Re: diesel exhaust insulation

2018-10-18 Thread John Denhardt
Check the data sheet for the engine from Clarke or whoever else is supplying the engine. It will list the maximum exhaust temperature. Start with that and talk to an insulation company for a recommendation. Make sure the insulation is rated for the maximum temperature. You do not want to know

diesel exhaust insulation

2018-10-18 Thread Matt Grise
We are getting ready to insulate the exhaust pipes for a diesel motor pump. Is there a particular style or type of insulation that works better than others? Thanks! Matt ___ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org

Re: Exhaust Insulation

2007-12-16 Thread Frans Stoop
Yes, there is good other reason: NFPA 20 - 2007 par. 11.3.2.1: Ventilation shall be provided for the following functions: (1) To control the maximum temperature to 120°F (49°C) at the combustion air cleaner inlet with engine running at rated load Uninsulated exhaust(s) and muffler(s)

Exhaust Insulation

2007-12-15 Thread å... ....
if the exhaust is run at the overhead, and there is no potential for burns from that run, then what other guard would we need, beyond the air gap? scot deal excelsior fire engineering I'm more interested in what everyone else is using. The standard is very vague: 11.5.3.3 The exhaust pipe shall

Re: Exhaust Insulation

2007-12-15 Thread Forestfwl
THE INSULATION IS ONLY USED TO PROTECT PEOPLE FROM BURNS. YOU DO NOT NEED IT IF IT IS RAN OVERHEAD; FOREST CHEROKEE FIRE In a message dated 12/15/2007 9:51:19 A.M. Eastern Standard Time, [EMAIL PROTECTED] writes: if the exhaust is run at the overhead, and there is no potential

Re: Exhaust Insulation

2007-12-15 Thread douglas hicks
3M has a product used to insulate commercial kitchen exhaust duct. Two layers of the material is rated for zero clearance to combustibles. The insulation is available in 24 inch and 48 inch by 20 foot lengths. Douglas Hicks General Fire Equipment Co of Eastern Oregon, Inc

Exhaust Insulation

2007-12-14 Thread Ryan Peterson
Can anyone recommend a product for insulating diesel fire pump exhaust? Thank you, Ryan Peterson Wayne Automatic Fire Sprinklers, Inc. ___ Sprinklerforum mailing list Sprinklerforum@firesprinkler.org

Exhaust Insulation

2007-12-14 Thread å... ....
why not use rock wool / mineral wool? It is commonly used in UL listed Perimeter Fire Containment Systems. One problem is vibrations and consequent shaking of material loose. Frangible fibers below 10 microns get stuck in the alveolars and might / probably cause cancer (like asbestos, though