Re: Dry system return bend - aux drain needed?

2017-03-30 Thread Roland Huggins
Another one of those things are are assumed to be understood. Since the return bend is not in an area that is subject to freezing, we don’t worry about getting the water out. Having said that, with the new emphasize on corrosion, that’s a problem. It’s still allowed but needs to be

Re: Dry system return bend - aux drain needed?

2017-03-29 Thread Forest Wilson
What a horrible waste of time. Hopefully this wasnt your local government inspector asking this. If so, you should call the mayor and ask to be reimbursed. Of course you dont need a drain on every sprinkler. On Fri, Mar 3, 2017 at 1:49 PM, Dewayne Martinez < dmarti...@total-mechanical.com> wrote:

RE: Dry system return bend - aux drain needed?

2017-03-03 Thread Matthew J Willis
3 Cell-605.391.2733 Fax:-605.348.0108 [cid:image001.png@01D159E8.1A3A2D00] From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Dewayne Martinez Sent: Friday, March 3, 2017 11:50 AM To: sprinklerforum@lists.firesprinkler.org Subject: Dry system return bend - aux

Dry system return bend - aux drain needed?

2017-03-03 Thread Dewayne Martinez
NFPA 13 (07ed) Section 8.16.2.5.3.3 states that aux drains are not required for pipe drops supplying dry-pendant sprinklers installed per 7.2.2 7.2.2 address both listed dry type sprinklers and pendant sprinklers installed on a return bend in a heated space I have someone questioning if aux