Thanks, I'll look at these sections. The situation is an IBC building
code Building Separation Wall dividing a public structure from
another public structure so that they function code-wise as two
separate buildings. A gut instinct says a sprinkler system should not
cross this type of separation and so I am looking for some backup,
but now I am beginning to taste crow.
Allan Seidel
St. Louis, MO
On Dec 10, 2007, at 4:57 PM, Roland Huggins wrote:
There was an old formal interpretation that said one building, one
system. There is criteria in the 2007 edition under 8.2.4 and
8.2.5 (and Annex). We could discuss what 8.2.4 means by multiple
buildings with a common wall when they are owned by different
parties but that's a different question.
Roland
On Dec 8, 2007, at 11:06 AM, Ron Greenman wrote:
Allan,
I believe this is a mass imaginary rule. It has come up here many
times and although it may not be advisable or a "best practice" I've
never found a prohibition and have on many occasions seen it in
application. Logically the only reasons I can see for limiting a
system to a single building would be to avoid confusion in an
emergency (but then I'd think we'd have more stringent rules defining
the location of the riser itself, etc.) and as to ownership when when
the buildings were legally controlled by different entities. Going
back to is it a good idea or not I'd tend to avoid it whenever
possible. Have I missed something in (for me) IBC? Have you missed
something in the codes applicable to St. Louis? By the way I was in
St. Louis in September out by Westport. I didn't have a chance to see
much but the area of the hotel, Busch Gardens and the Dent/Grant
House
but it seemed a pleasant city.
On 12/7/07, Allan Seidel <[EMAIL PROTECTED]> wrote:
Folks, it has been my understanding that a sprinkler system
cannot be
used to serve sprinklers in another building. I cannot find the
chapter and verse. This is not a matter of convincing someone it
is a
bad idea. Am I imagining this rule?
Allan Seidel
St. Louis, MO
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:Sprinklerforum-
[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
--
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:Sprinklerforum-
[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:Sprinklerforum-
[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)