why not use rock wool / mineral wool?  It is
commonly used in UL listed Perimeter Fire
Containment Systems.  One problem is
vibrations and consequent shaking of material
loose.  Frangible fibers below 10 microns get
stuck in the alveolars and might / probably
cause cancer (like asbestos, though that
is my guess only).   So I would wrap
it tight.  the other option is to do what the
mechanical trades do with ducts running
vertically between floors:  wrap
it in a 1 hour chase (5/8 inch Type X rock)
with minimum 18 inch clearance from combustible
framing and have maintenance inspection ports.

would not semi- muffler shops have something
more finely tuned to your challenge, though?

scot deal
excelsior fire


On 12/13/07, Ryan Peterson <[EMAIL PROTECTED]> wrote:
>
> Can anyone recommend a product for insulating diesel fire pump exhaust?
>