"In order to form a more perfect thirteen" we play like walls are not
there even when they are, and rated no less-- density/area method--
and we play like walls are there when they are not-- as in this and
the recent 'saw-tooth type' ceiling discussions.
TC members have always kept it
Larry:
I think the original question is asking what is the area of coverage of this
setup. You have two lines that are 10' apart with sprinklers 13' on center on
the lines. Call these lines A and B. Then in the adjacent bay, you have lines
15' on center with sprinklers 8' on center. Call
Who said they wouldn't obstruct heat flow?
Because they are more than 7.5 ft apart it can be considered to be
"unobstructed" construction. But of course they are obstructions.
With unobstructed construction the deflector distance has to be 1" to 12" below
the ceiling.
You can't space the
Going after the individual inspector for an inspection not happening is a
different question. I had zero influence on the budget for the organization.
Maybe advocating for new flow test equipment. But as far as number of
inspectors? No. That’s a city council responsibility. And in my office new
But Larry, if the beams are not an obstruction to heat flow OR spray
pattern, it's like they don't exist, no?
Brad.
Quoting Larry Keeping :
You don't need to do anything special with the deflector distance.
As per 8.5.2.1.1 (2), the line spacing is to a wall or
You don't need to do anything special with the deflector distance. As per
8.5.2.1.1 (2), the line spacing is to a wall or obstruction:
(2) Between branch lines as follows:
(a) Determine perpendicular distance to the sprinkler on the adjacent branch
line (or to a wall or obstruction in the case
I recently learned that the beam only acts like a wall if you can't
throw under it, so get those deflectors way up there!
(Crow and Thunderbird rocks)
Merry Christmas Forum,
Brad.
Quoting Bob :
The beam is an obstruction that acts like a wall. You’re covering floor
The beam is an obstruction that acts like a wall. Youre covering floor
space, so as long as each sprinkler covers the correct area (30 sf), then
the spacing that you are describing sounds in compliance with NFPA 13
spacing rules.
Thank you,
Bob Knight, CET III
208-318-3057
From:
I see nothing wrong with that. The beam is your "protection line" or
"wall". The heads are spaced properly in each area they are protecting. The
heads protecting 5'-0 to the beam (10'-0) are spaced along the branch line
properly for that coverage. And the heads throwing 7'-6 to the beam (15'-0)
I was always taught to treat the beam as a wall. However, I can see an
argument for viewing on the floor. If that is the case, I would not have done
3 lines in the 30’ bay. I would shorten up the spacing on the line adjacent to
the beam in the 20’ bay. It is relatively cheap to add
Tort when done right, should right some wrongs.
It is not thought, that civic immunity helped much, if any, in the case
of a Fire Marshal who inspected The Station before it burned.
It is not thought that tort got it right by removing hose from
standpipe connections; but N.A.'s building
Me personally, I would treat the beam as a wall, the spray pattern cannot
carry over to the next row on the other side, so why would I carry over its
dimension for the SxL
Best regards,
*Joe Burtell, SET, CFPS*
[image: Burtell Fire_Small]
Phone | Fax | Mobile| Text *406-545-0784
Assumed a flat ceiling
Thank you
James Crawford
Phaser Fire Protection Ltd.
Phone 604-888-0318
Fax 604-888-4732
Cel 604-790-0938
Email jcrawf...@phaserfire.ca
Web www.phaserfire.ca
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Is the spacing along the branchline measured along the floor or the roof
pitch?
Best regards,
*Joe Burtell, SET, CFPS*
[image: Burtell Fire_Small]
Phone | Fax | Mobile| Text *406-545-0784 <++1-406-545-0784>*
116 N. 11th Street | Billings, MT 59101
Email: j...@burtellfire.com
Web Site:
We have been having a discussion in the office about the S rule for
spacing of sprinkler heads. We received a sprinkler drawing with some
spacing that we do not agree with, see below, but can find no specific
direction in NFPA #13 (2013) that says it is wrong.
Basic situation we have a small
A SSP has a maximum distance of 12" below the ceiling, which you are within.
Even if you wanted to add a level of protection above, the short space would
not allow for a full development of the spray pattern.
Taylor Schumacher
From: Sprinklerforum
I'm still trying to wrap my head around this. For the most part I don't this
the area above the floating ceilings can be classified as a concealed space
from the rules in 13 (2016). All the ceiling are less than 12" below a
concrete deck, but I don't know why that would exclude sprinkler above
Based on what, specifically?
Steve
Original message
From: tcfire
Date: 12/21/17 5:54 AM (GMT-08:00)
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Corrosion
Seems to make a great argument for nitrogen infusion.
Sent from my Sprint Samsung
Seems to make a great argument for nitrogen infusion.
Sent from my Sprint Samsung Galaxy S7.
Original message From: Steve Leyton
Date: 12/20/17 8:51 PM (GMT-05:00) To:
sprinklerforum@lists.firesprinkler.org Subject: RE: Corrosion
The fact that
I’ve got a 10+2 Sty building that needs a new pump for a myriad of reasons.
Replacement will be larger to satisfy Standpipe demand. New system pressures
will require PRV’s to the 10th flr. and maybe one or both levels of mechanical
above. None currently installed, 190 PSI in the pump room.