Maybe the steel pipe is at the high point of the system and buried, then, maybe 
it would be worth it.

If you’re trying to solve the corrosion problem, then there’s better ways to 
accomplish that. Figure the cost of the air vent, the additional maintenance 
costs for the lifetime of drains/refills/purges of the system? An air vent, 
manual or automatic, isn’t going to purge all of the air out of that system to 
begin with. I’m not sure the upfront cost to save that stick of pipe warrants 
it.

You might try to encourage the designer/installer to change that piece of pipe 
to CPVC…


Taylor Schumacher
Security Fire Sprinkler<http://www.j-berd.com/>
1 Industrial Blvd | Sauk Rapids, MN 56379
Office: 320.656.0847 | Direct: 320.640.7050

From: Ken Wagoner <k...@parsleyconsulting.com>
Sent: Tuesday, October 10, 2023 4:05 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: [Sprinklerforum] Re: Air venting


Caution: This email originated from outside your organization. Please take care 
when clicking links or opening attachments.


Matt,

I feel it's worth mentioning that on two floors of the building, the only 
metallic pipe is ± 25' of Schedule 10, and then in transitions to CPVC.

When I expressed the need for venting on those floors, the response was similar 
to "Nobody else makes us do that!"

I still believe that a means to vent that short segment of steel should be 
provided.  Absent any code/standard guidance to the contrary I'm maintaining 
that position.

sincerely,
Ken Wagoner, SET
Parsley Consulting
500 West Mechanic Street
Harrisonville, Missouri 64701-2235
Phone: (760) 745-6181
Visit the 
website<https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fwww.parsleyconsulting.com%2f&c=E,1,Y5zKJKPEh1mBEBqSR-VE9cUKl5y-eyP8BpvmE_5j9ZqW2eJbNphYzrCMBZ-2YuX6d-RRkHI4gQ1FV-cvOeCfRC58uZS9NiToZv2mx7909oCqLvCW_n5hDHeK&typo=1>
On 10/10/2023 5:58 AM, 
matthew.will...@ferguson.com<mailto:matthew.will...@ferguson.com> wrote:
To answer your question Todd,

The SYSTEM is required to be vented each time the system is drained and 
refilled.
The check valve or physics do not come into play.

The 2-story example you provided is only one System. Therefore, if drained, 
then refilled, it would be the entirety of the System.
Separate Control valves and a drain indicate that only that system would be 
drained then refilled.

It is about corrosion and not drifting air bubbles.

Now, to Taylor’s point about CPVC, what if following the control valve, there 
is 1 foot of SCH10 pipe, then a transition.

Accordig to the book, steel piping is present. So, a vent is required.

R/
Matt

A.16.7<https://link.nfpa.org/publications/13/2022/chapters/16#ID000130006575>
A manual or automatic air venting valve can be a reasonable approach on wet 
pipe sprinkler systems to reduce corrosion activity. The purpose of the air 
venting valve is to exhaust as much trapped air as possible from a single 
location every time the system is filled. The objective of venting is to reduce 
the amount of oxygen trapped in the system that will fuel corrosion and 
microbial activity. It is neither the intent nor practical to exhaust all 
trapped air from a single location on a wet pipe sprinkler system; however, 
more than one vent can be used on a system at the designer's discretion. 
Interconnection of branch line piping for venting purposes is not necessary. An 
inspector's test valve can serve this purpose.
The air venting valve should be located where it will be most effective. System 
piping layout will guide the designer in choosing an effective location for 
venting. In order to effectively accomplish venting, it is necessary to choose 
a location where the greatest volume of trapped air is vented during the first 
fill and each subsequent drain and fill event. The vent connection to the 
system should be located off the top of horizontal piping at a high point in 
the system; however, the vent connection can also be effectively located off 
the side of a riser or riser nipple at a high point in the system.
Manual air venting valves should be accessible. The manual air venting valve 
should be located at an accessible point and preferably not over 7 ft (2.1 m) 
above the floor. Automatic air valves are not required to comply with the 
accessibility requirement of manual air venting valves; however, it is 
recommended the designer locate automatic air vents over areas without 
ceilings, above a lay-in ceiling, or above an access panel.
Each wet pipe sprinkler system should be vented every time the system is filled.



Please rate our customer 
service<https://survey.medallia.com/?emailsignature&fc=3539&bg=Fire%20and%20Fabrication>

Matthew J. Willis, CWBSP, CET
Engineering Manager – Southwest Region
FERGUSON FIRE DESIGN, LLC
A Wholly Owned Subsidiary of Ferguson Fire & Fabrication, LLC
3508 Hwy. 557
West Monroe, LA. 71292
C: 307-236-8249
matthew.will...@ferguson.com<mailto:matthew.will...@ferguson.com>
www.FergusonFire.com<http://www.fergusonfire.com/>


From: Ken Wagoner 
<k...@parsleyconsulting.com><mailto:k...@parsleyconsulting.com>
Sent: Monday, October 9, 2023 7:26 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: [Sprinklerforum] Re: Air venting

I understand and agree Todd, before I shot my mouth of to the layout tech I 
wanted to make sure I was headed in the right direction.

Thank you!
Ken Wagoner, SET
Parsley Consulting
500 West Mechanic Street
Harrisonville, Missouri 64701-2235
Phone: (760) 745-6181
Visit the 
website<https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fwww.parsleyconsulting.com%2f&c=E,1,Y5zKJKPEh1mBEBqSR-VE9cUKl5y-eyP8BpvmE_5j9ZqW2eJbNphYzrCMBZ-2YuX6d-RRkHI4gQ1FV-cvOeCfRC58uZS9NiToZv2mx7909oCqLvCW_n5hDHeK&typo=1>
On 10/9/2023 11:27 AM, Fpdcdesign wrote:
Ken, I think you would have to with the check valve. I would push back a little 
in that by adding a normally open valve and a flow switch or manifold would not 
change the physics of the system enough to warrant the additional vents. If you 
had a 2 story building without zone valves, you would only need one vent. 
However, if you add normally open valves and flow switches, you would now need 
2 (or 3?). From the standpoint of physics, why?

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080<tel:860-535-2080> (ofc)
860-554-7054<tel:860-554-7054>  (fax)
860-608-4559<tel:860-608-4559> (cell)




On Oct 9, 2023 at 12:06 PM, <Ken Wagoner<mailto:k...@parsleyconsulting.com>> 
wrote:
Yes, Todd, on each floor, as they're using a Victaulic UMC manifold which 
includes a check valve.

thanks for the information,
Ken Wagoner, SET
Parsley Consulting
500 West Mechanic Street
Harrisonville, Missouri 64701-2235
Phone: (760) 745-6181
Visit the 
website<https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fwww.parsleyconsulting.com%2f&c=E,1,Y5zKJKPEh1mBEBqSR-VE9cUKl5y-eyP8BpvmE_5j9ZqW2eJbNphYzrCMBZ-2YuX6d-RRkHI4gQ1FV-cvOeCfRC58uZS9NiToZv2mx7909oCqLvCW_n5hDHeK&typo=1>
On 10/9/2023 10:49 AM, Fpdcdesign wrote:
Is there a check valve on the floor control assembly?

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080<tel:860-535-2080> (ofc)
860-554-7054<tel:860-554-7054>  (fax)
860-608-4559<tel:860-608-4559> (cell)




On Oct 9, 2023 at 11:44 AM, <Ken Wagoner<mailto:k...@parsleyconsulting.com>> 
wrote:
Forumites,

I'm working on a multi-story building protected per NFPA 13.  As each floor has 
a separate control valve, is a means to vent trapped air required on each 
floor?  Or is it only required at the highest level of the building?

My thinking is that each floor has a separate fire sprinklers system.

Any thoughts?
Ken Wagoner, SET
Parsley Consulting
500 West Mechanic Street
Harrisonville, Missouri 64701-2235
Phone: (760) 745-6181
Visit the 
website<https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fwww.parsleyconsulting.com%2f&c=E,1,Y5zKJKPEh1mBEBqSR-VE9cUKl5y-eyP8BpvmE_5j9ZqW2eJbNphYzrCMBZ-2YuX6d-RRkHI4gQ1FV-cvOeCfRC58uZS9NiToZv2mx7909oCqLvCW_n5hDHeK&typo=1>

_________________________________________________________ SprinklerForum 
mailing list: 
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org To 
unsubscribe send an email to 
sprinklerforum-le...@lists.firesprinkler.org<mailto:sprinklerforum-le...@lists.firesprinkler.org>




_________________________________________________________

SprinklerForum mailing list:

https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org

To unsubscribe send an email to 
sprinklerforum-le...@lists.firesprinkler.org<mailto:sprinklerforum-le...@lists.firesprinkler.org>

_________________________________________________________ SprinklerForum 
mailing list: 
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org To 
unsubscribe send an email to 
sprinklerforum-le...@lists.firesprinkler.org<mailto:sprinklerforum-le...@lists.firesprinkler.org>






_________________________________________________________

SprinklerForum mailing list:

https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org

To unsubscribe send an email to 
sprinklerforum-le...@lists.firesprinkler.org<mailto:sprinklerforum-le...@lists.firesprinkler.org>






_________________________________________________________

SprinklerForum mailing list:

https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org

To unsubscribe send an email to 
sprinklerforum-le...@lists.firesprinkler.org<mailto:sprinklerforum-le...@lists.firesprinkler.org>