You're welcome Taylor.
Hopefully it holds up and that's what's great about this Forum.
Brad
On Jul 18, 2016 3:53 PM, "Taylor Schumacher" wrote:
> Brad,
>
>
>
> Thanks for the why.
>
>
>
> *TAYLOR SCHUMACHER, CET*
>
> Security Fire Sprinkler
>
> *P* 320.656.0847 | *F*
Brad,
Thanks for the why.
TAYLOR SCHUMACHER, CET
Security Fire Sprinkler
P 320.656.0847 | F 320.656.0312 | E tay...@sfsprinkler.com
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Brad Casterline
Sent: Monday, July 18, 2016 3:23 PM
To:
2010 edition.
This rule is for actiavation so it is the position of the bulb that
matters, not the deflector orientation, just my two cents.
Brad
On Jul 18, 2016 2:35 PM, "Parsley Consulting"
wrote:
> Taylor,
> perhaps expanding on Ryan's comment, it doesn't
Taylor,
perhaps expanding on Ryan's comment, it doesn't appear to me that
it would be applicable as the EC HSW above is not governed by anything
in section 8.8, rather it's covered in 8.9, and there's nothing in 8.9
or its annex which matches the diagrams you referred to in 8.8.
Count
I understand that, but, the head making up the distance to the high head is
still a pendent. Just curious why this couldn't apply to the type of
arrangement I'm proposing.
TAYLOR SCHUMACHER, CET
Security Fire Sprinkler
P 320.656.0847 | F 320.656.0312 | E tay...@sfsprinkler.com
From:
I would say no. 8.8 is rules for "Extended Coverage Upright and Pendent Spray
Sprinklers".
Ryan Labrie
Fire Protection Designer
Critical System Solutions, LLC
2830 Scherer Drive, Suite 300
St. Petersburg, FL 33716
Office: 727.209.5122
Fax: 727.209.5126
Cell: 813.394.3978
Email:
Can the rules of NFPA 13, 2013 ed., 8.8.4.1.1.4(B)-see also Figure
A.8.8.4.1.1.4(A) be applied where the low sprinkler is a pendant in a soffit
and the high sprinkler is a sidewall?
It reads "Where the distance between the upper ceiling and the sprinkler
deflector is less than or equal to 36
The drain test is needed if it is downstream of a valve. Every valve needs
exercised, and a flow test needs conducted after the closed valve is
restored to the open position.
On Jul 18, 2016 1:05 PM, "rongreenman ." wrote:
> John has stated and defended. Mike has stated.
13 only requires an initial acceptance test to establish baselines for the
subsequent maintenance checks per NFPA 25. What a local yokel requires is
only relevant to that locality and shouldn't be presented on the Forum as
unequivocal without propose references. It's also important to know what a
NFPA 25 (2014) section 13.2.5 states “A main drain test shall be conducted
annual for each water supply lead-in to a building water based fire protection
system to determine whether there has been a change in the condition of the
water supply.”
13.2.5.1 “Where the lead-in to a building
All the AHJ's in my area require a main drain test for all systems even if you
have a header with multiple
riser checks and dry pipe valves on it.
NFPA -13 does not state that only one main drain test is acceptable, it plural
not singular in the text.
Mike
John has stated and defended. Mike has stated. Mike, defend your position.
I'll side with John, using his defense and add that that only one main
drain test is needed for any lead-in, no matter how many systems and
auxiliary systems it supplies if all originate from the same header. And,
as an
Yes
From: Sprinklerforum on behalf
of Todd Williams
Sent: Monday, July 18, 2016 11:55 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Auxiliary dry valve drains
Are full flow 2"
Todd:
The 2" main drain test is primarily intended to verify that the water supply
to the sprinkler system is not impaired, not to make sure the drain flows
freely. 8.16.2.5 (2013) Has no requirement for a full flow drain test. It
only details the size requirements relating to the capacity of
Are full flow 2" drain tests required for auxiliary dry valves?
Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT