Subject: Fire Flow vs Hydraulic calc's
Can someone please put into laymen's terms the difference between doing a fire
flow demand calc for the underground and the hydraulic calc's for the sprinkler
system? We have been running into some projects lately where
@lists.firesprinkler.org
Subject: RE: Fire Flow vs Hydraulic calc's
Fire flow is a term and issue not often addressed by A/E and fire protection
engineers.
Fire Flow is a requirement within the IFC, Section 507.3 to be specific.
There are numerous methods available to use to determine Fire Flow
Can someone please put into laymen's terms the difference between doing a fire
flow demand calc for the underground and the hydraulic calc's for the sprinkler
system? We have been running into some projects lately where the civil engineer
tries to pawn sizing the underground off onto the
: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Duane Johnson
Sent: Tuesday, December 22, 2015 1:48 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Fire Flow vs Hydraulic calc's
To add, the fire flow is based on construction type, building height/area
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Brian Harris
Sent: Tuesday, December 22, 2015 12:47 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Fire Flow vs Hydraulic calc's
Can someone please put into laymen's terms the difference between doing a fire
flow demand
Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Brian Harris
Sent: Tuesday, December 22, 2015 1:47 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Fire Flow vs Hydraulic calc's
*** SCDLLR NOTICE *** This email is from an external email address. Please use
7 ph
913.888.0618 f
913.526.7443 cell
www. AFPsprink.com
-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Brian Harris
Sent: Tuesday, December 22, 2015 12:47 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Fire Flow vs Hydra
-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Ron Fletcher
Sent: Tuesday, December 22, 2015 2:14 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Fire Flow vs Hydraulic calc's
It's in Appendix B of IFC and is definitely in the realm
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Brian Harris
Sent: Tuesday, December 22, 2015 2:13 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Fire Flow vs Hydraulic calc's
Peter-
Much appreciated.
Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Brian Harris
Sent: Tuesday, December 22, 2015 1:55 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Fire Flow vs Hydraulic calc's
Definitely out of our control but I was looking for the differences between the
(2) calculations. I
Office
301-455-0010 Cell
-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Matt Grise
Sent: Tuesday, December 22, 2015 1:50 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Fire Flow vs Hydraulic calc's
Check the IBC/IFC
It's in Appendix B of IFC and is definitely in the realm of A/E team. Fire
flow, hydrant spacing etc.. Is required for building permits (usually) and the
fire line size should have been determined well before a sprinkler contractor
was involved.
Sent from my iPhone
> On Dec 22, 2015, at 1:46
@lists.firesprinkler.org
Subject: Re: Fire Flow vs Hydraulic calc's
You can tell them they need a 20" line and that they might want to have the
architect verify your findings.
.
On Tue, Dec 22, 2015 at 12:17 PM, Brian Harris <bhar...@bvssystemsinc.com>
wrote:
> Ron-
> I totally
ete Schwab
Sent: Tuesday, December 22, 2015 1:59 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Fire Flow vs Hydraulic calc's
See NFPA 13 2016 Edition A.11.1.4.2
Peter Schwab
VP of Purchasing and Engineering technologies
Wayne Automatic Fire Sprinklers Inc.
222 Capitol Court
Ocoee, Fl 347
--
> From: Sprinklerforum [mailto:
> sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Ron Fletcher
> Sent: Tuesday, December 22, 2015 2:14 PM
> To: sprinklerforum@lists.firesprinkler.org
> Subject: Re: Fire Flow vs Hydraulic calc's
>
> It's in Appendix B of IFC and is definitely in the r
: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Matt Grise
Sent: Tuesday, December 22, 2015 1:50 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Fire Flow vs Hydraulic calc's
Check the IBC/IFC (index... not sure what section). Fire Flow is the amount
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Fire Flow vs Hydraulic calc's
See NFPA 13 2016 Edition A.11.1.4.2
Peter Schwab
VP of Purchasing and Engineering technologies
Wayne Automatic Fire Sprinklers Inc.
222 Capitol Court
Ocoee, Fl 34761
Mobile: (407) 468-8248
Direct: (407) 877-5570
Fax
Subject: RE: Fire Flow vs Hydraulic calc's
Brian
A.11.1.4.2 Appropriate area/density, other design criteria, and water supply
requirements should be based on scientifically based engineering analyses that
can include submitted fire testing, calculations, or results from appropriate
computational