Lots of items to think about.  I always recommend using the tank at the
lowest available level.

   - What is the level of the tank before refilled?
   - Is the tank being utilized for any other purposes.


Reminder - account for the friction loss between the tank and the suction
side of the fire pump.

Thanks,
John

John August Denhardt, PE
*Vice President, Engineering and Technical Services*

*American Fire Sprinkler Association*
m: p: 301-343-1457
214-349-5965 ext 121
w: firesprinkler.org
<https://www.facebook.com/firesprinkler.org/>
<https://twitter.com/afsa/status/1039528345367732224>
<https://www.linkedin.com/company/american-fire-sprinkler-association-afsa-/>
   <https://www.instagram.com/firesprinklerorg/>

*Our members are at the heart of everything we do*


*Train a safer, more efficient workforce.*

By enrolling your employees in the AFSA Apprenticeship Training Series for
Sprinkler Fitters
<https://www.firesprinkler.org/WWW/Education/Apprentice_Training/WWW/Education/Apprenticeship_Training.aspx?hkey=e88ef09e-d74c-407f-abcd-995aff866149>,
you will reap the benefits of a qualified, professional installation crew.
Well-trained employees will work smarter, increasing your company's
productivity and, in turn, its profits. Learn more
<https://www.firesprinkler.org/WWW/Education/Apprentice_Training/WWW/Education/Apprenticeship_Training.aspx?hkey=e88ef09e-d74c-407f-abcd-995aff866149>
.




On Fri, May 7, 2021 at 1:13 PM Kyle.Montgomery via Sprinklerforum <
[email protected]> wrote:

> I'm working on a project where they are adding a new building to an
> existing campus. There is an existing fire water storage tank and fire
> pump  that serves the site underground fire loop. The new building has a
> very demanding sprinkler system that just barely exceeds the fire pump's
> pressure available at the demand flow (using just the pump curve as the
> water supply).
>
> Normally, I would be conservative and use just a few psi as my water
> supply from the tank (as though it were nearly empty). But, is that overly
> conservative? The tank is mounted on the ground, at the same elevation as
> the fire pump, but it is nearly 45 feet tall, with a total capacity of over
> 500,000 gallons. Can I use some of that elevation pressure, or do I need to
> design and calc as though the tank is nearly depleted?
>
> -Kyle M
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to