PortE Cochere

2009-03-28 Thread å . . . . . . .
some IBC jurisdictions, and I am not includingall because of my limited experience, require sprinkler protection under [and in] Porte Cochere's if they are attached to the main structure [ and combustible construction]. Variances granted if noncombustible construction or separated with fire barrie

Re: Exterior Decks/Balconies 13R

2009-03-28 Thread Ron Greenman
And Ed's comments bring us back to the size of fire. Sprinklers in racks because we expect big fires in racks so big fires set off sprinklers shielded by commodities above. No commodities above and we have ceiling sprinklers with a ceiling above. There are apartment buildings in the NW with no eave

RE: Porto Cochere

2009-03-28 Thread Todd Williams
See NFPA 13 (2002) section 8.14.7, especially handbook commentary. However, local building code may trump this and you will need to check them. (Porte Cochere: french for coach door) At 11:03 PM 3/28/2009, you wrote: >I can't address how the IBC looks at porte cocheres, but by definition >(Webs

RE: NFPA 14 roof access

2009-03-28 Thread Ed Kramer
I've reread (several times) the proposed change to 7.3.2(5) and I think I now understand the intent. But I'm still confused. The proposed change to A.7.3.2 (also part of 14-53 Log#CP3) adds a sentence that reads "Only one standpipe is necessary to serve the roof, it is not the intent to extend

RE: Porto Cochere

2009-03-28 Thread Ed Kramer
I can't address how the IBC looks at porte cocheres, but by definition (Webster's & others), they are for picking up and dropping off passengers, not for parking. Ed Kramer Littleton, CO > Are Porto Cochere's considered a parking structure, if open on 3 sides. > Does anyone know where this is in

RE: Exterior Decks/Balconies 13R

2009-03-28 Thread Ed Kramer
The problem we designers have is that neither 13R nor the IBC addresses the spacing of sprinks protecting the decks/balconies. That leaves us with the criteria located in NFPA 13. NFPA 13 says sidewall sprinks can be located up to 14' on-center (light hazard) and upright/pendent sprinks can be lo

HEF generator detail

2009-03-28 Thread Scott A. Futrell
Does anyone have a detail of the pipe support for a HEF generator that they would be willing to share with me offline? I need a detail that is not all thread rod only, but includes either strut or angle iron and sway bracing and we will further modify as necessary, but I thought maybe someone

Urgent matter in Ohio

2009-03-28 Thread Forest Wilson
I was informed by the NFSA rep today that HB 2 a transportation bill has been altered to stop residential sprinklers. There is a public hearing on this Monday morning at 10:00 am. It has passed the house and senate and is in a conference committee. If it passes this committee it will go to the

RE: Exterior Decks/Balconies 13R

2009-03-28 Thread John Drucker
Dave, I know firsthand of the issue. I was a firefighter assigned to the Truck (L-180) at the Dunes Condo Fire in Port Monmouth (Middletown), NJ. Heres the video; http://video.google.com/videoplay?docid=7755300206427539841 (The audio narration is the cameraman speculating yada yada) Ladder 18

Re: NFPA 14 roof access

2009-03-28 Thread steve
o the building codes define "stairway access"? > > Ed Kramer > Littleton, CO ___ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum <http://lists.firesprinkler.org/mailman/listinfo/sprink

RE: NFPA 14 roof access

2009-03-28 Thread Thom McMahon
Ed If your still on IBC 2003 check out 1009.12 Stairway to roof It allows an alternating tread device. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 ___ Sprinkle

Porto Cochere

2009-03-28 Thread Nick Melosi
Are Porto Cochere's considered a parking structure, if open on 3 sides. Does anyone know where this is in IBC? -- Nick Melosi 813.944.2008 ___ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assis

Re: Exterior Decks/Balconies 13R

2009-03-28 Thread Dave Phelan
I believe the focus on this requirement is that these exterior spaces (decks, balconies, whatever you call thems) represent an appreciable risk to the building due to human activity. There have been some losses of mid-rise 13R properties that were spectacular to watch as an exterior fire on the b

RE: NFPA 14 roof access

2009-03-28 Thread Ed Kramer
Thanks, John and thanks Thom. So, NFPA 14 and the IBC use slightly different phrasing (stairway access vs stair access). A ladder leading from the highest landing up to a roof hatch might qualify as 'stairway access', but not as 'stair access'. I may need a formal interpretation on this one.

RE: Exterior Decks/Balconies 13R

2009-03-28 Thread John Drucker
What's the AFSA position on this issue, i.e. "Exterior Decks/Balconies 13R Sprinklers" ? Thanks John Drucker Fire Protection Subcode Official New Jersey -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Ron