Re: How to Know what is a Reasonable fire flow : Fire Hydrant fire water flow for a building

2019-06-13 Thread Salvatore Izzo
Not to refute Scot’s points which provide excellent insight, but be advised that the Needed Fire Flows in the IFC or NFPA 1 are generally less than those calculated by the Insurance Services Office (ISO) Needed Fire Flow Formula, which incorporates additional factors for the calculation. For a spec

Re: How to Know what is a Reasonable fire flow : Fire Hydrant fire water flow for a building

2019-06-13 Thread Bruce Verhei
We did not track maximum fire flow used in the fire ground. I informally interviewed pump operators on a few heavily involved fires, and calc’ed fire flow for same. I was shocked calc’s and flow approximated each other. I’ve always considered origin of flow tables to be lost in history, and akin

How to Know what is a Reasonable fire flow : Fire Hydrant fire water flow for a building

2019-06-13 Thread å . . . . . . .
Adel: In some situations, I concur that NFPA 1, Table 18.4.5.2.1 is excessive. This has been documented by Benfer and Scheffey[1]. I have compared fire flows from different countries for an 'industrial occupancy'. A large part of the comparison was completed by Benfer and Scheffey, who noted som

Re: fire hydrant

2019-05-20 Thread Ron Greenman
> 217.607.0325 > www.sprinkleracademy.com > ce...@sprinkleracademy.com > > OUR STUDENTS SAVE LIVES!! > > > -- > *From:* Sprinklerforum > on behalf of Easter, Tim (Contractor) > *Sent:* Monday, May 20, 2019 1:33 PM > *To:* sprinklerforum@lists.firesprinkler.org

Re: fire hydrant

2019-05-20 Thread Sprinkler Academy - C Bilbo
t; OUR STUDENTS SAVE LIVES!! From: Sprinklerforum on behalf of Easter, Tim (Contractor) Sent: Monday, May 20, 2019 1:33 PM To: sprinklerforum@lists.firesprinkler.org Subject: fire hydrant NFPA 24 7.2.3 Hydrants shall be located not less than 40ft from the buildings to be protected. This

Re: fire hydrant

2019-05-20 Thread Salvatore Izzo
its PPC grading. On Mon, May 20, 2019 at 2:47 PM Steele, Andrew wrote: > Ask the AHJ. If explosives, then other NFPA standards, more specific, are > likely to apply. > > > > If 40-ft stands, then it’s possible to consider that the fire hydrant > might be used for maintenanc

Re: fire hydrant

2019-05-20 Thread Parsley Consulting
t from the buildings to be protected. This seems awfully close if you have an explosive building. What is usual distance for a fire hydrant from an explosive building? The fire brigade does not fight fires here. Best, Timothy M. Easter

RE: fire hydrant

2019-05-20 Thread Steele, Andrew
Ask the AHJ. If explosives, then other NFPA standards, more specific, are likely to apply. If 40-ft stands, then it's possible to consider that the fire hydrant might be used for maintenance flushing/testing of the water service, and/or as a supply to a fire apparatus taking a pos

fire hydrant

2019-05-20 Thread Easter, Tim (Contractor)
NFPA 24 7.2.3 Hydrants shall be located not less than 40ft from the buildings to be protected. This seems awfully close if you have an explosive building. What is usual distance for a fire hydrant from an explosive building? The fire brigade does not fight fires here. Best, Timothy M

Re: Fire Hydrant Calculation Information

2010-10-19 Thread Ron Greenman
You answered your question when you talked about the incline ofd the curve. Send two guys or buy remote reading equipment so one guy can be in two places at once. Without mentioning products I'd like to say that one of my favorite children's books is famous Tales of MONSTERS and Trolls. On Tue, Oc

RE: Fire Hydrant Calculation Information

2010-10-19 Thread Andy
I have found a lot of the municipalities have been using just one hydrant flow test for determining the flow @ 20 PSI Some are just using the available flow for color coding caps rather than figuring it @ 20 psi. NFPA says color code @ 20 PSI if the curve is steep it can be a difference. If I do a

RE: Fire Hydrant Calculation Method

2010-10-19 Thread John Drucker
r.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of George Medina Jr Sent: Monday, October 18, 2010 10:02 PM To: sprinklerforum@firesprinkler.org Subject: Re: Fire Hydrant Calculation Method I am calcing for the system (private fire hydrant). I do not need a hose stream ( I was told to add the 1500

Re: Fire Hydrant Calculation Method

2010-10-18 Thread George Medina Jr
thod for calculating the actual flow through the fire hydrant? Just my opinion.' George Medina Jr. -Original Message- From: Ron Greenman To: sprinklerforum@firesprinkler.org Sent: Mon, Oct 18, 2010 10:41 pm Subject: Re: Fire Hydrant Calculation Method George, I was being harassed by

Re: Fire Hydrant Calculation Method

2010-10-18 Thread Ron Greenman
g for the system (private fire hydrant). I do not need a hose > stream ( I was told to add the 1500 as a hose stream allowance in the Hass > program [not by any Hass Rep's] to simulate 1500 gpm flowing to the hydrant) > > There is going to be a new private fire hydrant on private pr

Re: Fire Hydrant Calculation Method

2010-10-18 Thread Ron Greenman
I get 7645gpm @ 20psi at the hydrant tested. On Mon, Oct 18, 2010 at 7:01 PM, George Medina Jr wrote: > > I am calcing for the system (private fire hydrant). I do not need a hose > stream ( I was told to add the 1500 as a hose stream allowance in the Hass > program [not by any Hass Rep&#x

Re: Fire Hydrant Calculation Method

2010-10-18 Thread AKS-Gmail-IMAP
u can understand it two years from now at a glance without having to wonder how the heck it was done. Allan Seidel St. Louis. MO On Oct 18, 2010, at 9:01 PM, George Medina Jr wrote: I am calcing for the system (private fire hydrant). I do not need a hose stream ( I was told to add the 1500 as a

Re: Fire Hydrant Calculation Method

2010-10-18 Thread George Medina Jr
I am calcing for the system (private fire hydrant). I do not need a hose stream ( I was told to add the 1500 as a hose stream allowance in the Hass program [not by any Hass Rep's] to simulate 1500 gpm flowing to the hydrant) There is going to be a new private fire hydrant on private pro

Re: Fire Hydrant Calculation Method

2010-10-18 Thread Ron Greenman
e formula I was looking for, Thanks. > >  Now to change the subject slightly, I am about to calculate a fire hydrant > using the Hass program. The Inspector wants a minimum of 1500gpm at 20psi. > The hydrant is a Clow 4"x4"x2½" hydrant ( I was told to just enter the flo

Fire Hydrant Calculation Method

2010-10-18 Thread George Medina Jr
That is the formula I was looking for, Thanks. Now to change the subject slightly, I am about to calculate a fire hydrant using the Hass program. The Inspector wants a minimum of 1500gpm at 20psi. The hydrant is a Clow 4"x4"x2½" hydrant ( I was told to just enter the flow in th

RE: Fire Hydrant Calculation Information

2010-10-18 Thread Scott A. Futrell
@firesprinkler.org Subject: Re: Fire Hydrant Calculation Information On my email it wasn't clear that it should be to the power of 0.54 and not times 0.54. Just so everyone knows ... ^0.54 -- Trevor Spain Fire Pro Corporation On 10/18/2010 10:24 AM, Scott A. Futrell wrote: > Anothe

Re: Fire Hydrant Calculation Information

2010-10-18 Thread Trevor Spain
QR=Residual flow measured in test Scott -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of David de Vries Sent: Sunday, October 17, 2010 11:08 PM To: sprinklerforum@firesprinkler.org Subject: Re: Fi

RE: Fire Hydrant Calculation Information

2010-10-18 Thread Scott A. Futrell
unday, October 17, 2010 11:08 PM To: sprinklerforum@firesprinkler.org Subject: Re: Fire Hydrant Calculation Information George, you can look up NFPA 291 on NFPA's website and read all about it. If you don't have a copy, go to the Codes and Standards link at www.nfpa.org, then half wa

Re: Fire Hydrant Calculation Information

2010-10-18 Thread David de Vries
P.E., CSP Firetech Engineering Incorporated --- On Fri, 10/15/10, George Medina Jr wrote: From: George Medina Jr Subject: Fire Hydrant Calculation Information To: sprinklerforum@firesprinkler.org Date: Friday, October 15, 2010, 6:39 PM Forum, What is the formula to find Hydrant flows a

Re: Fire Hydrant Calculation Information

2010-10-18 Thread Trevor Spain
George, Given the hydrant flow test information, flow at any pressure may be calculated as follows: 1. calculate and save K = (static - residual) / (measure flow^1.85) 2. Now calculate flow at any pressure "p": flow = [ (static - p) / K ]^(1/1.85) The flow test information should already

Re: Fire Hydrant Calculation Information

2010-10-18 Thread George Medina Jr
Thanks guys. George Medina Jr. -Original Message- From: George Medina Jr To: sprinklerforum@firesprinkler.org Sent: Fri, Oct 15, 2010 4:39 pm Subject: Fire Hydrant Calculation Information orum, What is the formula to find Hydrant flows at 20 psi? ( Was that said correctly

Re: Fire Hydrant Calculation Information

2010-10-15 Thread Ron Greenman
George, On Fri, Oct 15, 2010 at 4:39 PM, George Medina Jr wrote: > > Forum, > > What is the formula to find Hydrant flows at 20 psi? ( Was that said > correctly) > I used to have the formula set up in an excel spread sheet but lost it during > file transfer from old computer to new computer.

Fire Hydrant Calculation Information

2010-10-15 Thread George Medina Jr
Forum, What is the formula to find Hydrant flows at 20 psi? ( Was that said correctly) I used to have the formula set up in an excel spread sheet but lost it during file transfer from old computer to new computer. I also remember having a spreadsheet containing coefficients for the three types

Re: fire hydrant repair

2010-06-11 Thread cherokeefire...@aol.com
Question for those that work with fire hydrants : What is the average time spent in the field on a job repairing hydrants from a collission? Just an average of labor hours, Thanks Forest Wilson Cherokee Fire Sent from my Verizon Wireless Phone - Reply message - From: "Steve Leyton

[Sprinklerforum] Fire Hydrant Flow Test

2009-08-25 Thread Gregg Fontes
Regarding my first posting, when flowing the 4 1/2" outlet, per NFPA 291, you do adjust the coefficient per Table 4.8.2. As an example, if out of the 4 1/2" outlet the pitot reading is 19 psi (hydrant outlet coef. Of .9 per Figure 4.7.1) you would adjust the .9 coef. by .83 to get the coefficient

Re: [Sprinklerforum] Fire Hydrant Flow Test

2009-08-25 Thread Johnson, Duane (NIH/OD/ORS) [C]
@firesprinkler.org Subject: [Sprinklerforum] Fire Hydrant Flow Test When flowing a 4" or 4 1/2" outlet on a fire hydrant, is there a multiple coefficient that needs to be applied or do you use the same coefficient used for a 2 1/2" outlet? Thanks, Gregg Fontes Cen-Cal Fire Systems

[Sprinklerforum] Fire Hydrant Flow Test

2009-08-25 Thread Gregg Fontes
When flowing a 4" or 4 1/2" outlet on a fire hydrant, is there a multiple coefficient that needs to be applied or do you use the same coefficient used for a 2 1/2" outlet? Thanks, Gregg Fontes Cen-Cal Fire Systems, Inc

Re: Fire Hydrant & Sprinkler System Water Supply

2009-06-03 Thread Stewart Kidd
l in Paris (?). I always specify them and quite often they are deleted by developers and architects when the local FD says they don't want them. Regards Stewart On 2 Jun 2009, at 21:50, Reza Esmaeili wrote: > Hi All, > I would appreciate if someone explain for me Fire Hydrant &

RE: Fire Hydrant & Sprinkler System Water Supply

2009-06-02 Thread Steve Leyton
From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Reza Esmaeili Sent: Tuesday, June 02, 2009 1:51 PM To: sprinklerforum@firesprinkler.org Subject: Fire Hydrant & Sprinkler System Water Supply Hi All, I would appreciate if someone explai

RE: Fire Hydrant & Sprinkler System Water Supply

2009-06-02 Thread Chris Cahill
3:51 PM To: sprinklerforum@firesprinkler.org Subject: Fire Hydrant & Sprinkler System Water Supply Hi All, I would appreciate if someone explain for me Fire Hydrant & Sprinkler System Water Supply. I know that hydrants are for delivering water for professional fire fighting for fire depar

Fire Hydrant & Sprinkler System Water Supply

2009-06-02 Thread Reza Esmaeili
Hi All, I would appreciate if someone explain for me Fire Hydrant & Sprinkler System Water Supply. I know that hydrants are for delivering water for professional fire fighting for fire department at 20 psi residual pressure. Can fire hydrants installed in same main as the Fire sprinklers? If

RE: Fire Hydrant Butts

2009-01-29 Thread George Church
bastard hose thread. glc -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Russell Sent: Wednesday, January 28, 2009 3:49 PM To: sprinklerforum@firesprinkler.org Subject: RE: Fire Hydrant Butts I had

Re: Fire Hydrant Butts

2009-01-28 Thread Daniel Merkle
tection Systems Inc. 937 Linden Ave. W. E. Rochester, N.Y. 14445 Office-(585) 381-7362 Fax-(585) 381-8263 E-mail - dlmcolon...@yahoo.com From: Paul Johnson To: sprinklerforum@firesprinkler.org Sent: Wednesday, January 28, 2009 3:25:09 PM Subject: Re: Fire Hyd

RE: Fire Hydrant Butts

2009-01-28 Thread Russell
I had contacted the city's fire department chief (all volunteer fire department) when I noticed something wasn't right and he says they are all 2-1/2". What he didn't tell me is that they are all 2-1/2" NPT thread and not hose thread. I guess I had hose thread mentality at the time and not imaginin

Re: Fire Hydrant Butts

2009-01-28 Thread Paul Johnson
How are things? Mobile message from Paul Johnson Bardane, Inc. 407-399-5081 - Wireless -Original Message- From: Daniel Merkle Date: Wed, 28 Jan 2009 12:25:01 To: Subject: Re: Fire Hydrant Butts You could check with the local fire dept. and see what they use or if they have

Re: Fire Hydrant Butts

2009-01-28 Thread Daniel Merkle
You could check with the local fire dept. and see what they use or if they have something you could borrow. Daniel L. Merkle, CET From: Russell To: sprinklerforum@firesprinkler.org Sent: Wednesday, January 28, 2009 3:11:07 PM Subject: RE: Fire Hydrant

RE: Fire Hydrant Butts

2009-01-28 Thread Russell
I measured the inside diameter and it was 2" (not that that means it's officially deemed a 2" butt). This hydrant isn't in Valdosta but in a south Georgia town smaller than Valdosta (if that's possible). This hydrant appears to be very old and only has the two small butts which are at an angle to o

Re: Fire Hydrant Butts

2009-01-28 Thread Todd Williams
You can probably get adapters. But be sure to check the thread type. At 02:38 PM 1/28/2009, you wrote: Anyone ever seen a fire hydrant with 2" hose butts rather than the most common 2-1/2"? I need a cap in order to perform a flow test. Russell Rewis Brown Automatic Sprin

RE: Fire Hydrant Butts

2009-01-28 Thread Thom McMahon
x: 970-879-7926 -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Russell Sent: Wednesday, January 28, 2009 12:38 PM To: AFSA Subject: Fire Hydrant Butts Anyone ever seen a fire hydrant with 2" hose butts

RE: Fire Hydrant Butts

2009-01-28 Thread Eckard, Mark
Fax: 704-391-2709 Cell: 828-851-0080 ecka...@cintas.com -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Russell Sent: Wednesday, January 28, 2009 2:38 PM To: AFSA Subject: Fire Hydrant Butts Anyone ever s

Fire Hydrant Butts

2009-01-28 Thread Russell
Anyone ever seen a fire hydrant with 2" hose butts rather than the most common 2-1/2"? I need a cap in order to perform a flow test. Russell Rewis Brown Automatic Sprinklers, Inc. 107C Hemlock Street Valdosta, Georgia 31601 229-244-8130 russ...@brownaut

Re: Fire hydrant hydraulics

2008-08-25 Thread Ron
in, other than that just go to the manufacturing company & they will get you what you need. - Original Message - From: "Steve Leyton" <[EMAIL PROTECTED]> To: Sent: Monday, August 25, 2008 10:16 AM Subject: Fire hydrant hydraulics Does anyone have or know of a referen

Fire hydrant hydraulics

2008-08-25 Thread Steve Leyton
Does anyone have or know of a reference for the actual head loss through fire hydrants? The civil engineering community is apparently now so diluted here in SoCal that we're being asked more and more to furnish fire flow data AND calculations. Steve Leyton PROTECTION DESIGN & CONSULTING 884

Re: Fire hydrant testing

2008-03-25 Thread Gregg Key
sprinklerforum@firesprinkler.org Subject: Fire hydrant testing Greetings, I was asked an interesting question this morning by the local fire marshal, so I thought I would pass it along to get your feedback. What should be the minimum qualifications needed to be allowed to test a fire hydrant

RE: Fire hydrant testing

2008-03-25 Thread Joe Powell
Sent: Tuesday, March 25, 2008 10:58 AM To: sprinklerforum@firesprinkler.org Subject: Fire hydrant testing Greetings, I was asked an interesting question this morning by the local fire marshal, so I thought I would pass it along to get your feedback. What should be the minimum qualifications n

RE: Fire hydrant testing

2008-03-25 Thread Steve Leyton
Williams - FPDC Sent: Tuesday, March 25, 2008 9:22 AM To: sprinklerforum@firesprinkler.org Subject: Re: Fire hydrant testing What does the licensing board have to say? At 11:57 AM 3/25/2008, you wrote: >Greetings, I was asked an interesting question this morning by the >local fire marsh

RE: Fire hydrant testing

2008-03-25 Thread Matthew J. Willis
0-937-1852 Facsimile [EMAIL PROTECTED] - >-Original Message- - >From: [EMAIL PROTECTED] - >[mailto:[EMAIL PROTECTED] On - >Behalf Of Gregg Key - >Sent: Tuesday, March 25, 2008 10:58 AM - >To: sprinklerforum@firesprinkler.org - &g

RE: Fire hydrant testing

2008-03-25 Thread Tom Duross
as asked an interesting question this morning by the >local fire marshal, so I thought I would pass it along to get your feedback. > >What should be the minimum qualifications needed to be allowed to >test a fire hydrant per NFPA 25 or 291 requirements? > >Due to a local fire w

Re: Fire hydrant testing

2008-03-25 Thread Todd Williams - FPDC
test a fire hydrant per NFPA 25 or 291 requirements? Due to a local fire where the hydrant failed to work, the local Fire Department is now enforcing the requirement that they be tested every year. Problem is that plumbers and fire equipment guys are jumping in and testing them as well as the

Fire hydrant testing

2008-03-25 Thread Gregg Key
Greetings, I was asked an interesting question this morning by the local fire marshal, so I thought I would pass it along to get your feedback. What should be the minimum qualifications needed to be allowed to test a fire hydrant per NFPA 25 or 291 requirements? Due to a local fire where

RE: Fire Hydrant and Pump Testing

2007-10-23 Thread Bobby McCullough
lto:[EMAIL PROTECTED] On Behalf Of Matthew J. Willis Sent: Tuesday, October 23, 2007 9:44 AM To: sprinklerforum@firesprinkler.org Subject: RE: Fire Hydrant and Pump Testing Bobby, I went thru that some time back. Almost a bad case dealing with a theater. Only thing I can suggest is if you still ha

RE: Fire Hydrant and Pump Testing

2007-10-23 Thread Matthew J. Willis
- >Bob, Heres a copy of NJ's water restrictions back in - >2002. Hope this helps. - > - >John Drucker - >Fire Protection Subcode Official - > - > - > I, Bradley M. Campbell, Commissioner of the New Jersey - >Department of Environment John, thanks for confirm

Re: Fire Hydrant and Pump Testing

2007-10-23 Thread Todd Williams - FPDC
I was wondering how you guys were making out down there. When I can't get hydrant test due to a water emergency and have to work with old data, I leave a bigger gap. If there is no data and I need something, I have been known to do a "Captain Midnight" water test. Also, if it is a LH occupanc

RE: Fire Hydrant and Pump Testing

2007-10-23 Thread John Drucker
[mailto:[EMAIL PROTECTED] On Behalf Of Bobby McCullough Sent: Tuesday, October 23, 2007 6:51 AM To: SprinklerFORUM@firesprinkler.org Subject: Fire Hydrant and Pump Testing Can any of you share your experience with drought conditions? A city near metro Atlanta sent this message and the fir

Fire Hydrant and Pump Testing

2007-10-23 Thread Bobby McCullough
Can any of you share your experience with drought conditions? A city near metro Atlanta sent this message and the fire marshal wants to know how others might handle this. Bobby McCullough Atlanta Sprinkler Inspection The email from the fire marshal: Please inform your management companies that