From: Prahl, Craig/GVL
Sent: Wednesday, January 26, 2022 3:32 PM
To: Steve Mackinnon ;
sprinklerforum@lists.firesprinkler.org
Cc: Art Tiroly
Subject: RE: question about Storage height
The liquid is a corrosive, non-issue from our perspective.
I would wager they don't have adequate secondary c
raig/GVL
> Sent: Wednesday, January 26, 2022 2:53 PM
> To: sprinklerforum@lists.firesprinkler.org
> Cc: Steve Mackinnon ; Art Tiroly <
> atir...@atcofirepro.com>
> Subject: RE: question about Storage height
>
> You don't have 5 ft of commodity. The liquid within the
rahl, Craig/GVL ;
sprinklerforum@lists.firesprinkler.org
Cc: Art Tiroly
Subject: [EXTERNAL] RE: question about Storage height
I'm not sure if attachments are allowed, if yes this is the situation...
I believe the liquid is classified as a low commodity, leaving the plastic
containers as the driving
day, January 26, 2022 1:46 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Steve Mackinnon ; Art Tiroly
Subject: [EXTERNAL] RE: question about Storage height
Thank you everyone who replied, it appears it's not as clear cut as one would
think lol.
The plastic tote below does have a solid top
forum@lists.firesprinkler.org
Cc: Steve Mackinnon ; Art Tiroly
Subject: [EXTERNAL] RE: question about Storage height
Thank you everyone who replied, it appears it's not as clear cut as one would
think lol.
The plastic tote below does have a solid top, but I would assume there would be
open
ainer.
-Kyle M
-Original Message-
From: Sprinklerforum On Behalf
Of Steve Mackinnon via Sprinklerforum
Sent: Wednesday, January 26, 2022 11:46 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Steve Mackinnon ; Art Tiroly
Subject: [EXTERNAL] RE: question about Storage height
Thank you everyone
m On Behalf
Of Art Tiroly via Sprinklerforum
Sent: Wednesday, January 26, 2022 1:35 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Art Tiroly
Subject: RE: question about Storage height
Is the spill container open top? That will be an issue. These sound like
plastic totes. If the liquid i
:32 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Scott Futrell ; Mike Hairfield
Subject: RE: question about Storage height
You didn't mention what the liquid is. If it is a hazardous material as
recognized by the International Fire Code then the 'empty' container is
still
;
Mike Hairfield
Subject: [EXTERNAL] RE: question about Storage height
It's a non flammable, non combustible liquid. Sodium hydroxide 10 N
The storage container and empty vessel are one time use only. There would be no
cleaning of containers for use again.
Hope this helps.
-Original Me
: [EXTERNAL] RE: question about Storage height
It's a non flammable, non combustible liquid. Sodium hydroxide 10 N
The storage container and empty vessel are one time use only. There would be no
cleaning of containers for use again.
Hope this helps.
-Original Message-
From: Sprinkler
l via Sprinklerforum
Sent: Wednesday, January 26, 2022 9:32 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Scott Futrell ; Mike Hairfield
Subject: RE: question about Storage height
You didn't mention what the liquid is. If it is a hazardous material as
recognized by the International Fire Cod
ssage-
From: Sprinklerforum On Behalf
Of Mike Hairfield via Sprinklerforum
Sent: Wednesday, January 26, 2022 8:08 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Mike Hairfield
Subject: Re: question about Storage height
It should be 10 feet even though the other container is empty it's s
It should be 10 feet even though the other container is empty it's still
plastic.
Mike
From: Sprinklerforum on behalf
of Steve Mackinnon via Sprinklerforum
Sent: Wednesday, January 26, 2022 9:02 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Steve Mackinno