Re: Apartment Crawl Space

2018-01-11 Thread Roland Huggins
This is indeed the opinion of the 13R technical committee. The problem is that it isn’t their decision to make. That belongs to the building code and it says it is possible with the right combination of variables. Same things applies to NFPA 13 equipment that the ENTIRE building must be prote

Re: Apartment Crawl Space

2018-01-11 Thread Roland Huggins
I disagree completely with this simplified approach. It is possible to mix the two system types but there are multiple variables that come into play, the most significant being it must qualify as a separated mixed occupancy and it must contain the right combination of occupancies. The building

RE: Apartment Crawl Space

2018-01-11 Thread David Bitton
I would also add the following excerpt from the Annex of NFPA 13R (2013 Edition) A1.1 Where buildings are greater than four stories in height, or where buildings are of mixed use where residential is not the predominant occupancy, residential portions of such buildings should be protecte

Apartment Crawl Space

2018-01-11 Thread Fpdcdesign
Duane, I respectfully question that. Section 1.1 of the 2016 NFPA 13R states: "This standard shall cover the design and installation of automatic sprinkler systems for protection against fire hazards in residential occupancies up to and including four stories in height in bu

Re: Apartment Crawl Space

2018-01-11 Thread Travis Mack
You have to follow the IBC/IFC first in most areas. That is going to point you to one or the other, unless they get creative with horizontal and vertical separations. A 3 story type V-A construction building with R2 occupancy (IBC code) of 36k sq ft per floor is going to be NFPA 13 unless they

RE: Apartment Crawl Space

2018-01-11 Thread Steve Leyton
Duane: Having taught NFPA sprinkler seminars for 8 or 9 years and having served on the AUTRSS for 5 cycles, I am reasonably certain that this isn't accurate. NFPA 13R has had various explanations in A.1.1 over the years, but the current one states, "NFPA 13R is appropriate for use as an alte

RE: Apartment Crawl Space

2018-01-11 Thread Fox, Duane T. (FireMarshal)
Brian, NFPA and NFA seminars. The definition of 13R is for up to and including four floors. It doesn't prohibit the building from having more floors just like if the first floor was mercantile or business (like a hotel). You would design the first floor, fifth floor, and attic as NFPA 13,

RE: Apartment Crawl Space

2018-01-11 Thread Brian Harris
Ed- Great point, thank you. Brian Harris, CET BVS Systems Inc. bvssytemsinc.com From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Ed Kramer Sent: Thursday, January 11, 2018 3:02 PM To: sprinklerforum@lists.firesprinkler.org Subje

RE: Apartment Crawl Space

2018-01-11 Thread Ed Kramer
And remember to increase the design area to 3000 sf (11.2.3.1.5), or 8 sprinks (11.3.1.2). Ed K From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of John O'Connor Sent: Thursday, January 11, 2018 1:41 PM To: sprinklerforum@lists.firesprinkler.org Subject

RE: Apartment Crawl Space

2018-01-11 Thread Art Tiroly
Check out the residential rules in NFPA 13, Section 8.4.5. Similar to 13-R. 4 heads. Art Tiroly ATCO Fire Protection/Tiroly 24400 Highland Rd CLE 44143 216-621-8899 216-570-7030 cell From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Brian

RE: Apartment Crawl Space

2018-01-11 Thread Brian Harris
Duane- That's an interesting thought. What section in 13 ? Brian Harris, CET BVS Systems Inc. bvssytemsinc.com From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Fox, Duane T. (FireMarshal) Sent: Thursday, January 11, 2018 2:52 PM

RE: Apartment Crawl Space

2018-01-11 Thread Fox, Duane T. (FireMarshal)
According to NFPA you can do a 13-R for the first four floors and a 13 system on the 5th floor and attic. I think you need to look at the IBC/IRC to see if there are building code requirements in the crawl space (assuming a normal crawl space). Duane T. Fox, Jr., CFPS, CFI, CFPE Asst Chief, Te

RE: Apartment Crawl Space

2018-01-11 Thread Brian Harris
Thank you. Brian Harris, CET BVS Systems Inc. bvssytemsinc.com From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of John O'Connor Sent: Thursday, January 11, 2018 2:41 PM To: sprinklerforum@lists.firesprinkler.org Subject: RE: Apart

RE: Apartment Crawl Space

2018-01-11 Thread John O'Connor
Brian, Per 13, crawl spaces are generally not required. See NFPA-13, 2016 Ed, page 92, 8.15.6.2. As for interstitial spaces in combustible const., as often found in residential work, sprinklers will be required. You would have been in luck with 4 floors or less, but not 5. Good luck. John O'C

Apartment Crawl Space

2018-01-11 Thread Brian Harris
Looking at a (5) story apartment building so I assume it would need to be per NFPA-13 correct? With that being said is there anything in the Standard that addresses the crawl space underneath? Concealed Space? Brian Harris, CET BVS Systems Inc. Design Manager bvssystemsinc.com

Re: [EXTERNAL] RE: Deflector Distance for Sprinklers in Skylights

2018-01-11 Thread bcasterline
I've tried to refind that fire modeling you did Roland a couple three centuries ago re how the deeper the pocket the better. It makes sense how if you have a huge mass of cool air above the area of the opening the ceiling jet just keeps on trucking like the opening wasn't there. It was Teach