The NFPA 13 technical committee has addressed partial height walls in
ordinary hazard occupancies in the NFPA 13, 2022 edition. Section
10.2.7.3.2.3 and 10.2.7.3.2.4 address partial height walls 12 in. or less
in width. If a sprinkler is installed within 6 in. of the centerline of
the partial
I would think you have to space to the walls or have the walls stop 18"
below the ceiling which it appears it does. The obstructions change for
things below 18" and the chart stops at 18" as well.
Best regards,
*Joe Burtell, SET, CFPS*
[image: Burtell Fire_Small]
Phone | Fax | Mobile| Text
Apologies. I meant to note that theses were originally my comments. bv
> On 09/14/2021 2:27 PM BRUCE VERHEI via Sprinklerforum
> wrote:
>
>
> This is cut and past of partial comments from discussion on another forum,
> originating from an NFSA post.
>
> What is missing from this excerpt is
This is cut and past of partial comments from discussion on another forum,
originating from an NFSA post.
What is missing from this excerpt is pressure rating of the hose. At acceptance
and annually FD’s test hose at 250 psi. You are quickly going to lose
persuasion ability with your fire plan
I am working on the renovation of an upscale bridal store where there a
several partial height walls being installed. The spaces created by the walls
are semi-private consulting areas. The top of the walls is 1’-10” below the
ceiling. The existing concealed sprinklers are spaced at
This is the answer I was looking for. We will contact the city for their
pumping ability.
Thank you
John Irwin
Branch Manager - Florida West Coast
Quick Response Fire Protection
Cell: 727-282-9243
"The bitterness of poor quality remains long after the sweetness of low price
is forgotten." -
By my reckoning, you need about 300 PSI at the ground level to pump 100 PSI to
the roof of what I'll call a 385' tall standpipe system (35x11). Bottom line:
Can the responding FD pump 750 or 1,000 GPM at 300 psi? Most muni
departments can, but that might be at the limit of what they can
It might also depend on the pumping ability of the fire department? How much
pump can they drive up with?
Matt
-Original Message-
From: Sprinklerforum On Behalf
Of Spencer Tomlinson via Sprinklerforum
Sent: Tuesday, September 14, 2021 11:16 AM
To:
Might come from the requirements of IFC Section 914, etcpending height.
Just another place to look anyway.
Spencer Tomlinson, PE
Owner, Fire Protection Engineer
Ph: 316-202-6412
Fax: 316-202-2346
Cell: 620-955-7293
-Original Message-
From: Sprinklerforum On Behalf
Of John
Starting design on a 35 story residential tower. Engineers plans show two
identical fire pumps. Client wants to know if we need two fire pumps. I want to
answer him with the code reference below, but experience has taught me that it
may not be as simple as this ... Am I missing something or