RE: Parking Garage Sprinkler System *** THANKS!

2008-02-04 Thread Reza Esmaeili
Thanks to all for helping me with my question, according to your valuable comments I concluded that I should try the followings: I think an option is talking to a well known sprinkler manufacture to see if they can offer an extended coverage sprinkler suitable for my application, which

Re: Parking Garage Sprinkler System

2008-02-01 Thread Todd Williams - FPDC
One more thing, make sure that your churn pressure on the pump plus the elevation gain going down the two levels does not exceed 175 psi. This may be the pressure the system feels when the system first trips (or in the case of an accidental trip) At 11:17 AM 1/31/2008, you wrote: Hi All,

RE: Parking Garage Sprinkler System ***

2008-02-01 Thread Reza Esmaeili
Dears friends Craig, Travis, Kurt Todd, Many thanks for your detailed answer, your answers were very helpful,. I will use the sprinkler piping for my fire hoses to save some pipe, after calculation, the water velocity in piping is about 20 ft/s and the capacity of sprinkler piping in each

RE: Parking Garage Sprinkler System

2008-02-01 Thread Reza Esmaeili
Mike, Thanks for your kind email, I would be very grateful if you send it to me, it is a real pleasure to have help from an expert in Reliable Sprinkler. Please send to [EMAIL PROTECTED] Thanks, Reza Mike Brown (TECH- GVL) [EMAIL PROTECTED] wrote: If you would like one I will send you a

RE: Parking Garage Sprinkler System ***

2008-02-01 Thread George Church
@firesprinkler.org Subject: RE: Parking Garage Sprinkler System *** Depending on where your riser is in relation to the remote part of your system you may have to have multiple systems to deal with the time factor. It's a bit hard to determine without actually seeing everything you're seeing. Make

RE: Parking Garage Sprinkler System

2008-02-01 Thread Mike Brown (TECH- GVL)
If you would like one I will send you a copy of my Rules of Thumb for designing large dry systems. You can contact me off line at [EMAIL PROTECTED] MLB -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Reza Esmaeili Sent: Thursday, January 31, 2008 11:17

RE: Parking Garage Sprinkler System ***

2008-02-01 Thread Craig.Prahl
: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Reza Esmaeili Sent: Friday, February 01, 2008 10:48 AM To: sprinklerforum@firesprinkler.org Subject: RE: Parking Garage Sprinkler System *** Thanks Craig, As I am connecting fire hoses to my sprinkler system, then the system pressure would

Re: Parking Garage Sprinkler System

2008-02-01 Thread Jim . Roberts
Forumites: It's not often that we all get to see the fruits of our labors. In 1986 I designed a dry pipe system for a 7-8 level parking garage for a high riser building. 14 years later I had an NSPE state convention, which my Piedmont Chapter was sponsoring. While there a car caught fire

Re: Parking Garage Sprinkler System ***

2008-02-01 Thread Ron Greenman
Garage Sprinkler System *** Depending on where your riser is in relation to the remote part of your system you may have to have multiple systems to deal with the time factor. It's a bit hard to determine without actually seeing everything you're seeing. Make the electrical guy move his

RE: Parking Garage Sprinkler System ***

2008-02-01 Thread Reza Esmaeili
-0491 Direct - 864.599.4102 Fax - 864.599.8439 [EMAIL PROTECTED] http://www.lg.com -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Reza Esmaeili Sent: Friday, February 01, 2008 9:40 AM To: sprinklerforum@firesprinkler.org Subject: RE: Parking Garage

RE: Parking Garage Sprinkler System ***

2008-02-01 Thread Sal Izzo (TECH- 103)
@firesprinkler.org Subject: RE: Parking Garage Sprinkler System *** Thanks Craig, As I am connecting fire hoses to my sprinkler system, then the system pressure would be high to comply with NFPA-14 minimum residual pressure requirements at the outlet of most remote 1 1/2 in. hose station which

Re: Parking Garage Sprinkler System ***

2008-02-01 Thread Joe Hankins
Direct - 864.599.4102 Fax - 864.599.8439 [EMAIL PROTECTED] http://www.lg.com -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Reza Esmaeili Sent: Friday, February 01, 2008 9:40 AM To: sprinklerforum@firesprinkler.org Subject: RE: Parking Garage Sprinkler System

Re: Parking Garage Sprinkler System ***

2008-02-01 Thread steve
Wireless BlackBerry -Original Message- From: Reza Esmaeili [EMAIL PROTECTED] Date: Fri, 1 Feb 2008 07:48:02 To:sprinklerforum@firesprinkler.org Subject: RE: Parking Garage Sprinkler System *** Thanks Craig, As I am connecting fire hoses to my sprinkler system, then the system pressure

RE: Parking Garage Sprinkler System ***

2008-02-01 Thread art
. Should be separate standpipe system if required. -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Reza Esmaeili Sent: Friday, February 01, 2008 10:48 AM To: sprinklerforum@firesprinkler.org Subject: RE: Parking Garage Sprinkler System *** Thanks Craig, As I

RE: Parking Garage Sprinkler System ***

2008-02-01 Thread George Church
: RE: Parking Garage Sprinkler System *** I believe NFPA 13 allows the use of small orifice sprinklers on light hazard, wet systems only. Salvatore Izzo, P.E. Relible Automatic Sprinkler Company, Inc. From: [EMAIL PROTECTED] on behalf of Reza Esmaeili Sent

RE: Parking Garage Sprinkler System ***

2008-02-01 Thread Todd Williams - FPDC
Reza, If it doesn't work and you have to install two extra dry valves, that would most likely be a very expensive operation. Is it worth the chance? As Clint Eastwood once said, Do you feel lucky? Todd At 09:40 AM 2/1/2008, you wrote: Dears friends Craig, Travis, Kurt Todd, Many

Re: Parking Garage Sprinkler System /FDT program

2008-02-01 Thread Todd Williams - FPDC
, 2008 8:35 AM Subject: Re: Parking Garage Sprinkler System *** Consider low pressure DPVs if you have no way to determine trip time (the expensive program). low pressure DPVs work on about a 30:1 differential rather than the more typical 6:1. On Feb 1, 2008 7:06 AM, George Church [EMAIL

RE: Parking Garage Sprinkler System /FDT program

2008-02-01 Thread Travis Mack, SET
- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Todd Williams - FPDC Sent: Friday, February 01, 2008 9:53 AM To: sprinklerforum@firesprinkler.org Subject: Re: Parking Garage Sprinkler System /FDT program How accurate is the FDT program based on comparison to field tests? At 11:27

Re: Parking Garage Sprinkler System /FDT program

2008-02-01 Thread Thom McMahon
Fax: 970-879-7926 - Original Message - From: Todd Williams - FPDC [EMAIL PROTECTED] To: sprinklerforum@firesprinkler.org Sent: Friday, February 01, 2008 9:52 AM Subject: Re: Parking Garage Sprinkler System /FDT program How accurate is the FDT program based on comparison to field tests

RE: Parking Garage Sprinkler System ***

2008-02-01 Thread Mike Brown (TECH- GVL)
PROTECTED] On Behalf Of Reza Esmaeili Sent: Friday, February 01, 2008 10:48 AM To: sprinklerforum@firesprinkler.org Subject: RE: Parking Garage Sprinkler System *** Thanks Craig, As I am connecting fire hoses to my sprinkler system, then the system pressure would be high to comply with NFPA-14

RE: Parking Garage Sprinkler System /FDT program

2008-02-01 Thread George Church
Glc Putting it in perspective -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Thom McMahon Sent: Friday, February 01, 2008 1:34 PM To: sprinklerforum@firesprinkler.org Subject: Re: Parking Garage Sprinkler System /FDT program FDT is the base program

RE: Parking Garage Sprinkler System

2008-01-31 Thread Kurt Kingston
Reza, A few random comments: 2- When we have the pressure and flows available the Tyco EC uprights (like EC-11) have worked out well on a few recent jobs but you really start accumulating over discharge on the branch lines quickly with the higher end head pressures. That issue also tends to fight

RE: Parking Garage Sprinkler System

2008-01-31 Thread Craig.Prahl
Reza, 1- What is your recommended Area of sprinkler operation and Density for my application after determining from the Density/Area curve? ANSWER: .15/1500 works but don't forget to increase the design area by 30% due to it being a dry system. So you would have .15/1950 sq. ft 2-