Bob-
Thanks for the reply. I guess my only question then is it seems to me there
should be some type of a limitation on 8.8.5.1.2 (2) with regard to
deflector distance above the obstruction, similar to table 8.8.5.1.2.?
Brian Harris, CET
FDFP Inc.
-Original Message-
From:
mailto:mja...@brigadefire.com
www.brigadefire.com http://www.brigadefire.com/
-- next part --
An HTML attachment was scrubbed...
URL:
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20111026/9e5e827b/attachment.html
/20111026/9e5e827b/attachment.html
-- next part --
A non-text attachment was scrubbed...
Name: image003.jpg
Type: image/jpeg
Size: 9587 bytes
Desc: image003.jpg
URL:
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20111026/9e5e827b/attachment.jpg
/
-- next part --
An HTML attachment was scrubbed...
URL:
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attach
ments/20111026/9e5e827b/attachment.html
-- next part --
A non-text attachment was scrubbed...
Name: image003.jpg
Type: image/jpeg
Size: 9587
.
mja...@brigadefire.com mailto:mja...@brigadefire.com
www.brigadefire.com http://www.brigadefire.com/
-- next part --
An HTML attachment was scrubbed...
URL:
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attach
ments/20111026
://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
-- next part --
An HTML attachment was scrubbed...
URL:
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20111026/932eeba3/attachment.html
/20111026/932eeba3/attachment.html
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
___
Sprinklerforum mailing list
Sprinklerforum
/listinfo/sprinklerforum
-- next part --
An HTML attachment was scrubbed...
URL:
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20111026/932eeba3/attachment.html
___
Sprinklerforum mailing
Is anyone aware of a prohibition against having two floor control assemblies
on each floor connected to two different standpipes and calculating the loop to
size the sprinkler main?
Ron Fletcher
Aero Automatic
Phoenix, AZ
___
Sprinklerforum
:
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20111026/7d40f17b/attachment.bin
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
-- next part --
A non-text attachment was scrubbed...
Name: winmail.dat
Type: application/ms-tnef
Size: 3521 bytes
Desc: not available
URL:
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20111026/7d40f17b/attachment.bin
Hello Ronl.Fletcher,
There are a few high rises here setup that way around here... BIG thing is the
alarm company has to put the flow switches on different points so it can be
verified that BOTH work during the test. Inspectors need to know to look for 2
flow alarms from each floor and have a
bytes
Desc: not available
URL:
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20111026/7d40f17b/attachment.bin
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo
If my memory serves me correctly, there was a time when NFPA 14 prohibited
it. My 2003 edition doesn't have it. So if it was prohibited, it was in an
edition older than 2003.
Ed Kramer
Littleton, CO
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
I have had some jurisdictions require it as a precautionary measure i.e. a
standpipe that might be out of service. However, I have not seen it allowed
to improve hydraulics.
SHARON ALVES
Senior Fire Sprinkler Designer
LP Consulting Engineers, Inc.
Mechanical -MElectrical -EPlumbing Engineers
When I get in the way back machine I remember that it was verboten at some
point. It seems to be okay now so long as the flow switch operates on the flow
of one head.
Ron Fletcher
Aero Automatic
Phoenix, AZ
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
part --
A non-text attachment was scrubbed...
Name: winmail.dat
Type: application/ms-tnef
Size: 3521 bytes
Desc: not available
URL:
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attach
ments/20111026/7d40f17b/attachment.bin
://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20111026/53edf952/attachment.html
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
.
-- next part --
An HTML attachment was scrubbed...
URL:
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
s/20111026/53edf952/attachment.html
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http
://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
s/20111026/53edf952/attachment.html
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
-
No virus
/sprinklerforum/attachment
s/20111026/53edf952/attachment.html
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
-
No virus found in this message.
Checked by AVG
not make a difference for low street pressure.
-- next part --
An HTML attachment was scrubbed...
URL:
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
s/20111026/53edf952/attachment.html
for low street pressure.