RE: COMBUSTIBLE CEILING SPACE

2019-09-21 Thread cliff--- via Sprinklerforum
@lists.firesprinkler.org Cc: Matthew J Willis ; Travis Mack Subject: Re: COMBUSTIBLE CEILING SPACE Allow me to associate myself with Mr. Mack's position. Matt On the road.. _ From: Sprinklerforum mailto:sprinklerforum-boun...@lists.firesprinkler.org> > on behalf of Travis Mack via Spr

Re: COMBUSTIBLE CEILING SPACE

2019-09-21 Thread Matthew J Willis via Sprinklerforum
t: Re: COMBUSTIBLE CEILING SPACE In that case I go from floor to deck to apply QR reduction. Travis Mack, CFPS, CWBSP, RME-G, SET 480-505-9271 MFP Design, LLC www.mfpdesign,com Send large files to MFP Design via: https://www.hightail.com/u/MFPDesign Sent from my iPhone On Sep 20, 2019, at 6:57 PM

Re: COMBUSTIBLE CEILING SPACE

2019-09-20 Thread Travis Mack via Sprinklerforum
0:04 PM >> To: 'Phillips, Mark' ; >> sprinklerforum@lists.firesprinkler.org >> ; vi...@wtfp.net >> Cc: Matthew J Willis >> Subject: RE: COMBUSTIBLE CEILING SPACE >> >> I think with cloud ceilings, you will need to go from the floor. With full

Re: COMBUSTIBLE CEILING SPACE

2019-09-20 Thread Ron Greenman via Sprinklerforum
g < > sprinklerforum@lists.firesprinkler.org>; vi...@wtfp.net > *Cc:* Matthew J Willis > *Subject:* RE: COMBUSTIBLE CEILING SPACE > > > *I think with cloud ceilings, you will need to go from the floor. With > full ceilings, you can use the ceiling as the floor

Re: COMBUSTIBLE CEILING SPACE

2019-09-20 Thread Matthew J Willis via Sprinklerforum
Mark' ; sprinklerforum@lists.firesprinkler.org ; vi...@wtfp.net Cc: Matthew J Willis Subject: RE: COMBUSTIBLE CEILING SPACE I think with cloud ceilings, you will need to go from the floor. With full ceilings, you can use the ceiling as the floor level. That may be a good one for an A

RE: COMBUSTIBLE CEILING SPACE

2019-09-20 Thread Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
g after the sweetness of low price is forgotten.” From: Phillips, Mark Sent: Friday, September 20, 2019 5:00 PM To: sprinklerforum@lists.firesprinkler.org; vi...@wtfp.net Cc: Matthew J Willis ; Travis Mack, SET, CFPS, CWBSP, RME-G Subject: Re: COMBUSTIBLE CEILING SPACE Is there any co

Re: COMBUSTIBLE CEILING SPACE

2019-09-20 Thread Phillips, Mark via Sprinklerforum
lerforum Date: 9/20/19 7:49 PM (GMT-05:00) To: sprinklerforum@lists.firesprinkler.org, vi...@wtfp.net Cc: Matthew J Willis , "Travis Mack, SET, CFPS, CWBSP, RME-G" Subject: Re: COMBUSTIBLE CEILING SPACE Caution: This email originated from outside the organization. Do not click links o

Re: COMBUSTIBLE CEILING SPACE

2019-09-20 Thread Matthew J Willis via Sprinklerforum
: Travis Mack, SET, CFPS, CWBSP, RME-G Subject: RE: COMBUSTIBLE CEILING SPACE It is my understanding you can use the ceiling with the pendent sprinklers as the floor level when measuring the QR reduction. [MFP_logo_F]<http://www.mfpdesign.com/> Travis Mack, CFPS, CWBSP, RME-G, SET MFP Desig

RE: COMBUSTIBLE CEILING SPACE

2019-09-20 Thread Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
From: Sprinklerforum On Behalf Of Vince Sabolik via Sprinklerforum Sent: Friday, September 20, 2019 4:46 PM To: Vince Sabolik via Sprinklerforum Cc: Vince Sabolik Subject: Re: COMBUSTIBLE CEILING SPACE Thanks, guys. I thought similar. Why do you suppose the height applies from the flo

Re: COMBUSTIBLE CEILING SPACE

2019-09-20 Thread Phillips, Mark via Sprinklerforum
gh Dr, Raleigh, NC 27617 Original message From: Vince Sabolik via Sprinklerforum Date: 9/20/19 7:36 PM (GMT-05:00) To: sprinklerforum@lists.firesprinkler.org Cc: Vince Sabolik Subject: COMBUSTIBLE CEILING SPACE Caution: This email originated from outside the organization. Do not

RE: COMBUSTIBLE CEILING SPACE

2019-09-20 Thread Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
y, September 20, 2019 4:37 PM To: sprinklerforum@lists.firesprinkler.org Cc: Vince Sabolik Subject: COMBUSTIBLE CEILING SPACE The area above the ceiling requires protection. Is the reduced area (use of QR) applicable? -- Vince Sabolik West Tech Fire Protection, Inc. 11351 Pearl Road /

COMBUSTIBLE CEILING SPACE

2019-09-20 Thread Vince Sabolik via Sprinklerforum
The area above the ceiling requires protection. Is the reduced area (use of QR) applicable? -- *Vince Sabolik* *West Tech Fire Protection, Inc.*** 11351 Pearl Road   /   Strongsville, Ohio   44136 Phone 440 238-4800    Fax 440 238-4876   Cell 440 724-7601

RE: Sloped combustible ceiling space

2008-01-28 Thread art
rum@firesprinkler.org Subject: Sloped combustible ceiling space I'm reviewing a design for a wet system in a sloped combustible ceiling space. The 12:3 sloped roof is supported on wood trusses. There is drywall at the bottom of the wood trusses and the insulation is on the roof. The roof peak is

RE: Sloped combustible ceiling space

2008-01-27 Thread A.P.Silva
feet, allowing the 40% reduction. Tony -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Parsley Consulting Sent: January 27, 2008 4:25 PM To: sprinklerforum@firesprinkler.org Subject: Re: Sloped combustible ceiling space Tony, I think you're headed in

Re: Sloped combustible ceiling space

2008-01-27 Thread Parsley Consulting
0.745.6181 voice* *760.745.0537 fax* *www.parsleyconsulting.com <http://www.parsleyconsulting.com/>* * * A.P.Silva wrote: I'm reviewing a design for a wet system in a sloped combustible ceiling space. The 12:3 sloped roof is supported on wood trusses. There is drywall at the bottom of the wood

RE: Sloped combustible ceiling space

2008-01-27 Thread Ed Kramer
rg Subject: Sloped combustible ceiling space I'm reviewing a design for a wet system in a sloped combustible ceiling space. The 12:3 sloped roof is supported on wood trusses. There is drywall at the bottom of the wood trusses and the insulation is on the roof. The roof peak is about 16 feet high.

Sloped combustible ceiling space

2008-01-27 Thread A.P.Silva
I'm reviewing a design for a wet system in a sloped combustible ceiling space. The 12:3 sloped roof is supported on wood trusses. There is drywall at the bottom of the wood trusses and the insulation is on the roof. The roof peak is about 16 feet high. There is a wet sprinkler system i