Re: POD Storage

2007-01-18 Thread Thom McMahon
You really would have to sprinkler it like 24' to 25' or idle pallet storage with solid shelves (Anyone ever seen any criteria for that?) to have any chance that you'd put enough water in and around the fire to protect the building, while the Pod's burn. Maybe we could submit a code change to on

RE: POD Storage

2007-01-18 Thread Craig.Prahl
The biggest problem with interior fire protection of a POD is that you have no assurance that the thing isn't packed wall to wall and floor to ceiling. The sprinkler won't do any good when stuff is jammed up against it. Also, no guarantee that the sprinkler wouldn't get damaged or broke off altog

RE: POD Storage

2007-01-18 Thread George Church
Why couldn't you install a couple heads, even HSW with pipe strapped to the wall, and have the POD equipped with a quick-release connection or even a grooved connection. Have drops coming down from the overhead system with flex-head style connection to match the quick-connect, or an 1 -1/4" grooved

RE: POD Storage

2007-01-18 Thread Craig.Prahl
One other issue, it depends on which "POD" you are talking about. The brand name "POD" is of a different construction than the so called pod storage units that Home Depot handles. I wonder if POD corporate headquarters would happen to have some fire protection guidelines for warehouses stori

RE: POD Storage

2007-01-18 Thread Craig.Prahl
You cannot internally sprinkle the POD units. If you haven't seen them they are for lack of better description, a shipping container. Similar to what you see on ocean going freighters. Those are much larger of course but same basic principal. They are designed to be dropped off at your house an

RE: Sprinkler Piping in Unsprinklered Areas

2007-01-18 Thread John Drucker
The requirement can be found in the Building Code (IBC). For the 2000 Edition 704.12 Opening Protection, Exception; "Fire Protective Assemblies are not required where the building is protected throughout by an automatic sprinkler system AND the exterior openings are protected by an approved water

ceiling cloud update.

2007-01-18 Thread Todd Williams - work
I know this topic has been beaten to death more than once, but I was just wondering if there is any new data, fire tests, loss data or concepts for LH occupancies with ceiling clouds? Todd G. Williams, PE Fire Protection Design/Consulting Stonington, Connecticut 860-535-2080 www.fpdc.com ___

Re: Sprinkler Piping in Unsprinklered Areas

2007-01-18 Thread Joe Hankins
This is one where a little common sense is required on the part of the AHJ. If there is a fire in the space the piping is running through, the the sprinklers at windows are of no use. Joe Reed Roisum wrote: John, 8.15.3.3 (2002 ed.) may be what you are looking for. Reed Roisum -Orig

Re: POD Storage

2007-01-18 Thread Joe Hankins
Approaching this from a commodity perspective is inappropriate. Commodity classification is based on storage "units" roughly 42 in. x 42in x 42 in. in size. 8' x 8' x 16' PODS where a fire can start within a unit are in an entirely different league. If you were to remove the sides of the pods

Re: POD Storage

2007-01-18 Thread Thom McMahon
If your still in negotiations with the owner / developer, add an alternate or allowance for FPE design work in your proposal, and explain to them why this would be a good idea. Thom McMahon Firetech, Inc. 2560 Copper Ridge Dr Steamboat Springs, CO 80488-2136 Tel: 970-879-7952 Fax: 970-879-7926

RE: Dry pipe systems & trapped water

2007-01-18 Thread ROB FISHER
>On Behalf of Mike Cabral: If you have a measurable head of pressure .433528 psi for every foot of head. . > . compounded by a differential dry pipe valve of say 6 to 1. . . a water filled > pipe 20 feet high would produce 52 psi on the system side of the clapper. If you > had 50 psi supply p

RE: Sprinkler Piping in Unsprinklered Areas

2007-01-18 Thread Reed Roisum
John, 8.15.3.3 (2002 ed.) may be what you are looking for. Reed Roisum -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of [EMAIL PROTECTED] Sent: Thursday, January 18, 2007 7:52 AM To: sprinklerforum@firesprinkler.org Subject: Sprinkler Piping in Unsprink

RE: POD Storage

2007-01-18 Thread George Church
In #13, it's the paragraph just after the criteria we apply for anonymous insurance underwriters that are referenced generically in the spec. glc -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of [EMAIL PROTECTED] Sent: Thursday, January 18, 2007 9:11 AM To

RE: POD Storage

2007-01-18 Thread Craig.Prahl
Jim In a perfect world that might be the case but in actuality, the majority of bid projects come with a line on some architectural plan that says "Provide sprinkler protection per NFPA 13 for our highly experimental, top secret, intergalactic, space fuel project" and that's all you get. What yo

RE: Hollywoods version of LH Office Sprinkler Systems

2007-01-18 Thread Thomas Reinhardt
How about an old movie "The Trouble with Angels" -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Stewart Kidd Sent: Wednesday, January 17, 2007 5:16 PM To: sprinklerforum@firesprinkler.org Subject: RE: Hollywoods version of LH Office Sprinkler Systems In

Sprinkler Piping in Unsprinklered Areas

2007-01-18 Thread John . Kaminski
All, I've been told we can't run new sprinkler piping through an existing unsprinklered building without sprinklering the space where we run. The goal is to provide to sprinkler protection along windows for separation issues but to not have to sprinkler the entire existing space under this pr

RE: POD Storage

2007-01-18 Thread Greg McGahan
There is always a story Matt, this one is (at this point) a negotiated job with a GC we have done work for previously. Once the budget is solidified and they have been committed to we will be glad to invest more money into the project. If the overall budget works out then we will dig deep. Right no

RE: POD Storage

2007-01-18 Thread Jim Davidson
Greg In most areas the AHJ has required the building owner/developer to have a fire protection engineering analysis done for the PODs storage configuration. This analysis needs to address as a minimum the storage configuration, fuel loads, building's construction, exterior access, proposed sprinkl

RE: POD Storage

2007-01-18 Thread Matthew J. Willis
Jim has given some great advice in his response. But I wanted to tell you it is hard, but we have refused bids or sent out RFI prior to bid crying foul, outside scope. Not enough info to provide bid. Then they get an engineer (which should have been done prior to releasing for bid) If there IS an e

RE: POD Storage

2007-01-18 Thread Greg McGahan
Thanks Jim, that gives me something to work with and it makes sense. Greg Living Water Fire Protection, LLC 1160 McKenzie Road Cantonment, FL 32533 850-937-1850 Fax: 850-937-1852 -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Jim Davidson Sent: Thursday

RE: POD Storage

2007-01-18 Thread Jim Davidson
Greg There has been no full scale fire testing of the PODs storage configuration, and until there has been testing the design of sprinkler protection for this storage needs to be very conservative, addressing some of the unique features and problems presented by this storage configuration. Re

RE: POD Storage

2007-01-18 Thread Greg McGahan
Not yet, It is hard to pay an engineer to help you bid a job and then someone else can use the criteria you paid for. Greg Living Water Fire Protection, LLC 1160 McKenzie Road Cantonment, FL 32533 850-937-1850 Fax: 850-937-1852 -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PR

RE: POD Storage

2007-01-18 Thread Matthew J. Willis
Yeah I know. This is why you didn't see a solution from the last time. Please consider Mr. Joe's words as well. Not everything falls in the scope of 13. Is there an engineer involved at all? Might be a good time to make one of those folks earn their $$. Matt -Original Message- From: [EMA

RE: POD Storage

2007-01-18 Thread Brooks, Bill
For those (like me) not familiar with this application. www.pods.com/ Bill Brooks Pittsburgh -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] Behalf Of Matthew J. Willis Sent: Thursday, January 18, 2007 7:48 AM To: sprinklerforum@firesprinkler.org Subject: RE: POD Sto

RE: POD Storage

2007-01-18 Thread Greg McGahan
The formal restrictions are what you would expect: No flammable liquids, hazardous materials, explosives and blah blah blah. I know there is the possibility of dangerous stuff but I do believe the majority of the stuff in the containers is going to be normal household items that are either in tra

RE: POD Storage

2007-01-18 Thread Matthew J. Willis
If I recall the last time we discussed this, it was the "other" stuff that can be placed in the PODS that make a big IF appear on the horizon. I know you can't design to "if" but... Has anyone set fire on these yet since our last discussion? Matt -Original Message- From: [EMAIL PROTECTED

RE: POD Storage

2007-01-18 Thread Todd Williams - work
Greg, From what I can tell, this would essentially be container storage. It could be worthwhile to find out who they are marketing to to figure out what might show up. If they are marketing to primarily individuals, the chances of their being a POD of rubber tires would be slim. Does the compan

RE: POD Storage

2007-01-18 Thread Michael O'Brian
Why can't it be designed as solid pile group A plastics. The fire code will speculate the distance between piles and the total size of the piles go to chapter 23 of the IFC( 2003 edition) for a high hazard commoditiy So, why wouldn't a density for a group A plastic up to (I think it was speculate

RE: POD Storage

2007-01-18 Thread Greg McGahan
Is there no help from the forum on this one?! The guy has to protect the building and the one thing I am absolutely sure about is that we will not be putting sprinklers inside the PODs themselves. Other than that it is in the air - water - foam? Has there been any recorded fires in these facilit