RE: Sprinkler system serving two different buildings

2007-12-10 Thread George Church
Yeah, the systems were shut off by the new owner and the open spaces are unheated and a few rented out- to plastic furniture storage... (Alcoa plant, Lebanon, PA) glc -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Mike Cabral Sent: Saturday, December

Fire Pump+Jockey Pump+Wet Alarm Valve Combined Riser Diagram

2007-12-10 Thread Aydın ÖZKAYA
Dear All, I'm looking for an explicit literature reference, showing how Fire Pump+Jockey Pump+Wet Alarm Valve are connected (piped) all together, as a combined riser diagram, based on NFPA or FM, For instance, if you look up NFPA 20, in A-2-19.3 you will notice that pump connection

ESFR Pressure Anomaly

2007-12-10 Thread Chris Cahill
Anyone have a theory why uncartoned unexpanded plastics doesn't follow the pressure patterns of everything else. In all other cases outside this the smaller the orifice the larger the pressure. For example 25' storage ESFR 25 - 50 psi, ESFR 14 - 50 psi, ESFR 17 - 35 psi. Slight changes as

ESFR Pressure Anomaly

2007-12-10 Thread å... ....
I can´t find your numbers. I think what you are referring to is: 2007 NFPA 13, Table 17.2.3.1 but for uncartoned (exposed) unexpanded, the pressures and K-factors do not match your quotations at the 25 ft storage height. the pressures and K-factors come close to matching -- for cartoned

RE: Fire Pump+Jockey Pump+Wet Alarm Valve Combined Riser Diagram

2007-12-10 Thread Aydın ÖZKAYA
Dear Craig, I checked the web site, but couldn't find something with reference to FP+JP connection, there is just the fire water mains feed configuration. So I'm still looking for... Thanks for yr interest... Aydin -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL

Re: ESFR Pressure Anomaly

2007-12-10 Thread Joe Hankins
Chris, The simple reason is that the test for K25s was run at 50 psi because the manufacturer wanted a success and there was no previous data. The test could be re-run at a lower pressure anytime somebody wants to to risk the money it would cost. K25 applications are based on individual

RE: ESFR Pressure Anomaly

2007-12-10 Thread George Church
Joe- These words, and the time bombs we can plant while being right or compliant should be required to be memorized by large groups of us; including ourselves as contractors, your insurance side of the house, AHJ/Inspectors, and PE's who assume anything specified to less than 3 decimal places is

RE: Fire Pump+Jockey Pump+Wet Alarm Valve Combined Riser Diagram

2007-12-10 Thread Craig.Prahl
What exactly are you trying to find? There are drawings of fire pump arrangements by several pump manufacturers and interior sprinkler system arrangements as Viking has. Craig L. Prahl, CET Fire Protection Group Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box

RE: ESFR Pressure Anomaly

2007-12-10 Thread Chris Cahill
I was reading from the cut sheet, technically FM criteria. NFPA according to the cut sheet there is no protection scheme for the K25. Even in the table you reference there is no ESFR 25 for this. As far as flows 25's = 178gpm, 17's = 99.4pgm and 14's 99 gpm. So I can go along with the

ESFR Pressure Anomaly

2007-12-10 Thread å... ....
Table 17.2.3.1 DOES reference the K25 for your case, uncartoned (exposed) unexpanded plastic. look at 25 ft storage (your specification) at 40 ft storage height. (per my reference). The flows in that NFPA row goes as you shows below. I think the reason the K25 is required to thrown down so much

Re: ESFR Pressure Anomaly

2007-12-10 Thread Thom McMahon
The main point James has made for class I-IV, is that the lower end of the curve, may actually work most of the time, but as soon as you try to rise up the curve the greater the risk of failure. (Tyco has this nice test facility where he can play, and see things that have not been tested for FM

RE: ESFR Pressure Anomaly

2007-12-10 Thread George Church
Thom- If you're a contractor- and I know you don't just play one on TV :)- You're a risk-taker. In this litigious society, you can be held liable for meeting the adopted standard, but not applying a newer code. Or, for that matter, the reverse. So even with staying within the boundaries of

RE: ESFR Pressure Anomaly

2007-12-10 Thread Mike Brown (TECH- GVL)
Before you get too excited about the engineering process and testing I offer the following: In the early 70's, GEM (Not called Tyco then) had a HSW that covered 16 x 28 ft. It was UL Listed until they figured out that they did not test it with a ceiling. When they did, the water spray hit the

Re: ESFR Pressure Anomaly

2007-12-10 Thread Joe Hankins
Mike, My point is that NFPA 13 should be read literally rather than being interpreted on the basis of assumptions about the depth and breadth of testing that may or may not be true, depending on the application. 13 is not defective, but some of the interpretations of it are. Joe Mike

Re: performance

2007-12-10 Thread Roland Huggins
Joe and I are on the same page on this issue but I wanted to clarify a minor point. I think the standards says equally ACCEPTABLE with no statement about performance. Another good example is ceiling only verses ceiling with in-racks. Both are equally acceptable but not even close to the

Re: Sprinkler system serving two different buildings

2007-12-10 Thread Roland Huggins
There was an old formal interpretation that said one building, one system. There is criteria in the 2007 edition under 8.2.4 and 8.2.5 (and Annex). We could discuss what 8.2.4 means by multiple buildings with a common wall when they are owned by different parties but that's a different

RE: Sprinkler system serving two different buildings

2007-12-10 Thread Ed Cyr
Here in California, Mixed Use Construction is becoming more common. One structure, multi story, individually owned units. Several units can occupy an entire floor, or vertically several floors with an attic. Common walls separate these units. Ground and second floors include parking and

RE: Sprinkler system serving two different buildings

2007-12-10 Thread George Church
One things for sure- If you zone it for today's layout of ownership lines, it will be wrong before its occupied. glc -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Ed Cyr Sent: Monday, December 10, 2007 6:28 PM To: sprinklerforum@firesprinkler.org

Sprinkler system serving two different buildings

2007-12-10 Thread å... ....
mixed use is the natural evolution of urban space. Mixed use is an efficient means for cities to do what they do best, rapid exchange of information and materials. fire prtection should facilitate that, not dictate single use design for our own ease of mind. to every tenant a riser, and

Re: Sprinkler system serving two different buildings

2007-12-10 Thread Allan Seidel
Thanks, I'll look at these sections. The situation is an IBC building code Building Separation Wall dividing a public structure from another public structure so that they function code-wise as two separate buildings. A gut instinct says a sprinkler system should not cross this type of

RE: Sprinkler system serving two different buildings

2007-12-10 Thread bill . brooks
___ Sprinklerforum mailing list Sprinklerforum@firesprinkler.org http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)

RE: Sprinkler system serving two different buildings

2007-12-10 Thread bill . brooks
This topic was discussed in the past year. Although your gut feeling is probably the way it should be, it is not the way it is. When this was discussed previously I had the opinion that a building is intended to be a stand alone structure and not subject to being degraded by a problem in an

RE: ESFR Pressure Anomaly

2007-12-10 Thread A.P.Silva
What about the low flow heads that were designed at very low flows? Can't remember, was it 8 gpm for pendents 16'x16'? Anyway, some value really low. When the density was increased, it was never admitted that the previous densities did not work. Sprinklers manufactured after a certain date were