[Sprinklerforum] Re: Air venting

2023-10-10 Thread Taylor Schumacher
Maybe the steel pipe is at the high point of the system and buried, then, maybe it would be worth it. If you’re trying to solve the corrosion problem, then there’s better ways to accomplish that. Figure the cost of the air vent, the additional maintenance costs for the lifetime of

[Sprinklerforum] Re: Air venting

2023-10-10 Thread Ken Wagoner
Matt, I feel it's worth mentioning that on two floors of the building, the only metallic pipe is ± 25' of Schedule 10, and then in transitions to CPVC. When I expressed the need for venting on those floors, the response was similar to "Nobody else makes us do that!" I still believe that a

[Sprinklerforum] Re: fire sprinkler flow switch

2023-10-10 Thread kevin . farrey
thank you for your input it’s just odd, that 4 risers, 2 work perfectly. 2 have a delay on the first test, then work perfectly after that. _ SprinklerForum mailing list:

[Sprinklerforum] Re: fire sprinkler flow switch

2023-10-10 Thread Skyler Bilbo
This could be several things. Bruce already mentioned one. My next guess is that your backflow spring pressure is being overcome at seemingly random times (this is the backflow differential pressure). The pressure in the system has to drop some (drain off the system side) before any water

[Sprinklerforum] Re: Air venting

2023-10-10 Thread matthew.willis1
To answer your question Todd, The SYSTEM is required to be vented each time the system is drained and refilled. The check valve or physics do not come into play. The 2-story example you provided is only one System. Therefore, if drained, then refilled, it would be the entirety of the System.