Re: Testing of existing systems (solution!)

2020-08-19 Thread John Irwin via Sprinklerforum
Cecil, I received several responses outside the user group and that section was pointed out to me. And it was noted in my response to the AHJ. Thank you John Irwin West Coast Branch Manager Quick Response Fire Protection 727-282-9243 Typed on tiny keys, just for you. Please forgive spelling

Re: Testing of existing systems (solution!)

2020-08-19 Thread Sprinkler Academy - C Bilbo via Sprinklerforum
John, I am very surprised that no one has pointed you to our newest changes to the testing of modifications on existing systems. Take a look at the newly numbered Chapter 29. The Committee debated this for a long time. The argument that won the day came from AFSA's rep (and former AFSA

Re: [EXTERNAL] Re: Testing of existing systems

2020-08-19 Thread BRUCE VERHEI via Sprinklerforum
Ron’s proposal is appropriate if AHJ driving hydro is other than a fire marshal’s office. If you’ve bought a 1970 building, there are no current tenants with property to damage, assuring current condition might be a good idea. Unless single new taps are supplying the code minimum number of

Re: [EXTERNAL] Re: Testing of existing systems

2020-08-19 Thread Ron Greenman via Sprinklerforum
Craig brings up an interesting thought. Perhaps a requirement to do a hydro before a job of this magnitude is embarked upon would shift the onus from contractor to owner, it then being HIS responsibility to correct HIS existing system before the contractor modifies it. The likelihood of a leak on

RE: [EXTERNAL] Re: Testing of existing systems

2020-08-19 Thread Prahl, Craig/GVL via Sprinklerforum
Exactly. That statement should be made in your bid under Exceptions and Clarifications. No responsibility or liability related to leaks in existing systems if 200 psi pressure test is required. Craig Prahl | Jacobs | Group Lead/SME - Fire Protection | 864.676.5252 | craig.pr...@jacobs.com |

Re: Testing of existing systems

2020-08-19 Thread Jeremy Van Ness via Sprinklerforum
Have the customer sign off saying if any pipe from the old system leaks, they are responsible to cover the cost of any damage that might occur. We come across this issue quite often. On Wed, Aug 19, 2020, 12:13 PM Ken Wagoner via Sprinklerforum < sprinklerforum@lists.firesprinkler.org> wrote: >

RE: [EXTERNAL] Re: Testing of existing systems

2020-08-19 Thread Richard Carr via Sprinklerforum
Did you ask if they would accept an air test? Richard M. Carr, SET Project Manager/Design Diboco Fire Sprinklers, Inc. 325 Jackson Loop Road Flat Rock, NC  28731 rich...@diboco.com 828-696-3400 828-696-2288 Fax 828-708-9118 Mobile -Original Message- From: Sprinklerforum On Behalf Of

RE: [EXTERNAL] Re: Testing of existing systems

2020-08-19 Thread Prahl, Craig/GVL via Sprinklerforum
Sometimes it's not about how good of a job your fitters did but the unknown age and condition of the existing system piping you're tying into. There are times when a 200 psi test is all it takes to open up pinholes and create leaks. Now the owner looks at you as being responsible and you're

Re: Testing of existing systems

2020-08-19 Thread Bobby via Sprinklerforum
I would think 25.2.1.4., 25.2.1.4.1 and 25.2.1.4.2 of NFPA 13 - 2016 would apply. Bobby Gillett Seago Fire Protection, LLC 850-836-2288 Office 850-217-3899 cell 850-836-2277 fax From: Sprinklerforum on behalf of Ken Wagoner via Sprinklerforum Sent:

RE: Testing of existing systems

2020-08-19 Thread Matthew J Willis via Sprinklerforum
Agreed. Book is clear. If you cannot isolate, then it is 2 hours at city pressure. Unless they have amended locally. You will probably need to push this one back or get legal documents out the wazoo.. I wouldn't 200 pound the existing. R/ Matt -Original Message- From: Sprinklerforum

Re: Testing of existing systems

2020-08-19 Thread Ken Wagoner via Sprinklerforum
I respectfully disagree, Jim. While I'm confident that John's installers are competent and will do a good job, I have to observe that unless John's company did the original install, they're putting their liability at serious risk for work which they have no control over. It all comes down

RE: Testing of existing systems

2020-08-19 Thread John Irwin via Sprinklerforum
I could not disagree with you more. And I am certain my insurance agent would side with me. I am not the least bit worried about my little pieces of 1” sched 40 and cast iron fittings letting go. I am not so certain about the 20 year old 4” main running over the top of a newly upgraded

Re: Testing of existing systems

2020-08-19 Thread tfscolorado via Sprinklerforum
John, you have probably spent more time and effort fighting this issue versus just doing a test.  200 add and relocates is a lot and I would think you should put a test on it even if it is not code required (which I believe it is) for your benefit and warranty.  If your guys did a good job, a

Re: Testing of existing systems

2020-08-19 Thread John Irwin via Sprinklerforum
I included this reference in my response. From 4 different editions of 13. As well as a half dozen informal interpretations from AFSA and explanatory comments from the handbook. John Irwin West Coast Branch Manager Quick Response Fire Protection 727-282-9243 Typed on tiny keys, just for you.

RE: Testing of existing systems

2020-08-19 Thread Mark Phillips via Sprinklerforum
I would be arguing the point of 25.2.1.4.2 of NFPA 13 2016 How are you isolating relocated drops? Mark Phillips Branch Manager Fire Sprinkler Design, Install, Inspections Service, Backflows, Fire Alarm Inspections 832-101 Purser Drive Raleigh NC 27603 Phone: 919-779-4010 Fax    :