Don’t forget that, along with your pump(s) churn, the high water level in the 
tank must be used to determine maximum downstream system pressure.

Sent from my iPhone

> On May 7, 2021, at 4:06 PM, Mark.Phelps via Sprinklerforum 
> <[email protected]> wrote:
> 
> So,  if this same tank and pump were at the same elevation and  5 blocks 
> away in a Water Utility Yard owned by the city water department, what 
> pressure and flow rate would one use to design a sprinkler system?
> 
> Mark at Aero
> 602 820-7894
> 
> -----Original Message-----
> From: Sprinklerforum <[email protected]> On 
> Behalf Of Bob Caputo via Sprinklerforum
> Sent: Friday, May 7, 2021 11:21 AM
> To: [email protected]
> Cc: Bob Caputo <[email protected]>
> Subject: [EXTERNAL] Re: Available Pressure from Fire Water Storage Tank
> 
> No, you are not permitted to use elevation pressure from a gravity tank.
> You do not know the elevation of the water in the tank which is depleted 
> during the operation of the systems in fighting the fire.  You are permitted 
> to use the pumps productive curve at 150% of rated flow and 65% of rated 
> pressure
> 
>> On Fri, May 7, 2021 at 11:13 AM Kyle.Montgomery via Sprinklerforum < 
>> [email protected]> wrote:
>> 
>> I'm working on a project where they are adding a new building to an 
>> existing campus. There is an existing fire water storage tank and fire 
>> pump  that serves the site underground fire loop. The new building has 
>> a very demanding sprinkler system that just barely exceeds the fire 
>> pump's pressure available at the demand flow (using just the pump 
>> curve as the water supply).
>> 
>> Normally, I would be conservative and use just a few psi as my water 
>> supply from the tank (as though it were nearly empty). But, is that 
>> overly conservative? The tank is mounted on the ground, at the same 
>> elevation as the fire pump, but it is nearly 45 feet tall, with a 
>> total capacity of over
>> 500,000 gallons. Can I use some of that elevation pressure, or do I 
>> need to design and calc as though the tank is nearly depleted?
>> 
>> -Kyle M
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> 
>> https://nam12.safelinks.protection.outlook.com/?url=https%3A%2F%2Furldefense.proofpoint.com%2Fv2%2Furl%3Fu%3Dhttp-3A__lists.firesprinkle&amp;data=04%7C01%7Crhinson%40burnsmcd.com%7C16898695b528484c6ff408d9119c046e%7Cbfbb9a2b6d994e78b3c795005d555c8b%7C0%7C1%7C637560184075025189%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000&amp;sdata=FlAYNVXV%2BQH9O6XoNg%2F%2B7OHZUG29BMzeAKphsphf2ZI%3D&amp;reserved=0
>> r.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwICAg&c=wn3mZ
>> QLIuInh2ClcJ0_DIA&r=dLwiR71i_XhSFqam3ZLeaFLiQJ3cDTUB0ReB4-yDDcg&m=sbcv
>> VKDiY86Z6_d0cmGpUAE-yKbUHdvwJfxJIwZih14&s=xW_3DXTpaglGRp_Lod9_4SygFCmo
>> JqtVkLeqtK_Eczg&e=
>> 
> --
> Bob Caputo, CFPS
> *President*
> 
> *American Fire Sprinkler Association*
> p: 214-349-5965 ext124
> w: firesprinkler.org
> <https://nam12.safelinks.protection.outlook.com/?url=https%3A%2F%2Furldefense.proofpoint.com%2Fv2%2Furl%3Fu%3Dhttps-3A__www.facebook.com_firesprinkler.org_%26d%3DDwICAg%26c%3Dwn3mZQLIuInh2ClcJ0_DIA%26r%3DdLwiR71i_XhSFqam3ZLeaFLiQJ3cDTUB0ReB4-yDDcg%26m%3DsbcvVKDiY86Z6_d0cmGpUAE-yKbUHdvwJfxJIwZih14%26s%3D9_q6urq9zEQtQy7i4Nd_rk4BBZBOiJsNCVSFRpcdMjg%26e%3D&amp;data=04%7C01%7Crhinson%40burnsmcd.com%7C16898695b528484c6ff408d9119c046e%7Cbfbb9a2b6d994e78b3c795005d555c8b%7C0%7C1%7C637560184075025189%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000&amp;sdata=fPOTiCmyAbs07sjP34NbIX7stz2agQqcyAa56fUGN34%3D&amp;reserved=0
>  > 
> <https://nam12.safelinks.protection.outlook.com/?url=https%3A%2F%2Furldefense.proofpoint.com%2Fv2%2Furl%3Fu%3Dhttps-3A__twitter.com_afsa_status_1039528345367732224%26d%3DDwICAg%26c%3Dwn3mZQLIuInh2ClcJ0_DIA%26r%3DdLwiR71i_XhSFqam3ZLeaFLiQJ3cDTUB0ReB4-yDDcg%26m%3DsbcvVKDiY86Z6_d0cmGpUAE-yKbUHdvwJfxJIwZih14%26s%3DPSOMCv00HpTP3bMjgG5Wczk2iOEH35yxgU-i0lh4kvM%26e%3D&amp;data=04%7C01%7Crhinson%40burnsmcd.com%7C16898695b528484c6ff408d9119c046e%7Cbfbb9a2b6d994e78b3c795005d555c8b%7C0%7C1%7C637560184075025189%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000&amp;sdata=Rmy7Q8bvkrAmSoUXygiWg9mUbkGmdnQRaO%2Fj%2Bt1onAg%3D&amp;reserved=0
>  > 
> <https://nam12.safelinks.protection.outlook.com/?url=https%3A%2F%2Furldefense.proofpoint.com%2Fv2%2Furl%3Fu%3Dhttps-3A__www.linkedin.com_company_american-2Dfire-2Dsprinkler-2Dassociation-2Dafsa-2D_%26d%3DDwICAg%26c%3Dwn3mZQLIuInh2ClcJ0_DIA%26r%3DdLwiR71i_XhSFqam3ZLeaFLiQJ3cDTUB0ReB4-yDDcg%26m%3DsbcvVKDiY86Z6_d0cmGpUAE-yKbUHdvwJfxJIwZih14%26s%3D4hyISelb176OLCvYsOKsSvSbu842IyJoPrQ706vZmVA%26e%3D&amp;data=04%7C01%7Crhinson%40burnsmcd.com%7C16898695b528484c6ff408d9119c046e%7Cbfbb9a2b6d994e78b3c795005d555c8b%7C0%7C1%7C637560184075025189%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000&amp;sdata=4nsyugKpe8Ijoms6d7zzuEPlTZPbG7X6qxaJI%2FFnS5s%3D&amp;reserved=0
>  >
>   
> <https://nam12.safelinks.protection.outlook.com/?url=https%3A%2F%2Furldefense.proofpoint.com%2Fv2%2Furl%3Fu%3Dhttps-3A__www.instagram.com_firesprinklerorg_%26d%3DDwICAg%26c%3Dwn3mZQLIuInh2ClcJ0_DIA%26r%3DdLwiR71i_XhSFqam3ZLeaFLiQJ3cDTUB0ReB4-yDDcg%26m%3DsbcvVKDiY86Z6_d0cmGpUAE-yKbUHdvwJfxJIwZih14%26s%3DWnV3x7dwAvD344IBMMjlrMdRQMfoQ8YIBkyVCR4kNW4%26e%3D&amp;data=04%7C01%7Crhinson%40burnsmcd.com%7C16898695b528484c6ff408d9119c046e%7Cbfbb9a2b6d994e78b3c795005d555c8b%7C0%7C1%7C637560184075025189%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000&amp;sdata=liD5AzsGZ302cheWcG%2FS3ZQyf%2BT%2FQ5k4%2B1bdtzlJpj8%3D&amp;reserved=0
>  >
> 
> *Train a safer, more efficient workforce.*
> 
> By enrolling your employees in the AFSA Apprenticeship Training Series for 
> Sprinkler Fitters 
> <https://nam12.safelinks.protection.outlook.com/?url=https%3A%2F%2Furldefense.proofpoint.com%2Fv2%2Furl%3Fu%3Dhttps-3A__www.firesprinkler.org_WWW_Education_Apprentice-5FTraining_WWW_Education_Apprenticeship-5FTraining.aspx-3Fhkey-3De88ef09e-2Dd74c-2D407f-2Dabcd-2D995aff866149%26d%3DDwICAg%26c%3Dwn3mZQLIuInh2ClcJ0_DIA%26r%3DdLwiR71i_XhSFqam3ZLeaFLiQJ3cDTUB0ReB4-yDDcg%26m%3DsbcvVKDiY86Z6_d0cmGpUAE-yKbUHdvwJfxJIwZih14%26s%3D_6Tmf4i1Euk-al8jqF5PF4JDRqcO13XAFZjt64gY110%26e%3D&amp;data=04%7C01%7Crhinson%40burnsmcd.com%7C16898695b528484c6ff408d9119c046e%7Cbfbb9a2b6d994e78b3c795005d555c8b%7C0%7C1%7C637560184075025189%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000&amp;sdata=SuPAj%2Fyye2CRcdapnFjotoWgBpQnsrP8gHWwBk5DyKA%3D&amp;reserved=0
>  >, you will reap the benefits of a qualified, professional installation crew.
> Well-trained employees will work smarter, increasing your company's 
> productivity and, in turn, its profits. Learn more 
> <https://nam12.safelinks.protection.outlook.com/?url=https%3A%2F%2Furldefense.proofpoint.com%2Fv2%2Furl%3Fu%3Dhttps-3A__www.firesprinkler.org_WWW_Education_Apprentice-5FTraining_WWW_Education_Apprenticeship-5FTraining.aspx-3Fhkey-3De88ef09e-2Dd74c-2D407f-2Dabcd-2D995aff866149%26d%3DDwICAg%26c%3Dwn3mZQLIuInh2ClcJ0_DIA%26r%3DdLwiR71i_XhSFqam3ZLeaFLiQJ3cDTUB0ReB4-yDDcg%26m%3DsbcvVKDiY86Z6_d0cmGpUAE-yKbUHdvwJfxJIwZih14%26s%3D_6Tmf4i1Euk-al8jqF5PF4JDRqcO13XAFZjt64gY110%26e%3D&amp;data=04%7C01%7Crhinson%40burnsmcd.com%7C16898695b528484c6ff408d9119c046e%7Cbfbb9a2b6d994e78b3c795005d555c8b%7C0%7C1%7C637560184075035141%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000&amp;sdata=SfvV%2BElaYo9xezKywZR9%2B9NBMtuMeVQO5bUwUyPV92A%3D&amp;reserved=0
>  > .
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> https://nam12.safelinks.protection.outlook.com/?url=https%3A%2F%2Furldefense.proofpoint.com%2Fv2%2Furl%3Fu%3Dhttp-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org%26d%3DDwICAg%26c%3Dwn3mZQLIuInh2ClcJ0_DIA%26r%3DdLwiR71i_XhSFqam3ZLeaFLiQJ3cDTUB0ReB4-yDDcg%26m%3DsbcvVKDiY86Z6_d0cmGpUAE-yKbUHdvwJfxJIwZih14%26s%3DxW_3DXTpaglGRp_Lod9_4SygFCmoJqtVkLeqtK_Eczg%26e%3D&amp;data=04%7C01%7Crhinson%40burnsmcd.com%7C16898695b528484c6ff408d9119c046e%7Cbfbb9a2b6d994e78b3c795005d555c8b%7C0%7C1%7C637560184075035141%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000&amp;sdata=pNKs4x0UCAOfp6v%2FjngKEWUMJmplxUCa3%2BluXAfsVTo%3D&amp;reserved=0
>  
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> https://nam12.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.org&amp;data=04%7C01%7Crhinson%40burnsmcd.com%7C16898695b528484c6ff408d9119c046e%7Cbfbb9a2b6d994e78b3c795005d555c8b%7C0%7C1%7C637560184075035141%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000&amp;sdata=R0bQnwYhDarChypX%2BvbTO5CkhG4AIjM%2BD%2FBCLyfP61g%3D&amp;reserved=0
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to