If you're still concerned about pressure you can get higher pressure rated
sprinkler heads as well for a minor extra cost. I believe Reliable has most
of their sprinklers rated to 250 PSI now? (Double check that)
On Sat, Sep 15, 2018 at 3:15 AM Douglas Hicks wrote:
>
> what is the failure rate
what is the failure rate of SR heads at 50 years and 75 years? 1 % or 95% ?
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesp
If it is 175, I want the PRV to release before that.
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of John Irwin
Sent: Friday, September 14, 2018 5:23 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: [EXTERNAL] RE: Sprinkler heads popping off randoml
ehalf Of *John Irwin
> *Sent:* Friday, September 14, 2018 5:23 PM
>
>
> *To:* sprinklerforum@lists.firesprinkler.org
> *Subject:* RE: [EXTERNAL] RE: Sprinkler heads popping off randomly
>
>
>
> Is there a fire pump on the system? I mean you cant just pick a pressure
>
want the PRV to release before that.
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of John Irwin
Sent: Friday, September 14, 2018 5:23 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: [EXTERNAL] RE: Sprinkler heads popping off randomly
Is there
nt: Friday, September 14, 2018 11:01 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: [EXTERNAL] RE: Sprinkler heads popping off randomly
If the sprinklers weren’t 50 years old, I would be on board with you 100%. But
in this case, even if they determine there was a manufacturing
m:* Sprinklerforum [mailto:
> sprinklerforum-boun...@lists.firesprinkler.org] *On Behalf Of *Scott
> Futrell
> *Sent:* Friday, September 14, 2018 9:13 AM
>
>
> *To:* sprinklerforum@lists.firesprinkler.org
> *Subject:* RE: [EXTERNAL] RE: Sprinkler heads popping off randomly
>
] RE: Sprinkler heads popping off randomly
Sorry, my last words.
Some of you have concluded its pressure. What does replacing them all do to fix
the pressure.
Some of you have concluded age.
Others creep.
I don’t remember me writing this is age, or manufacturing, did I? I wrote that
all
:01 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: [EXTERNAL] RE: Sprinkler heads popping off randomly
If the sprinklers weren’t 50 years old, I would be on board with you 100%. But
in this case, even if they determine there was a manufacturing defect, wouldn’t
the “statute of
t to see the results of piece-meal far too often.
>
>
>
> Scott
>
>
>
> Office: (763) 425-1001 x 2
>
> Cell: (612) 759-5556
>
>
>
> *From:* Sprinklerforum [
> mailto:sprinklerforum-boun...@lists.firesprinkler.org
> ] *On Behalf Of *Kyle
> Montgom
? That’s all I’m trying
to get at.
-Kyle M
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Scott Futrell
Sent: Friday, September 14, 2018 8:47 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: [EXTERNAL] RE: Sprinkler heads popping off randomly
I
: sprinklerforum@lists.firesprinkler.org
Subject: RE: [EXTERNAL] RE: Sprinkler heads popping off randomly
Please read thoroughly and carefully all of the emails I posted and don’t start
picking at one aspect.
It can be done properly or it can be done piece-meal. I don’t care.
What’s the cost of one more
...@lists.firesprinkler.org] On
Behalf Of Scott Futrell
Sent: Friday, September 14, 2018 10:28 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: [EXTERNAL] RE: Sprinkler heads popping off randomly
Please read thoroughly and carefully all of the emails I posted and don’t start
picking at one aspect.
It can
er.org>>
Subject: Re: Sprinkler heads popping off randomly
Contact the sprinkler contractor that services you systems. That should be able
to steer you in the right direction. They can be added at the riser and will
prevent over pressurization
On Sep 13, 2018 at 8:48 PM, mailto:larry.stew...@e
2018 7:57 PM
To: Sprinklerforum
mailto:sprinklerforum@lists.firesprinkler.org>>
Subject: Re: Sprinkler heads popping off randomly
Contact the sprinkler contractor that services you systems. That should be able
to steer you in the right direction. They can be added at the riser and will
prevent over pres
s. Is that the
> solution here, most likely, no.
>
>
>
> Scott
>
>
>
> Office: (763) 425-1001 x2
>
> Cell: (612) 759-5556
>
>
>
> *From:* Sprinklerforum [mailto:
> sprinklerforum-boun...@lists.firesprinkler.org] *On Behalf Of *Fpdcdesign
> *Sent
>
>
>
> Office: (763) 425-1001 x2
>
>
>
> Cell: (612) 759-5556
>
>
>
>
>
>
>
>
>
>
> From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
> On Behalf Of Fpdcdesign
> Sent: Thursda
nklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Larry Block, Property Manager
Sent: Thursday, September 13, 2018 8:20 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: [EXTERNAL] RE: Sprinkler heads popping off randomly
Do the new, non glass-tube heads still ha
t;> Office: (763) 425-1001 x2
>>> Cell: (612) 759-5556
>>>
>>> From: Sprinklerforum
>>> [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of
>>> Fpdcdesign
>>> Sent: Thursday, September 13, 2018 7:57 PM
>>> To: Sprinklerforum
;> Office: (763) 425-1001 x2
>> Cell: (612) 759-5556
>>
>> From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
>> On Behalf Of Fpdcdesign
>> Sent: Thursday, September 13, 2018 7:57 PM
>> To: Sprinklerforum
>> Subject: Re: Sprinkler heads
nklerforum
Subject: Re: Sprinkler heads popping off randomly
A relief vale would be a good place to start. That could tell you if it is a
pressure or temperature problem.
On Sep 13, 2018 at 6:29 PM, mailto:larry.stew...@earthlink.net>> wrote:
Blown heads have been located at branch ends, so
How do you get a building built in 67 that needs a 50 year test in 4 years when
it is already 51 years old. Maybe it’s just time to change the heads.
Bill
Sent from my iPhone
> On Sep 13, 2018, at 6:32 PM, Jamie Seidl wrote:
>
> To me this sounds like classic Solder creep. The solder softens
Can I install 200 F non glass heads?
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Jamie Seidl
Sent: Thursday, September 13, 2018 6:33 PM
To: Sprinklerforum
Subject: Re: Sprinkler heads popping off randomly
To me this sounds like classic Solder creep
To me this sounds like classic Solder creep. The solder softens furring
warm conditions, and after many many (years) of hot days, you start to have
heads pop as the solder has finally given in to the pressure it has been
holding back. I think your correction on this would be glass bulb
sprinkler
.firesprinkler.org]
> On Behalf Of Bruce Verhei
> Sent: Thursday, September 13, 2018 6:03 PM
> To: sprinklerforum@lists.firesprinkler.org
> Subject: Re: Sprinkler heads popping off randomly
>
> Tom mentioned a pilot valve pressure relief valve. Presumably adjustable.
> O
Thanks Bruce, I will ck out a pilot PRV.
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Bruce Verhei
Sent: Thursday, September 13, 2018 6:03 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Sprinkler heads popping off randomly
Tom mentioned a
Thanks FPDC
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Fpdcdesign
Sent: Thursday, September 13, 2018 5:57 PM
To: Sprinklerforum
Subject: Re: Sprinkler heads popping off randomly
Contact the sprinkler contractor that services you systems. That
y? … and starts dripping for no reason? J
>
>
> From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
> On Behalf Of Fpdcdesign
> Sent: Thursday, September 13, 2018 5:31 PM
> To: Sprinklerforum
> Subject: Re: Sprinkler heads popping off randomly
>
) 759-5556
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Fpdcdesign
Sent: Thursday, September 13, 2018 7:57 PM
To: Sprinklerforum
Subject: Re: Sprinkler heads popping off randomly
Contact the sprinkler contractor that services you systems. That should be
>
>
>
>
>
>
> From: Sprinklerforum
> [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of
> Fpdcdesign
> Sent: Thursday, September 13, 2018 5:31 PM
> To: Sprinklerforum
> Subject: Re: Sprinkler heads popping off randomly
759-5556
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Larry Block, Property Manager
Sent: Thursday, September 13, 2018 7:37 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Sprinkler heads popping off randomly
Scott, will the 50 year testing expose
: Sprinklerforum
Subject: Re: Sprinkler heads popping off randomly
A relief vale would be a good place to start. That could tell you if it is a
pressure or temperature problem.
On Sep 13, 2018 at 6:29 PM, mailto:larry.stew...@earthlink.net> > wrote:
Blown heads have been located at branc
: Thursday, September 13, 2018 5:35 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Sprinkler heads popping off randomly
A couple of thoughts:
- Any heat producing machinery, (shrink wrap station for example), skylight
or steam pipe in proximity to a sprinkler LINE?
- Is there a pressure
, September 13, 2018 5:34 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Sprinkler heads popping off randomly
Larry,
You need to hire a forensic fire protection engineer. Sample and evaluate a
few sprinklers in a forensic metallurgical lab accustomed and familiar with
fire sprinklers
A couple of thoughts:
- Any heat producing machinery, (shrink wrap station for example), skylight or
steam pipe in proximity to a sprinkler LINE?
- Is there a pressure relief device anywhere on the system? (My guess, you are
slowly building up system pressure in excess of head test pressure, I
Larry,
You need to hire a forensic fire protection engineer. Sample and evaluate a few
sprinklers in a forensic metallurgical lab accustomed and familiar with fire
sprinklers and also, put pressure recording devices on the system and
thermocouples with temperature recording devices at the roof
forum-boun...@lists.firesprinkler.org] On Behalf Of
> Matthew J Willis
> Sent: Thursday, September 13, 2018 3:01 PM
> To: sprinklerforum@lists.firesprinkler.org
> Subject: RE: Sprinkler heads popping off randomly
>
>
>
>
>
>
>
>
>
e link solder cracking
>>>
>>>
>>>
>>>
>>>
>>> Art Tiroly
>>>
>>> ATCO Fire Protection/Tiroly
>>>
>>> 24400 Highland Rd CLE 44143
>>>
>>> 216-621-8899
>>>
>>> 216-570-7030 cell
>>
gt; 24400 Highland Rd CLE 44143
>
> 216-621-8899
>
> 216-570-7030 cell
>
>
>
>
>
>
>
> *From:* Sprinklerforum [
> mailto:sprinklerforum-boun...@lists.firesprinkler.org
> ] *On Behalf Of *Tom
> Duross
> *Sent:* Thursday, September 13, 2018 5:43 PM
> *
570-7030 cell
>
>
>
> From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
> On Behalf Of Tom Duross
> Sent: Thursday, September 13, 2018 5:43 PM
> To: sprinklerforum@lists.firesprinkler.org
> Subject: RE: Sprinkler heads popping off randomly
>
> Pro
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Larry Block, Property Manager
Sent: Thursday, September 13, 2018 3:15 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: [EXTERNAL] RE: Sprinkler heads popping off randomly
HI John,
It has happened at
, September 13, 2018 3:01 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Sprinkler heads popping off randomly
Sounds like it could be a combination.
Maybe some solder creep from the temps, location of building if it is one a
dead end or circulating part of the main, lower water usage has
tember 13, 2018 3:05 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Sprinkler heads popping off randomly
Are the sprinklers that actuate all in one area? Any chance there was a
previous heat incident that damaged a group of sprinklers?
John Irwin
Quick Response Fire Protection
West Coa
this a possibility??
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of John Irwin
Sent: Thursday, September 13, 2018 3:05 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Sprinkler heads popping off randomly
Are the sprinklers that actuate all in
Are the sprinklers that actuate all in one area? Any chance there was a
previous heat incident that damaged a group of sprinklers?
John Irwin
Quick Response Fire Protection
West Coast Branch Manager
CELL 727-282-9243
Typed on tiny keys, just for you. Please forgive spelling errors, typographical
lf
Of Larry Block, Property Manager
Sent: Thursday, September 13, 2018 3:53 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Sprinkler heads popping off randomly
Thanks Tom. Not sure what heat rejection is. This is happening at night so the
roof will have already cooled significantly fr
Tom Duross
Sent: Thursday, September 13, 2018 5:43 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Sprinkler heads popping off randomly
Probably a buildup of pressure from heat rejection off the roof. Check system
gauges. A good pilot operated relief valve would open to relieve and
: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Tom Duross
Sent: Thursday, September 13, 2018 2:43 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Sprinkler heads popping off randomly
Probably a buildup of pressure from heat rejection off the roof. Check
Subject: Re: Sprinkler heads popping off randomly
Does it only happen in the summertime or hot days?
165 F sprinklers at the roof of a warehouse, this would normally require 200 F
sprinklers.
That would be my first guess but if it is only 1 sprinkler at a time, I just
don't know.
: Sprinkler heads popping off randomly
Does it only happen in the summertime or hot days?
165 F sprinklers at the roof of a warehouse, this would normally require 200 F
sprinklers.
That would be my first guess but if it is only 1 sprinkler at a time, I just
don't know.
On Thu, Sep 13, 2018
Does it only happen in the summertime or hot days?
165 F sprinklers at the roof of a warehouse, this would normally require
200 F sprinklers.
That would be my first guess but if it is only 1 sprinkler at a time, I
just don't know.
On Thu, Sep 13, 2018 at 4:20 PM Larry Block, Property Manager <
51 matches
Mail list logo