Area of Reduction 11.2.3

2008-05-20 Thread Bobby Gillett
We have a 4 story building with mercantile on the 1st floor and residential living on the top 3 floors (Light Hazard). This is wood construction and we have to put sprinklers in between the ceiling and floor space. Can the area of reduction be taken in the remote area for the sprinklers between

RE: Area of Reduction 11.2.3

2008-05-20 Thread Matthew J. Willis
Yes as far as I see. As long as all conditions are met, there are no other restrictions mentioned. R/ Matt Matthew J. Willis Living Water Fire Protection, LLC. 1160 McKenzie Rd. PO Box 877 Cantonment, FL. 32533 850-937-1850 Voice 850-937-1852 Facsimile [EMAIL PROTECTED] - -Original

RE: unified facilities criteria question

2008-05-20 Thread bill . brooks
In my opinion, the small room rule can be used. I believe the 225 sq ft and 130 sq ft limits are there to restrict the use of special sprinklers, not to limit the use of other NFPA 13 spacing rules. Bill Brooks William N. Brooks, P.E. Brooks Fire Protection Engineering Inc. 372 Wilett Drive

RE: unified facilities criteria question

2008-05-20 Thread Vince Sabolik
Ed -- I wasn't able to use small room at a USMC facility recently, in fact they required a base of 3.000 sf for a wet system. You are however allowed to discount for use of QR heads applied to that 3,000 sf. You can look this up in Table 4-1 in the Unified Facilities Criteria Fire

RE: Area of Reduction 11.2.3

2008-05-20 Thread Ray Vance
Bobby, If the area in the floor/ceiling space is a horizontal combustible conceled space 36 of less in height (and I presume they are), you must use a LISTED sprinkler for this space and abide by all requirements of the sprinkler's listings, including appropriate compartmentalization. If the

RE: Area of Reduction 11.2.3

2008-05-20 Thread Steve Leyton
Not necessarily - remember his question is predicated by the application of the DOD standards, not NFPA 13. The UFC's supersede those listings in many cases and I would check with the AHJ in any case; we have had the concealed space sprinklers shot down by NAVFAC in the past. Unfortunately, a

RE: Area of Reduction 11.2.3

2008-05-20 Thread Chris Cahill
I assume you are talking about '02-8.14.1.6. The other issue is the members are capable of trapping heat. The annex section says more than 2 top cord. Around here these are usually (but not always) 2x materials on the flat and thus wouldn't trap heat by the criteria and thus no listed sprinklers

RE: Area of Reduction 11.2.3

2008-05-20 Thread Cliff Whitfield
Steve, I think you are cross-threading here. There are 2 different questions going on this morning on the forum. But you do make some very good points! Cliff Whitfield, SET Fire Design, Inc .-Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Steve Leyton

Re: unified facilities criteria question

2008-05-20 Thread [EMAIL PROTECTED]
Ed, No, it doesn't rule out the small room rule specifically, because under the provisions of NFPA-13, 07, 8.6.3.2.4, the spacing of sprinklers in such small rooms can be up to 9'-0 off of any one wall, but cannot exceed the maximum spacing limitations in table 8.6.2.2.1(a), which is either

RE: Area of Reduction 11.2.3

2008-05-20 Thread Steve Leyton
Heh, heh, heh. More coffee please. Steve Leyton Protection Design Consulting -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Cliff Whitfield Sent: Tuesday, May 20, 2008 8:34 AM To: sprinklerforum@firesprinkler.org Subject: RE: Area of Reduction 11.2.3

Trapeze lengths beyond 10'-0

2008-05-20 Thread Randy Knutson
Forumites, I searched the archives and didn't find a discussion on this topic. Here's my question? Can I extrapolate out beyond the 10'-0 length on the section modulus required for trapeze in table 9.1.1.6.1(a) '07ed.? A fitter called this morning wanting 14' trapeze hangers for 4

RE: Trapeze lengths beyond 10'-0

2008-05-20 Thread Matthew J. Willis
Can you apply the formula and get an equivalent modulus based on not center loading the members? R/ Matt Matthew J. Willis Living Water Fire Protection, LLC. 1160 McKenzie Rd. PO Box 877 Cantonment, FL. 32533 850-937-1850 Voice 850-937-1852 Facsimile [EMAIL PROTECTED] - -Original

RE: Trapeze lengths beyond 10'-0

2008-05-20 Thread Ray Vance
As for a definitive answer to this question, I can not provide. What I can provide is this... there is no direction in the NFPA standard (that I can find) on how to determine a section modulus for spans over 10ft. However... (1) Adding the 4ft span modulus to the 10ft span modulus does seem to

Re: Trapeze lengths beyond 10'-0

2008-05-20 Thread Todd Williams - FPDC
Can you extrapolate from the table, I wouldn't. Can you calculate the required section modulus for a 14 ft trapeze span, yes. Would you want someone whose name ends in PE to sign off on it, definitely. . At 12:04 PM 5/20/2008, you wrote: Forumites, I searched the archives and didn't find

Re: Trapeze lengths beyond 10'-0

2008-05-20 Thread [EMAIL PROTECTED]
Randy, I'm not sure I agree with a couple of the responses you've received, so I'll weigh in with my own. The values shown in Table 9.1.1.6.1(b) in the '02 edition of NFPA-13 are based on the required section modulus for a load created by 15'-0 of pipe filled with water, plus 250 pounds,

Re: Trapeze lengths beyond 10'-0

2008-05-20 Thread Todd Williams - FPDC
Ken, Something drove me a little crazy because you units weren't working out. The 17,921.4 in-lbs translates to 17.921 in-kips (1 kip = 1000 lbs, for those who have not run into it before, and even for those who have). When you divide that by the bending stress of 15 ksi, the units now work

RE: unified facilities criteria question

2008-05-20 Thread Thom McMahon
We just finished a layout for NAVFAC PACDIV, for a 2 story dorm. Poured concrete construction, full height concrete walls, floors and roof, every 24'-0 with only 30'-0 front to back.(5200 Sf per floor total) UFC say's you can use 13R, NAVFAC say's NO. UFC say's reduced area for QR heads, NAVFAC

Re: Trapeze lengths beyond 10'-0

2008-05-20 Thread [EMAIL PROTECTED]
Todd, You're right, the proper unit of measure should have been in-kips when using 17.921. I wasn't keeping the units straight, and that can give very odd results. I saw the equation a little differently than the one you quoted, but only because the structural who taught me all this stuff

RE: unified facilities criteria question

2008-05-20 Thread bill . brooks
What are the NAVFAC references for no use of 13R and no area reduction for QR heads? Bill Brooks William N. Brooks, P.E. Brooks Fire Protection Engineering Inc. 372 Wilett Drive Severna Park, MD 21146 410-544-3620 Phone 410-544-3032 FAX 412-400-6528 Cell Original Message