We have a contractor that is refusing to flush the UG pipe prior to tie in
because he "has never done it in 20 years". I can find something in NFPA 13R
that requires a flush but nothing in 13D.. Anyone have any insight on why
its not required in 13D?
Rocci Cetani III, CET
Senior Designer
W
separate sheets and taking out graphics on
forms.
Taylor Schumacher
-Original Message-
From: Sprinklerforum On Behalf
Of Rocci 3 Cetani via Sprinklerforum
Sent: Wednesday, November 17, 2021 5:22 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Rocci 3 Cetani ; Fpdcdesign
Subject: RE
Todd,
We want them to be able to mark up changes on plans ( they will still have a
paper copy of plans) but on projects that are congested and 1/8" scale we want
them to be able to zoom in for clarification. We also want to be able to load
all of our forms on there so they can do paper work st
77d19bafe511-257C0-257C0-257C636379016677342180-26sdata-3DeGdMZGu2wXhUupGwgGTrqF3b54OP5-252BAZvlHhABSexWY-253D-26reserved-3D0&d=DwICAg&c=euGZstcaTDllvimEN8b7jXrwqOf-v5A_CdpgnVfiiMM&r=hLXh1DXRDwJ3oz4y7iNesSsetYhUUV0wawfPGfwmYxQ&m=-a9TTSMWkj7wLyyL4EuRnaT_bY4FzgE4SWLFKw0yORU&s=I65Ynl8ZAVrcl0th
Ok hopefully this is allowed, if not I apologize. So our company is in the
process of going paperless and we are trying to find software (compatible with
iPads) where we can share files/plans between the office staff and our fitters.
We would like to have them be able to edit the files or ma
NFPA 13 8.17.2.4.7.1 says the lettering needs to be at least 1" in height on
plate or fitting reading service design. Is this just referring to "FDC
AUTOSPRINK" or should every letter on the sign (address) be min. 1" in height?
Rocci Cetani III, CET
Senior Designer
Water-Based Fire Protections S
We run into this all the time, we have a code interpretation from the state
fire marshal (California) stating a system is deficient if its missing it.
Rocci Cetani III, CET
Senior Designer
Water-Based Fire Protections Systems Layout, Nicet Level III
Northern California Fire Protection Services
I don't see a 12.1.11.2.2
But for a floor mounted obstruction you should be using figure 8.10.6.2.2
Rocci Cetani III, CET
Senior Designer
Water-Based Fire Protections Systems Layout, Nicet Level III
Northern California Fire Protection Services Inc.
16840 Joleen Way Bldg. A
Morgan Hill, CA 93037
Only problem is its vague and I think the committee did that on purpose. “minor
quantities” is up for too much interpretation
Rocci Cetani III, CET
Senior Designer
Water-Based Fire Protections Systems Layout, Nicet Level III
Northern California Fire Protection Services Inc.
16840 Joleen Way Bld
This one is intriguing to me If chapter 13 designates it an OH2 shouldn't a
system be allowed to be @ 52,000 sqft regardless of rack storage?
Rocci Cetani III, CET
Senior Designer
Water-Based Fire Protections Systems Layout, Nicet Level III
Northern California Fire Protection Services Inc.