumbo
My application for #8 and #6 is in conduit from the PV array combiner to the DC disconnect/inverter. So, UV protection is not important. Better quality insulation is my concern. We had a couple of spools of #8 THHN/THWN-2 test below the norm with a Fluke insulation tester recently. My local CED di

Re: [RE-wrenches] Delta LA's

2010-09-01 Thread Dave Palumbo
I am concerned with Delta LA 600VDC cans being mounted exterior from J-boxes (or disconnect switches) on ground mounts. I remember hearing from an old hand that these devices can fail in a manner that could possibly expose the wiring to human hands. The wires would have high voltage DC potential.

Re: [RE-wrenches] Lightning protection (was Delta LA's)

2010-09-14 Thread Dave Palumbo
I agree with Augusts' point. We use Delta LA's because some manufacturers (OutBack and Trace) recommended using them years ago. So, sort of the same reasoning Jay was saying about insurance. Unscientific evidence from 22 years of experience with off grid systems in a fairly high lightning pron

Re: [RE-wrenches] Delta LA's in or out? It's our choice.

2010-09-15 Thread Dave Palumbo
oncerned about unqualified people coming in contact with conductors, put a guard around it. Bill. From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Dave Palumbo Sent: Wednesday, September 01, 2010 5:32 PM To: 'RE-wrenches&#x

Re: [RE-wrenches] Supply side connection to a dedicated panel

2010-10-11 Thread Dave Palumbo
or even a 150Amp panel. A local electrician proposed this "dedicated panel" to avoid the larger load center panel. I cannot find any mention of "dedicated panel" in the NEC. I think what I am proposing follows 690.64. Any opinions, or advice would be appreciated. Dave

Re: [RE-wrenches] Are Thick Plate Batteries Worth the Price?

2010-10-29 Thread Dave Palumbo
ger system's there are more choices. A string, or two, of 2v cells can be an excellent choice depending on the price/value ratio. Medium size systems will normally call for Surrette/Rolls 6v, or Trojan L-16 batteries. All for off grid applications. Sealed batteries for battery backup grid tied.

Re: [RE-wrenches] 3.7kW grid tie

2010-10-31 Thread Dave Palumbo
add a Plug In Breaker. There is a GE "feeder type" breaker # THQL2190 (90 A DP). Could we use this as the main breaker for the load center above? It is listed as a 10KAIC breaker. #3) Swap out existing 32 space load center and replace with 150AML panel with 100A MB kit. Thanks

Re: [RE-wrenches] Trace Series TR2424 causing blinking lights

2010-11-05 Thread Dave Palumbo
Kent, Is this a "flickering" of the lights when the generator is running and charging the battery bank? Which I have seen. Or, something that is going on all the time? Which I have not experienced. Dave Palumbo Independent Power -Original Message- From: re-wrenches-boun..

Re: [RE-wrenches] Allied Schools - Training 4 Green

2010-11-21 Thread Dave Palumbo
Anybody have any experience with Allied Schools - Training 4 Green programs? Online courses, NABCEP approved (so they claim on the web www.training4green.com Thanks, Dave ___ List sponsored by Home Power magazine List Address: RE-wrenches@li

Re: [RE-wrenches] Mounting L feet on corrugated metal roof.

2010-11-26 Thread Dave Palumbo
John, We have done several of these corrugated steel roofs. We like using 3/8" x 8" Hanger Bolts from UniRac part #310025. These are a long custom lag screw designed to have an L foot fastened on it. Allows you to get the L feet above the plane of the ribs so you can place the hanger bolts wher

Re: [RE-wrenches] 24v Battery Charger 80 Amps?

2010-12-09 Thread Dave Palumbo
nt to balance off the second leg of this new generators output with a battery charger that puts out anywhere from 80 to 100 Amps into the 24v battery bank. I could use two Iota 24 volt 40 Amp chargers for the 80 Amp max total. Other options? Dave Palumbo Independent Powe

Re: [RE-wrenches] 24v Battery Charger 80 Amps?

2010-12-09 Thread Dave Palumbo
sitive Energy, Inc. 3201 Calle Marie Santa Fe, New Mexico 87507 505 424-1112 www.positiveenergysolar.com <http://www.positiveenergysolar.com/> On 12/9/2010 9:12 AM, Dave Palumbo wrote: Wrenchsters, Any recommendations on a generator fed Battery Charger for a large 24v battery bank (1,

Re: [RE-wrenches] Battery based hydrogen incidents

2010-12-15 Thread Dave Palumbo
Dana, 25 yrs experience. No incidents. Dave From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Dana Sent: Wednesday, December 15, 2010 11:10 AM To: 'RE-wrenches' Subject: [RE-wrenches] Battery based hydrogen incidents Ken

Re: [RE-wrenches] Federal ITC

2011-01-04 Thread Dave Palumbo
Wrenches, I'm looking for confirmation on the expiration dates on the Federal Investment Tax Credit for businesses, as wells as the Individual Tax Credit (or Personal Tax Credit) for individuals. As I understand it the ITC Grant for businesses (money up front) expired at the end of 2010.

Re: [RE-wrenches] Matching modules into Xantrex GT

2011-01-15 Thread Dave Palumbo
Direct Power & Water (DPW) had SW175's in the fall of 2010. Or, the Schuco MPE 180 MS05 is single crystal module with similar voltage numbers as the SW. Dave David Palumbo Independent Power LLC 462 Solar Way Drive Hyde Park, VT 05655 www.independentpowerllc.com NABCEP Certified PV Insta

Re: [RE-wrenches] Inverter oversizing

2011-01-19 Thread Dave Palumbo
Bill, In addition to power production losses due to arrays that are oversized for the inverter (although within manufacturers specs) how concerned should we be with shorter inverter service life because the inverter is working at its maximum? David Palumbo Independent Power LLC 462 Solar

Re: [RE-wrenches] NABCEP marketing

2011-02-07 Thread Dave Palumbo
Larry, It's easy to become frustrated browsing, or studying, anyone's marketing these days. It's OK to squeak once in a while on topics like this (in my opinion). NABCEP has not been discussed too much lately and your comment brought some good discussion to the group. Sounds like you are doing

Re: [RE-wrenches] Quick Cote troubles

2011-02-22 Thread Dave Palumbo
Years ago on this list we had a good discussion on the subject of battery terminal protection. The favorite at that time (by a geographically diverse group of installers) was to use a light coating of petroleum jelly (Vaseline or generic versions). We continue to use it after 25 years of good resul

Re: [RE-wrenches] Array tilt angle doesn't matter?

2011-02-22 Thread Dave Palumbo
Tom, This is coming from old memory, so I give this with a grain of salt, but I believe the noontime sun angle at my latitude (44.5) is about 78 degrees on June 21st and about 22 degrees on December 21st. That’s a difference of 56 degrees. David Palumbo Independent Power LLC 462 Solar

Re: [RE-wrenches] Quick Cote troubles

2011-02-23 Thread Dave Palumbo
Allan, 5 years in a scenario like that would certainly be a reasonable life expectancy for those cells. Deep discharges followed by inadequate recharging would cause sulfation in a short period of time and with many cycles due to the undersizing. 5 years sounds like fair performance given the s

Re: [RE-wrenches] York furnace

2011-03-03 Thread Dave Palumbo
William, It's been yrs since I dealt with this issue, and it wasn't a York specifically.. But I had an issue with a furnace and an old black Trace mod sine. A capacitor in the feed to the furnace did the trick. Dave From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-bou

Re: [RE-wrenches] Trojan tech contact?

2011-03-22 Thread Dave Palumbo
Wrenches, Looking for someone to speak with on technical questions on Trojan L-16 RE batteries. David Palumbo Independent Power LLC 462 Solar Way Drive Hyde Park, VT 05655 www.independentpowerllc.com NABCEP Certified PV Installer Vermont Solar Partner 23 Years Experience, (802) 888

Re: [RE-wrenches] Trojan tech contact?

2011-03-22 Thread Dave Palumbo
rpare...@trojanbattery.com www.trojanbatteryre.com <http://www.trojanbatteryre.com/> Trojan Battery Company - Clean Energy for LifeT From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Dave Palumbo Sent: Tuesday, March 22, 2

Re: [RE-wrenches] Hydrometer source

2011-05-09 Thread Dave Palumbo
We used to buy temperature compensated hydrometers from AEE to include with the sale of a battery bank for off grid customers. My sales person says AEE is no longer carrying that item. I believe they were made by Dekka. Recommendations for a new source for battery hydrometers in the $8 to $ 15

Re: [RE-wrenches] Fed ITC

2011-07-09 Thread Dave Palumbo
Can individuals take a Fed ITC on a SHW system installed on a second home property? David Palumbo Independent Power LLC 462 Solar Way Drive Hyde Park, VT 05655 www.independentpowerllc.com NABCEP Certified PV Installer Vermont Solar Partner 23 Years Experience, (802) 888-7194 _

Re: [RE-wrenches] enphase D380 reliability

2011-07-11 Thread Dave Palumbo
We have a small job with (18) 72 cell modules (3.3kW), the site has some shading issues and we will be using enphase inverters. I am weighing using two branch circuits (one with 10, one with 8) of M190's. Or, using one branch circuit of (9) D380's. D380's will cost less, BUT are being disconti

Re: [RE-wrenches] pole mounts

2011-07-26 Thread Dave Palumbo
Todd, We add concrete inside of our steel pipe masts, up to grade level, in the interest of having more weight below ground level. I wouldn’t say that it made the pipe stronger (that better be strong enough as is) but more weight down low will help keep it rooted in a big wind event. Dav

Re: [RE-wrenches] pole mounts

2011-07-26 Thread Dave Palumbo
ust a thought. Roy Rakobitsch NABCEP Certified Small Wind Installer® NABCEP Certified Solar PV Installer® NYSERDA eligible Small Wind installer Wind/PV Design Engineer Windsine Inc. 631-514-4166 www.windsine.org On Tue, July 26, 2011 3:05 pm, Dave Palumbo wrote: > Todd, > > > > We ad

Re: [RE-wrenches] Trojan RE Series Tech question

2011-08-02 Thread Dave Palumbo
Our go to guy at Trojan, Ron Parades, is evidently gone. That's what they said at his old phone extension at Trojan. I left a message for tech support there and have not heard back as of yet. Is there another Trojan Tech person to specifically ask for now? And is there one on this list helping

Re: [RE-wrenches] Enphase M190 availability?

2011-08-12 Thread Dave Palumbo
Do you know of a source for (18) enhase M190's? Thanks, David Palumbo Independent Power LLC 462 Solar Way Drive Hyde Park, VT 05655 www.independentpowerllc.com NABCEP Certified PV Installer Vermont Solar Partner 23 Years Experience, (802) 888-7194 _

Re: [RE-wrenches] Lithium Ion Phosphate for grid back up

2011-08-21 Thread Dave Palumbo
We have a potential client for a net metered PV with battery backup system with a serious interest in using lithium ion storage batteries. I do not know of any systems that have used these batteries yet. From some quick calcs I come up with 105 LiFEYPo4 3.2 volt cells. 7 strings of 15 cells for 700

Re: [RE-wrenches] Pump

2011-08-24 Thread Dave Palumbo
Hi Jeff, Do you see the increased pressure on the pump submerged an extra 180' deep as a non issue? I know with cheaper pumps it is an issue to consider. Here in the soggy northeast static water levels hardly fluctuate at all. Dave From: re-wrenches-boun...@lists.re-wrenches.org [mailto

Re: [RE-wrenches] Enphase 215

2011-08-24 Thread Dave Palumbo
Do the 215's output more than 215 Watts? From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Keith Cronin Sent: Wednesday, August 24, 2011 12:21 AM To: RE-Wrenches Subject: [RE-wrenches] Enphase 215 Hey gang With the 215's on

Re: [RE-wrenches] AUO Unison integrated inverter modules

2011-08-24 Thread Dave Palumbo
Has anyone gotten their hands on the AUO modules with the built in micro inverter? Cut sheets on mono and poly modules. AC Unison PM240PA0 AC Unison PM250MA0 David Palumbo Independent Power LLC 462 Sol

Re: [RE-wrenches] Enphase M190 source?

2011-09-12 Thread Dave Palumbo
I'm looking for 18 enphase M-190's for an installation here in Vermont. 72 cell modules 185 Watts. Anybody know of a source? David Palumbo Independent Power LLC 462 Solar Way Drive Hyde Park, VT 05655 www.independentpowerllc.com NABCEP Certified PV Installer Vermont Solar Partner 23 Ye

Re: [RE-wrenches] intermittent battery problem

2011-10-22 Thread Dave Palumbo
I have been following this topic over the past couple of weeks. What Dave Katz said matches up with what I have seen over the years. Although it can be difficult to diagnose battery issues from long distance there has been a fair amount of information that points to sulfation. I think Mr. Katz is r

Re: [RE-wrenches] SMA electrical noise?

2011-10-28 Thread Dave Palumbo
Wrenches, This is a new one on me. Any ideas of what may be happening? In a follow up she said it happens every day. System was installed two months ago. SB8000US inverter 8.28kW array. << Dave We are experiencing electrical noise at dawn and dusk. The power back ups for our computers

Re: [RE-wrenches] [!! SPAM] Re: SMA electrical noise?

2011-10-28 Thread Dave Palumbo
e-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Christopher Warfel Sent: Friday, October 28, 2011 9:32 AM To: RE-wrenches Subject: [!! SPAM] Re: [RE-wrenches] SMA electrical noise? Check array open circuit voltage calculation? On 10/28/2011 8:46 AM, Dave Palumbo wrote: > > Wrenches, > &

Re: [RE-wrenches] OB Radian Inverter avilability

2011-11-03 Thread Dave Palumbo
We were recently told by OutBack that they would not be making anymore Radian GS8048's until December. We've had one on order thru SunWize since Sept 16th. I'm concerned that I may not receive it until too late to get the installation completed by December 31st as contracted. Does anyone know

Re: [RE-wrenches] OB Radian Inverter availability

2011-11-03 Thread Dave Palumbo
things about it. Dave From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Dave Palumbo Sent: Thursday, November 03, 2011 7:44 AM To: 'RE-wrenches' Subject: Re: [RE-wrenches] OB Radian Inverter avilability We were recent

Re: [RE-wrenches] federal tax credit

2011-11-11 Thread Dave Palumbo
I support what Daryl DeJoy said below. Although it's not that straightforward an issue. Check out http://www.dsireusa.org/incentives/incentive.cfm?Incentive_Code=US37F&re=1&e e=0 you'll see that for Solar Electric, Solar Water Heating, Small Wind and Geothermal Heat Pumps it is stated "The home se

Re: [RE-wrenches] Gross PV production meter options

2011-12-06 Thread Dave Palumbo
We are installing a grid interactive, with battery back-up, OutBack Radian GS8048 with 5kW of PV. Vermont has a "Solar Adder" premium that varies from utility to utility but in this case adds 6 cents per kWh over and above net-metering (basically to come up to a par value of 20 cents/kWh for PV pro

Re: [RE-wrenches] Supply Side Tap Overcurrent Protection

2010-03-28 Thread Dave Palumbo
Wrenches, I am tasked with reviewing an installation by a licensed electrician in Vermont and would like help with the following: Grid-tied PV system with battery back-up. AC point of connection is a supply side tap (done on customer side of utility meter ) then traveling 5 feet of #2 THHWN

Re: [RE-wrenches] Ground Mount PV DC Disconnects and 690.13

2010-03-30 Thread Dave Palumbo
Wrenches, For a ground mounted PV array I do NOT see where 690.13, 690.14 mandates a DC disconnect at the array itself. My question is what do you do as "best practice" for safety, or for service of inverter disconnect. I have been using 600VDC SQ-D disconnects at our ground mounts and I'm wond

Re: [RE-wrenches] Grid-tie Sunny Island

2010-04-11 Thread Dave Palumbo
We have a new (for us) application for grid connected net-metered PV with battery back-up as follows. The twist is that the entire load center in the house will be the "protected loads panel". - 5kW PV ground mount located 250 feet East of their barn. - Will utilize AC Coupled

Re: [RE-wrenches] Apollo T80HV

2010-04-18 Thread Dave Palumbo
Looking for comments on the Apollo T80HV charge controller. We require a MPPT controller that will accept up to 3 Sanyo 215N's in series (194Voc / 157Vmp with 1.25 factor). To my knowledge this is the only controller that will do the job. This HV Apollo is publishing it's Max Voc at 200 and Max o

Re: [RE-wrenches] Lorentz Sub Pump

2010-04-19 Thread Dave Palumbo
Wrenchers, Looking for advice on the following pump. Lorentz PS600-HR04H-1-48B with power pack option and controller. I will be doing an off-grid system for a homeowner who already who had purchased this pump, in fact it is down the well already, although not working, or even wired to anyth

Re: [RE-wrenches] overfeed 7kW gridtie inverter or drop a mod per string?

2010-04-20 Thread Dave Palumbo
Jim, You have probably seen this already but it’s worth a mention here. Good article in SolarPro magazine April/May “Optimal PV-to-Inverter Sizing Ratio”. Dave From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jim MacDona

Re: [RE-wrenches] PV Module Favorite (was Whats with Kyocera)

2010-05-19 Thread Dave Palumbo
Joel, Schuco - Good German quality, wide range of modules, good energy output tolerance, good availability, good pricing. Company appears to be solid, which is important to me. I'm presently designing several systems around the Schuco MPE 180 MS05 "Black Line" modules, -0%/+5% tolerance, 36Vmp

Re: [RE-wrenches] Flashed Footing Requirements

2010-06-24 Thread Dave Palumbo
For comp shingle jobs there is now a good economical choice. Actually two choices from one manufacturer EcoFasten www.ecofastensolar.com They make Quickfoot and also GreenFasten. Good quality products, good price points. They are also sold under other names by distributors such as DPW which calls

Re: [RE-wrenches] Interstate UL-16 HC problem

2010-06-29 Thread Dave Palumbo
Bob, Sulfation, I'd say. Try EDTA. Trailhead Supply. See Home Power marketplace ad for contact info. If it's not sulfation then maybe it's simply diluted electrolyte(accidental, or intentional) which would make the batteries have lower performance AH wise but should last a long time (plates h

Re: [RE-wrenches] Ground mount wire shielding

2010-06-29 Thread Dave Palumbo
Andy, Contact me off list and I'll send a photo of what we do. This is something I came up with to comply with Article 690.31. No guarantee your AHJ will like it. I shared this on list last year, nothing really new. We don't drill into module frames, but use the aluminum mounting rack to fasten

Re: [RE-wrenches] Interstate UL-16 HC problem

2010-07-01 Thread Dave Palumbo
Tom, I have seen many Surrette battery banks of two series strings in parallel last 10 to 12 years. Also have had a few with three string banks go that long. All were well designed systems with homeowners providing good maintenance. Dave From: re-wrenches-boun...@lists.re-wrenches.org [

Re: [RE-wrenches] Off Grid LP Gen advice

2013-09-14 Thread Dave Palumbo
lding up for off grid use over the past few years. This for northern Vermont where even with C/8 PV to battery charge rate we need to run the generator about 250 hours per year as the cloud cover is dense for weeks at a time. Thanks, Dave Pa

Re: [RE-wrenches] Off Grid LP Gen advice

2013-09-15 Thread Dave Palumbo
en is your best choice. It was specifically designed for the long runs associated with charing batteries for off-grid work. On Sat, Sep 14, 2013 at 11:58 AM, Dave Palumbo wrote: Wrenchsters, Looking for a good quality, long lasting, LP gas genset for my off grid rental house. 6 to 8kW. Ful

Re: [RE-wrenches] Off Grid LP Gen advice

2013-09-28 Thread Dave Palumbo
I purchased through Norwall PowerSystems www.Norwall.com I did not price it at Lowes so I don't know if I paid more or less but it was the lowest price I could find. Easy to deal with so far. Received EcoGen yesterday. Dave Palumbo Independent Power LLC From: re-wrenches

Re: [RE-wrenches] 12V battery charger

2013-10-30 Thread Dave Palumbo
Wrenches, I'm looking for a battery charger to augment an OutBack FX 2012 inverter/charger for a 12V off-grid system that could use shorter charging times during our cloudy late fall/winter periods in northern Vermont. Both the generator and the battery bank are amply sized as is the PV array.

Re: [RE-wrenches] SW repair

2013-12-04 Thread Dave Palumbo
Tekris Power Electronics in NJ. Chris Hanrahan has been repairing these for many years and is top notch. 732-938-4996 David Palumbo Independent Power LLC 462 Solar Way Drive Hyde Park, VT 05655 NABCEPTM Inaugural Certificant (802) 888-7194 From: re-wrenches-boun...@lists.re-wre

Re: [RE-wrenches] Heart Interface Idle Draw

2013-12-09 Thread Dave Palumbo
William, My first inverter in my own home in 1985 was a Heart Interface. I may have the specs on that inverter. I will look around tomorrow for them. I'm remembering the idle draw as about 10 Watts. What make and model battery are these? My house is on its third set of batteries and also 3r

Re: [RE-wrenches] Higher LVR to force full re-charge in small OGPV systems

2014-01-02 Thread Dave Palumbo
Allan, The Full River sealed battery line also has charging voltages similar to the numbers for the Rhino’s. We have had good results with many Full River battery banks, no premature failures to date. Certainly these are higher charging voltages than the early VRLA batteries we saw years ago.

Re: [RE-wrenches] Solar World shattered module

2014-04-21 Thread Dave Palumbo
Wrenches, I have a customer with one SW 230 poly V2.0 frame (top mount) module that has shattered glass. It is on a DPW TPM10 pole mount. She noticed it the other day and does not think that it was hit by anything. I agree that is unlikely based on the site conditions. Other than by a falli

Re: [RE-wrenches] Fire fighters safety class

2016-09-19 Thread Dave Palumbo
Wrenches, I will be presenting a class on "Solar Home Fire Fighter Safety" to our local volunteer fire department this coming weekend. I will tour them around my off grid neighborhood so that we can review various PV, micro-hydro, different inverters and battery systems, various back-up generat

Re: [RE-wrenches] Fire fighters safety class

2016-09-20 Thread Dave Palumbo
tting off the fuel sources and or throwing disconnect switches as required. Dave Palumbo Independent Power LLC Hyde Park, VT From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of d...@foxfire-energy.com Sent: Tuesday, September 20, 2016 9:10 AM To: RE-wrenches Su

Re: [RE-wrenches] Load Management vs Multiple Inverters and OutBack Radian vs Flexware systems

2016-12-15 Thread Dave Palumbo
Wrenchers, I am involved in designing an off grid system that will need multiple inverters (probably OutBack). My experience over the years has been limited to no more than 8kW's of inverter on a big system (for me). The load profile is not completed yet, but it is looking like this may requir

Re: [RE-wrenches] Load Management vs Multiple Inverters and OutBack Radian vs Flexware systems

2016-12-15 Thread Dave Palumbo
be upgraded to 8k in the future? I will reach out to you, off wrench list, for more info on your Radian GSLC cabinet methods. Dave Palumbo From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of William Miller Sent: Thursday, December 15, 2016 2:18 PM To

Re: [RE-wrenches] Generac EcoGen 6

2016-12-30 Thread Dave Palumbo
Wrenches, I have a 6 kW Generac EcoGen (1,300 hrs on it) with a new problem. . After swapping in a new battery the other day the generator now starts and runs when its start switch is positioned to Auto. . The OutBack inverter w Mate2 is not calling for an auto start. .

Re: [RE-wrenches] Solar Bridge microinverters power usage

2017-01-06 Thread Dave Palumbo
I have a net metered system using six AUO Unison PM 250W modules with built in SolarBridge microinverters. It is a 1.5kW system installed in late 2011. . Homeowner called today saying her PV production meter (standard analog EZ read kWh meter) has gone backwards. She read 7,006 kWh on 12/2

Re: [RE-wrenches] Hidden corrosion caused catastrophic battery system failure

2017-01-20 Thread Dave Palumbo
Following is an entry from a Backwoods Solar email that I received today. I would like to share this as a teachable point for RE techs not familiar enough with proper battery bank care and as a reminder for those of us with years of storage battery experience. I have underlined the two issues in

Re: [RE-wrenches] Hidden corrosion caused catastrophic battery system failure

2017-01-21 Thread Dave Palumbo
e-wrenches-boun...@lists.re-wrenches.org] On Behalf Of cwarfel Sent: Saturday, January 21, 2017 9:54 AM To: re-wrenches@lists.re-wrenches.org Subject: Re: [RE-wrenches] Hidden corrosion caused catastrophic battery system failure Hi David, do you have any pictures of this that could be shared? C

Re: [RE-wrenches] Hidden corrosion caused catastrophic battery system failure

2017-01-21 Thread Dave Palumbo
d Master Electrician Solar Design Engineer 303 505-8760 On 1/21/2017 8:52 AM, Dave Palumbo wrote: Hi Chris, I don't have any pictures myself, the Backwoods email included a photo of a corroded bolt and a clean assembly which I've snipped and attached. Off the Wrenches list

Re: [RE-wrenches] High End battery

2017-03-27 Thread Dave Palumbo
Mac, I have had good success using Full River AGM's in difficult situations. One system near the Canadian border here in Vermont had no homeowner care for two months in the winter. PV array became covered with snow and they had left their inverter on to run a refrigerator. Of course the batteri

Re: [RE-wrenches] OutBack FX Internal Fan Failure

2017-03-27 Thread Dave Palumbo
Fellow Wrenches, I have an OutBack FX inverter (manufactured in 2011) with a flashing Red LED. The MATE warns "Internal Fan Failure Detected" . Before I call OutBack support I'd like to gain a little knowledge from you folks. . Will I be asked to send the inverter in, or can I get the

Re: [RE-wrenches] Hydro Off-grid Battery Sizing

2017-04-26 Thread Dave Palumbo
Hi Matt, Short answer is yes, 2 days of autonomy should be fine. I am presently operating our off rid PV/hydro system at well under two days of autonomy. I just crunched some numbers for our situation here in Vermont. Off grid system that is now 4.3kW PV and with a Harris micro-hydro turb

Re: [RE-wrenches] Failed L16 with perfect Sp.Gr.

2017-04-27 Thread Dave Palumbo
Not familiar with LG RESU 10 battery. What are they and why do you like them Dave? Thanks, David Palumbo Independent Power LLC 462 Solar Way Drive Hyde Park, VT 05655 802-371-8678 cell 802-888-4917 home -Original Message- From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches

Re: [RE-wrenches] OutBack FX Internal Fan running 24/7

2017-04-30 Thread Dave Palumbo
Wrenches, We recently swapped in a new internal fan on a OB FX 2524T after the original fan stopped working on the 6 yr old inverter. Now the new internal fan is running all the time. Unrelated to temperature (Air, Fet and Cap temps all good). I've tried removing all loads from the inverte

Re: [RE-wrenches] OutBack FX Internal Fan running 24/7

2017-04-30 Thread Dave Palumbo
, 2017, at 6:30 AM, Dave Palumbo wrote: Wrenches, We recently swapped in a new internal fan on a OB FX 2524T after the original fan stopped working on the 6 yr old inverter. Now the new internal fan is running all the time. Unrelated to temperature (Air, Fet and Cap temps all good). I&#x

Re: [RE-wrenches] battery venting

2011-12-31 Thread Dave Palumbo
Zephyr vent fans have a small vent hole located on the pvc housing below the damper flap so if/when the fan fails the gasses are still able to escape from the battery box and dissipate into a larger space. David Palumbo Independent Power LLC 462 Solar Way Drive Hyde Park, VT 05655 www.independent

Re: [RE-wrenches] Electrolytic Caps vs. Thin Film Caps

2012-01-15 Thread Dave Palumbo
Dan, Any worries with inverters located out in 30 below zero temps with either Electrolytic Caps or Film Capacitors? It's very cold here this AM (minus twenty something F) and it makes me wonder about all the inverters, both micro's and string, outside in cold weather areas. We've been told in the

Re: [RE-wrenches] Request for Gennie Recommendation

2012-01-16 Thread Dave Palumbo
Chris, It would be very helpful if you quote "run hours" rather than "years". For example we have seen: . Inexpensive small generators (generally not worth rebuilding) 300 to 500 hours. These are gasoline models of various brands and Generac LP gas models. 3kW to 10kW in size typi

Re: [RE-wrenches] Electrolytic Caps vs. Thin Film Caps

2012-01-18 Thread Dave Palumbo
rated to operate at -40C, and have been tested to that temperature by the UL test lab. This rating is stated in writing in our brochures as well as the PVAC Module Installation Manual/User's Guide. Dan --- On Sun, 1/15/12, Dave Palumbo wrote: > From: Dave Palumbo > Subject: Re: [RE-

Re: [RE-wrenches] Electrolytic Caps vs. Thin Film Caps

2012-01-19 Thread Dave Palumbo
he UL test lab. This rating is stated in writing in our brochures as well as the PVAC Module Installation Manual/User's Guide. Dan --- On Sun, 1/15/12, Dave Palumbo wrote: > From: Dave Palumbo > Subject: Re: [RE-wrenches] Electrolytic Caps vs. Thin Film Caps > To: "

Re: [RE-wrenches] Electrolytic Caps vs. Thin Film Caps

2012-01-19 Thread Dave Palumbo
test lab. This rating is stated in writing in our brochures as well as the PVAC Module Installation Manual/User's Guide. Dan --- On Sun, 1/15/12, Dave Palumbo wrote: > From: Dave Palumbo > Subject: Re: [RE-wrenches] Electrolytic Caps vs. Thin Film Caps > To: "'RE-wrenc

Re: [RE-wrenches] Grounding Separately Derived AC System

2012-01-23 Thread Dave Palumbo
Regarding NEC Article 250.30 does Informational Note #1 mean that a standard (no battery) grid-tied PV system is not a Separately Derived System? I'm primarily interested on the consensus view of Bonding the Neutral (grounded conductor) to Equipment Ground in a 60 Amp Fused Disconnect located b

Re: [RE-wrenches] Community says farewell to solar pioneer Gottlieb - Brattleboro Reformer

2012-02-24 Thread Dave Palumbo
Dan, Thanks for the news. Richard was a wonderful man. One of my first mentors in the solar business. Dave Palumbo ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Options & settings: http://list

Re: [RE-wrenches] Listed battery cable

2012-02-28 Thread Dave Palumbo
William, Try Cobra Wire & Cable (215) 674-8773 www.cobrawire.com Their X-Flex is UL listed Dave David Palumbo Independent Power LLC 462 Solar Way Drive Hyde Park, VT 05655 www.independentpowerllc.com NABCEP Certified PV Installer Vermont Solar Partner 24 Years Experience, (802) 888-7194

Re: [RE-wrenches] NABCEP Credits

2012-04-06 Thread Dave Palumbo
Wrenches, I am trying to chase down NABCEP credit hours from the Feb 28/29th ALT E Dealer Conference in Waterville Valley, NH. The trainers said they would send the certificates out to folks when they got back to their offices. 4 weeks later and no certificates (needed for recertification for

Re: [RE-wrenches] Combining Solectria PVI 2500 with SB3000

2012-04-19 Thread Dave Palumbo
Wrenches, We have an installation in place since 2008 working well with a Solectria PVI 2500 feeding a supply side grid connection. Homeowner wants us to double the system size now. I can buy a SB3000 inverter for $ 300 less than the Solectria PVI 2500 (with upcharge for 10 yr warranty) and I

Re: [RE-wrenches] Combining Solectria PVI 2500 with SB3000

2012-04-19 Thread Dave Palumbo
Dave, Very good. Thanks for the pick up on the 650A Service Disconnect issue. Dave Palumbo -Original Message- From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Dave Click Sent: Thursday, April 19, 2012 1:39 PM To: re-wrenches

Re: [RE-wrenches] Solar World 2.0 frames

2012-05-04 Thread Dave Palumbo
All, We are considering using Solar World 2.0 framed modules. Not having put hands on these yet, we are looking for testimonials and opinions on these "top mount only" modules. And while we're at, it what about Solar World's 2.5's with the bottom mount flange? David Palumbo Independent P

Re: [RE-wrenches] Battery Experience

2012-06-29 Thread Dave Palumbo
We have had less than stellar performance out of the Crown L-16's that we installed 4 to 5 years ago. Premature failure is my experience. About 60% of the cycle life compared to Trojan L-16's and also Surrette/Rolls. I've been using those since 1985. Back to using Trojan. Specifically RE-B's ei

Re: [RE-wrenches] Voltage settings for AGM's in grid tie with back up

2012-07-16 Thread Dave Palumbo
I am looking for a recommendation for Max Voltage, and how often to attain this bulk voltage? For the following system: . Trojan 8D AGM battery bank (4 bats for 11kWh rated storage with 900 Watts of PV) . Home was previously off gird. We upgraded it to a grid tied net metered sys

Re: [RE-wrenches] Metering a whole house Outback system

2012-08-20 Thread Dave Palumbo
Dave, Sounds like a great solution. We have an OB Radian net-metered PV with battery back-up coming up this fall. Where do we source an "Elkor" meter? Thanks, Dave David Palumbo Independent Power LLC 462 Solar Way Drive Hyde Park, VT 05655 www.independentpowerllc.com NABCEP Cer

Re: [RE-wrenches] Off-grid non-inverter battery charger recommendations?

2012-10-15 Thread Dave Palumbo
There is a potentiometer on the board of the IOTA chargers that used to be assessable through a hole in the cover. I adjusted a new one two weeks ago and had to open it up to get at the pot. Adjusts up 15.6VDC with plug in and 14.8 with the jumper plug out. Some of the older models would adjust up

Re: [RE-wrenches] Outback Mate3

2012-10-20 Thread Dave Palumbo
Howie, We have a couple of these out there now. They are good for techno geek types. But for regular people they are no easier than the Mate 2. David Palumbo Independent Power LLC 462 Solar Way Drive Hyde Park, VT 05655 www.independentpowerllc.com NABCEP Certified PV Installer Vermont Solar Par

Re: [RE-wrenches] Best practices for conduit penetration on roof

2012-11-25 Thread Dave Palumbo
Rich, We have been using SolaDeck PV roof mount enclosure. NEMA 3R with a flashed penetration. Can use for combining, or simply as a pass through box. Dave David Palumbo Independent Power LLC 462 Solar Way Drive Hyde Park, VT 05655 www.independentpowerllc.com NABCEP Certified PV Installer Verm

Re: [RE-wrenches] Best practices for conduit penetration on roof

2012-11-25 Thread Dave Palumbo
enches.org] On Behalf Of Dave Palumbo Sent: Sunday, November 25, 2012 8:20 AM To: 'RE-wrenches' Subject: Re: [RE-wrenches] Best practices for conduit penetration on roof Rich, We have been using SolaDeck PV roof mount enclosure. NEMA 3R with a flashed penetration. Can use for combining,

Re: [RE-wrenches] Fridge recommendations?

2013-01-09 Thread Dave Palumbo
I'm having difficulty finding a RF in the 16 to 20 cu ft range that uses less than 350kWh/yr. All of the GE units listed by Energy Star as 300 to 311kWh/yr are no longer being manufactured according to my local appliance dealers. I see a Fridgidaire 18.2 cu ft that uses 335kWh/yr (reviews that

Re: [RE-wrenches] Fridge recommendations?

2013-01-09 Thread Dave Palumbo
w.CatamountSolar.com 802-272-0004 On Wed, January 9, 2013 2:44 pm, Dave Palumbo wrote: > I'm having difficulty finding a RF in the 16 to 20 cu ft range that > uses less than 350kWh/yr. All of the GE units listed by Energy Star as > 300 to 311kWh/yr are no longer being manufactu

Re: [RE-wrenches] Fridge recommendations?

2013-01-09 Thread Dave Palumbo
Education Providers 970.672.4342 (voicemail) On Wed, Jan 9, 2013 at 12:44 PM, Dave Palumbo wrote: I'm having difficulty finding a RF in the 16 to 20 cu ft range that uses less than 350kWh/yr. All of the GE units listed by Energy Star as 300 to 311kWh/yr are no longer being manufactured according to m