Re: [EXTERNAL] Re: Available Pressure from Fire Water Storage Tank

2021-05-07 Thread Hinson, Ryan via Sprinklerforum
Don’t forget that, along with your pump(s) churn, the high water level in the tank must be used to determine maximum downstream system pressure. Sent from my iPhone > On May 7, 2021, at 4:06 PM, Mark.Phelps via Sprinklerforum > wrote: > > So, if this same tank and pump were at the same elev

RE: [EXTERNAL] Re: Available Pressure from Fire Water Storage Tank

2021-05-07 Thread Mark.Phelps via Sprinklerforum
So, if this same tank and pump were at the same elevation and 5 blocks away in a Water Utility Yard owned by the city water department, what pressure and flow rate would one use to design a sprinkler system? Mark at Aero 602 820-7894 -Original Message- From: Sprinklerforum On Behalf

RE: Available Pressure from Fire Water Storage Tank

2021-05-07 Thread Kyle.Montgomery via Sprinklerforum
That's kind of the crux of my issue. For the new system, demand x duration probably uses about half of the tank. But since the tank is sized for site fire flow (hydrants... I assume, at least) then do I have to consider that demand as part of what depletes the tank? Or is that completely separat

RE: Available Pressure from Fire Water Storage Tank

2021-05-07 Thread Mike Morey via Sprinklerforum
If you didn't have a pump at all and put the same tank 100' above ground, you'd calculate to the minimum anticipated water level after demand x duration is subtracted from the fill turn on point would you not? What would make this any different? Genuine question, I've always used minimum water

Re: Available Pressure from Fire Water Storage Tank

2021-05-07 Thread John Denhardt via Sprinklerforum
Lots of items to think about. I always recommend using the tank at the lowest available level. - What is the level of the tank before refilled? - Is the tank being utilized for any other purposes. Reminder - account for the friction loss between the tank and the suction side of the fire p

Re: Available Pressure from Fire Water Storage Tank

2021-05-07 Thread Bob Caputo via Sprinklerforum
😀 On Fri, May 7, 2021 at 11:23 AM Michael Hill via Sprinklerforum < sprinklerforum@lists.firesprinkler.org> wrote: > There goes my logic, right out the window..again. > > Mike Hill > > -Original Message- > From: Sprinklerforum On > Behalf Of Bob Caputo via Sprinklerforum > Sent: Frid

RE: Available Pressure from Fire Water Storage Tank

2021-05-07 Thread Michael Hill via Sprinklerforum
There goes my logic, right out the window..again. Mike Hill -Original Message- From: Sprinklerforum On Behalf Of Bob Caputo via Sprinklerforum Sent: Friday, May 7, 2021 2:21 PM To: sprinklerforum@lists.firesprinkler.org Cc: Bob Caputo Subject: Re: Available Pressure from Fire Water

Re: Available Pressure from Fire Water Storage Tank

2021-05-07 Thread Bob Caputo via Sprinklerforum
No, you are not permitted to use elevation pressure from a gravity tank. You do not know the elevation of the water in the tank which is depleted during the operation of the systems in fighting the fire. You are permitted to use the pumps productive curve at 150% of rated flow and 65% of rated pre

RE: Available Pressure from Fire Water Storage Tank

2021-05-07 Thread Michael Hill via Sprinklerforum
I would think you could subtract the sprinkler demand x required duration from the lowest expected capacity of the tank and use the height of the remaining water column as your supply. The tank would also probably need an automatic fill. I have no codes to back this up, but logic says it should

Available Pressure from Fire Water Storage Tank

2021-05-07 Thread Kyle.Montgomery via Sprinklerforum
I'm working on a project where they are adding a new building to an existing campus. There is an existing fire water storage tank and fire pump that serves the site underground fire loop. The new building has a very demanding sprinkler system that just barely exceeds the fire pump's pressure av

Re: Location of hydrant valves in CA.

2021-05-07 Thread David Williams via Sprinklerforum
Thanks all…The civil thought he had this covered with the idea of adding a second valve, but no dice with the water supplier! David Toshio Williams, PE*, FPE (*Registered in MN, WI, MI, IA, IL, IN, ND, VT) (218) 279-2436 direct | (218) 310-2446 cell LHB, Inc. | PERFORMANCE DRIVEN DESIGN From: K

Re: Location of hydrant valves in CA.

2021-05-07 Thread Ron Greenman via Sprinklerforum
Not having ever been on any committee making up any rules regarding this I'm going to take some logic shots at the issue as to the whys. If the hydrant is along a right of way then the service valve will be in the street somewhere perpendicular to the direction of the street in a straight line from

Re: Location of hydrant valves in CA.

2021-05-07 Thread John Denhardt via Sprinklerforum
NFPA 24 - 2019 7.1.1.2.2 Valves required by 7.1.1.2 shall be installed within 20 ft (6.1 m) of the hydrant. 7.1.1.2.2.1 Valves shall be clearly identified and kept free of obstructions. 7.1.1.2.3 Where valves cannot be located in accordance with 7.1.1.2.2, valve locations shall be permitted w

Location of hydrant valves in CA.

2021-05-07 Thread David Williams via Sprinklerforum
A civil engineer friend of mine is working on a state project in California and there is a fight between the water purveyor and the state fire marshal as to the location of the hydrant valves. The water purveyor wants the valves to be right off the main and does not feel a need to keep the valve

RE: Commodity Classification

2021-05-07 Thread Dick Culver via Sprinklerforum
Tim I would recommend you get a completed Owner's Information Certificate for your files. Dick -Original Message- From: Sprinklerforum On Behalf Of tstone52--- via Sprinklerforum Sent: Thursday, May 06, 2021 1:38 PM To: sprinklerforum@lists.firesprinkler